Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor.
This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? |
#2
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/24/2015 5:08 PM, Arnie Goetchius wrote:
I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#3
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Monday, August 24, 2015 at 7:26:00 PM UTC-4, Stormin Mormon wrote:
On 8/24/2015 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago.. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. -- . Christopher A. Young learn more about Jesus . www.lds.org . . wonder if the air filter is clogged? |
#4
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/24/15 5:08 PM, Arnie Goetchius wrote:
I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. |
#5
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Mon, 24 Aug 2015 17:08:41 -0400, Arnie Goetchius
wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Does it have a restart lockout timer to prevent the compressor from short cycling? If not, it may have been liquid slugged and overheated. Letting it settle for a while got it working again and I hope you didn't really hurt anything. |
#6
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
J Burns wrote:
On 8/24/15 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. It seemed like something like that might have happened BUT the noise and vibration started exactly when the A/C started. The noise I hard was probably from the compressor trying to start after being off for at least a couple of hours. I had set the thermostat up a couple of degrees in the morning because it was a nice day and we opened the doors. In the afternoon, it got hot so I closed the doors and lowered the thermostat and that's when the lights blinked at the same time as the compressor tried to start. |
#7
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
|
#8
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
bob haller wrote:
On Monday, August 24, 2015 at 7:26:00 PM UTC-4, Stormin Mormon wrote: On 8/24/2015 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. -- . Christopher A. Young learn more about Jesus . www.lds.org . . wonder if the air filter is clogged? I have a Dust Eater filter that was back washed about 10 days ago. In any event, the Condensing Unit (probably the compressor) had a problem as soon as it started so I don't think the filter came into play. |
#9
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/24/15 8:41 PM, Arnie Goetchius wrote:
J Burns wrote: What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. It seemed like something like that might have happened BUT the noise and vibration started exactly when the A/C started. The noise I hard was probably from the compressor trying to start after being off for at least a couple of hours. I had set the thermostat up a couple of degrees in the morning because it was a nice day and we opened the doors. In the afternoon, it got hot so I closed the doors and lowered the thermostat and that's when the lights blinked at the same time as the compressor tried to start. I've had my refrigerator compressor overheat and shut off because of a power interruption, but the interruption occurred after it was running. I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. |
#10
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
J Burns wrote:
On 8/24/15 8:41 PM, Arnie Goetchius wrote: J Burns wrote: What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. It seemed like something like that might have happened BUT the noise and vibration started exactly when the A/C started. The noise I hard was probably from the compressor trying to start after being off for at least a couple of hours. I had set the thermostat up a couple of degrees in the morning because it was a nice day and we opened the doors. In the afternoon, it got hot so I closed the doors and lowered the thermostat and that's when the lights blinked at the same time as the compressor tried to start. I've had my refrigerator compressor overheat and shut off because of a power interruption, but the interruption occurred after it was running. I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. |
#11
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Mon, 24 Aug 2015 22:29:12 -0400, Arnie Goetchius
wrote: In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. If they are switching power around the grid, you can get little "blinks" of the lights. (up to a couple seconds). That is why the UPS is such a popular thing. |
#12
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Monday, August 24, 2015 at 6:26:00 PM UTC-5, Stormin Mormon wrote:
On 8/24/2015 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago.. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. -- . I'd have to wonder about dirt and grass clippings clogging the condenser from when the lawn was mowed near the AC unit. Me and the guys I did HVAC work with admonished homeowners to always turn the AC off when a lawnmower is being used on the same side of the house as the condensing unit. Of course this is when homes are close together not for huge lots. For large lots, we'd tell them to turn the AC off when the lawn was being mowed within 10 yards unless a cloud of dust is being kicked up then turn the AC off until the mowing is done and the dust settles. I have explained to some people that the discharge from a mower should never be toward the AC unit and the unit should be hosed off with a gentle fan spray so as not to damage the fins before turning the AC back on. A lot of homeowners have never thought it necessary to turn the AC off when the lawn was being mowed, not because they're stupid it's because they don't know any better. ^_^ [8~{} Uncle Lawn Monster |
#13
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/24/15 10:29 PM, Arnie Goetchius wrote:
J Burns wrote: On 8/24/15 8:41 PM, Arnie Goetchius wrote: J Burns wrote: What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. It seemed like something like that might have happened BUT the noise and vibration started exactly when the A/C started. The noise I hard was probably from the compressor trying to start after being off for at least a couple of hours. I had set the thermostat up a couple of degrees in the morning because it was a nice day and we opened the doors. In the afternoon, it got hot so I closed the doors and lowered the thermostat and that's when the lights blinked at the same time as the compressor tried to start. I've had my refrigerator compressor overheat and shut off because of a power interruption, but the interruption occurred after it was running. I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. http://www.oncor.com/EN/Pages/Common-Utility-Terms.aspx This says a fuse must be replaced if it disconnects the circuit. It says the small circuit breaker on a distribution lines is a recloser. When a pecan limb fell onto bare distribution wires behind my house, lights in the neighborhood blinked. I imagine that was the recloser across the street. If the limb had kept the lines pressed together, the lever on the recloser would have popped down and a guy with a long pole would have had to come to reset it. |
#14
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Tue, 25 Aug 2015 01:12:46 -0400, J Burns
wrote: On 8/24/15 10:29 PM, Arnie Goetchius wrote: J Burns wrote: On 8/24/15 8:41 PM, Arnie Goetchius wrote: J Burns wrote: What if you lost power for 1/2 second from a squirrel playing on the line of a train hitting a utility tower? Maybe the noise you heard was not the condenser fan but the compressor trying to resume operation against too much pressure. In a couple of minutes, a protection device shut off the compressor because of heat or pressure. It seemed like something like that might have happened BUT the noise and vibration started exactly when the A/C started. The noise I hard was probably from the compressor trying to start after being off for at least a couple of hours. I had set the thermostat up a couple of degrees in the morning because it was a nice day and we opened the doors. In the afternoon, it got hot so I closed the doors and lowered the thermostat and that's when the lights blinked at the same time as the compressor tried to start. I've had my refrigerator compressor overheat and shut off because of a power interruption, but the interruption occurred after it was running. I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. http://www.oncor.com/EN/Pages/Common-Utility-Terms.aspx This says a fuse must be replaced if it disconnects the circuit. It says the small circuit breaker on a distribution lines is a recloser. When a pecan limb fell onto bare distribution wires behind my house, lights in the neighborhood blinked. I imagine that was the recloser across the street. If the limb had kept the lines pressed together, the lever on the recloser would have popped down and a guy with a long pole would have had to come to reset it. Reclosers usually reset themselves (AKA automatic recloser). That is why you may see it come on a couple times before it stays off. |
#15
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
Uncle Monster wrote:
On Monday, August 24, 2015 at 6:26:00 PM UTC-5, Stormin Mormon wrote: On 8/24/2015 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. -- . I'd have to wonder about dirt and grass clippings clogging the condenser from when the lawn was mowed near the AC unit. Me and the guys I did HVAC work with admonished homeowners to always turn the AC off when a lawnmower is being used on the same side of the house as the condensing unit. Of course this is when homes are close together not for huge lots. For large lots, we'd tell them to turn the AC off when the lawn was being mowed within 10 yards unless a cloud of dust is being kicked up then turn the AC off until the mowing is done and the dust settles. I have explained to some people that the discharge from a mower should never be toward the AC unit and the unit should be hosed off with a gentle fan spray so as not to damage the fins before turning the AC back on. A lot of homeowners have never thought it necessary to turn the AC off when the lawn was being mowed, not because they're stupid it's because they don't know any better. ^_^ [8~{} Uncle Lawn Monster Good point. In my case, the lawn is at about 5 yards away from the A/C. However, when I do the lawn, the output of the mower is always directed away from the A/C so I don't think that is the problem. |
#16
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/24/2015 10:29 PM, Arnie Goetchius wrote:
I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. We have that at least once a month on one of the phases. Drops out the one AC, TV box will have to reboot. PITA, but no damage. |
#17
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
Stormin Mormon wrote:
On 8/24/2015 5:08 PM, Arnie Goetchius wrote: I have a new 4 ton A/C and gas furnace installed in Jan 2015 by a contractor. This replaced a Colman 4 ton that I installed myself about 25 years ago. The new A/C Condensing Unit is a Trane 4 ton 4TTR3018-60. The A/C has been running all summer with out a problem. Today, after being off for a couple of hours, it started up and the following happened: (1) the house lights blinked for about 1/4 to 1/2 second. (2) the condensing unit ran twice as loud with more vibration as it normally does for about a couple of minutes and then it resumed its normal noise/vibration level. (3) During the time it was running, there was absolutely no cooling. The temperature at the bonnet was the same as the temperature at the return air duct. I shut the A/C down by adjusting the thermostat up and called the service tech who is coming tomorrow morning. After waiting an hour, I dropped the thermostat and it started right up with no lights blinking. The bonnet is running about 14-16 degrees cooler than the return duct which is normal. When I read the specs for the compressor, it says the following: "The Climatuff® compressor features internal over temperature and pressure protector, total dipped hermetic motor and thermostatically controlled sump heater. Other features include: roto lock suction and discharge refrigeration connections, centrifugal oil pump, and low vibration and noise." Question: Is it possible that the compressor detected a problem and just shut down but the Condensing Unit fan would still keep running? Also would a 1/4 to 1/2 second blinking of the lights be symptomatic of the problem? Without being there, I'm not getting any big ideas what might be wrong. My first thought was dusty condenser, but that's unlikely on a unit less than a year old. Be interesting, see what the tech finds. Please follow up on this list, we can learn from you. Thank you. Here is what the tech said: While it is possible that there was a temporary power failure that caused all of the compressor racket, the more likely problem was a stuck TXV valve in the A coil as described in the links below. Starting in 2014, Copeland, who makes the compressor, started adding a rust inhibitor to the compressor. The inhibitor had the consequence of occasionally freezing the TXV valve thus preventing any circulation in the system. When the TXV valve freezes, it causes the compressor to struggle and finally shut down. The solution is to add a cleaning fluid of some kind (A/C Re-New ?) to the system and run it for 48 hours to get rid of the anti rust inhibitor and free up the TXV valve. If the TXV valve is still frozen, then the TXV valve has to be replaced. The tech said keep an eye on it and if it happens again, they will come out and flush the system and replace the TXV valve if that is necessary. Here are some relevant links: Explanation of Problem https://www.reddit.com/r/HVAC/commen...s_many_brands/ Copeland Lawsuit http://www.chimicles.com/thermostati...defect-lawsuit Youtube Video How to Fix. Includes about about 140 comments https://www.youtube.com/watch?v=Amo2eRlYrzg |
#18
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/25/15 10:29 AM, Ed Pawlowski wrote:
On 8/24/2015 10:29 PM, Arnie Goetchius wrote: I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. We have that at least once a month on one of the phases. Drops out the one AC, TV box will have to reboot. PITA, but no damage. Does it reclose, or do you call the man with the pole? |
#19
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
J Burns wrote:
On 8/25/15 10:29 AM, Ed Pawlowski wrote: On 8/24/2015 10:29 PM, Arnie Goetchius wrote: I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. We have that at least once a month on one of the phases. Drops out the one AC, TV box will have to reboot. PITA, but no damage. Does it reclose, or do you call the man with the pole? I have to call the man with the pole. When I call, I tell that I am out there with my tree trimmer and is it okay if I do it myself. Of course, they scream at me No! No! and send their own pole guy out IMMEDIATELY!! |
#20
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On Tuesday, August 25, 2015 at 10:22:18 AM UTC-5, Arnie Goetchius wrote:
J Burns wrote: On 8/25/15 10:29 AM, Ed Pawlowski wrote: On 8/24/2015 10:29 PM, Arnie Goetchius wrote: I don't know how many amps it take to trip a momentary interrupter on a power line. Maybe there happened to be an exceptional load on the line at that instant. Your compressor was enough to trip the power company's device, and your lights flickered. In our neighborhood, we have drop down fuses that will disconnect the transformer if there is a high current problem. Then you have to call the utility to come out and close the fuse. No momentary interrupters that I know of unless there is something at the sub-station (2 miles from my house) that does a momentary interruption. We have that at least once a month on one of the phases. Drops out the one AC, TV box will have to reboot. PITA, but no damage. Does it reclose, or do you call the man with the pole? I have to call the man with the pole. When I call, I tell that I am out there with my tree trimmer and is it okay if I do it myself. Of course, they scream at me No! No! and send their own pole guy out IMMEDIATELY!! Well hell it's only 13,800 volts, so what's the problem? ^_^ [8~{} Uncle Insane Monster |
#21
Posted to alt.home.repair
|
|||
|
|||
HVAC Not Cooling, sometimes.
On 8/25/2015 11:17 AM, J Burns wrote:
We have that at least once a month on one of the phases. Drops out the one AC, TV box will have to reboot. PITA, but no damage. Does it reclose, or do you call the man with the pole? Drops and goes back by itself. Just goes out long enough to cause things to stop. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||