Volts500, Mark and Sue,
Thanks to your help and the help of others I now feel I know enough to keep the electrician honest. I've got the soars book on order and I plan to do some of the grunt work myself. I honestly didn't realize this thread would get so involved. It's very kind of you to help out while keeping the focus on my safety. To ease my guilt at having imposed on so much of your time, I can only hope others will get some use out of it as well. Keeping everything in mind, I'm going to follow Volt's advice for all the grounding. I'm also going to replace the Service Disconnect (as Mark suggested), and rewire the panelboard. Now, this opens up a few more questions. If I had any shame, I would feel too guilty to ask any more, but I guess I'm a bit shameless. If you guys would start giving crappy and vague advice, you really would avoid people like me buggying you so much. ![]() Volts: It appears that the metal housing of the water meter negates the need to jumper it. In this case, I think it would be better to simply attach the grounding clamp as near as possible to the point at which the pipe enters the home. Agreed? (See image) http://www.geocities.com/mydeadpresidents/index.html As for outgoing circuits, what kind of trouble can be caused by having a mix of neutrals and grounds on each bus? I'm gonna fix it no matter what, but it won't be the first thing I do. You've seen my Service Disconnect box. Is it common to have a separate service disconnect box as I do? Had it been wired correctly, couldn't I have just used the panelboard which has it's own 100 AMP breaker) and then skip the current Service Disconnect box? Tell me I have this right. Let's assume I keep the Service Disconnect at 100 AMP but I want to upgrade the box. I would then get a new box (that supports at least 100amps) then add a 100 AMP breaker for the incoming power and then get another 100 AMP breaker for the power outgoing to the panelboard. In other words, because my panelboard has room for the circuits I need and that I forsee needing, I see no reason to try to run circuits from my new Service Disconnect box and therfore, the power should just go straight through. Put another way, I'm not using the panelboard as a subpanel in the traditonal sense. I'm using the panelboard for ALL circuits and the Service Disconnect is really nothing more than a way to kill the main power and provide a lauching point for grouding conductors. Is there anything wrong with this setup? My main service breaker only allows for 100amps. I've read that a 100 breaker usually means you can go 200 or more, but I've totaled up the amps of the circuits in my panel box and it's around 500! However, in the two years I've lived here, I've never once thrown a breaker. Also, some of the circuits are used seasonally. I've got 60 amps dedicated to the AC, but I also have 160 amps dedicated to space heaters which I almost never use, not even in the winter time (because that same room also has a wood stove). Is it time to upgrade to 200amps? I regards to power coming into my home (2 hot/1 neutral), how much power is available? I mean, right now, judging by the breaker in my Service Disconnect, I'm utilizing up to 100 AMPs of power. If I wanted to go 200, then can I just upgrade to a breaker and panel that support the extra amps? Or, is there some kind of physical change the Power Co will have to make? Thanks |
#2
![]() |
|||
|
|||
![]()
"Mark Wilson" wrote in message
... Volts500, Mark and Sue, Thanks to your help and the help of others I now feel I know enough to keep the electrician honest. I've got the soars book on order and I plan to do some of the grunt work myself. I honestly didn't realize this thread would get so involved. It's very kind of you to help out while keeping the focus on my safety. To ease my guilt at having imposed on so much of your time, I can only hope others will get some use out of it as well. Keeping everything in mind, I'm going to follow Volt's advice for all the grounding. I'm also going to replace the Service Disconnect (as Mark suggested), and rewire the panelboard. Now, this opens up a few more questions. If I had any shame, I would feel too guilty to ask any more, but I guess I'm a bit shameless. If you guys would start giving crappy and vague advice, you really would avoid people like me buggying you so much. ![]() Don't feel guilty -- that what these forums are for. If we get tired of your questions, you'll only get lame (or no) answers. Volts: It appears that the metal housing of the water meter negates the need to jumper it. In this case, I think it would be better to simply attach the grounding clamp as near as possible to the point at which the pipe enters the home. Agreed? (See image) http://www.geocities.com/mydeadpresidents/index.html As for outgoing circuits, what kind of trouble can be caused by having a mix of neutrals and grounds on each bus? I'm gonna fix it no matter what, but it won't be the first thing I do. If it is service equipment, then none as ground and neutral are the same. In a subpanel, the voltage drop across the neutral will raise your ground this same amount (typically 1 to 3 volts). For things that actually go to a true ground, such as audio tuners and cable TV cables, you'll get a current flowing in the shield causing noise, hum, or other interesting behavior. You've seen my Service Disconnect box. Is it common to have a separate service disconnect box as I do? Had it been wired correctly, couldn't I have just used the panelboard which has it's own 100 AMP breaker) and then skip the current Service Disconnect box? This seems to be a regional thing. Some areas demand an outside disconnect. Where I live, the disconnects can be inside the house as long as they are very near where the service cables enter. Since your second panel is also outside, you meet the outside disconnect rule. The only other issue would be if your area has a limitation on how far the main disconnect needs to be from the meter. If they have one, it may be short, like 5 feet. The intent here is to minimize the length of unfused service conductors and the amount of structure they will damage should they flame up. Tell me I have this right. Let's assume I keep the Service Disconnect at 100 AMP but I want to upgrade the box. I would then get a new box (that supports at least 100amps) then add a 100 AMP breaker for the incoming power and then get another 100 AMP breaker for the power outgoing to the panelboard. In other words, because my panelboard has room for the circuits I need and that I forsee needing, I see no reason to try to run circuits from my new Service Disconnect box and therfore, the power should just go straight through. Put another way, I'm not using the panelboard as a subpanel in the traditonal sense. I'm using the panelboard for ALL circuits and the Service Disconnect is really nothing more than a way to kill the main power and provide a lauching point for grouding conductors. Is there anything wrong with this setup? The first panel is still your service disconnect because it has a breaker in it. Additional service rated panels must be grouped (can't be 20 feet across the wall) and there is usually no fusing between them. If your local inspector says its OK, you may be able to replace the 100A disconnect with just a junction box if the existing house circuit panel has a 100A main disconnect. Then run new wires from the meter base to the panel where all your circuits are and use it as a main service rated panel. My main service breaker only allows for 100amps. I've read that a 100 breaker usually means you can go 200 or more, but I've totaled up the amps of the circuits in my panel box and it's around 500! However, in the two years I've lived here, I've never once thrown a breaker. Also, some of the circuits are used seasonally. I've got 60 amps dedicated to the AC, but I also have 160 amps dedicated to space heaters which I almost never use, not even in the winter time (because that same room also has a wood stove). Is it time to upgrade to 200amps? Again a local thing. Here, all services must be wired for 200A, but you could put in a 100A breakered panel if you want to. The wires will have to be sized for 200A though. If your service wires are 100A, then you can't increase to 200A without replacing them. Same with your meter base -- is it 100A or 200A? You can put a 200A breakered panel on a 100A service if you've done a load calculation and it indicates you're not exceeding the 100A service. Finally, check with your utility to see how big your transformer is. You'll want at least a 20 KVA for a 200A service, and preferably a 25 or 30 KVA. I regards to power coming into my home (2 hot/1 neutral), how much power is available? I mean, right now, judging by the breaker in my Service Disconnect, I'm utilizing up to 100 AMPs of power. If I wanted to go 200, then can I just upgrade to a breaker and panel that support the extra amps? Or, is there some kind of physical change the Power Co will have to make? 100A is available at 240V (24 KVA). Power company may have to increase their wires to you and may have to increase the transformer. You may have to increase the meter base, the service entrance wires and the main panel. -- Mark Kent, WA |
#3
![]() |
|||
|
|||
![]() "Mark Wilson" wrote in message ... Volts: It appears that the metal housing of the water meter negates the need to jumper it. In this case, I think it would be better to simply attach the grounding clamp as near as possible to the point at which the pipe enters the home. Agreed? (See image) http://www.geocities.com/mydeadpresidents/index.html Now we're getting into the what if's and why for's (Although you seem to be grasping the concepts, I'm trying to avoid all of that to keep misunderstandings to a minimum.) Best to jumper the meter and be done with it.......$2 part, 5 min. work, tops. Don't forget to jumper the hot water to the cold water at the water meter. As for outgoing circuits, what kind of trouble can be caused by having a mix of neutrals and grounds on each bus? I'm gonna fix it no matter what, but it won't be the first thing I do. Can cause all sorts of nasty problems. I think Mark covered that and the rest of it pretty well. |
#4
![]() |
|||
|
|||
![]() "volts500" wrote "Mark Wilson" wrote in message ... Volts: It appears that the metal housing of the water meter negates the need to jumper it. In this case, I think it would be better to simply attach the grounding clamp as near as possible to the point at which the pipe enters the home. Agreed? (See image) http://www.geocities.com/mydeadpresidents/index.html Now we're getting into the what if's and why for's (Although you seem to be grasping the concepts, I'm trying to avoid all of that to keep misunderstandings to a minimum.) Best to jumper the meter and be done with it.......$2 part, 5 min. work, tops. Don't forget to jumper the hot water to the cold water at the water meter. As for outgoing circuits, what kind of trouble can be caused by having a mix of neutrals and grounds on each bus? I'm gonna fix it no matter what, but it won't be the first thing I do. Can cause all sorts of nasty problems. I think Mark covered that and the rest of it pretty well. Most water meters that I'm familiar with use rubber compression or washer type seals. Those big brass nuts, they really don't connect electrically to the tubing to the meter body all that well. Gary Quality Water Associates |
#5
![]() |
|||
|
|||
![]()
Mark,
You've seen my Service Disconnect box. Is it common to have a separate service disconnect box as I do? Had it been wired correctly, couldn't I have just used the panelboard which has it's own 100 AMP breaker) and then skip the current Service Disconnect box? This seems to be a regional thing. Some areas demand an outside disconnect. Where I live, the disconnects can be inside the house as long as they are very near where the service cables enter. Since your second panel is also outside, you meet the outside disconnect rule. The only other issue would be if your area has a limitation on how far the main disconnect needs to be from the meter. If they have one, it may be short, like 5 feet. The intent here is to minimize the length of unfused service conductors and the amount of structure they will damage should they flame up. Actually, both my Service Disconnect and Panelboard are inside the house. Outside the house there is only a meter. All in all, having a separate Service Disconnect is fine for now, although I think I'll replace it with the Cutler Hammer box you suggested. Of course the Power Co will have to someone disconnect power for the Service Disconnect to be rewired. How does the Power Co go about shutting down power? Do they have to climb the pole or is there something they can do at the meter? My main service breaker only allows for 100amps. I've read that a 100 breaker usually means you can go 200 or more, but I've totaled up the amps of the circuits in my panel box and it's around 500! However, in the two years I've lived here, I've never once thrown a breaker. Also, some of the circuits are used seasonally. I've got 60 amps dedicated to the AC, but I also have 160 amps dedicated to space heaters which I almost never use, not even in the winter time (because that same room also has a wood stove). Is it time to upgrade to 200amps? Again a local thing. Here, all services must be wired for 200A, but you could put in a 100A breakered panel if you want to. The wires will have to be sized for 200A though. If your service wires are 100A, then you can't increase to 200A without replacing them. Same with your meter base -- is it 100A or 200A? You can put a 200A breakered panel on a 100A service if you've done a load calculation and it indicates you're not exceeding the 100A service. Finally, check with your utility to see how big your transformer is. You'll want at least a 20 KVA for a 200A service, and preferably a 25 or 30 KVA. The meter says something like "200cl 240v 3w" I'll give the Power Co a call and look into it. I'm sure it's not a black and white issue, but if I'm not throwing breakers, is it fair to say I don't really need 200A at this time? I hate to rewire everything only to decide later that I need to upgrade the panelboard too. |
#6
![]() |
|||
|
|||
![]()
"Mark Wilson" wrote in message
... Actually, both my Service Disconnect and Panelboard are inside the house. Outside the house there is only a meter. All in all, having a separate Service Disconnect is fine for now, although I think I'll replace it with the Cutler Hammer box you suggested. Of course the Power Co will have to someone disconnect power for the Service Disconnect to be rewired. How does the Power Co go about shutting down power? Do they have to climb the pole or is there something they can do at the meter? Ah, now were making progress. Inside the house, they want your main disconnect as soon as possible. Usually, this means within 5' of where the wire penetrates the exterior wall. If your service panel is 20 feet from the disconnect, that explains why you have a disconnect. Why they didn't put a normal panelboard where the disconnect is located I don't know.... Usually, power is disconnected by pulling the meter. Sometimes, you can do this yourself, but you must inform the power company so they can come back and seal it (and know why the seal has been broken). It would be better to have the power company come pull your meter, as they can deal with any oh-****s that happen. A service enclosure is not a nice place to have things stuck or falling out! The only thing that sucks here is re-establishing service. You may be without power for a day while you wait for the power company to come back. You may feel more comfortable putting the meter back in than taking it out. That would get you going again sooner. Climbing the pole would work too, but they'll only do that if you need to work in or replace the meter enclosure. The meter says something like "200cl 240v 3w" I'll give the Power Co a call and look into it. I'm sure it's not a black and white issue, but if I'm not throwing breakers, is it fair to say I don't really need 200A at this time? I hate to rewire everything only to decide later that I need to upgrade the panelboard too. That would be a Class 200 meter for normal 240/120 household service. You probably have a 200A meter enclosure if you have a 200A meter, so perhaps this part can stay forever (unless its deteriorated). Yes, if that main is not tripping you're probably OK (unless that breaker is defective). However, you may want to measure your voltage sometime when you're pushing things and see how much it sags. A wimpy transformer will help prevent you blowing the breaker. I think that is why my power company uses a transformer that is about half the size of your needs. When you really need 100A, you're going to have a fair amount of voltage drop and may not get to drawing 100A because things are drawing less current at the lower voltage. Finally, just because you have a 200A meter doesn't mean you had 200A service entrance conductors installed. If you ever decide to upgrade the main disconnect to 200A, you'll need to check the wires to the meter and from the meter for proper size. You can defer that task if you just replace the 100A disconect with another 100A unit. -- Mark Kent, WA |
#7
![]() |
|||
|
|||
![]()
"Mark Wilson" wrote in message
... Actually, both my Service Disconnect and Panelboard are inside the house. Outside the house there is only a meter. All in all, having a separate Service Disconnect is fine for now, although I think I'll replace it with the Cutler Hammer box you suggested. Of course the Power Co will have to someone disconnect power for the Service Disconnect to be rewired. How does the Power Co go about shutting down power? Do they have to climb the pole or is there something they can do at the meter? Ah, now were making progress. Inside the house, they want your main disconnect as soon as possible. Usually, this means within 5' of where the wire penetrates the exterior wall. If your service panel is 20 feet from the disconnect, that explains why you have a disconnect. Why they didn't put a normal panelboard where the disconnect is located I don't know.... Usually, power is disconnected by pulling the meter. Sometimes, you can do this yourself, but you must inform the power company so they can come back and seal it (and know why the seal has been broken). It would be better to have the power company come pull your meter, as they can deal with any oh-****s that happen. A service enclosure is not a nice place to have things stuck or falling out! The only thing that sucks here is re-establishing service. You may be without power for a day while you wait for the power company to come back. You may feel more comfortable putting the meter back in than taking it out. That would get you going again sooner. Climbing the pole would work too, but they'll only do that if you need to work in or replace the meter enclosure. The meter says something like "200cl 240v 3w" I'll give the Power Co a call and look into it. I'm sure it's not a black and white issue, but if I'm not throwing breakers, is it fair to say I don't really need 200A at this time? I hate to rewire everything only to decide later that I need to upgrade the panelboard too. That would be a Class 200 meter for normal 240/120 household service. You probably have a 200A meter enclosure if you have a 200A meter, so perhaps this part can stay forever (unless its deteriorated). Yes, if that main is not tripping you're probably OK (unless that breaker is defective). However, you may want to measure your voltage sometime when you're pushing things and see how much it sags. A wimpy transformer will help prevent you blowing the breaker. I think that is why my power company uses a transformer that is about half the size of your needs. When you really need 100A, you're going to have a fair amount of voltage drop and may not get to drawing 100A because things are drawing less current at the lower voltage. Finally, just because you have a 200A meter doesn't mean you had 200A service entrance conductors installed. If you ever decide to upgrade the main disconnect to 200A, you'll need to check the wires to the meter and from the meter for proper size. You can defer that task if you just replace the 100A disconect with another 100A unit. -- Mark Kent, WA |
#8
![]() |
|||
|
|||
![]()
Volts,
I'll go ahead and jumper that water meter as you said. Regarding the ground wire going from netural bar to water heater over to water meter.... While trying not to make dramtic bends in the conductor, it's going to be almost impossible to prevent the it from contacting the metal ducts and armored cable that run along the ceiling. I suppose I could try to insulate the wire somehow when it gets near the AC, or perhaps I can find some insulated green #4 (afterall, this is being used inside anyway). Does contact with the ducts or AC create a problem? About how much bend can a ground wire take (and still function well)? 135 degrees? |
#9
![]() |
|||
|
|||
![]() "Mark Wilson" wrote in message ... "Mark Wilson" wrote in message ... With what you've said now, your panels are OK. Both are service rated panels, and you have two disconnects. One of those disconnects is not really needed and could be removed. Or, perhaps replace it with a 100A transfer switch if you've thought about generator power... oh no, not another tangent... lol. (generator) I was wrong about the panelboard. It's actually rated at 200A and the breaker is 200, not 100. I'm still considering an upgrade to 200A. Because the panelboard is rated for 200, if I upgrade to 200, I could skip the first disconnect which might be the cost effective way to go. This would mean about a 5 foot run from the outside meter to the panelboard. If I did this, I'm guessing I'd just run all my GEC and other grounds from the ground bus bar. I might check back with you guys on a few things, but I've got enough to get to work now and I think I'll let this thread die. So your 100A disconnect is required. A single disconnect can not be greater than the size of the service, so a 100A breaker had to be placed in front of the 200A panel main. And right again, if you upgrade to 200, just remove that 100A disconnect box and go straight to the 200A panel you already have. understood. Oh, but I am still wondering about that ground conductor going from the Service Disconnect to my water meter and pipe (from the inside of the house). Is it bad for the bare conductor to contact armored cable (bx) or metal duct work? Knowing the answer will make a big difference in the amount of work I have to do to run the wire. No, it is not bad. Those things should already be grounded by the circuit that feeds them. Those items touching the GEC won't change anything. If you just don't like doing that, you can run insulated wire, but you'll need to color it green (use tape or paint) where it is exposed. If you're planning on a 200A upgrade at some point, run a #4 copper GEC to the water pipe. Otherwise, you'll need to upsize it when you upgrade the service. In my case it will be MUCH easier if I don't have to worry about the GEC touching the ducts. -- Mark Kent, WA That's it for me on this thread. Thanks! |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
WTD Info on Tapmatic 700X and info on Tapmatics | Metalworking | |||
Jointech routerbits? | Woodworking | |||
Lorch Junior lathe slide rest info? | Metalworking | |||
*** Rec.Woodworking Mini-FAQ *** 126 (w/Filter info!) | Woodworking | |||
Grounding Rod *and* Rebar for service grounds? | Home Repair |