When the phone company installed my outdoor phone connection box, they
installed a separate ground rod. But the one for my electric panel is
50 feet away. I'm running my own phone line from my house to another
building at quite a distance. I intend to install another outdoor box
with built in lightning protection. (same as the one from the phone
company). The ground rod from my electric service is 6 feet away. Is
there any reason not to use the same rod? It dont seem to make much
sense to drive in another rod.

Note: I intend to also ground a tv antenna to it.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,029
Default Grounding a telephone line.

On Wednesday, November 27, 2013 9:14:26 PM UTC-6, wrote:
When the phone company installed my outdoor phone connection box, they installed a separate ground rod. But the one for my electric panel is 50 feet away. I'm running my own phone line from my house to another building at quite a distance. I intend to install another outdoor box with built in lightning protection. (same as the one from the phone company). The ground rod from my electric service is 6 feet away. Is there any reason not to use the same rod? It dont seem to make much sense to drive in another rod. Note: I intend to also ground a tv antenna to it.


Only thing that concerns me would be if there was a nearby lightning strike and the ground potential between the two ground locations differed by several hundres volts for the duration of the strike. I am not sure what would happen in terms of ground loop currents if the protectors broke down, but at different voltages. That would put both of the two telephone conductors (tip and ring) at widely different voltages at the two locations, and there would be a huge current flow between the two protectors through the telephone lines. I think it might be better to only ground at the first point of entrance, which is already grounded.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 302
Default Grounding a telephone line.

On Wed, 27 Nov 2013 23:46:37 -0500, wrote:

On Wed, 27 Nov 2013 21:14:26 -0600,
wrote:

When the phone company installed my outdoor phone connection box, they
installed a separate ground rod. But the one for my electric panel is
50 feet away. I'm running my own phone line from my house to another
building at quite a distance. I intend to install another outdoor box
with built in lightning protection. (same as the one from the phone
company). The ground rod from my electric service is 6 feet away. Is
there any reason not to use the same rod? It dont seem to make much
sense to drive in another rod.

Note: I intend to also ground a tv antenna to it.


The NEC requires that ALL ground electrodes must be bonded together.
It is also the recommended practice for lightning protection.
If line powered telephone equipment is the only place here this bond
occurs (incidently) that will be where any difference is reconciled.
Back in the modem days, separate grounding systems was the most common
cause of smoking modems PCs etc

The same is true of satellite installations. They usually drive a
separate rod. You should bond this to your grounding electrode system
for the service.


In that case, I may as well just use the same ground rod.

And since you mentioned the modems, as I said in my original post, the
phone line ground rod is 50 ft from the power ground rod. Being rural,
my only option for internet is a dialup modem, or spending a fortune on
satellite dish internet, which will force me to have satellite tv, and I
dont watch much tv. Every year I lose at least one modem from
lightning, even if the lightning is miles away. I've partly solved that
by unplugging the phone line from the modem when I'm offline. Maybe
that separate ground is why???? Cuz my phone lines are still wire and
underground.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Grounding a telephone line.

On Thursday, November 28, 2013 3:56:46 AM UTC-5, wrote:
On Wed, 27 Nov 2013 23:46:37 -0500, wrote:



On Wed, 27 Nov 2013 21:14:26 -0600,
wrote:



When the phone company installed my outdoor phone connection box, they


installed a separate ground rod. But the one for my electric panel is


50 feet away. I'm running my own phone line from my house to another


building at quite a distance. I intend to install another outdoor box


with built in lightning protection. (same as the one from the phone


company). The ground rod from my electric service is 6 feet away. Is


there any reason not to use the same rod? It dont seem to make much


sense to drive in another rod.




Note: I intend to also ground a tv antenna to it.




The NEC requires that ALL ground electrodes must be bonded together.


It is also the recommended practice for lightning protection.


If line powered telephone equipment is the only place here this bond


occurs (incidently) that will be where any difference is reconciled.


Back in the modem days, separate grounding systems was the most common


cause of smoking modems PCs etc




The same is true of satellite installations. They usually drive a


separate rod. You should bond this to your grounding electrode system


for the service.




In that case, I may as well just use the same ground rod.



That's how it's done in current code. An inter-system bonding
termination block is installed by the panel. It's connected
to the ground system for the panel and usually phone, cable, etc
are brought in near there and tied to it. If they can't be
brought in nearby, then they can be grounded elsewhere, but
that ground is then still supposed to be bonded back to the main ground
system for the building.




And since you mentioned the modems, as I said in my original post, the

phone line ground rod is 50 ft from the power ground rod. Being rural,

my only option for internet is a dialup modem, or spending a fortune on

satellite dish internet, which will force me to have satellite tv, and I

dont watch much tv. Every year I lose at least one modem from

lightning, even if the lightning is miles away. I've partly solved that

by unplugging the phone line from the modem when I'm offline. Maybe

that separate ground is why???? Cuz my phone lines are still wire and

underground.


Yes, if that's a seperate ground rod and not bonded to the
building system, you could have a big potential difference with
a lightning surge.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Grounding a telephone line.

On 11/27/2013 10:46 PM, wrote:
On Wed, 27 Nov 2013 21:14:26 -0600,
wrote:

When the phone company installed my outdoor phone connection box, they
installed a separate ground rod. But the one for my electric panel is
50 feet away. I'm running my own phone line from my house to another
building at quite a distance. I intend to install another outdoor box
with built in lightning protection. (same as the one from the phone
company). The ground rod from my electric service is 6 feet away. Is
there any reason not to use the same rod? It dont seem to make much
sense to drive in another rod.

Note: I intend to also ground a tv antenna to it.


The NEC requires that ALL ground electrodes must be bonded together.
It is also the recommended practice for lightning protection.
If line powered telephone equipment is the only place here this bond
occurs (incidently) that will be where any difference is reconciled.
Back in the modem days, separate grounding systems was the most common
cause of smoking modems PCs etc

The same is true of satellite installations. They usually drive a
separate rod. You should bond this to your grounding electrode system
for the service.


This is a major point for protecting equipment.

You want a single earthing system with a single connection to the house,
and short wires from entrance protectors to that earthing system.

During an "event" the ground rod 50 ft away may be many thousands of
volts different from the house. That voltage shows up at equipment
connected to both phone and power. I would put a second phone entry
protector at the house and connect it to the house earthing system.
There is no direct connection from protectors to the phone wires so
there should be no noise introduced.

Bonding the rod 50 ft away doesn't work as well as you might think. You
could have a relatively large current through the bond wire during an
"event" since that ground rod is part of the earthing system. Lightning
has relatively high frequency components, so the inductance of the wire
is more important than the resistance. The inductance doesn't decrease
very fast as you increase the wire size.

  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Grounding a telephone line.

On Thursday, November 28, 2013 12:30:46 PM UTC-5, wrote:
On Thu, 28 Nov 2013 02:56:46 -0600, wrote:



On Wed, 27 Nov 2013 23:46:37 -0500,
wrote:



On Wed, 27 Nov 2013 21:14:26 -0600,
wrote:



When the phone company installed my outdoor phone connection box, they


installed a separate ground rod. But the one for my electric panel is


50 feet away. I'm running my own phone line from my house to another


building at quite a distance. I intend to install another outdoor box


with built in lightning protection. (same as the one from the phone


company). The ground rod from my electric service is 6 feet away. Is


there any reason not to use the same rod? It dont seem to make much


sense to drive in another rod.




Note: I intend to also ground a tv antenna to it.




The NEC requires that ALL ground electrodes must be bonded together.


It is also the recommended practice for lightning protection.


If line powered telephone equipment is the only place here this bond


occurs (incidently) that will be where any difference is reconciled.


Back in the modem days, separate grounding systems was the most common


cause of smoking modems PCs etc




The same is true of satellite installations. They usually drive a


separate rod. You should bond this to your grounding electrode system


for the service.




In that case, I may as well just use the same ground rod.




And since you mentioned the modems, as I said in my original post, the


phone line ground rod is 50 ft from the power ground rod. Being rural,


my only option for internet is a dialup modem, or spending a fortune on


satellite dish internet, which will force me to have satellite tv, and I


dont watch much tv. Every year I lose at least one modem from


lightning, even if the lightning is miles away. I've partly solved that


by unplugging the phone line from the modem when I'm offline. Maybe


that separate ground is why???? Cuz my phone lines are still wire and


underground.




Another important thing is a point of use protector at the PC that

picks up the phone line and power, sinking them to a common point.

That is in addition to a panel protector and the protection the phone

company has.although phone protectors are usually pretty lousy. If it

is a carbon element protector it is useless



Any predicitions on how soon we'll be hearing from Tom?
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 22,192
Default Grounding a telephone line.

On Thu, 28 Nov 2013 10:10:44 -0800 (PST), "
wrote:

Any predicitions on how soon we'll be hearing from Tom?


:-\
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,463
Default Grounding a telephone line.

On 11/27/2013 9:14 PM, wrote:
When the phone company installed my outdoor phone connection box,
they installed a separate ground rod. But the one for my electric
panel is 50 feet away. I'm running my own phone line from my house
to another building at quite a distance. I intend to install another
outdoor box with built in lightning protection. (same as the one
from the phone company). The ground rod from my electric service is
6 feet away. Is there any reason not to use the same rod? It dont
seem to make much sense to drive in another rod.

Note: I intend to also ground a tv antenna to it.


You don't ground the phone line, you ground the lightning protector. The
protector technology has changed over the years but neither side of the
phone lines is ever tied to ground. The wires are designated "Tip and
Ring" with a standard color code of green for Tip and red for Ring.
This comes from the old days when an operator actually made connections
at a switchboard by manually plugging in a "phone plug" then flipping a
switch to ring the phone at the other end. Tip is the tip of the phone
plug and Ring is the ring around the shaft of the phone plug, much like
the 1/4" plug on a big set of stereo headphones. Anyway, there is a
separate surge arresting element connected from Tip and Ring to ground.
The elements have changed over the years from a carbon resistor or spark
gap to gas tube elements and now solid state elements that conduct
whenever a voltage surge comes in over either side of the phone line
pair. I know this stuff because I've had to argue with the phone company
when my customer's phone line is dead and there is nothing wrong with
the inside wiring of the building. Often lightning will burn out a
switching module of the switch at the phone company's central office
that serves that particular customer. I've had to add extra lightning
protection at commercial customer's locations because lightning was
damaging the multi line phone systems at their businesses. o_O

A very good source of parts and information about all things telephone
where I've purchased parts and systems:

http://www.sandman.com/

http://preview.tinyurl.com/k48cp4b

A lightning protector like what I picked up for a customer. This one has
gas tube modules which are replaceable by plugging in a new one:

http://preview.tinyurl.com/leo22nu

The same base but equipped with delta modules which are a hybrid of gas
tube and solid state elements. The modules are interchangeable:

http://preview.tinyurl.com/l8pauwm

TDD


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Telephone line troubleshooting PaulD Home Repair 26 December 23rd 07 07:23 PM
Noise in Telephone Line malam Home Repair 12 September 19th 06 03:41 AM
telephone twin line martin.shaw11 UK diy 5 April 2nd 05 12:41 AM
Telephone Line 1/ 2 barry martin Home Repair 0 March 8th 04 07:49 PM
Too many devices on telephone line Morgan Home Repair 8 July 1st 03 12:54 AM


All times are GMT +1. The time now is 03:46 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"