  #1   Report Post  
Yi Jin
 
Posts: n/a
Default Use pigtails on receptacle


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.
  #2   Report Post  
indago
 
Posts: n/a
Default Use pigtails on receptacle

040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.


It would be beneficial to wire nut the circuit wires together with a pigtail
of 14 guage wire to the outlet.

  #3   Report Post  
DanG
 
Posts: n/a
Default Use pigtails on receptacle

What you are proposing is the preferred way of wiring an
intermediate recep.

I do hope you have the deep rough-in boxes to allow more room for
wire, wire nuts, pigtails.

^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Keep the whole world singing. . . .
DanG


"Yi Jin" wrote in message
...

I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.



  #4   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default Use pigtails on receptacle


"indago" wrote in message
...
040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.


It would be beneficial to wire nut the circuit wires together with a

pigtail
of 14 guage wire to the outlet.


14 ga is insufficient for use on a 20A feeder, use 12 ga instead.

--

SVL



  #5   Report Post  
Yi Jin
 
Posts: n/a
Default Use pigtails on receptacle

Thank you.

As I understand, as long as I have space to put those two extra pigtails
and wire two wire nuts in, I am OK with the box. The pigtails and wire
nuts don't reduce the number of allowable wires printed on the box,
correct?

Y.

In article WxZyc.7723$wS2.737@okepread03, DanG wrote:
What you are proposing is the preferred way of wiring an
intermediate recep.

I do hope you have the deep rough-in boxes to allow more room for
wire, wire nuts, pigtails.

^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Keep the whole world singing. . . .
DanG


"Yi Jin" wrote in message
...

I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.







  #7   Report Post  
bill allemann
 
Posts: n/a
Default Use pigtails on receptacle

It is OK to use 14ga at the end of 20A run, like in this example.
Also, using separate posts on a strap to create a circuit passthrough is
prohibited in most codes. The "pigtail" as described by the original
poster is the correct method.

Bill

"PrecisionMachinisT" wrote in message
...

"indago" wrote in message
...
040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.


It would be beneficial to wire nut the circuit wires together with a

pigtail
of 14 guage wire to the outlet.


14 ga is insufficient for use on a 20A feeder, use 12 ga instead.

--

SVL




  #8   Report Post  
zxcvbob
 
Posts: n/a
Default Use pigtails on receptacle

Yi Jin wrote:

I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.



Yes you can do that, although the box gets kind of crowded with the
pigtails if the box is only marginally big enough to start with. You
*could* even use stranded wire for the pigtails if the outlets will take
stranded wires or if you crimp terminals on the ends.

You also might look for heavy-duty back-wired outlets. I'm not talking
about the cheap ones that have a stab-lok connector for a #14 wire, but
commercial-grade outlets with wire clamps in the back that will take #12
(or even #10) wires. They're not that expensive -- maybe $1 more than
the cheap ones -- and they are easy to wire. Just strip the wires, put
them in the holes, and tighten the screws on the sides.

Best regards,
Bob
  #9   Report Post  
PrecisionMachinisT
 
Posts: n/a
Default Use pigtails on receptacle


"bill allemann" wrote in message
. ..
"PrecisionMachinisT" wrote in message
...

"indago" wrote in message
...
040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.

It would be beneficial to wire nut the circuit wires together with a

pigtail
of 14 guage wire to the outlet.


14 ga is insufficient for use on a 20A feeder, use 12 ga instead.

It is OK to use 14ga at the end of 20A run, like in this example.
Also, using separate posts on a strap to create a circuit passthrough is
prohibited in most codes. The "pigtail" as described by the original
poster is the correct method.


You would need to show me the pertinent code in order to convince me of
this, and still it would be unlikely I would do it myself anyways.

Fairly recent, but at least in our area, outlets must be of the heavy duty
( 20amp ) if a 20 A breaker is used to feed the line--the more common
outlets are only rated for 15 amps--and they no longer even accept #12 wire
into the pushlock terminals.

--

SVL



  #10   Report Post  
Jake
 
Posts: n/a
Default Use pigtails on receptacle


"bill allemann" wrote in message
. ..
It is OK to use 14ga at the end of 20A run, like in this example.
Also, using separate posts on a strap to create a circuit passthrough is
prohibited in most codes. The "pigtail" as described by the original
poster is the correct method.

Bill


It is NOT OK to use down-sized conductors ANYWHERE in a residential branch
circuit without a overcurrent device suitable to protect the smaller wire.

It IS OK to use a strap on the receptacle, PROVIDED that device has the same
rating or higher than the overcurrent device.

I think, from memory (so don't ding me if it isn't exact) the relevant NEC
articles are 210-21 (Outlet Devices) and 210-19 (Branch Circuit Conductors).

Having said those two things, here's what I recommend:

If you want to use pigtails, that's OK so long as you've got permissible
room in the box and you use the same size wire. I would buy the commercial
grade 20 amp recepts. and use the screw-down clamps that a previous poster
suggested.

In commercial buildings, and retrofits it is common to use pigtails so that
we can replace outlets hot without disrupting the neutral, and to sometimes
meet NEC requirements for conductor lengths inside the box... but these
systems have conduit and stranded wire instead of the stuff you're working
with here.

Jake





  #11   Report Post  
HorneTD
 
Posts: n/a
Default Use pigtails on receptacle

bill allemann wrote:
It is OK to use 14ga at the end of 20A run, like in this example.
Also, using separate posts on a strap to create a circuit passthrough is
prohibited in most codes. The "pigtail" as described by the original
poster is the correct method.

Bill

"PrecisionMachinisT" wrote in message
...

"indago" wrote in message
...

040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.

It would be beneficial to wire nut the circuit wires together with a


pigtail

of 14 guage wire to the outlet.


14 ga is insufficient for use on a 20A feeder, use 12 ga instead.

--

SVL






Can you back up yor asertion with a code section that applies? What
makes you think it is OK to downsize the conductor below that which the
code requires for twenty ampere overcurrent protection?
--
Tom H

  #12   Report Post  
HorneTD
 
Posts: n/a
Default Use pigtails on receptacle

indago wrote:

040613 0947 - Yi Jin posted:


I am wiring a 20amp circuit. The #12 seems pretty hard to
deal inside the electral box for the with the receptacle.

I notice all the books demonstrates that incoming wires
and outgoing ones connect to the seperate screws on the
receptacle. Is there any reason not to use a pigtail
and connect to the receptacle first, then connect it
together in/out wires with a wire nut, just like what
is done to a ground wires? That would be much easier
than to bend those short and hard #12 wires and try to
screw on those 4 hot/neutral wires?

I am talking about the middle of the run, non-split
receptacle.

Thanks.

Y.



It would be beneficial to wire nut the circuit wires together with a pigtail
of 14 guage wire to the outlet.


If you pigtail fifteen ampere wire to a duplex fifteen ampere receptacle
then you can draw more current through the two receptacles than the
pigtails can safely carry without opening the Over Current Protective
Device (OCPD).

There are some instances were a conductor ampacity that is less than the
circuits OCPD rating can be connected to a circuit but those exceptions
all involve conductors that terminate at overload protection or serve
fixed amperage loads. None of that applies to the conductors serving
general use receptacles.
--
Tom H
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shallow Receptacle For Under Cabinet LIghting Michael Roback Home Repair 3 May 1st 04 03:48 PM
Doulble Receptacle Grounding Question/ Switch Grounding Michael Roback Home Repair 1 September 7th 03 07:37 AM


All times are GMT +1. The time now is 03:09 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"