20-amp ktichen circuit, 15-amp GFI okay?
I am adding two 20-amp circuits to provide a total of 6 above-the-countertop
receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. |
#2
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On Nov 10, 3:49*pm, "RogerT" wrote:
I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. *I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. *And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. Two 20 amp circuits is over kill iif you only have enough counter space for 6 outlets mho. But you are correct, you can place multiple 15 amp receps on a 20 amp circuit. |
#3
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
"RogerT" wrote in message ... I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. You are correct, the pass through is rated for 20 amps |
#4
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
"jamesgangnc" wrote in message ... On Nov 10, 3:49 pm, "RogerT" wrote: I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. Two 20 amp circuits is over kill iif you only have enough counter space for 6 outlets mho. But you are correct, you can place multiple 15 amp receps on a 20 amp circuit. A minimum of 2 -20 amp circuits is required by the Nec for kitchen counter outlets |
#5
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On Nov 10, 4:20*pm, "RBM" wrote:
"jamesgangnc" wrote in message ... On Nov 10, 3:49 pm, "RogerT" wrote: I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. Two 20 amp circuits is over kill iif you only have enough counter space for 6 outlets mho. *But you are correct, you can place multiple 15 amp receps on a 20 amp circuit. A minimum of 2 -20 amp circuits is required by the Nec for kitchen counter outlets yes, so it's not really overkill now is it. I believe that many "15A" GFCIs are actually rated at 20A for the GFCI portion if you read the label, so that would be OK, but read the label. nate |
#6
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On 11/10/2010 2:49 PM, RogerT wrote:
I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. Personally, I would install 20 amp rated because I own electrical plug-in appliances that draw a lot of current like electric grills and large toaster ovens. TDD |
#7
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On 2010-11-10, The Daring Dufas wrote:
Personally, I would install 20 amp rated because I own electrical plug-in appliances that draw a lot of current like electric grills and large toaster ovens. The only difference between a 15 amp receptacle and a 20 amp receptacle of a given grade(*) is the face plate, the 20 amp receptacle has the extra slot to accept 20 amp plugs. The innards are the same and are rated for 20 amps pass through. Cheers, Wayne (*) 20 amp receptacles may not be available in the cheapest grades, but I only use the better grades that provide back pressure-plate connections. |
#8
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On 11/10/2010 5:09 PM, Wayne Whitney wrote:
On 2010-11-10, The Daring wrote: Personally, I would install 20 amp rated because I own electrical plug-in appliances that draw a lot of current like electric grills and large toaster ovens. The only difference between a 15 amp receptacle and a 20 amp receptacle of a given grade(*) is the face plate, the 20 amp receptacle has the extra slot to accept 20 amp plugs. The innards are the same and are rated for 20 amps pass through. Cheers, Wayne (*) 20 amp receptacles may not be available in the cheapest grades, but I only use the better grades that provide back pressure-plate connections. I certainly wouldn't use 59 cent receptacles. I will often install a 20 amp plug on something that I don't want anyone plugging to a 15 amp receptacle. One of the problems I often come across in commercial settings is a receptacle burning up. An industrial or commercial grade 20 amp receptacle solves the problem. If I have a situation where items are being plugged in and unplugged a lot, I install a hospital grade receptacle. TDD |
#9
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On 11/10/2010 4:20 PM, RBM wrote:
snip Two 20 amp circuits is over kill iif you only have enough counter space for 6 outlets mho. But you are correct, you can place multiple 15 amp receps on a 20 amp circuit. A minimum of 2 -20 amp circuits is required by the Nec for kitchen counter outlets I'm about to wire up my kitchen counter. What I'd like is two pairs of two duplex outlets. That would be a total of 8 outlets in two groups. Should I: A) split wire all the duplex outlets. B) wire each duplex in the same box to a different circuit/phase. C) wire each double duplex all to the same circuit. It's an L counter and these outlets will be in each side of the corner. I'll have the MW, toaster oven and coffee maker plugged in, who knows what else. Outlets will be in the wall, a few inches over the backsplash. Stove on the left, sink to the right, and a duplex outlet on each end of the L. Does the fridge need to be on a separate circuit? Jeff |
#10
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
"Jeff Thies" wrote in message ... On 11/10/2010 4:20 PM, RBM wrote: snip Two 20 amp circuits is over kill iif you only have enough counter space for 6 outlets mho. But you are correct, you can place multiple 15 amp receps on a 20 amp circuit. A minimum of 2 -20 amp circuits is required by the Nec for kitchen counter outlets I'm about to wire up my kitchen counter. What I'd like is two pairs of two duplex outlets. That would be a total of 8 outlets in two groups. Should I: A) split wire all the duplex outlets. B) wire each duplex in the same box to a different circuit/phase. C) wire each double duplex all to the same circuit. It's an L counter and these outlets will be in each side of the corner. I'll have the MW, toaster oven and coffee maker plugged in, who knows what else. Outlets will be in the wall, a few inches over the backsplash. Stove on the left, sink to the right, and a duplex outlet on each end of the L. Does the fridge need to be on a separate circuit? Jeff The Nec doesn't require the refrigerator to be on a dedicated circuit, but some refrigerator manufacturers do , so I routinely use a dedicated circuit for fridges. I prefer to wire counter outlets with large boxes and 3 wire cables between all of them. This way I have both circuits at every outlet, not knowing what may be plugged in and where, it gives me the flexibility to adjust the two circuits |
#11
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
Thanks everyone for the replies. Looks like what I want to do will work and
will meet the code requirements. "RogerT" wrote in message ... I am adding two 20-amp circuits to provide a total of 6 above-the-countertop receptacles. I will be wiring them so that every other receptacle is on a different circuit -- so two sets of 3 receptacles per circuit. And, the first receptacle for each circuit will be a GFI with the remaining two receptacles on each circuit being covered by the GFI at the beginning of that circuit. My question is, can the two GFI's be 15-amp rated GFI receptacles, or do they have to be 20-amp rated GFI's? I am thinking that the GFI's and the remaining receptacles can all be 15-amp rated receptacles, but I wanted to check here in case I am wrong about that. |
#12
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
No, it is not. 15/20 Amp breakers are NOT guaranteed to have 20 amp
capability in a 15 amp component. Internal wire gages & all connections are usually NOT capable of 20 amps because it's cheaper to make them for 15 amps. Every penny saved is important on a manufacturing line. In , The Daring Dufas typed: On 11/10/2010 5:09 PM, Wayne Whitney wrote: On 2010-11-10, The Daring wrote: Personally, I would install 20 amp rated because I own electrical plug-in appliances that draw a lot of current like electric grills and large toaster ovens. The only difference between a 15 amp receptacle and a 20 amp receptacle of a given grade(*) is the face plate, the 20 amp receptacle has the extra slot to accept 20 amp plugs. The innards are the same and are rated for 20 amps pass through. Cheers, Wayne (*) 20 amp receptacles may not be available in the cheapest grades, but I only use the better grades that provide back pressure-plate connections. I certainly wouldn't use 59 cent receptacles. I will often install a 20 amp plug on something that I don't want anyone plugging to a 15 amp receptacle. One of the problems I often come across in commercial settings is a receptacle burning up. An industrial or commercial grade 20 amp receptacle solves the problem. If I have a situation where items are being plugged in and unplugged a lot, I install a hospital grade receptacle. TDD |
#13
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
On 2010-11-11, Twayne wrote:
No, it is not. 15/20 Amp breakers are NOT guaranteed to have 20 amp capability in a 15 amp component. Internal wire gages & all connections are usually NOT capable of 20 amps because it's cheaper to make them for 15 amps. Every penny saved is important on a manufacturing line. 15 amp receptacles are required by UL to handle 20 amps feed through. The UL directory information for RTRT (receptacles) does not make that 100% clear, but UL has provided further detail. See, for example, their response included in this thread (third to last post): http://forums.mikeholt.com/archive/i...p/t-61043.html Cheers, Wayne |
#14
Posted to alt.home.repair
|
|||
|
|||
20-amp ktichen circuit, 15-amp GFI okay?
"Wayne Whitney" wrote in message ... On 2010-11-11, Twayne wrote: No, it is not. 15/20 Amp breakers are NOT guaranteed to have 20 amp capability in a 15 amp component. Internal wire gages & all connections are usually NOT capable of 20 amps because it's cheaper to make them for 15 amps. Every penny saved is important on a manufacturing line. 15 amp receptacles are required by UL to handle 20 amps feed through. The UL directory information for RTRT (receptacles) does not make that 100% clear, but UL has provided further detail. See, for example, their response included in this thread (third to last post): http://forums.mikeholt.com/archive/i...p/t-61043.html Cheers, Wayne Also, if 15 amp receptacles didn't have 20 amp pass through, the Nec wouldn't allow them on 20 amp branch circuits |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
How do you know a new circuit breaker is protecting the circuit properly? | Home Repair | |||
12-3 Double Circuit Run Length - Should I Split the Circuit? | Home Repair | |||
Short in Circuit or Circuit breaker? | Home Repair | |||
circuit is off, circuit breaker is on | Home Repair | |||
Convert radial (cooker) circuit to socket circuit | UK diy |