What amperage is Romex #8 copper wire? On some charts I see 40 A and
on some I see 50 A. |
#2
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
"ls02" wrote in message ... What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. In a NM cable #8 uses the 60 degree figure, which is 40 amp |
#3
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On Feb 1, 10:27*am, ls02 wrote:
What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. Plus what's at the other end. Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at urge current. |
#4
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On Feb 1, 10:59*am, jamesgangnc wrote:
On Feb 1, 10:27*am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. *There are a number of calculators out there on the web that will help with wire selection. *Distance is a factor as well. *Plus what's at the other end. *Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at *urge current. The wire is used to connect sub-panel to mail panel. The distance is 3'. |
#5
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On Feb 1, 10:59*am, jamesgangnc wrote:
On Feb 1, 10:27*am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. *There are a number of calculators out there on the web that will help with wire selection. *Distance is a factor as well. *Plus what's at the other end. *Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at *urge current. In the case of general loads and Romex, it's 8 gauge for 40. With an HVAC load, the rules change. The circuit has to be wire sized to at least the minimum specd by the manufacturer. The breaker has to be sized between the min and max specd by the manufacturer. This leads to installations that are correct and to code, but that would be a violation of the rules for general purpose branch circuits. As an example, if you have an AC unit rated for 35 amp min circuit and rated for a breaker of 40amp min, 60 max, you could have a 60 amp breaker using 8 gauge wire. The reasoning to this is that: A - the AC has a high starting current that doesn't last B- the AC has it's own built-in over current protection and is the only device on that circuit. |
#6
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
"ls02" wrote in message ... On Feb 1, 10:59 am, jamesgangnc wrote: On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. Plus what's at the other end. Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at urge current. The wire is used to connect sub-panel to mail panel. The distance is 3'. Run a 3' length of 1" PVC between the panels and use #8 THHN copper on a 50 amp breaker |
#7
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
So, 8 gage wire is 8 gage? He asked the amp capacity of #8
copper. -- Christopher A. Young Learn more about Jesus www.lds.org .. "jamesgangnc" wrote in message ... On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. Plus what's at the other end. Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at urge current. |
#8
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
wrote in message ... On Tue, 1 Feb 2011 11:26:16 -0500, "RBM" wrote: "ls02" wrote in message ... On Feb 1, 10:59 am, jamesgangnc wrote: On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. Plus what's at the other end. Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at urge current. The wire is used to connect sub-panel to mail panel. The distance is 3'. Run a 3' length of 1" PVC between the panels and use #8 THHN copper on a 50 amp breaker If this is only 3 feet, why cheap out on the wire. Put in #2 and you can set a 100a sub panel. You may never need it but you have it for virtually no additional expense. A moment after I hit the send button, I had that exact thought |
#9
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On 2/1/2011 11:54 AM, Stormin Mormon wrote:
So, 8 gage wire is 8 gage? He asked the amp capacity of #8 copper. Actually, you could put 100 amps through an 8 gauge wire ... not for very long. It's all a matter of heating and insulation and how many wires are packing into a tight (conduit) space. That's why we have NEC which specifies the current for different sizes and types of wires and how they are routed. |
#10
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On Feb 1, 11:54*am, "Stormin Mormon"
wrote: So, 8 gage wire is 8 gage? He asked the amp capacity of #8 copper. -- Christopher A. Young Learn more about Jesus *www.lds.org . "jamesgangnc" wrote in message ... On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. *There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. *Plus what's at the other end. *Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at *urge current. Umm no, the OP asked the rating of #8 Romex wire... Some have responded that #8 THHN individual wires are rated slightly higher... Are you unable to actually read the entire thread before adding your own "wisdom"... ~~ Evan |
#11
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
On Feb 1, 10:23*pm, Evan wrote:
On Feb 1, 11:54*am, "Stormin Mormon" wrote: So, 8 gage wire is 8 gage? He asked the amp capacity of #8 copper. -- Christopher A. Young Learn more about Jesus *www.lds.org . "jamesgangnc" wrote in message .... On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Individual wires you could use 8. *There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. *Plus what's at the other end. *Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at *urge current. Umm no, the OP asked the rating of #8 Romex wire... Some have responded that #8 THHN individual wires are rated slightly higher... Are you unable to actually read the entire thread before adding your own "wisdom"... ~~ Evan- Hide quoted text - - Show quoted text - Same response I gave. I just added other factors that might affect wire choice. Now that we know it's 3 feet to a subpanel there's not much reason not to use bigger wire since there would be no noticable cost difference. |
#12
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
RBM wrote:
"ls02" wrote in message ... On Feb 1, 10:59 am, jamesgangnc wrote: On Feb 1, 10:27 am, ls02 wrote: What amperage is Romex #8 copper wire? On some charts I see 40 A and on some I see 50 A. Wire have many different kinds of electrical insulation. Some kinds of insulation can be used at various higher temperatures. That allows a higher current rating - higher current produces more heat. Romex is limited to the current for 60 degree insulation, which for #8 is 40A. (There further details you don't want to know about.) Individual wires you could use 8. There are a number of calculators out there on the web that will help with wire selection. Distance is a factor as well. Plus what's at the other end. Motors that start under a load like a big hvac compressor may need bigger wire simply to prevent to much voltage drop at urge current. The wire is used to connect sub-panel to mail panel. The distance is 3'. Run a 3' length of 1" PVC between the panels and use #8 THHN copper on a 50 amp breaker There is a limitation (110.14-C-1) on "ampacity" rating of the wire based on the terminals the wire is connected to. for circuits 100A and less, or terminals marked #14 through #1, the 60 degree ampacity of the wire is used. for circuits over 100A, or terminals marked larger than #1, the 75 degree ampacity of the wire is used (unless the wire is rated 60 degrees) In both cases wires of a higher temperature rating can be used, but the current allowed is limited to the 60 or 75 degree column. In both cases the wire can be used at a higher current if both terminal devices are marked for a higher temperature. I expect you know all that, but some may not. Long time since I looked at a breaker - a new 20A SquareD breaker is marked for 60 or 75 degree wire, which means the 75 degree column can be used for 90 degree rated THHN. If a 50A breaker is similarly marked, the usable rating for #8 THHN is 50 amps, as stated. Are most new breakers marked for 75 degrees these days? Is this enforced? Presumably connections to old breakers that aren't marked would hit the 60/75 degree temp limit. -- bud-- |
#13
Posted to alt.home.repair
|
|||
|
|||
Wire gauge and amperage
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
wire gauge | Home Repair | |||
8 gauge wire to 30 amp circuit | Home Repair | |||
What gauge wire for fuse; VA vs. W | Electronics Repair | |||
Can I stick two 4 gauge and one 6 gauge wire into a 3/4" conduit | Home Repair |