Hey folks,

I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. I don't understand this
requirement. I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. I'm trying to understand this requirement but have not been
able to find anything online. Maybe the inspector thought I would be
running the horizontal run underground? Can anyone give me some
insight into this? A website or code section cite would be great.

Any help would be greatly appreciated.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default Code question - conduit from weatherhead to meter


"John" wrote in message
...
Hey folks,

I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. I don't understand this
requirement. I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. I'm trying to understand this requirement but have not been
able to find anything online. Maybe the inspector thought I would be
running the horizontal run underground? Can anyone give me some
insight into this? A website or code section cite would be great.

Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility companies
wires. There is probably a maximum distance the head can be from the point
of attachment. Call the guy back and get clarification. It does sound like
he misunderstood your intent


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Code question - conduit from weatherhead to meter

I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. I don't understand this
requirement. I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. I'm trying to understand this requirement but have not been
able to find anything online. Maybe the inspector thought I would be
running the horizontal run underground? Can anyone give me some
insight into this? A website or code section cite would be great.

Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be from
the point of attachment. Call the guy back and get clarification. It does
sound like he misunderstood your intent



*I agree with RBM. It doesn't sound as though concrete encasement is called
for, but Los Angeles has their own electrical code. I think the best thing
would be for you to take a photo of your house with the electrical service
path drawn onto the photo and bring it down to show an electrical inspector.
You could also consult with an electrical contractor.

I know one power company here in NJ frowns upon having an LB condulet before
the meter. They are afraid that someone could open the LB and tap into the
power before it gets metered.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,567
Default Code question - conduit from weatherhead to meter

On Apr 6, 7:55*am, "John Grabowski" wrote:
I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.


The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). *I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. *The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. *The
horizontal run of conduit would be something like 3-4' off the ground.


I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.


I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. *He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. *I don't understand this
requirement. *I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. *I'm trying to understand this requirement but have not been
able to find anything online. *Maybe the inspector thought I would be
running the horizontal run underground? *Can anyone give me some
insight into this? *A website or code section cite would be great.


Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be from
the point of attachment. Call the guy back and get clarification. It does
sound like he misunderstood your intent


*I agree with RBM. *It doesn't sound as though concrete encasement is called
for, but Los Angeles has their own electrical code. *I think the best thing
would be for you to take a photo of your house with the electrical service
path drawn onto the photo and bring it down to show an electrical inspector.
You could also consult with an electrical contractor.

I know one power company here in NJ frowns upon having an LB condulet before
the meter. *They are afraid that someone could open the LB and tap into the
power before it gets metered.- Hide quoted text -

- Show quoted text -


I think this is going to be an uphill battle for you. I'd take some
good pictures. Upload them and then draw my proposed conduit on them
using a picture editing tool. "Paint" will do. Then take a trip
downtoem to visit the inspector. CAll first and find out when they
are in the office and if an appointment is possible. Most have
regular office hours in the mornings before they go out for the day.
Once you get past them you still have to conveince the power company
it's ok. That will be easier if you have the local building authority
sold.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,106
Default Code question - conduit from weatherhead to meter

On Apr 6, 1:20*am, John wrote:
Hey folks,

I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). *I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. *The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. *The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. *He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. *I don't understand this
requirement. *I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. *I'm trying to understand this requirement but have not been
able to find anything online. *Maybe the inspector thought I would be
running the horizontal run underground? *Can anyone give me some
insight into this? *A website or code section cite would be great.

Any help would be greatly appreciated.



I think you are going and busting your own balls over a matter
of aesthetics modifying a rather simple straight pipe from the
weatherhead to the meter socket box because you don't like the
look of it...

Wow...

It is a pipe... Paint it... Get over yourself and let your
electrician
do it the easy way... Do you really want to have to submit plans
and have to wait for them to be approved ?

I haven't ever seen a service entry pipe buried inside the wall of
a house before... Maybe that is an LA thing but seems like a
lot of B.S. to go through... If you don't like wires and pipes coming
in
from above, ask the electric company if it is possible to do an
underground service feeder and then you would only see a few
feet of pipe coming up out of the ground feeding into the meter
box...

~~ Evan


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default Code question - conduit from weatherhead to meter


"John Grabowski" wrote in message
...
I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. I don't understand this
requirement. I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. I'm trying to understand this requirement but have not been
able to find anything online. Maybe the inspector thought I would be
running the horizontal run underground? Can anyone give me some
insight into this? A website or code section cite would be great.

Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be
from the point of attachment. Call the guy back and get clarification. It
does sound like he misunderstood your intent



*I agree with RBM. It doesn't sound as though concrete encasement is
called for, but Los Angeles has their own electrical code. I think the
best thing would be for you to take a photo of your house with the
electrical service path drawn onto the photo and bring it down to show an
electrical inspector. You could also consult with an electrical
contractor.

I know one power company here in NJ frowns upon having an LB condulet
before the meter. They are afraid that someone could open the LB and tap
into the power before it gets metered.


** The picture of 3- 2/0 bugs in a 2" condulet ain't a pretty one (lol)



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,538
Default Code question - conduit from weatherhead to meter

John wrote:
Hey folks,

I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.

The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. The
horizontal run of conduit would be something like 3-4' off the ground.

I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.

I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. I don't understand this
requirement. I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. I'm trying to understand this requirement but have not been
able to find anything online. Maybe the inspector thought I would be
running the horizontal run underground? Can anyone give me some
insight into this? A website or code section cite would be great.

Any help would be greatly appreciated.


Consider the solution to esthetic mistakes often used by architects:

Ivy.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,106
Default Code question - conduit from weatherhead to meter

On Apr 6, 6:14*pm, "RBM" wrote:
"John Grabowski" wrote in message

...



I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.


The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). *I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. *The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. *The
horizontal run of conduit would be something like 3-4' off the ground..


I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.


I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. *He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. *I don't understand this
requirement. *I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. *I'm trying to understand this requirement but have not been
able to find anything online. *Maybe the inspector thought I would be
running the horizontal run underground? *Can anyone give me some
insight into this? *A website or code section cite would be great.


Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be
from the point of attachment. Call the guy back and get clarification. It
does sound like he misunderstood your intent


*I agree with RBM. *It doesn't sound as though concrete encasement is
called for, but Los Angeles has their own electrical code. *I think the
best thing would be for you to take a photo of your house with the
electrical service path drawn onto the photo and bring it down to show an
electrical inspector. You could also consult with an electrical
contractor.


I know one power company here in NJ frowns upon having an LB condulet
before the meter. *They are afraid that someone could open the LB and tap
into the power before it gets metered.


** The picture of 3- 2/0 bugs in a 2" condulet ain't a pretty one (lol)




It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...

Its funny how people think that conduits and pipes for utility
services
are like tinker toys and "oh just move that out of where it can be
seen,
you can do that with those 90° elbow fitting things, can't you" when
they have no clue of pull-points and how much more difficult it
becomes
to do such things...

~~ Evan
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,025
Default Code question - conduit from weatherhead to meter


"Evan" wrote

It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...


I'm curious as to how you arrived at that. Have you seen the installation,
the poll location, and availability of underground feed? You're not one of
those guys that thinks every house is built like theirs are you?

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,106
Default Code question - conduit from weatherhead to meter

On Apr 6, 11:09*pm, "Ed Pawlowski" wrote:
"Evan" wrote



It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...


I'm curious as to how you arrived at that. *Have you seen the installation,
the poll location, and availability of underground feed? * You're not one of
those guys that thinks every house is built like theirs are you?



Because the owner in question has asked how to make a conduit
necessary for his upgraded electrical service disappear by means
of stupidly complex methods when the alternative to NOT see it is
to have it buried, but trenching, installing underground conduit,
protecting the underground conduit, backfilling and then pulling
the conductors costs a lot more than "hiding" the conduit around
the corner...

Asking for a "pie-in-the-sky" stupid solution over one that would
look MUCH better but is more expensive can ONLY be explained
by the owner being too cheap to do it right...

That is why I told him to get over himself and let the electrician
install the straight pipe from the weatherhead to the meter can...

~~ Evan


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,025
Default Code question - conduit from weatherhead to meter


"Evan" wrote in message
...
On Apr 6, 11:09 pm, "Ed Pawlowski" wrote:
"Evan" wrote



It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...


I'm curious as to how you arrived at that. Have you seen the
installation,
the poll location, and availability of underground feed? You're not one
of
those guys that thinks every house is built like theirs are you?



Because the owner in question has asked how to make a conduit
necessary for his upgraded electrical service disappear by means
of stupidly complex methods when the alternative to NOT see it is
to have it buried, but trenching, installing underground conduit,
protecting the underground conduit, backfilling and then pulling
the conductors costs a lot more than "hiding" the conduit around
the corner...

Asking for a "pie-in-the-sky" stupid solution over one that would
look MUCH better but is more expensive can ONLY be explained
by the owner being too cheap to do it right...

That is why I told him to get over himself and let the electrician
install the straight pipe from the weatherhead to the meter can...

~~ Evan


The solution may be stupid to an informed person, but not always to a
homeowner ignorant of power feeds. Not every location allows for underground
installation. He may not have that option It may be more than just
trenching from a pole, but may include a right of way across many feet of
concrete, across a highway, or who knows what. You look foolish making
accusations with no facts, but you are entitles to an opinion. .



  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,644
Default Code question - conduit from weatherhead to meter

On Apr 7, 5:55*am, "Ed Pawlowski" wrote:
"Evan" wrote in message

...





On Apr 6, 11:09 pm, "Ed Pawlowski" wrote:
"Evan" wrote


It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...


I'm curious as to how you arrived at that. *Have you seen the
installation,
the poll location, and availability of underground feed? * You're not one
of
those guys that thinks every house is built like theirs are you?


Because the owner in question has asked how to make a conduit
necessary for his upgraded electrical service disappear by means
of stupidly complex methods when the alternative to NOT see it is
to have it buried, but trenching, installing underground conduit,
protecting the underground conduit, backfilling and then pulling
the conductors costs a lot more than "hiding" the conduit around
the corner...


Asking for a "pie-in-the-sky" stupid solution over one that would
look MUCH better but is more expensive can ONLY be explained
by the owner being too cheap to do it right...


That is why I told him to get over himself and let the electrician
install the straight pipe from the weatherhead to the meter can...


~~ Evan


The solution may be stupid to an informed person, but not always to a
homeowner ignorant of power feeds. Not every location allows for underground
installation. He may not have that option * It may be more than just
trenching from a pole, but may include a right of way across many feet of
concrete, across a highway, or who knows what. * You look foolish making
accusations with no facts, but you are entitles to an opinion. .- Hide quoted text -

- Show quoted text -


I had a friend who fixated over never drilling a hole in his home,
keeping it pristine, never do anything.

Thats not a uncommon desire even though lots of holes are made during
construction, the outside has windows, gutters downspouts, power phone
and cable......

yet someone would go postal not wanting a dish anywhere on their home.
Years ago I installed dish tv for awhile.

The OP might get away by putting a main disconnect as early as
possible before the line runs around the house

  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,764
Default Code question - conduit from weatherhead to meter

On Apr 6, 7:25*pm, Evan wrote:
On Apr 6, 6:14*pm, "RBM" wrote:
"John Grabowski" wrote in message



I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.


The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). *I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. *The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. *The
horizontal run of conduit would be something like 3-4' off the ground.


I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.


I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. *He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. *I don't understand this
requirement. *I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. *I'm trying to understand this requirement but have not been
able to find anything online. *Maybe the inspector thought I would be
running the horizontal run underground? *Can anyone give me some
insight into this? *A website or code section cite would be great..


Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be
from the point of attachment. Call the guy back and get clarification. It
does sound like he misunderstood your intent


*I agree with RBM. *It doesn't sound as though concrete encasement is
called for, but Los Angeles has their own electrical code. *I think the
best thing would be for you to take a photo of your house with the
electrical service path drawn onto the photo and bring it down to show an
electrical inspector. You could also consult with an electrical
contractor.


I know one power company here in NJ frowns upon having an LB condulet
before the meter. *They are afraid that someone could open the LB and tap
into the power before it gets metered.


** The picture of 3- 2/0 bugs in a 2" condulet ain't a pretty one (lol)


It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...

Its funny how people think that conduits and pipes for utility services
are like tinker toys and "oh just move that out of where it can be seen,
you can do that with those 90° elbow fitting things, can't you" when
they have no clue of pull-points and how much more difficult it becomes
to do such things...


It's also funny when a person on the internet attempts to foist their
aesthetic opinion on a homeowner, site and sight unseen. And it's
funny when a person on the internet reads all sorts of **** into a
post and then pronounces all kinds of "facts" about the situation.

I agree with your assessment that someone needs to get over
themselves, just not with your conclusion as to who that party is.

R
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,106
Default Code question - conduit from weatherhead to meter

On Apr 7, 2:09*pm, RicodJour wrote:
On Apr 6, 7:25*pm, Evan wrote:



On Apr 6, 6:14*pm, "RBM" wrote:
"John Grabowski" wrote in message


I'm upgrading my house (in Los Angeles) to 200A service and I am
trying to find out some info on code requirements for the conduit run
from the weatherhead to the meter main.


The city requires me to put the new meter on the back of the house.
The easiest way to hook up the service drop is a straight 2" GS
conduit going up the outside wall but, as this is a 2 story house, I
think this will look really ugly (even if I paint it). *I would prefer
not opening up a wall to run the conduit so I thought that, maybe, we
could run the conduit down the side of the house (which is out of
sight), use a right angle 2" GS conduit bend to bring it horizontal
and then use an LB to go around the corner to the back of the house
and run GS into the side of the meter main. *The distance from the
meter to the corner of the house is about 3' and the distance from the
corner to where the vertical conduit would be is about 2-3'. *The
horizontal run of conduit would be something like 3-4' off the ground.


I know that I need approval from both the city's DWP and the building
inspector (in L.A. these are separate agencies) and I'm waiting for a
return call from the DWP.


I tried to get hold of a building inspector to ask if this was OK and,
after some effort, did manage to speak to one very briefly. *He told
me that the horizontal run needs to be incased in concrete, then said
he had others to help and hung up on me. *I don't understand this
requirement. *I have looked at the city's DWP Electric Service
Requirements and it only mentions concrete encasement in underground
runs. *I'm trying to understand this requirement but have not been
able to find anything online. *Maybe the inspector thought I would be
running the horizontal run underground? *Can anyone give me some
insight into this? *A website or code section cite would be great.


Any help would be greatly appreciated.


**He is the one who must ultimately interpret the local code. I would be
concerned about the distance the service head is from the utility
companies wires. There is probably a maximum distance the head can be
from the point of attachment. Call the guy back and get clarification. It
does sound like he misunderstood your intent


*I agree with RBM. *It doesn't sound as though concrete encasement is
called for, but Los Angeles has their own electrical code. *I think the
best thing would be for you to take a photo of your house with the
electrical service path drawn onto the photo and bring it down to show an
electrical inspector. You could also consult with an electrical
contractor.


I know one power company here in NJ frowns upon having an LB condulet
before the meter. *They are afraid that someone could open the LB and tap
into the power before it gets metered.


** The picture of 3- 2/0 bugs in a 2" condulet ain't a pretty one (lol)


It sounds like a cheap homeowner who doesn't want to pay what it
costs to do an underground feed...


Its funny how people think that conduits and pipes for utility services
are like tinker toys and "oh just move that out of where it can be seen,
you can do that with those 90° elbow fitting things, can't you" when
they have no clue of pull-points and how much more difficult it becomes
to do such things...


It's also funny when a person on the internet attempts to foist their
aesthetic opinion on a homeowner, site and sight unseen. *And it's
funny when a person on the internet reads all sorts of **** into a
post and then pronounces all kinds of "facts" about the situation.

I agree with your assessment that someone needs to get over
themselves, just not with your conclusion as to who that party is.

R



He umm has the option of NOT upgrading his service if it is
too expensive to do it correctly OR he can't get over the
required visual appearance changes to his house...

But "I don't like how the conduit looks" has to be the top
bullcrap reason of all time to decide not to go through
with some sort of improvement to the house which
would allow for a better electrical service...

~~ Evan
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Code question - conduit from weatherhead to meter

Thought I would post a single reply to all the responses to my orginal
post.

Frist off, thanks to all who took the time to respond. Appreciate
your time and effort. I spoke with DWP again and the service rep
offered to come out and look things over again. After going through
some options, he will allow me to move the meter and riser to a better
location; one out of sight from the backyard. Still have to play with
the riser a bit, but everyone's happy (well, maybe not Evan ;-).


As to Evan's comments.....

Much amused at what was the grandest display of "Ignorant Buffoonery"
I've seen in a long time. Rather than bother to reply to each of his
comments individually, let me summarize.

The city will not approve an underground feed. If you had bothered to
ask rather than rant, you might have found that out. But ranting on
without knowing the facts is one of the signs of "IB."

You comment about the hassle of plans and approvals. If you had read
(and understood) my original post you would have been able to figure
out that everything is being done to code, with permits and
inspections. After all, I mentioned "code" and "inspectors" and "DWP"
in my post. Permits/inspections are already factored in. Lacking in
reading comprehension isn't itself a sin. However when you not only
demonstrate but wallow proudly in your ignorance you make a total fool
of yourself and, again, assume the mantle of "IB."

You discount the homeowner's desire to achieve their aesthetic vision
and say to just let the electrician do it the "easy way." All I can
say is "Wow!" Maybe you've never owned your own home. Or maybe you
simply don't have any pride in workmanship. Contrary to what you may
think, I pay those who work for me quite well and, in return, I expect
them to produce very high quality results. I would never just tell
people to do what is easy whatever the results; but I guess you
would. "IB" yet again.

Finally without even trying to understand the situation, you presented
the false dicothomy of either "bury the cable" or "don't upgrade the
service." You seem to be incapable of understanding that your limited
knowledge and perception may not allow for solutions beyond the
immediately obvious. Can I get an "IB" from the congregation?

I could go on but I think that everyone who has read my original post
and your comments can come to their own conclusions. But, honestly, I
haven't seen anyone embarrass themselves as much as you have done here
in a very long time.

To everyone else, once again thank you all for your comments. The
meter and riser will go where I want, LADWP was a pleasure to work
with, and everyone (who matters) is happy.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Steel Conduit Question Doug White Metalworking 56 July 12th 10 02:52 PM
conduit question Fred UK diy 10 January 7th 10 09:56 PM
Electric conduit question Ivan Vegvary Home Repair 4 June 30th 09 04:56 AM
Replacing Electrical Weatherhead ? Tube Audio[_2_] Home Repair 4 July 18th 08 12:05 PM
conduit question for garage Chris Friesen Home Repair 5 October 22nd 06 09:58 AM


All times are GMT +1. The time now is 09:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"