Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default New Pressure Tank in Hydronic System Issue

I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
I like to keep the system pressure at between 15 and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
I did not check the tank pressure before installing.
What is wrong and what should I do? I'd like not to have to drain
the system again.
Thanks in advance.
Frank

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default New Pressure Tank in Hydronic System Issue

Just heard a loud "whoosh" and the pressure has gone to zero again.
Nothing is leaking. Add that to the clues.






On Wed, 30 Dec 2009 01:25:50 -0500, frank1492
wrote:

I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
I like to keep the system pressure at between 15 and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
I did not check the tank pressure before installing.
What is wrong and what should I do? I'd like not to have to drain
the system again.
Thanks in advance.
Frank


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,926
Default New Pressure Tank in Hydronic System Issue

On Dec 30, 12:38*am, frank1492 wrote:
Just heard a loud "whoosh" and the pressure has gone to zero again.
Nothing is leaking. Add that to the clues.

On Wed, 30 Dec 2009 01:25:50 -0500, frank1492
wrote:



I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
* I like to keep the system pressure at between 15 *and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
* I did not check the tank pressure before installing.
*What is wrong and what should I do? I'd like not to have to drain
the system again.
*Thanks in advance.
* * * Frank- Hide quoted text -


- Show quoted text -


Do you mean the pressure gauge on the boiler, how much does pressure
change from high to low, is your house 1 or 3 story, with radiators I
can not go to zero unless my system is empty, to keep my 3rd floor
radiator full of water I need near 12-15lb and only increase a few
pounds as water heats. Maybe a bad gauge, what was wrong with old
tank, to small a tank and pressure can jump when heated and be
erratic, when our boiler was changed the attic expansion tank was
eliminated and a basement tank installed, but we eventualy needed two
tanks as one was to small and pressure jumped 15-20lb with every
heating cycle. www.heatinghelp.com "the wall" is where boiler pros
are.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default New Pressure Tank in Hydronic System Issue

Sorry I wasn't clear. This is a *closed leg* with a circulator,
pressure tank and gauge. (Runs through a heat exhanger or tankless
heater, heat supplied by circulating steam boiler water- old boiler.)
Has always worked perfectly with identical components until the old
tank sprung a leak. I realize the ideal situation would be to have a
pressure reducing valve and backflow preventer permanently attached
but letting in the water manually on rare occasions has always worked
fine.
So the only thing that's new is the new pressure tank, same
capacity, style as before. As I say, when you let water in now, the
pressure rises very quickly as if there was no air cushion.








On Wed, 30 Dec 2009 03:06:45 -0800 (PST), ransley
wrote:

On Dec 30, 12:38*am, frank1492 wrote:
Just heard a loud "whoosh" and the pressure has gone to zero again.
Nothing is leaking. Add that to the clues.

On Wed, 30 Dec 2009 01:25:50 -0500, frank1492
wrote:



I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
* I like to keep the system pressure at between 15 *and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
* I did not check the tank pressure before installing.
*What is wrong and what should I do? I'd like not to have to drain
the system again.
*Thanks in advance.
* * * Frank- Hide quoted text -


- Show quoted text -


Do you mean the pressure gauge on the boiler, how much does pressure
change from high to low, is your house 1 or 3 story, with radiators I
can not go to zero unless my system is empty, to keep my 3rd floor
radiator full of water I need near 12-15lb and only increase a few
pounds as water heats. Maybe a bad gauge, what was wrong with old
tank, to small a tank and pressure can jump when heated and be
erratic, when our boiler was changed the attic expansion tank was
eliminated and a basement tank installed, but we eventualy needed two
tanks as one was to small and pressure jumped 15-20lb with every
heating cycle. www.heatinghelp.com "the wall" is where boiler pros
are.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default New Pressure Tank in Hydronic System Issue

In article , frank1492 wrote:
Sorry I wasn't clear. This is a *closed leg* with a circulator,
pressure tank and gauge. (Runs through a heat exhanger or tankless
heater, heat supplied by circulating steam boiler water- old boiler.)
Has always worked perfectly with identical components until the old
tank sprung a leak. I realize the ideal situation would be to have a
pressure reducing valve and backflow preventer permanently attached
but letting in the water manually on rare occasions has always worked
fine.
So the only thing that's new is the new pressure tank, same
capacity, style as before. As I say, when you let water in now, the
pressure rises very quickly as if there was no air cushion.


That suggests strongly that there is not in fact an air cushion. By any chance
is there a valve between the gauge and the air tank? And is that valve open?








On Wed, 30 Dec 2009 03:06:45 -0800 (PST), ransley
wrote:

On Dec 30, 12:38*am, frank1492 wrote:
Just heard a loud "whoosh" and the pressure has gone to zero again.
Nothing is leaking. Add that to the clues.

On Wed, 30 Dec 2009 01:25:50 -0500, frank1492
wrote:



I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
* I like to keep the system pressure at between 15 *and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
* I did not check the tank pressure before installing.
*What is wrong and what should I do? I'd like not to have to drain
the system again.
*Thanks in advance.
* * * Frank- Hide quoted text -

- Show quoted text -


Do you mean the pressure gauge on the boiler, how much does pressure
change from high to low, is your house 1 or 3 story, with radiators I
can not go to zero unless my system is empty, to keep my 3rd floor
radiator full of water I need near 12-15lb and only increase a few
pounds as water heats. Maybe a bad gauge, what was wrong with old
tank, to small a tank and pressure can jump when heated and be
erratic, when our boiler was changed the attic expansion tank was
eliminated and a basement tank installed, but we eventualy needed two
tanks as one was to small and pressure jumped 15-20lb with every
heating cycle. www.heatinghelp.com "the wall" is where boiler pros
are.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default New Pressure Tank in Hydronic System Issue

The tank is on a tee in the loop and the gauge is on a separate tee.
There is no valve between gauge and air tank. I know, it's puzzling. I
really thought someone would have a quick answer. Of course I can
always disassemble everything and start over, but first I guess I
should ascertain if there is air in the tank at all.
It seems I should mention something: When filling the system, I
accidentally let the pressure get to about 80 lbs, but *only*
momentarily. The max tank pressure is supposed to be 75 lbs. I know
it's a stretch but any chance the bladder was damaged?




On Wed, 30 Dec 2009 17:38:47 GMT, (Doug Miller)
wrote:

In article , frank1492 wrote:
Sorry I wasn't clear. This is a *closed leg* with a circulator,
pressure tank and gauge. (Runs through a heat exhanger or tankless
heater, heat supplied by circulating steam boiler water- old boiler.)
Has always worked perfectly with identical components until the old
tank sprung a leak. I realize the ideal situation would be to have a
pressure reducing valve and backflow preventer permanently attached
but letting in the water manually on rare occasions has always worked
fine.
So the only thing that's new is the new pressure tank, same
capacity, style as before. As I say, when you let water in now, the
pressure rises very quickly as if there was no air cushion.


That suggests strongly that there is not in fact an air cushion. By any chance
is there a valve between the gauge and the air tank? And is that valve open?








On Wed, 30 Dec 2009 03:06:45 -0800 (PST), ransley
wrote:

On Dec 30, 12:38*am, frank1492 wrote:
Just heard a loud "whoosh" and the pressure has gone to zero again.
Nothing is leaking. Add that to the clues.

On Wed, 30 Dec 2009 01:25:50 -0500, frank1492
wrote:



I just installed a new pressure tank in my hydronic system. It said it
was pre-charged to 12 psi. When refilling the system I think I did a
good job of eliminating the air as there is little noise when the
circulator is running, plus there is a Spirovent installed.
* I like to keep the system pressure at between 15 *and 20 lbs. but I
noticed the pressure seems to drop back to 0 quite often. Then when I
add water, the pressure seems to rise very quickly. The only thing I
can think of is that I have no air cushion.
* I did not check the tank pressure before installing.
*What is wrong and what should I do? I'd like not to have to drain
the system again.
*Thanks in advance.
* * * Frank- Hide quoted text -

- Show quoted text -

Do you mean the pressure gauge on the boiler, how much does pressure
change from high to low, is your house 1 or 3 story, with radiators I
can not go to zero unless my system is empty, to keep my 3rd floor
radiator full of water I need near 12-15lb and only increase a few
pounds as water heats. Maybe a bad gauge, what was wrong with old
tank, to small a tank and pressure can jump when heated and be
erratic, when our boiler was changed the attic expansion tank was
eliminated and a basement tank installed, but we eventualy needed two
tanks as one was to small and pressure jumped 15-20lb with every
heating cycle.
www.heatinghelp.com "the wall" is where boiler pros
are.



  #7   Report Post  
Posted to alt.home.repair
Joe Joe is offline
external usenet poster
 
Posts: 2,837
Default New Pressure Tank in Hydronic System Issue

On Dec 30, 11:07*pm, frank1492 wrote:

snip


*It seems I should mention something: When filling the system, I
accidentally let the pressure get to about 80 lbs, but *only*
momentarily. The max tank pressure is supposed to be 75 lbs. I know
it's a stretch but any chance the bladder was damaged?

snip


Bingo!

Joe
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 82
Default New Pressure Tank in Hydronic System Issue

is these system steam or water

"Joe" wrote in message
...
On Dec 30, 11:07 pm, frank1492 wrote:

snip


It seems I should mention something: When filling the system, I
accidentally let the pressure get to about 80 lbs, but *only*
momentarily. The max tank pressure is supposed to be 75 lbs. I know
it's a stretch but any chance the bladder was damaged?

snip


Bingo!

Joe


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,640
Default New Pressure Tank in Hydronic System Issue

Grumpy wrote:
is these system steam or water

"Joe" wrote in message
...
On Dec 30, 11:07 pm, frank1492 wrote:

snip


It seems I should mention something: When filling the system, I
accidentally let the pressure get to about 80 lbs, but *only*
momentarily. The max tank pressure is supposed to be 75 lbs. I know
it's a stretch but any chance the bladder was damaged?

snip


Bingo!

Joe


It would not be steam in a residence with that pressure. Now would steam
have an expansion tank anyway.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 82
Default New Pressure Tank in Hydronic System Issue

you got point Ed but then I have never hear of any boiler that goes over 30
psi
in residential use, ideal pressure is around 15 psi. So where 80 and 75 psi
coming from

"Ed Pawlowski" wrote in message
...
Grumpy wrote:
is these system steam or water

"Joe" wrote in message
...
On Dec 30, 11:07 pm, frank1492 wrote:

snip


It seems I should mention something: When filling the system, I
accidentally let the pressure get to about 80 lbs, but *only*
momentarily. The max tank pressure is supposed to be 75 lbs. I know
it's a stretch but any chance the bladder was damaged?

snip


Bingo!

Joe


It would not be steam in a residence with that pressure. Now would steam
have an expansion tank anyway.




--- news://freenews.netfront.net/ - complaints: ---


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,640
Default New Pressure Tank in Hydronic System Issue

Grumpy wrote:
you got point Ed but then I have never hear of any boiler that goes
over 30 psi
in residential use, ideal pressure is around 15 psi. So where 80 and
75 psi coming from


Only way would be for a defective fill/pressure regulator valve allowing
full incoming pressure. Or, he is making steam in that water boiler because
it is not circulating and shutting down the burner.


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 82
Default New Pressure Tank in Hydronic System Issue

I think that he should call pro.

"Ed Pawlowski" wrote in message
...
Grumpy wrote:
you got point Ed but then I have never hear of any boiler that goes
over 30 psi
in residential use, ideal pressure is around 15 psi. So where 80 and
75 psi coming from


Only way would be for a defective fill/pressure regulator valve allowing
full incoming pressure. Or, he is making steam in that water boiler
because it is not circulating and shutting down the burner.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pressure in a hydronic heating system Marilyn & Bob Home Repair 31 February 15th 10 09:36 AM
Puzzling out a hydronic in-floor system [email protected] Home Repair 4 January 28th 07 01:46 AM
How do I mothball my hydronic heating system? auctoron Home Repair 0 December 15th 06 09:12 PM
Hydronic Heat Pressure too high jimi Home Repair 4 February 15th 06 01:28 AM
Purging a hydronic heat system [email protected] Home Repair 2 February 9th 06 05:49 AM


All times are GMT +1. The time now is 10:32 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"