Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
The CT area is forecasted to have a blizzrd, with the possible loss of
prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? |
#2
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ |
#3
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 01/26/2015 10:03 AM, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? Sure, just disconnect the AC power wires and with a cord plug it into the generator output |
#4
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 11:03:57 AM UTC-5, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? There are several ways. Ranging from code compliant to a suicide cord. Given that it's already snowing, the code compliant method window has likely closed. I've used the latter method for an emergency. But then I know what I'm doing. After this event, instead of a secondary panel, I'd look into a lockout kit for your existing panel. Basically, you put an new breaker into the first slot of your panel, move whatever was there somewhere else. That breaker goes to an inlet. You can put the inlet outside, where the generator would be used or put it at the panel and use an extension cord. There is a lockout slide that prevents that breaker and the main breaker from being closed at the same time. Check for your panel to see if one is available from the manufacturer. If so, get it. If not, there is an aftermarket supplier: http://www.interlockkit.com/ The manufacturer supplied one is 100% code compliant. The latter is likely acceptable, but some AHJs might have a beef. Why anyone would put in another panel, move circuits over, etc, when using a manual type generator is beyond me. The above approach is low cost and allows you to run anything in the house, manage the load at the panel, etc. |
#5
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote:
On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. It's certainly not the worst thing I've ever seen and if he wants to do that for the storm, I don't see a problem with that. There are other people who have done it. Just that if he wants a long term solution, expects to pull a permit, which is probably required in CT, have it inspected, it may not pass. He could go ask the inspector. It's also likely to get flagged on a future home inspection for sale, etc. The correct way of doing it at the furnace is with a transfer switch and inlet. |
#6
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 10:28:46 AM UTC-6, trader_4 wrote:
What Rick outlines there is not code compliant. Safe, fast, easy...it may not be code but I have heard (yes, anecdotal) it has passed inspections. |
#7
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 11:03:57 AM UTC-5, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? Before I had my generator wired into the breaker box (with a shut-out of course) I had the furnace on a plug system. I put an outlet into the circuit box above the furnace and put a plug on the cord coming up from the furnace.. When the power went out, I switched from the house current plug to the generator plug right next to it. Not up to code or high tech, but it kept us warm through several power outages. Paul |
#8
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/26/2015 11:03 AM, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? Yes, there is. I agree, best wishes not losing power. - .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#9
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
trader_4 wrote in news:1079ab5c-256f-4167-8200-
: What Rick outlines there is not code compliant. Stick the code up your ass. |
#10
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
Per Dave C:
I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. How big is the gennie and how much current does your house "Cruise" on? Peak demands? If the gennie is small enough, consider a "Smart" transfer switch/secondary panel that can shut down circuit "A" temporarily while circuit "B" needs enough to otherwise overload the gennie. Our house cruises on 800-1200 watts and runs comfortably on a 2KW generator with a smart switch in control - as long as we delegate making coffee, running the toaster and such to little propane stoves on the patio. The smart switch kicks in when older refrigerators with very high starting surges need to start up. When that happens, lights go out in the rec room and the computer equipment runs on UPS backup for about five minutes. We recently got a second 2KW generator that can run in parallel with the first - more for redundancy than the added capacity - but when both are online we can make toast, make coffee, and run the big microwave oven. -- Pete Cresswell |
#11
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 1:03:58 PM UTC-5, Zak W wrote:
trader_4 wrote in news:1079ab5c-256f-4167-8200- : What Rick outlines there is not code compliant. Stick the code up your ass. What exactly is your problem? I didn't tell him what he should or shouldn't do. But whatever he decides, I don't see the issue with him knowing what code is, what the implications are, etc. He can use a suicide cord. He can wire up something permanent. But if he's going to do the latter at the furnace, it's better he know the code and then make a rational decision, rather than just go buy stuff and wing it. |
#12
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/26/2015 11:03 AM, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? I've done it with a hot-water boiler while I lived in Alaska. My little Honda 350W generator of the time was sufficient to run the circulator pump and the control stuff on the boiler. I just disconnected the power feed to the boiler, took an old extension cord and cut off the receptacle end and wired that to the wires to the boiler using wire nuts. Ran the extension cord outside the garage and plugged it into the generator and I was good to go. The house was pretty well insulated so I just ran the generator long enough to heat the house to 75-degrees and shut it down until it got down to 65-degrees and repeated the process until the power poles got put back up. I didn't even lose any of my tropical fish since I threw a heavy comforter over the aquarium to keep some of the heat in. |
#13
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/26/2015 11:39 AM, bob_villa wrote:
On Monday, January 26, 2015 at 10:28:46 AM UTC-6, trader_4 wrote: What Rick outlines there is not code compliant. Safe, fast, easy...it may not be code but I have heard (yes, anecdotal) it has passed inspections. Think neighbor did it the dumb way: http://diy.stackexchange.com/questio...ctrical-system He later got a transfer panel which is the way I did it. |
#14
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/26/2015 8:28 AM, trader_4 wrote:
On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote: On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. That was my interpretation of the code. So, I went down to the permit office and asked the inspector. His response was that he'd never heard of such restriction and it would be no problem. I would feel better if he'd acknowledged the code statements before telling me it was no problem. It's certainly not the worst thing I've ever seen and if he wants to do that for the storm, I don't see a problem with that. There are other people who have done it. Just that if he wants a long term solution, expects to pull a permit, which is probably required in CT, have it inspected, it may not pass. He could go ask the inspector. It's also likely to get flagged on a future home inspection for sale, etc. The correct way of doing it at the furnace is with a transfer switch and inlet. |
#15
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Mon, 26 Jan 2015 15:05:33 -0500, Frank
wrote: On 1/26/2015 11:39 AM, bob_villa wrote: On Monday, January 26, 2015 at 10:28:46 AM UTC-6, trader_4 wrote: What Rick outlines there is not code compliant. Safe, fast, easy...it may not be code but I have heard (yes, anecdotal) it has passed inspections. Think neighbor did it the dumb way: http://diy.stackexchange.com/questio...ctrical-system He later got a transfer panel which is the way I did it. Well, when I had my 2500 watt generator I added a receptacle to both the furnace and the freezer/refrigerator circuits and put the two circuits on one 220 volt pull-out (fuse panel). In case of a power failure I could pull the fuse block and plug the generator into one or the other with the suicide cord. |
#16
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Mon, 26 Jan 2015 15:38:00 -0800, mike wrote:
On 1/26/2015 8:28 AM, trader_4 wrote: On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote: On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. There is a way around it. Hardwire the furnace to a "disconnect device" - which is just a junction box with a cord mounted with a strain relief, which plugs into a SINGLE outlet, not a duplex - and you are code compliant. A twist lock lug is recommended. The single outlet is crucial to making it compliant as the furnace MUST be on a dedicated circuit. Another way to do it is with a 3 way switch, hooking the furnace Live connection to the center terminal, and line to one of the switched terminals, and a line to the generator "port" on the other switched terminal, with the neutral and the ground "T"d (joined with wire nuts) in the box. (not neutral to ground, but furnace to panel to gen port for both neutral and ground) That was my interpretation of the code. So, I went down to the permit office and asked the inspector. His response was that he'd never heard of such restriction and it would be no problem. I would feel better if he'd acknowledged the code statements before telling me it was no problem. It's certainly not the worst thing I've ever seen and if he wants to do that for the storm, I don't see a problem with that. There are other people who have done it. Just that if he wants a long term solution, expects to pull a permit, which is probably required in CT, have it inspected, it may not pass. He could go ask the inspector. It's also likely to get flagged on a future home inspection for sale, etc. The correct way of doing it at the furnace is with a transfer switch and inlet. |
#17
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/26/2015 6:38 PM, mike wrote:
That was my interpretation of the code. So, I went down to the permit office and asked the inspector. His response was that he'd never heard of such restriction and it would be no problem. I would feel better if he'd acknowledged the code statements before telling me it was no problem. Inspector told me same thing. His only recommendation was to use quality materials meaning don't buy the 19 cent plugs and receptacles at McHarbor Freight. |
#18
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
"mike" wrote in message ... On 1/26/2015 8:28 AM, trader_4 wrote: On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote: On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. That was my interpretation of the code. So, I went down to the permit office and asked the inspector. His response was that he'd never heard of such restriction and it would be no problem. I would feel better if he'd acknowledged the code statements before telling me it was no problem. I'd feel better if people in this thread would quote the actual code language they say allows or prohibits. |
#19
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
|
#20
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 8:02:07 PM UTC-5, wrote:
On Mon, 26 Jan 2015 15:38:00 -0800, mike wrote: On 1/26/2015 8:28 AM, trader_4 wrote: On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote: On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. There is a way around it. Hardwire the furnace to a "disconnect device" - which is just a junction box with a cord mounted with a strain relief, which plugs into a SINGLE outlet, not a duplex - and you are code compliant. A twist lock lug is recommended. The single outlet is crucial to making it compliant as the furnace MUST be on a dedicated circuit. Another way to do it is with a 3 way switch, hooking the furnace Live connection to the center terminal, and line to one of the switched terminals, and a line to the generator "port" on the other switched terminal, with the neutral and the ground "T"d (joined with wire nuts) in the box. (not neutral to ground, but furnace to panel to gen port for both neutral and ground) If by port you mean an inlet, then I agree, that is code compliant. Of course with less work you could install an interlock, breaker and the same inlet on the main panel and power not only the furnace, but anything else in the house too. |
#21
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 8:57:38 PM UTC-5, Pico Rico wrote:
"mike" wrote in message ... On 1/26/2015 8:28 AM, trader_4 wrote: On Monday, January 26, 2015 at 11:17:26 AM UTC-5, bob_villa wrote: On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote: The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? http://ricksdiy.com/general/wirefurnacetoagenerator/ What Rick outlines there is not code compliant. We've been through this many times here. Code says that the only appliances that can be used on a cord and plug are ones that are designed to be used that way to allow servicing. Furnaces don't meet that test. There isn't an install manual for a furnace I've ever seen that says you can put it on a plug and cord of your choosing. That was my interpretation of the code. So, I went down to the permit office and asked the inspector. His response was that he'd never heard of such restriction and it would be no problem. I would feel better if he'd acknowledged the code statements before telling me it was no problem. I'd feel better if people in this thread would quote the actual code language they say allows or prohibits. Here's a good discussion of the subject: http://ecmweb.com/code-basics/flexib...d-fixture-wire This is the most pertinent part: *Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connections [422.16], but only when used with attachment plugs [400.7(B)]. It's hard to argue that a furnace is designed to be readily removable for maintenance. Even worse, it's clearly not intended or identified for use with a cord and plug. But, as has been reported here and in the past, some AHJs are OK with it. |
#22
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Tue, 27 Jan 2015 04:57:31 -0500, Mik Dundee wrote:
On 01/26/2015 07:54 PM, wrote: Well, when I had my 2500 watt generator I added a receptacle to both the furnace and the freezer/refrigerator circuits and put the two circuits on one 220 volt pull-out (fuse panel). In case of a power failure I could pull the fuse block and plug the generator into one or the other with the suicide cord. Suicide cord? Really? It's often easier to do it right. Installed a Siemens interlock and 40A breaker for less than $60. Fr a 2500 watt generator? To operate only the furnace or the 'fridge? Se my other (safer) solution - 3 way switsh |
#23
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Tuesday, January 27, 2015 at 12:58:40 PM UTC-5, wrote:
On Tue, 27 Jan 2015 04:57:31 -0500, Mik Dundee wrote: On 01/26/2015 07:54 PM, wrote: Well, when I had my 2500 watt generator I added a receptacle to both the furnace and the freezer/refrigerator circuits and put the two circuits on one 220 volt pull-out (fuse panel). In case of a power failure I could pull the fuse block and plug the generator into one or the other with the suicide cord. Suicide cord? Really? It's often easier to do it right. Installed a Siemens interlock and 40A breaker for less than $60. Fr a 2500 watt generator? To operate only the furnace or the 'fridge? Se my other (safer) solution - 3 way switsh Who says you have to be limited to a 2500 watt generator? And even if you are, the work to install the breaker and interlock is the same, or less than installing a transfer switch at the furnace. And with the interlock at the panel, you can power anything you want in the house, within the 2500 watt limit, or whatever the generator capability is. You can power up the commonly used outlets, so you can plug in your phone, watch TV. You can power up the bathrooms, so you can see to pee. You can power up all the light circuits in the whole house, and just turn the lights on that you need, when you're in that area. Power up the fridge, so your beer stays cold. Power up the garage doors, so you can open them. I'd say that beats just powering the furnace and screwing around with extension cords. One extension cord to an inlet at the panel, power anything you choose. |
#24
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Monday, January 26, 2015 at 10:03:57 AM UTC-6, Dave C wrote:
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? Let's keep it simple and not a bitch match...we want to keep the kids warm and the pipes from freezing, K? Put a salvaged power cord on your furnace...this is an emergency and you don't have time to wire the entire house! |
#25
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
Zak W wrote:
trader_4 wrote in news:1079ab5c-256f-4167-8200- : What Rick outlines there is not code compliant. Stick the code up your ass. And when his insurance refuses to cover his house burning down? |
#26
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
Dave C posted for all of us...
The CT area is forecasted to have a blizzrd, with the possible loss of prime power. My question: I have bought a gas powered generator, as a Back Up. I will, later, install a secondary breaker panel - for use under generator power. That seconadry panel would provide power to our key circuiots, including the furnace. In the interim, is there a way I can power our nat gas furnace electronics, from our BU generator. Hopefully we will not lose power??? This is what; the fifth time this has been asked this month? DAGS -- Tekkie *Please post a follow-up* |
#27
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
Per Tekkie®:
Hopefully we will not lose power??? This is what; the fifth time this has been asked this month? DAGS The thread-starter was on 1/26.... They could have that cutover switch installed by now. -- Pete Cresswell |
#28
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/29/2015 8:05 PM, Bob F wrote:
Zak W wrote: trader_4 wrote in news:1079ab5c-256f-4167-8200- : What Rick outlines there is not code compliant. Stick the code up your ass. And when his insurance refuses to cover his house burning down? Yah, that's when the insurance company sticks their dick in the policy holder's ass. |
#29
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 01/27/2015 01:14 PM, trader_4 wrote:
Power up the fridge, so your beer stays cold. #1 reason to install a power inlet and interlock breaker. |
#30
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 1/30/2015 4:01 PM, (PeteCresswell) wrote:
Per Tekkie®: Hopefully we will not lose power??? This is what; the fifth time this has been asked this month? DAGS The thread-starter was on 1/26.... They could have that cutover switch installed by now. If it has not been done, try this: http://www.interlockkit.com/ It is a mechanical interlock for your existing panel. It allows you to choose which circuits to power or not power. And, if you google "breaker panel transfer interlock" there seems to be others. Nice thing is that you don't have to rewire everything. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com |
#31
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Saturday, January 31, 2015 at 1:32:42 PM UTC-5, Art Todesco wrote:
On 1/30/2015 4:01 PM, (PeteCresswell) wrote: Per Tekkie®: Hopefully we will not lose power??? This is what; the fifth time this has been asked this month? DAGS The thread-starter was on 1/26.... They could have that cutover switch installed by now. If it has not been done, try this: http://www.interlockkit.com/ It is a mechanical interlock for your existing panel. It allows you to choose which circuits to power or not power. And, if you google "breaker panel transfer interlock" there seems to be others. Nice thing is that you don't have to rewire everything. I suggested that from day one, but we never heard back from the OP. My first choice would be one from the panel manufacturer though, because there are no issues about it being listed, code compliant when used with that main panel, etc. If not available, then the Interlockit would be my second choice. The key to the approach is exactly what you said, which is with the slide, an additional breaker and an inlet, you can power anything in the house, manage the loads from the main panel. It's not much different work than putting in a double throw switch arrangement at the furnace, but the resulting benefits sure are. |
#32
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
Feeding the house is nice, with a safe interlock of course.
The only down side i have seen is that it is hard to Know when the grid power comes back on. You have to keep an eye on the neighbors house. Anybody have a solution to that one? Mark |
#33
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
|
#34
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Sunday, February 1, 2015 at 8:16:38 AM UTC-5, wrote:
Feeding the house is nice, with a safe interlock of course. The only down side i have seen is that it is hard to Know when the grid power comes back on. You have to keep an eye on the neighbors house. Anybody have a solution to that one? Mark The power company here, when you call to report an outage, let's you put in a phone # or text where they will notify you when it's back on. Couple times I used it, it worked, and it's great because you can be anywhere, but I'm sure it's far from perfect. They also give estimates of how long until it's restored, and that's been in the ballpark too. I can also see a street light, have used that too, but you have to actively check. |
#35
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
wrote in message ... Feeding the house is nice, with a safe interlock of course. The only down side i have seen is that it is hard to Know when the grid power comes back on. You have to keep an eye on the neighbors house. Anybody have a solution to that one? Mark I had an electrician add a fused switch directly to the utility lines, before the transfer switch. When power goes out and we work the transfer switch, we turn on the "utility power indicator light" and keep an eye on it for when it comes on with utility power. We used a "plug fuse box cover": http://www.grainger.com/product/BUSSMANN-Box-Cover-1DH49?s_pp=false&picUrl=//static.grainger.com/rp/s/is/image/Grainger/1DH49_AS01?$smthumb$ |
#36
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
|
#37
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On Sunday, February 1, 2015 at 3:32:16 PM UTC-5, wrote:
On Sun, 1 Feb 2015 05:16:34 -0800 (PST), wrote: Feeding the house is nice, with a safe interlock of course. The only down side i have seen is that it is hard to Know when the grid power comes back on. You have to keep an eye on the neighbors house. Anybody have a solution to that one? Mark There are powerline monitors made for exactly that purpose. Reliance electric "powerback" THP108. About $40 at Home Despot. That looks like a great find. The only drawback I see is that to install it, you have to wrap the sensing wire around one of the hot legs which is right before the main breaker and always hot, unless you call the utility to cut off power at the meter. One thing I don't understand. In the install instructions, after it's installed, it says to: 1 - Turn the PowerBack on/off switch to on, the alarm will sound 2 - Turn the main breaker to the off position, the alarm will cease. http://www.homedepot.com/catalog/pdf...b1bda64a15.pdf How is #2 possible? With the main breaker on or off, there is still voltage present on the service before the main breaker. I don't see why the main breaker would have an effect. And even more bizarre, the whole purpose of the alarm is to sound when power is present and the main breaker is off. Am I missing something or do they have something screwed up here? |
#38
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
"trader_4" wrote in message ... On Sunday, February 1, 2015 at 3:32:16 PM UTC-5, wrote: On Sun, 1 Feb 2015 05:16:34 -0800 (PST), wrote: Feeding the house is nice, with a safe interlock of course. The only down side i have seen is that it is hard to Know when the grid power comes back on. You have to keep an eye on the neighbors house. Anybody have a solution to that one? Mark There are powerline monitors made for exactly that purpose. Reliance electric "powerback" THP108. About $40 at Home Despot. That looks like a great find. The only drawback I see is that to install it, you have to wrap the sensing wire around one of the hot legs which is right before the main breaker and always hot, unless you call the utility to cut off power at the meter. Just be careful. Insulated wires are insulated. One thing I don't understand. In the install instructions, after it's installed, it says to: 1 - Turn the PowerBack on/off switch to on, the alarm will sound 2 - Turn the main breaker to the off position, the alarm will cease. http://www.homedepot.com/catalog/pdf...b1bda64a15.pdf How is #2 possible? With the main breaker on or off, there is still voltage present on the service before the main breaker. I don't see why the main breaker would have an effect. And even more bizarre, the whole purpose of the alarm is to sound when power is present and the main breaker is off. Am I missing something or do they have something screwed up here? "When the main circuit breaker in a generator-ready load center, manual transfer panel or other panel, must be turned OFF during a power outage, in order for a standby generator to supply power to emergency circuits, the PowerBACK will sound a 100dB audible alert as soon as utility power is restored." http://www.readbag.com/reliancecontr...ll-sheet-final Poorly written, but they must mean turn off whatever removes utility power from your panel. I would think that would be the transfer switch. Or it could be a main switch/breaker that will not be fed by your generator. I still like my solution better. |
#39
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
On 2/1/2015 4:43 PM, trader_4 wrote:
On Sunday, February 1, 2015 at 3:32:16 PM UTC-5, wrote: On Sun, 1 Feb 2015 05:16:34 -0800 (PST), wrote: One thing I don't understand. In the install instructions, after it's installed, it says to: 1 - Turn the PowerBack on/off switch to on, the alarm will sound 2 - Turn the main breaker to the off position, the alarm will cease. http://www.homedepot.com/catalog/pdf...b1bda64a15.pdf How is #2 possible? With the main breaker on or off, there is still voltage present on the service before the main breaker. I don't see why the main breaker would have an effect. And even more bizarre, the whole purpose of the alarm is to sound when power is present and the main breaker is off. Am I missing something or do they have something screwed up here? I think the testing protocol works because the antenna is wrapped around one of the hot wires and is also grounded. As the antenna detects current FLOW when the utility power is on line, you "fool" it into believing the line is dead by opening the main breaker. (Remember, this is not for an interlock type setup, but rather a transfer panel) Since with the transfer panel you will only be energizing certain circuits, the other breakers are closed as is the Main when the power goes out. When utility power is restored, there will be flow that is detected by the antenna and... Neat little device. |
#40
Posted to alt.home.repair
|
|||
|
|||
Furnace Power, from a Generator
"Unquestionably Confused" wrote in message ... On 2/1/2015 4:43 PM, trader_4 wrote: On Sunday, February 1, 2015 at 3:32:16 PM UTC-5, wrote: On Sun, 1 Feb 2015 05:16:34 -0800 (PST), wrote: One thing I don't understand. In the install instructions, after it's installed, it says to: 1 - Turn the PowerBack on/off switch to on, the alarm will sound 2 - Turn the main breaker to the off position, the alarm will cease. http://www.homedepot.com/catalog/pdf...b1bda64a15.pdf How is #2 possible? With the main breaker on or off, there is still voltage present on the service before the main breaker. I don't see why the main breaker would have an effect. And even more bizarre, the whole purpose of the alarm is to sound when power is present and the main breaker is off. Am I missing something or do they have something screwed up here? I think the testing protocol works because the antenna is wrapped around one of the hot wires and is also grounded. As the antenna detects current FLOW when the utility power is on line, you "fool" it into believing the line is dead by opening the main breaker. (Remember, this is not for an interlock type setup, but rather a transfer panel) Since with the transfer panel you will only be energizing certain circuits, the other breakers are closed as is the Main when the power goes out. When utility power is restored, there will be flow that is detected by the antenna and... I don't think so. I think it detects the presence of voltage, not current, regardless of what it says. Otherwise it would be of no use to many transfer switches which disconnect the utility completely and put the generator in its place. wait: see, I was right! "When the power indicator wire senses an electromagnetic field from a voltage at the supply wire, the power indicator provides an appropriate audio and/or visual alert signaling that primary power is available at the load center." patft.uspto.gov/netacgi/nph-Parser?Sect1=PTO2&Sect2=HITOFF&p=1&u=%2Fnetahtml%2 FPTO%2Fsearch-bool.html&r=17&f=G&l=50&co1=AND&d=PTXT&s1="relianc e+controls".ASNM.&OS=AN/"reliance+controls"&RS=AN/"reliance+controls" |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Power Generator Question | Home Repair | |||
Generator 1 / Power cut 0 | UK diy | |||
Gas Generator Sets, Diesel Generator Sets, Gas Turbines and Power Plants | UK diy | |||
Generator question - no power | Home Repair | |||
Generator Power Shedding? | Home Repair |