Intermittent Furnace Problem--Shutting Down, Won't Reignite
The electric ignitor always starts up correctly (it's not a spark
igniter, it's more like a glow plug). Sometimes the solenoid for the the gas valve opens and the burners ignite the main blower comes on and it works fine for about five minutes. Even when this all works properly, after about five minutes of heating the burners go out, then the controller tries four times to light them. When the burners go out, the 24V on the gas valve connections goes away so the gas valve closes. But when the controller tries to restart the burners, the ingiter does come on, then there is 24V on the gas valve, but the gas valve doesn't open (at least I don't smell gas) and the burners don't ignite. What is it that is tripping and thinking that the gas needs to be shut down in the first place? Why doesn't the gas turn back on when the 24V is on the gas valve terminals? I don't think it's the flame sensor, because the gas should come on when the burners try to be ignited then the controller only turns off the gas if the flame sensor doesn't detect a flame. The draft inducer motor runs fine, and pulling off the hose, there is air coming out. I bypassed the pressure sensing switch (you have to have in open in order for the system to start, then closed once the draft inducer is running) to see if it was failing, and even with it bypassed the gas still shuts off long before the thermostat temperature is reached. I bypassed the three firebox flame-out sensors (one by one) and it didn't help (I did not try bypassing all three at a time). Any ideas? I would say it's the gas valve but since it works fine, one time, I wonder how likely intermittent operation is. The flashing trouble code LED just indicates "fail to ignite," and indicates that the trouble could be the gas valve, the gas pressure from the supply, or the flame sensor. It's an old Sears Furnace, probably 25 years old. I can't find the model number anywhere. The gas valve is a White-Rodgers 36E36 227. How hard is it to replace these. It looks like just removing the pipes from the gas supply and the manifold. I'm just worried about damaging the manifold if it's really tight. |
#2
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
SMS wrote: The electric ignitor always starts up correctly (it's not a spark igniter, it's more like a glow plug). Sometimes the solenoid for the the gas valve opens and the burners ignite the main blower comes on and it works fine for about five minutes. Even when this all works properly, after about five minutes of heating the burners go out, then the controller tries four times to light them. When the burners go out, the 24V on the gas valve connections goes away so the gas valve closes. But when the controller tries to restart the burners, the ingiter does come on, then there is 24V on the gas valve, but the gas valve doesn't open (at least I don't smell gas) and the burners don't ignite. What is it that is tripping and thinking that the gas needs to be shut down in the first place? Why doesn't the gas turn back on when the 24V is on the gas valve terminals? I don't think it's the flame sensor, because the gas should come on when the burners try to be ignited then the controller only turns off the gas if the flame sensor doesn't detect a flame. The draft inducer motor runs fine, and pulling off the hose, there is air coming out. I bypassed the pressure sensing switch (you have to have in open in order for the system to start, then closed once the draft inducer is running) to see if it was failing, and even with it bypassed the gas still shuts off long before the thermostat temperature is reached. I bypassed the three firebox flame-out sensors (one by one) and it didn't help (I did not try bypassing all three at a time). Any ideas? I would say it's the gas valve but since it works fine, one time, I wonder how likely intermittent operation is. The flashing trouble code LED just indicates "fail to ignite," and indicates that the trouble could be the gas valve, the gas pressure from the supply, or the flame sensor. It's an old Sears Furnace, probably 25 years old. I can't find the model number anywhere. The gas valve is a White-Rodgers 36E36 227. How hard is it to replace these. It looks like just removing the pipes from the gas supply and the manifold. I'm just worried about damaging the manifold if it's really tight. Hi, Doee the furnace have a flame sensor? Then that is prime suspect. Clean it and try again. Furnace usually goes into lock up mode when it fails to stay running after ignition(safety issue). It usually stay locked up an hour or two. If you want to reset it turn the power on/off. No blinking LED indicator to spell out the trouble code? |
#3
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On 11/11/2012 6:49 PM, Tony Hwang wrote:
Hi, Doee the furnace have a flame sensor? Then that is prime suspect. Clean it and try again. Furnace usually goes into lock up mode when it fails to stay running after ignition(safety issue). It usually stay locked up an hour or two. If you want to reset it turn the power on/off. No blinking LED indicator to spell out the trouble code? As I wrote above, The flashing trouble code LED just indicates "fail to ignite," and indicates that the trouble could be the gas valve, the gas pressure from the supply, or the flame sensor. A bad flame sensor would not stop the burners from igniting, it would just shut them down when the controller looked at the flame sensor and didn't see an indication that the flame was present (I've had that happen on a water heater). As I understand the operation, the controller checks the flame sensor maybe 5-10 seconds _after_ the gas valve opens and the burners light (to give some time for the flame to heat up the sensor). But in this case the gas valve doesn't open to start the flame. So yes, it's almost certainly the flame sensor that's the reason the system shuts down, but the reason there's no flame is because the gas valve isn't opening. I do see the controller trying to open the gas valve (24V on the gas valve terminals) but there is no gas. Things I tried: Ignite the flame manually in case the glow plug ignitor wasn't hot enough. No effect because I don't think the gas is on. Checked that the gas valve is getting 24V shortly after the glow plug ignitor is ready. The valve is getting 24V. The main solenoid coil is energized (can feel the magnetic force when it gets 24V). I can't feel anything on the secondary solenoid. Checked that none of the flame-out sensors or pressure switch sensor was tripped (but this is obviously the case since the controller would not even try to energize the gas valve if any sensor was tripped). I'm pretty sure that it's a flaky gas valve. One HVAC tech wrote: "Make sure you have a 24 volt signal to the gas valve terminals. If you do and it doesn't light, the gas valve is bad." This is exactly what is happening. |
#4
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
|
#5
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On 11/12/2012 9:27 AM, SMS wrote:
On 11/12/2012 5:20 AM, wrote: Given the above and the other symptoms, I would suspect either a bad gas valve or some kind of blockage in the gas lines. With the similar gas valves I've had, you could also hear it click when energized. If the valve is failing, but not completely shot, it may open sometimes, then later perhaps warm up, go open, causing the gas to then shut off again. The thing I don't understand is why the gas valve opens before the I mean "...why the gas valve closes..." thermostat temperature is reached. I suspect that the solenoid is occasionally able to open the valve but then as it heats up it releases it, then the flame goes out and the flame sensor removes the 24V from the valve. But verifying this sequence is difficult. I hooked up two volt meters, one to the gas valve connection and one to the flame sensor in an attempt to see the sequence of things. 1. If the furnace is cold: The hot surface ignitor comes on 24V goes to the gas valve The gas valve opens The burners ignite The hot surface ignitor goes off The flame sensor goes high About five minutes later the gas valve closes and the flame sensor goes low, but I can't see which happens first with a volt meter (need a logic analyzer). 2. If the furnace is warm: The hot surface ignitor comes on 24V goes to the gas valve The gas valve opens The burners ignite The hot surface ignitor goes off A few seconds later the gas valve closes and the flame sensor goes low, but I can't see which happens first with a volt meter (need a logic analyzer). It seems to me that the gas valve is opening too soon after the burners ignite for it to be the flame sensor causing it to open; I don't know how many seconds the controller waits before looking at the flame sensor. 3. If the furnace is hot: The hot surface ignitor comes on 24V goes to the gas valve The gas valve doesn't open The burners don't ignite The flame sensor stays low The hot surface ignitor goes off A few seconds 24V is removed from the gas valve, presumably because the flame sensor doesn't detect a flame. It's number 3 that leads me to believe that it's got to be the gas valve. In this case the gas valve isn't opening at all even with 24V on it. |
#6
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On Nov 12, 12:27*pm, SMS wrote:
On 11/12/2012 5:20 AM, wrote: Given the above and the other symptoms, I would suspect either a bad gas valve or some kind of blockage in the gas lines. *With the similar gas valves I've had, you could also hear it click when energized. *If the valve is failing, but not completely shot, it may open sometimes, then later perhaps warm up, go open, causing the gas to then shut off again. The thing I don't understand is why the gas valve opens before the thermostat temperature is reached. I suspect that the solenoid is occasionally able to open the valve but then as it heats up it releases it, then the flame goes out and the flame sensor removes the 24V from the valve. But verifying this sequence is difficult. I hooked up two volt meters, one to the gas valve connection and one to the flame sensor in an attempt to see the sequence of things. 1. If the furnace is cold: The hot surface ignitor comes on 24V goes to the gas valve The gas valve opens The burners ignite The hot surface ignitor goes off The flame sensor goes high About five minutes later the gas valve closes and the flame sensor goes low, but I can't see which happens first with a volt meter (need a logic analyzer). 2. If the furnace is warm: The hot surface ignitor comes on 24V goes to the gas valve The gas valve opens The burners ignite The hot surface ignitor goes off A few seconds later the gas valve closes and the flame sensor goes low, but I can't see which happens first with a volt meter (need a logic analyzer). Yes, I see what you mean. You can''t see what happens first. You could connect a volt meter on the gas valve and then stand there and watch the fire. If the control circuitry is shutting off the gas for some reason, then you should see the voltage go away and the flame go out at the same time. If the gas valve is closing on it's own, then you might be able to see a couple seconds between the flame first going out, then the voltage on the gas valve going away as the controller senses no flame and cuts it off. Alternatively, if you suspect the gas valve is bad and the coil goes open after it gets warmed up after a bit, here is what I'd do. Close the gas shut-off valve to the furnace so no gas can flow. Then jumper 24V direct to the gas valve for 15 mins. Then remove the jumper, turn the gas back on and try to start the furnace. |
#7
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
|
#9
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On 11/12/2012 7:57 PM, SMS wrote:
On 11/12/2012 10:45 AM, wrote: Alternatively, if you suspect the gas valve is bad and the coil goes open after it gets warmed up after a bit, here is what I'd do. Close the gas shut-off valve to the furnace so no gas can flow. Then jumper 24V direct to the gas valve for 15 mins. Then remove the jumper, turn the gas back on and try to start the furnace. I did this (had to run to the surplus store for a transformer). They only had a 42V CT, so I got 21V or so, but that was enough for the 24V solenoid, and if it's a heat problem in the coil then the lower voltage means higher current so it should heat up even more. The valve opens and closes just fine. Even after 1/2 hour if I turn on the gas it flows through the valve. I connected the valve back to the control board and started the furnace and it started. It ran for about the same amount of time before the valve closed. Then the same symptom, the 24V goes onto the terminals of the valve but the it doesn't open. Perhaps it's a heat related problem. Oh, and even though maybe I shouldn't have done this, after the control board would no longer open the gas valve I turned on the furnace with the gas control valve connected to the external transformer, and when the ignitor came on I plugged it in to open the valve and ignite the burners. It didn't open and the burners didn't ignite. |
#10
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On 11/12/2012 8:19 PM, Ned Flanders wrote:
SMS wrote: On 11/12/2012 10:45 AM, wrote: Alternatively, if you suspect the gas valve is bad and the coil goes open after it gets warmed up after a bit, here is what I'd do. Close the gas shut-off valve to the furnace so no gas can flow. Then jumper 24V direct to the gas valve for 15 mins. Then remove the jumper, turn the gas back on and try to start the furnace. I did this (had to run to the surplus store for a transformer). They only had a 42V CT, so I got 21V or so, but that was enough for the 24V solenoid, and if it's a heat problem in the coil then the lower voltage means higher current so it should heat up even more. The valve opens and closes just fine. Even after 1/2 hour if I turn on the gas it flows through the valve. I connected the valve back to the control board and started the furnace and it started. It ran for about the same amount of time before the valve closed. Then the same symptom, the 24V goes onto the terminals of the valve but the it doesn't open. Perhaps it's a heat related problem. Assuming the filter is clean, I would open all of the registers to insure the problem is not being caused by reduced air flow causing overheating in the furnace... I'm pretty sure it is heat related since when the furnace is off and I apply power to the valve it works just fine and stays open indefinitely. Early on, I tried running the furnace without the filter for a cycle in case the filter was the problem (even though it's not dirty) no dice. A lot of the registers are closed off, but they've been closed for years without a problem, but I opened them to try that theory--no dice. When the gas valve doesn't open, I do hear the click of the relay on the control board, but not the thunk of the solenoid on the valve (and as I said the valve is getting 24VAC). Even applying 21V directly on the solenoid (after the hot glow ignitor comes on) doesn't activate the solenoid. |
#11
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On Nov 13, 6:19*am, SMS wrote:
On 11/12/2012 8:19 PM, Ned Flanders wrote: SMS wrote: On 11/12/2012 10:45 AM, wrote: Alternatively, if you suspect the gas valve is bad and the coil goes open after it gets warmed up after a bit, here is what I'd do. * Close the gas shut-off valve to the furnace so no gas can flow. * Then jumper 24V direct to the gas valve for 15 mins. * Then remove the jumper, turn the gas back on and try to start the furnace. I did this (had to run to the surplus store for a transformer). They only had a 42V CT, so I got 21V or so, but that was enough for the 24V solenoid, and if it's a heat problem in the coil then the lower voltage means higher current so it should heat up even more. The valve opens and closes just fine. Even after 1/2 hour if I turn on the gas it flows through the valve. I connected the valve back to the control board and started the furnace and it started. It ran for about the same amount of time before the valve closed. Then the same symptom, the 24V goes onto the terminals of the valve but the it doesn't open. Perhaps it's a heat related problem. Assuming the filter is clean, I would open all of the registers to insure the problem is not being caused by reduced air flow causing overheating in the furnace... I'm pretty sure it is heat related since when the furnace is off and I apply power to the valve it works just fine and stays open indefinitely. Early on, I tried running the furnace without the filter for a cycle in case the filter was the problem (even though it's not dirty) no dice. A lot of the registers are closed off, but they've been closed for years without a problem, but I opened them to try that theory--no dice. When the gas valve doesn't open, I do hear the click of the relay on the control board, but not the thunk of the solenoid on the valve (and as I said the valve is getting 24VAC). Even applying 21V directly on the solenoid (after the hot glow ignitor comes on) doesn't activate the solenoid.- Hide quoted text - - Show quoted text - Well from the above it would seem very clear to me. You have a bad gas valve. At times, it won't open or stay open with 24V directly on it. You've seen that with the votage applied both from the furnace control board and from your seperate experimental transformer. Has 24V and won't open = bad gas valve. And you know it's an opening issue at the valve, not a gas supply problem, because you say you also don't here the normal "thunk" sound of it opening. |
#12
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
|
#13
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
SMS wrote:
The electric ignitor always starts up correctly (it's not a spark igniter, it's more like a glow plug). Sometimes the solenoid for the the gas valve opens and the burners ignite the main blower comes on and it works fine for about five minutes. Even when this all works properly, after about five minutes of heating the burners go out, then the controller tries four times to light them. When the burners go out, the 24V on the gas valve connections goes away so the gas valve closes. But when the controller tries to restart the burners, the ingiter does come on, then there is 24V on the gas valve, but the gas valve doesn't open (at least I don't smell gas) and the burners don't ignite. What is it that is tripping and thinking that the gas needs to be shut down in the first place? Why doesn't the gas turn back on when the 24V is on the gas valve terminals? I don't think it's the flame sensor, because the gas should come on when the burners try to be ignited then the controller only turns off the gas if the flame sensor doesn't detect a flame. The draft inducer motor runs fine, and pulling off the hose, there is air coming out. I bypassed the pressure sensing switch (you have to have in open in order for the system to start, then closed once the draft inducer is running) to see if it was failing, and even with it bypassed the gas still shuts off long before the thermostat temperature is reached. I bypassed the three firebox flame-out sensors (one by one) and it didn't help (I did not try bypassing all three at a time). Any ideas? I would say it's the gas valve but since it works fine, one time, I wonder how likely intermittent operation is. The flashing trouble code LED just indicates "fail to ignite," and indicates that the trouble could be the gas valve, the gas pressure from the supply, or the flame sensor. It's an old Sears Furnace, probably 25 years old. I can't find the model number anywhere. The gas valve is a White-Rodgers 36E36 227. How hard is it to replace these. It looks like just removing the pipes from the gas supply and the manifold. I'm just worried about damaging the manifold if it's really tight. I wonder if it is the electric ignitor that is the problem, even though the ignitor glows and appears to be working. The reason that I wonder about that is that I had a similar problem with a gas oven that wouldn't heat up. The ignitor appeared to be working because it glowed when the oven was turned on. I did some Google searching and learned that even though the ignitor was glowing, it still could be the cause of the problem. At least with a gas oven, the ignitor has to allow a certain amount of current to go through before the gas valve will open up so the oven can be ignited. If a gas furnace has a similar setup (I don't know if it does), then maybe the ignitor is the problem -- despite any voltage readings that you may be getting. Apparently, it is not just voltage (in the case of a gas oven), but it also requires a certain amount of current (amperage) to be drawn before the gas valve will open or open fully. Here are two links about that in regard to gas ovens: http://www.applianceblog.com/mainfor...ont-light.html http://www.youtube.com/watch?v=zkV4Wj0klkQ Again, I don't know if a gas oven and a gas furnace have a similar setup, but I thought I'd pass this on in case it helps. I also just tried a little Google search regarding furnace ignitors and this link has a post by "Kokomo" that says the only way to test the furnace ignitor is by measuring the current (amperage) draw: http://www.doityourself.com/forum/ga...e-igniter.html . Good luck and let us know what the problem turns out to be. |
#14
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On Tue, 13 Nov 2012 18:06:11 -0500, "TomR" wrote:
Again, I don't know if a gas oven and a gas furnace have a similar setup, but I thought I'd pass this on in case it helps. My furnace looks for inducer negative pressure and ignitor glow before the gas valve opens. Then good flame sensor sensing keeps it open if flame is present. I've replaced an inducer pressure switch for no purpose at all. You can hear the switch close, and if the ignitor glows, it's okay. Mine is timed for about 30 seconds before the ignitor glows. I don't know how "glow" is detected by the circuitry, but I do know no glow, no gas valve open, because I've replaced an ignitor that didn't glow. Gas valve never opened.. But maybe there's other failure modes. And I know a bad/dirty/flaky flame sensor can shut the gas valve. Seen that happen too. Always immediately after flame ignition in my case. Pretty sure the gas valve has 2 steps. Low volume during the flame sensor check, then high volume and main blower kicks on. Been about 5 years since I've had a problem and actually looked at it. This is all start-up ciruit logic, and I have no idea about logic in effect during running operation. AFAIK my roll-out sensors have never been tested, so I don't know if they work. A good manual for the controls should tell you all this. I also have schematics in the furnace case, but don't know how to read them. I'm an electricity know-nothing. My furnace manual came with about 5 different possible control setups, so you have to get that right first. There's control board logic circuitry that can get messed up just like an automobile ECU. If you're guessing and confused, a pro will fix you up. |
#15
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
On Nov 13, 8:59*am, SMS wrote:
On 11/13/2012 4:58 AM, wrote: Well from the above it would seem very clear to me. You have a bad gas valve. *At times, it won't open or stay open with 24V directly on it. * You've seen that with the votage applied both from the furnace control board and from your seperate experimental transformer. Has 24V and won't open = bad gas valve. *And you know it's an opening issue at the valve, not a gas supply problem, *because you say you also don't here the normal "thunk" sound of it opening. I hate intermittent problems. if you apply THE CORRECT voltage directly to the valve coil and it doesn't open, it's bad.. check it with an Ohm meter, the coil could be open intermittently or there could be an intermittent short from the coil to the frame which might mess up the controller but not mess up your external test power source or the valve could stick mechanically in which case you won't see any problem with electrical tests you're not in Indianapolis by any chance? Mark |
#16
Posted to alt.home.repair
|
|||
|
|||
Intermittent Furnace Problem--Shutting Down, Won't Reignite
why does no one ever effing post when they have found the solution?!
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Furnace keeps shutting off | Home Repair | |||
Intermittent problem with (furnace) firing burners | Home Repair | |||
Intermittent heat problem with Rheem electric furnace | Home Repair | |||
Furnace blows but does not heat (intermittent problem) | Home Repair | |||
Intermittent problem with furnace | Home Repair |