I have just discovered that our 120v microwave oven is tapped into the
240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? -- |
#2
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 03/11/2015 02:44 AM, ShirtFree wrote:
I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Fire and/or electrocution! Any ideas for a remedy? Apparently your house was wired by the village idiot. Get it repaired by a competent electrician. |
#3
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree
wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? Sounds like an Edison circuit. Two circuits on three wires. It is possible to split a 240 into two 120's using the common neutral, but I don't know if it is legal to have both voltages. I don't know enough about the code to say if it is compliant or not. The only way to eliminate it is to run a new wire either from the breaker box or from a junction box that can support the additional load. The Edison circuit was originally designed by Edison using his DC system, but he lost out to Westinghouse and AC. |
#4
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
I have just discovered that our 120v microwave oven is tapped into the
240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? *Your best remedy is to install a new 20 amp 120 volt circuit to power the microwave oven. John Grabowski http://www.MrElectrician.TV |
#5
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree
wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? There should not be too much danger as long as you pay the Fire Department to park and staff a fire truck in your driveway 24/7. They will likely be able to limit the fire, so it only destroys your kitchen. For a remedy, call an electrician, to wire it properly!!! That outlet is probably not even on a correct size breaker or fuse. |
#6
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 2:09:01 AM UTC-4, wrote:
On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? The major danger is the neutral current can show up on the frame of the stove if you have a fault in the grounded conductor. Agree with the above. The stove circuit is of the older variety, with one wire sharing the function of neutral and ground. That is assuming that the stove has 120V loads as well as 240V loads, which they typically do. If the stove was just 240V, then the one wire would be just the ground. Assuming it was wired up years ago when it was code compliant, there is no issue there with the stove. What some yahoo did was tap into it for the microwave and that is not code compliant. The best solution would be to do a new run back to the panel for the microwave outlet. It would also be an opportunity to add other receptacles if you need them. Contrary to what some are saying, assuming all else was done correctly, there is no fire danger, immediate safety hazard, etc. Like Gfre says, the danger would be if the ground/neutral were to be cut, disconnected at the panel, etc. In that case, the metal case of the microwave would become energized. But even with only the stove, installed to previous code, the same thing would happen with the stove metal itself and that was allowed for 50 years without disasters everywhere. The chance of the one wire being interrupted somehow is very low. So, it should be corrected, but no need to panic. |
#7
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 9:30:28 AM UTC-4, trader_4 wrote:
On Wednesday, March 11, 2015 at 2:09:01 AM UTC-4, wrote: On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? The major danger is the neutral current can show up on the frame of the stove if you have a fault in the grounded conductor. Agree with the above. The stove circuit is of the older variety, with one wire sharing the function of neutral and ground. That is assuming that the stove has 120V loads as well as 240V loads, which they typically do. If the stove was just 240V, then the one wire would be just the ground. Assuming it was wired up years ago when it was code compliant, there is no issue there with the stove. My stove is old enough to be 3 wire, and it has an outlet for plugging in a coffee pot, microwave, etc. Does the OP have a separate 120 outlet daisy chained to the stove outlet? That sounds out of code to me. |
#8
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 9:41:02 AM UTC-4, TimR wrote:
On Wednesday, March 11, 2015 at 9:30:28 AM UTC-4, trader_4 wrote: On Wednesday, March 11, 2015 at 2:09:01 AM UTC-4, wrote: On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? The major danger is the neutral current can show up on the frame of the stove if you have a fault in the grounded conductor. Agree with the above. The stove circuit is of the older variety, with one wire sharing the function of neutral and ground. That is assuming that the stove has 120V loads as well as 240V loads, which they typically do. If the stove was just 240V, then the one wire would be just the ground. Assuming it was wired up years ago when it was code compliant, there is no issue there with the stove. My stove is old enough to be 3 wire, and it has an outlet for plugging in a coffee pot, microwave, etc. Does the OP have a separate 120 outlet daisy chained to the stove outlet? That sounds out of code to me. From what was described, that's indeed what they have and it is a code violation and should be fixed. The thing I worry about with things like this is if some yahoo did this, what else did they do with that circuit and/or the rest of the house that you don't know about? |
#9
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 9:30:28 AM UTC-4, trader_4 wrote:
On Wednesday, March 11, 2015 at 2:09:01 AM UTC-4, wrote: On Wed, 11 Mar 2015 02:44:01 +0000, ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? The major danger is the neutral current can show up on the frame of the stove if you have a fault in the grounded conductor. Agree with the above. The stove circuit is of the older variety, with one wire sharing the function of neutral and ground. That is assuming that the stove has 120V loads as well as 240V loads, which they typically do. If the stove was just 240V, then the one wire would be just the ground. Assuming it was wired up years ago when it was code compliant, there is no issue there with the stove. What some yahoo did was tap into it for the microwave and that is not code compliant. The best solution would be to do a new run back to the panel for the microwave outlet. It would also be an opportunity to add other receptacles if you need them. Contrary to what some are saying, assuming all else was done correctly, there is no fire danger, immediate safety hazard, etc. Like Gfre says, the danger would be if the ground/neutral were to be cut, disconnected at the panel, etc. In that case, the metal case of the microwave would become energized. But even with only the stove, installed to previous code, the same thing would happen with the stove metal itself and that was allowed for 50 years without disasters everywhere. The chance of the one wire being interrupted somehow is very low. Must be running a bit slow today. I take back part of what I said above about the possible disconnection of the neutral/ground being the only safety issue. That is one angle, but there is a big safety issue here, and that is that the microwave outlet is being protected by the breaker for the stove. That's going to typically be a 40A or larger breaker. So, you have a 15 or 20 amp outlet plus the wiring between the outlet and stove, on a 40A or bigger breaker. That is a potential fire hazard. |
#10
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 9:55:03 AM UTC-4, trader_4 wrote:
Contrary to what some are saying, assuming all else was done correctly, there is no fire danger, immediate safety hazard, etc. Like Gfre says, the danger would be if the ground/neutral were to be cut, disconnected at the panel, etc. In that case, the metal case of the microwave would become energized. But even with only the stove, installed to previous code, the same thing would happen with the stove metal itself and that was allowed for 50 years without disasters everywhere. The chance of the one wire being interrupted somehow is very low. Must be running a bit slow today. I take back part of what I said above about the possible disconnection of the neutral/ground being the only safety issue. That is one angle, but there is a big safety issue here, and that is that the microwave outlet is being protected by the breaker for the stove. That's going to typically be a 40A or larger breaker. So, you have a 15 or 20 amp outlet plus the wiring between the outlet and stove, on a 40A or bigger breaker. That is a potential fire hazard. So you could potentially plug way too many devices into that outlet and never trip anything, that makes sense as the main safety issue. That 40 A breaker is a double. I'm not sure how they work. Does it take 40 A to trip either side? |
#11
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 10:38:15 AM UTC-4, TimR wrote:
So you could potentially plug way too many devices into that outlet and never trip anything, that makes sense as the main safety issue. That 40 A breaker is a double. I'm not sure how they work. Does it take 40 A to trip either side? Yes. |
#12
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
replying to ShirtFree, Chuck wrote:
ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? Thanks, guys, for all the input. There are no 120v devices on the stove (very cheap model). No clocks, outlets or the like. Strictly 240v heating elements. The house was constructed in the late 60's, early 70's (with aluminum wiring) and the kitchen "remodeling" was done in 2010, at which time the jerry rigged wiring was installed. I'm sure no permitting took place. Glad to learn about the extent and nature of the dangers, though. I will make sure that there is continuity in the ground between the stove and the distribution panel. I'm going to go with having a separate circuit installed as time and circumstances allow. PS The Anne Arundel County Fire Service was not interested in stationing fire fighters and equipment in the vicinity. The entire community has aluminum wiring and yet there have been no house fires that I am aware of. Thanks again to all of you for your help. -- |
#13
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
|
#14
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
replying to trader_4 , Chuck wrote:
trader4 wrote: From what was described, that's indeed what they have and it is a code violation and should be fixed. The thing I worry about with things like this is if some yahoo did this, what else did they do with that circuit and/or the rest of the house that you don't know about? Your point is well taken. You wouldn't believe what we have come across. For instance, the front porch light switch was wired to ground. Turn it on, and the breaker tripped. It has been an expensive nightmare, and it just keeps on. -- |
#15
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
|
#16
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 2:43:59 PM UTC-4, wrote:
Consider this. The Microwave (MW) develops a problem, causing a dead short. There is no properly sized breaker to trip. Several things can happen. A dead short will trip the existing 40A or whatever breaker for the stove instantly. It's an overload that exceeds the wiring to the outlet, but not the breaker, ie the range of 15A or 20A to 40A, that would be the fire hazard from the wiring overheating. If you're lucky. only the MW will be destroyed as smoke pours out of it, making it hard to breathe and sooting up the house, until it finally burns the internal wires and components enough to be disconnected from the power. -OR- If you're not so lucky, the unprotected #12 or #14 wires to that outlet ignite, setting the house on fire, destroying your home. It's a gamble, and with Alum wire, the odds are NOT in your favor. So, you might want to have some marshmallows handy to roast as your home burns to the ground. I have not addressed any possible electrocution issues in this reply. There really aren't any electrocution issues. No more so than with the stove that also uses a shared ground and neutral that is connected to it's metal case. And that is still code compliant as long as it was wired before the code changed. |
#18
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 03/11/2015 1:53 PM, trader_4 wrote:
On Wednesday, March 11, 2015 at 2:43:59 PM UTC-4, wrote: Consider this. The Microwave (MW) develops a problem, causing a dead short. There is no properly sized breaker to trip. Several things can happen. A dead short will trip the existing 40A or whatever breaker for the stove instantly. It's an overload that exceeds the wiring to the outlet, but not the breaker, ie the range of 15A or 20A to 40A, that would be the fire hazard from the wiring overheating. .... And, of course, while presuming 14ga/15A outlet, any load above that is in violation of Code, the actual breaker thermal trip level is generally about 5-7.5% _above_ the nominal breaker rating at which point the bimetallic strip opens so the actual load might be as much as 43A or so before the breaker itself saw the overload. But, mitigating that is that the actual current-carrying capacity of wiring or the outlet is quite a lot greater than that for which it is rated for Code application so there's quite a margin of safety before a real fire danger is present. I don't have the data at hand on what the temperature rise in a 14ga Cu would be in open air at 43A but it'll be warm...will it be fire-setting hot I don't know for certain. See the previous comment above as well...it certainly should be fixed but I don't believe it's an imminent hazard in the next 10 minutes. -- |
#19
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 03/11/2015 2:08 PM, Seymore4Head wrote:
On Wed, 11 Mar 2015 13:51:31 -0500, wrote: On 03/11/2015 2:43 PM, wrote: ... Consider this. The Microwave (MW) develops a problem, causing a dead short. There is no properly sized breaker to trip. ... A "dead short" will certainly trip even the 40A breaker instantly. The actual fire danger is, imo, quite low w/ the single device; where it would be a serious hazard from that standpoint would be multiple outlets where one could easily put a normal load that greatly exceeds the outlet/local wiring heating limits, but that isn't the case here of the single device. Is it right? No. Should it be corrected? Yes. But is it an _imminent,standing_ fire or safety hazard? No. Take a 20 A circuit in the kitchen. Each appliance used in the kitchen will normally max out the circuit. Is there a danger with only the microwave plugged in? Not normally. Plug a microwave and a deep fryer into the same outlet (on a 40A breaker). Fire hazard easily. That's the point though, there's only the one device here. -- |
#20
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 15:44:01 +0000, Chuck
wrote: replying to ShirtFree, Chuck wrote: ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? Thanks, guys, for all the input. There are no 120v devices on the stove (very cheap model). No clocks, outlets or the like. Strictly 240v heating elements. The house was constructed in the late 60's, early 70's (with aluminum wiring) and the kitchen "remodeling" was done in 2010, at which time the jerry rigged wiring was installed. I'm sure no permitting took place. And that outlet is probably wired with #12 or #14 wire, which is connected to a 40A or 50A breaker. And likely they have copper wire to the outlet connected to Alum wire, which is likely to corrode due to the dialectric action of different metals. Glad to learn about the extent and nature of the dangers, though. I will make sure that there is continuity in the ground between the stove and the distribution panel. I'm going to go with having a separate circuit installed as time and circumstances allow. What are you going to do, check the connections every day? I'd get that separate circuit installed THIS WEEK or sooner. PS The Anne Arundel County Fire Service was not interested in stationing fire fighters and equipment in the vicinity. The entire community has aluminum wiring and yet there have been no house fires that I am aware of. In that case, the whole house might burn to the ground. Your house could be the FIRST one to burn. Consider this. The Microwave (MW) develops a problem, causing a dead short. There is no properly sized breaker to trip. Several things can happen. If you're lucky. only the MW will be destroyed as smoke pours out of it, making it hard to breathe and sooting up the house, until it finally burns the internal wires and components enough to be disconnected from the power. -OR- If you're not so lucky, the unprotected #12 or #14 wires to that outlet ignite, setting the house on fire, destroying your home. It's a gamble, and with Alum wire, the odds are NOT in your favor. So, you might want to have some marshmallows handy to roast as your home burns to the ground. I have not addressed any possible electrocution issues in this reply. As another poster said "the person who wired that should be in jail". Thanks again to all of you for your help. |
#21
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 06:40:54 -0700 (PDT), TimR
wrote: My stove is old enough to be 3 wire, and it has an outlet for plugging in a coffee pot, microwave, etc. Stoves like that have an internal 15A or 20A fuse or breaker for those built in 120V devices. What the OP said, the outlet is wired directly to the RANGE outlet. THere is no smaller fuse or breaker. BIG DIFFERENCE! |
#22
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 15:44:01 +0000, Chuck
wrote: replying to ShirtFree, Chuck wrote: ShirtFree wrote: I have just discovered that our 120v microwave oven is tapped into the 240v stove circuit. The stove circuit is a two wire cable with ground, and the microwave is connected to one hot wire and the neutral is connected to the grounding wire of the stove circuit. I'm not an electrician, but I know intuitively this is not right. What is the major danger? Any ideas for a remedy? Thanks, guys, for all the input. There are no 120v devices on the stove (very cheap model). No clocks, outlets or the like. I never thought an outlet on the stove was a great idea. Eventually someone will turn the burner on when an electric cord is going over the burner. Strictly 240v heating elements. The house was constructed in the late 60's, early 70's (with aluminum wiring) and the kitchen "remodeling" was done in 2010, at which time the jerry rigged wiring was installed. I'm sure no permitting took place. Glad to learn about the extent and nature of the dangers, though. I will make sure that there is continuity in the ground between the stove and the distribution panel. I'm going to go with having a separate circuit installed as time and circumstances allow. PS The Anne Arundel County Fire Service was not interested in stationing I actually live in the next county (I think). fire fighters and equipment in the vicinity. The entire community has aluminum wiring and yet there have been no house fires that I am aware of. Thanks again to all of you for your help. |
#23
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 3/11/2015 4:34 PM, micky wrote:
I never thought an outlet on the stove was a great idea. Eventually someone will turn the burner on when an electric cord is going over the burner. Maybe we shouldn't put burners on the stove top because some dumbass democrat will burn themselves? And maybe limit the oven temp to 120F? |
#24
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wednesday, March 11, 2015 at 3:14:01 PM UTC-4, dpb wrote:
On 03/11/2015 1:53 PM, trader_4 wrote: On Wednesday, March 11, 2015 at 2:43:59 PM UTC-4, wrote: Consider this. The Microwave (MW) develops a problem, causing a dead short. There is no properly sized breaker to trip. Several things can happen. A dead short will trip the existing 40A or whatever breaker for the stove instantly. It's an overload that exceeds the wiring to the outlet, but not the breaker, ie the range of 15A or 20A to 40A, that would be the fire hazard from the wiring overheating. ... And, of course, while presuming 14ga/15A outlet, any load above that is in violation of Code, the actual breaker thermal trip level is generally about 5-7.5% _above_ the nominal breaker rating at which point the bimetallic strip opens so the actual load might be as much as 43A or so before the breaker itself saw the overload. But, mitigating that is that the actual current-carrying capacity of wiring or the outlet is quite a lot greater than that for which it is rated for Code application so there's quite a margin of safety before a real fire danger is present. I don't have the data at hand on what the temperature rise in a 14ga Cu would be in open air at 43A but it'll be warm...will it be fire-setting hot I don't know for certain. Copper 14g is 2.5 ohms per 1000 ft, or .0025 per ft. At 40 amps, I2R is 1600 x .0025, or 4 watts per foot. You have two conductors, so double that, 8W. 8W spread out over a foot of wire doesn't sound like a lot of heat to me either. Like you say, warm, but I doubt it would melt romex insulation. There is a lot of margin in the code. See the previous comment above as well...it certainly should be fixed but I don't believe it's an imminent hazard in the next 10 minutes. -- I agree, especially now that he knows not to plug another big load into that same receptacle with the microwave. |
#25
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 03/11/2015 4:34 PM, trader_4 wrote:
On Wednesday, March 11, 2015 at 3:14:01 PM UTC-4, dpb wrote: .... I don't have the data at hand on what the temperature rise in a 14ga Cu would be in open air at 43A but it'll be warm...will it be fire-setting hot I don't know for certain. Copper 14g is 2.5 ohms per 1000 ft, or .0025 per ft. At 40 amps, I2R is 1600 x .0025, or 4 watts per foot. You have two conductors, so double that, 8W. 8W spread out over a foot of wire doesn't sound like a lot of heat to me either. Like you say, warm, but I doubt it would melt romex insulation. There is a lot of margin in the code. .... Thanks for the update--I couldn't recall well enough to venture w/o looking it up and didn't want to take the time/effort at the time. Well, let's see if can do a little more on the temperature rise given the heat load... Well, shoot! Can't find in a quick search any specifically applicable heat transfer coefficients for romex so it'll have to wait until can find more time...by which time I'll likely have lost interest! -- |
#26
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On Wed, 11 Mar 2015 16:53:30 -0400, Dick
wrote: On 3/11/2015 4:34 PM, micky wrote: I never thought an outlet on the stove was a great idea. Eventually someone will turn the burner on when an electric cord is going over the burner. Maybe we shouldn't put burners on the stove top because some dumbass democrat will burn themselves? What does this have to do with Democrats? You need full-time therapy. And maybe limit the oven temp to 120F? |
#27
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 3/11/2015 3:43 PM, wrote:
On Wed, 11 Mar 2015 15:44:01 +0000, Chuck wrote: PS The Anne Arundel County Fire Service was not interested in stationing fire fighters and equipment in the vicinity. The entire community has aluminum wiring and yet there have been no house fires that I am aware of. In that case, the whole house might burn to the ground. Your house could be the FIRST one to burn. I have not addressed any possible electrocution issues in this reply. As another poster said "the person who wired that should be in jail". Another moaners hub poster, displaying intelligence. Yep, aluminum wiring and no problems. Yet. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#28
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
On 03/11/2015 5:13 PM, dpb wrote:
.... Well, let's see if can do a little more on the temperature rise given the heat load... Well, shoot! Can't find in a quick search any specifically applicable heat transfer coefficients for romex so it'll have to wait until can find more time...by which time I'll likely have lost interest! .... I've lost interest...but, I did find one study that bundled 12(!!!) various-sized cables from 14 to 10ga in a single bundle through a top plate hole as constricted as possible yet get them through it. They then powered each and every circuit to it's 80% rating by adjusting a bunch of resistance heat loads and watched. It raised the temperature to above the 90C (~200F) rating temperature after a period of several hours from which they concluded this was a bad idea and Code should prevent it! (DOH!) OBTW, this was on an experimental structure of a west-facing wall in the AZ desert at full summer sun... -- |
#29
Posted to alt.home.repair
|
|||
|
|||
Electrical Neutral Connected to Ground
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||