Colored Electrical Outlets
In some hospitals and office buildings, I see some electrical outlets that
are red or orange (not the outlets cover plates, the outlet itself). What's that all about? |
#2
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
"William Munny" wrote in message ... In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? they are on a ups for safety critical use during blackouts. |
#3
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
charlie wrote:
"William Munny" wrote in message ... In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? they are on a ups for safety critical use during blackouts. And orange is isolated ground for computer equipment/instrumentation that requires it. -- |
#4
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
William Munny wrote:
In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? If the power goes out, then emergency generators kick in. The red paneled outlets can be energized by the emergency system as well as the normal system; the white ones only work when normal power is running. We would then plug only essentials into the red paneled outlets. During the normal run of the day, it doesn't matter which outlet you use. The "red only" will only apply when the generator's are supplying things. In 17 years as a nurse, I've never had to use emergency power. But it's there.... Mortimer Schnerd, RN mschnerd at carolina.rr.com |
#5
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On 8/14/2009 10:29 AM William Munny spake thus:
In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Special sanitary electricity. They run it through an autoclave to disinfect it. -- Found--the gene that causes belief in genetic determinism |
#6
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
"charlie" wrote:
What's that all about? they are on a ups for safety critical use during blackouts. Or they are on an isolated ground. |
#7
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
"William Munny" wrote in message
... In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Cool, thanks... |
#8
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
But, that's before the centrifuge, to settle out the heavy
electrons. -- Christopher A. Young Learn more about Jesus www.lds.org .. "David Nebenzahl" wrote in message .com... On 8/14/2009 10:29 AM William Munny spake thus: In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Special sanitary electricity. They run it through an autoclave to disinfect it. -- Found--the gene that causes belief in genetic determinism |
#9
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
In article , "William Munny" wrote:
In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Red = connected to emergency power (nearly all hospitals, and many office buildings, have backup generators in case utility power fails) Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) |
#10
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
"William Munny" wrote in message ... In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? How's the hired gun business working out? |
#11
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Sat, 15 Aug 2009 09:49:15 -0400, "Perry Aynum"
wrote: "William Munny" wrote in message ... In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? How's the hired gun business working out? ORANGE receptacles are "isolated ground" (used to be - not necessarity true any more) meaning the "U" ground was not connected to the mounting tab. |
#12
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
|
#13
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Aug 18, 9:43*pm, (Doug Miller) wrote:
In article , Ashton Crusher wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 Thanks to all posters. Learned something. And made one think. Thank- you. Sounds like 'Isolated' Ground might also be called an 'Individual' Ground! In other words the grounding wire from this type of outlet (orange!) is run individually to the grounding point; not using the ground used for a 'run' or group of 'regular' outlets. Have only used an orange outlet once, connected to the output of a UPS located in our basement and wired up stairs to the room with the main PC etc. AFIK took the ground back to the output of the UPS. But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? The http://tinyurl.com/n937l4 was a useful explanatory. |
#14
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Aug 14, 1:29*pm, "William Munny" wrote:
In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Many building have three types of circuits. Commercial: Same old stuff you got at your house. Essential: These are backed up by generator. Critical: These are backed up by both a generator and an Uninterruptable Power Supply similar to the battery backup you may have for your PC. The critical circuits are marked so people will not know not to plug things into them they shouldn't like blow dryers, personal heaters, and janitorial equipment. Also it lets them know you could plug in a heart-lung machine there. There may also be rules about what you can use on essential circuits so they may also be marked. Jimmie |
#15
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Aug 18, 8:31*am, stan wrote:
On Aug 18, 9:43*pm, (Doug Miller) wrote: In article , Ashton Crusher wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 Thanks to all posters. Learned something. And made one think. Thank- you. Sounds like 'Isolated' Ground might also be called an 'Individual' Ground! In other words the grounding wire from this type of outlet (orange!) is run individually to the grounding point; not using the ground used for a 'run' or group of 'regular' outlets. Have only used an orange outlet once, connected to the output of a UPS located in our basement and wired up stairs to the room with the main PC etc. AFIK took the ground back to the output of the UPS. But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? The http://tinyurl.com/n937l4 was a useful explanatory. That's a good article about the hoo-hah surrounding isolated ground. I'm convinced that architects put them in out of rote habit. I've personally never seen a computer with documentation that requires them. I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. The orange outlet at least guarantees you a real copper ground all the way back to something earthed. As others have said, today's codes, especially for hospitals, now guarantee this for all outlets. I am also told that the orange outlets can indicate a circuit fed by a (nearby) isolation transformer, on the output side of which the neutral is re-referenced (ie, tied) to ground. This guarantees that at the outlet, ground and neutral are close together in voltage. Otherwise, in large commercial buildings, as you get further from the point of grounding you can find that ground and neutral not only have noise relative to each other but are far apart in DC levels. As others have said, the read outlets are on circuits that can be fed by the generators if the utility power cuts out. (And yes, the breakers for these circuits are in bright read service panels.) But be warned, a lot of places do generator and cutover tests at some regular schedule, usually at some early morning hour, which cause outages of a second or so. Much hospital equipment (fridges, lighting, elevators, plus patient support equipment that has internal batteries) ride through these fine, but computers don't. And of course, when a utility outage happens, it takes time for the generators to ramp up (the nominal standard is generally 15 seconds, in the real world can be longer). Bottom line: don't plug a computer in to a hospital red outlet without a UPS. Chip C |
#16
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Aug 18, 10:12*am, wrote:
On Tue, 18 Aug 2009 07:07:06 -0700 (PDT), Chip C wrote: On Aug 18, 8:31*am, stan wrote: On Aug 18, 9:43*pm, (Doug Miller) wrote: In article , Ashton Crusher wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 Thanks to all posters. Learned something. And made one think. Thank- you. Sounds like 'Isolated' Ground might also be called an 'Individual' Ground! In other words the grounding wire from this type of outlet (orange!) is run individually to the grounding point; not using the ground used for a 'run' or group of 'regular' outlets. Have only used an orange outlet once, connected to the output of a UPS located in our basement and wired up stairs to the room with the main PC etc. AFIK took the ground back to the output of the UPS. But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? The http://tinyurl.com/n937l4 was a useful explanatory. That's a good article about the hoo-hah surrounding isolated ground. I'm convinced that architects put them in out of rote habit. I've personally never seen a computer with documentation that requires them. I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. The orange outlet at least guarantees you a real copper ground all the way back to something earthed. As others have said, today's codes, especially for hospitals, now guarantee this for all outlets. I am also told that the orange outlets can indicate a circuit fed by a (nearby) isolation transformer, on the output side of which the neutral is re-referenced (ie, tied) to ground. This guarantees that at the outlet, ground and neutral are close together in voltage. Otherwise, in large commercial buildings, as you get further from the point of grounding you can find that ground and neutral not only have noise relative to each other but are far apart in DC levels. As others have said, the read outlets are on circuits that can be fed by the generators if the utility power cuts out. (And yes, the breakers for these circuits are in bright read service panels.) But be warned, a lot of places do generator and cutover tests at some regular schedule, usually at some early morning hour, which cause outages of a second or so. Much hospital equipment (fridges, lighting, elevators, plus patient support equipment that has internal batteries) ride through these fine, but computers don't. And of course, when a utility outage happens, it takes time for the generators to ramp up (the nominal standard is generally 15 seconds, in the real world can be longer). Bottom line: don't plug a computer in to a hospital red outlet without a UPS. Chip C Isolation transformer is there for safety. Yes, in cases where its output is not referenced to earth. The two- prong shaver outlets that used to be in bathroom light fixtures were like this. Also I hear that in the UK (and other 240V places??) they use 120V isolated power on outdoor construction sites. If the one of the transformer output legs is tied to earth, then I don't see the safety benefit. Chip C |
#18
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Aug 18, 1:12*pm, wrote:
On Tue, 18 Aug 2009 05:31:40 -0700 (PDT), stan wrote: But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? IBM decided IG was snake oil on the late 70s and removed the recommendation from the Physical Planning Manual. You are right, as soon as you connect equipment on different circuits together IG is meaningless, or worse a source of additional problems. Your bonding path becomes longer than the signal path so the line driver/receiver becomes your surge protection. We went the other way and added additional bonding, connecting machine frames directly together. I used to work on a mainframe computer system that was updated to isolated grounding. There were a few pieces of hardware on which it was impossible to isolate the grounds but the engineers decided this was OK. I have never seen so much blue smoke in my life as when they applied power. This happened nearly 20 years ago and the essence of ohms still lingers in the air. A few years ago all the equipment wa upgraded and it was all designed for IG and the appropriate IG system was installed. A few months ago the equipment was expanded and it was decide that IG was not needed so now we have bare ground wires laying in bare metal cable trays attached to IG ground points, cable trays are fastened to earth ground. Jimmie |
#19
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
Chip C wrote:
On Aug 18, 10:12 am, wrote: On Tue, 18 Aug 2009 07:07:06 -0700 (PDT), Chip C wrote: On Aug 18, 8:31 am, stan wrote: On Aug 18, 9:43 pm, (Doug Miller) wrote: In article , Ashton Crusher wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 Thanks to all posters. Learned something. And made one think. Thank- you. Sounds like 'Isolated' Ground might also be called an 'Individual' Ground! In other words the grounding wire from this type of outlet (orange!) is run individually to the grounding point; not using the ground used for a 'run' or group of 'regular' outlets. Have only used an orange outlet once, connected to the output of a UPS located in our basement and wired up stairs to the room with the main PC etc. AFIK took the ground back to the output of the UPS. But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? The http://tinyurl.com/n937l4 was a useful explanatory. That's a good article about the hoo-hah surrounding isolated ground. I'm convinced that architects put them in out of rote habit. I've personally never seen a computer with documentation that requires them. I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. The orange outlet at least guarantees you a real copper ground all the way back to something earthed. As others have said, today's codes, especially for hospitals, now guarantee this for all outlets. I am also told that the orange outlets can indicate a circuit fed by a (nearby) isolation transformer, on the output side of which the neutral is re-referenced (ie, tied) to ground. This guarantees that at the outlet, ground and neutral are close together in voltage. Otherwise, in large commercial buildings, as you get further from the point of grounding you can find that ground and neutral not only have noise relative to each other but are far apart in DC levels. As others have said, the read outlets are on circuits that can be fed by the generators if the utility power cuts out. (And yes, the breakers for these circuits are in bright read service panels.) But be warned, a lot of places do generator and cutover tests at some regular schedule, usually at some early morning hour, which cause outages of a second or so. Much hospital equipment (fridges, lighting, elevators, plus patient support equipment that has internal batteries) ride through these fine, but computers don't. And of course, when a utility outage happens, it takes time for the generators to ramp up (the nominal standard is generally 15 seconds, in the real world can be longer). Bottom line: don't plug a computer in to a hospital red outlet without a UPS. Chip C Isolation transformer is there for safety. Yes, in cases where its output is not referenced to earth. The two- prong shaver outlets that used to be in bathroom light fixtures were like this. Also I hear that in the UK (and other 240V places??) they use 120V isolated power on outdoor construction sites. The UK transformer has a centertap that is earthed. The hot wires are 60V from earth potential. If the one of the transformer output legs is tied to earth, then I don't see the safety benefit. It keeps the hot wires from being at 2000V with respect to earth. Or with 120V primary and secondary one secondary wire could be at 240V with respect to the earth. When servicing electronic equipment an isolation transformer with a completely floating secondary may be used. There can be significant hazards working on equipment with the DC power system tied to the neutral. Almost all systems are earthed. -- bud-- |
#20
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
JIMMIE wrote:
On Aug 18, 1:12 pm, wrote: On Tue, 18 Aug 2009 05:31:40 -0700 (PDT), stan wrote: But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? IBM decided IG was snake oil on the late 70s and removed the recommendation from the Physical Planning Manual. You are right, as soon as you connect equipment on different circuits together IG is meaningless, or worse a source of additional problems. Your bonding path becomes longer than the signal path so the line driver/receiver becomes your surge protection. We went the other way and added additional bonding, connecting machine frames directly together. I used to work on a mainframe computer system that was updated to isolated grounding. There were a few pieces of hardware on which it was impossible to isolate the grounds but the engineers decided this was OK. I have never seen so much blue smoke in my life as when they applied power. This happened nearly 20 years ago and the essence of ohms still lingers in the air. A few years ago all the equipment wa upgraded and it was all designed for IG and the appropriate IG system was installed. A few months ago the equipment was expanded and it was decide that IG was not needed so now we have bare ground wires laying in bare metal cable trays attached to IG ground points, cable trays are fastened to earth ground. Jimmie IMHO IG circuits were largely black magic. There were a few manufacturers that wanted the isolated ground to be tied *only* to a local ground rod (no connection to the electrical system). It was a major code violation and safety hazard. -- bud-- |
#21
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
In article , Ashton Crusher wrote:
On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 |
#22
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
|
#23
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Tue, 18 Aug 2009 00:05:10 -0700, Ashton Crusher
wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: In article , "William Munny" wrote: In some hospitals and office buildings, I see some electrical outlets that are red or orange (not the outlets cover plates, the outlet itself). What's that all about? Red = connected to emergency power (nearly all hospitals, and many office buildings, have backup generators in case utility power fails) Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? The "u" ground is not connected to the "frame" ground. |
#24
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Tue, 18 Aug 2009 10:30:21 -0400, wrote:
On Tue, 18 Aug 2009 07:22:52 -0700 (PDT), Chip C wrote: On Aug 18, 10:12Â*am, wrote: On Tue, 18 Aug 2009 07:07:06 -0700 (PDT), Chip C wrote: On Aug 18, 8:31Â*am, stan wrote: On Aug 18, 9:43Â*pm, (Doug Miller) wrote: In article , Ashton Crusher wrote: On Sat, 15 Aug 2009 08:33:57 GMT, (Doug Miller) wrote: Orange = isolated ground (used for sensitive electronic equipment, usually medical or laboratory instruments, or high-end computer gear) How is isolated ground different then "regular" ground? http://tinyurl.com/n937l4 Thanks to all posters. Learned something. And made one think. Thank- you. Sounds like 'Isolated' Ground might also be called an 'Individual' Ground! In other words the grounding wire from this type of outlet (orange!) is run individually to the grounding point; not using the ground used for a 'run' or group of 'regular' outlets. Have only used an orange outlet once, connected to the output of a UPS located in our basement and wired up stairs to the room with the main PC etc. AFIK took the ground back to the output of the UPS. But as one poster pointed out if we have other computer type gear (say printers or scanners etc. plugged into regular outlets) their grounds may inadvertently be connected via the various cables connecting them to the main computer with its isolated ground. Thus possibly defeating the purpose of the individual ground? The http://tinyurl.com/n937l4 was a useful explanatory. That's a good article about the hoo-hah surrounding isolated ground. I'm convinced that architects put them in out of rote habit. I've personally never seen a computer with documentation that requires them. I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. The orange outlet at least guarantees you a real copper ground all the way back to something earthed. As others have said, today's codes, especially for hospitals, now guarantee this for all outlets. I am also told that the orange outlets can indicate a circuit fed by a (nearby) isolation transformer, on the output side of which the neutral is re-referenced (ie, tied) to ground. This guarantees that at the outlet, ground and neutral are close together in voltage. Otherwise, in large commercial buildings, as you get further from the point of grounding you can find that ground and neutral not only have noise relative to each other but are far apart in DC levels. As others have said, the read outlets are on circuits that can be fed by the generators if the utility power cuts out. (And yes, the breakers for these circuits are in bright read service panels.) But be warned, a lot of places do generator and cutover tests at some regular schedule, usually at some early morning hour, which cause outages of a second or so. Much hospital equipment (fridges, lighting, elevators, plus patient support equipment that has internal batteries) ride through these fine, but computers don't. And of course, when a utility outage happens, it takes time for the generators to ramp up (the nominal standard is generally 15 seconds, in the real world can be longer). Bottom line: don't plug a computer in to a hospital red outlet without a UPS. Chip C Isolation transformer is there for safety. Yes, in cases where its output is not referenced to earth. The two- prong shaver outlets that used to be in bathroom light fixtures were like this. Also I hear that in the UK (and other 240V places??) they use 120V isolated power on outdoor construction sites. If the one of the transformer output legs is tied to earth, then I don't see the safety benefit. Chip C Isolation transformer is for human safety. A NON GROUNDED isolation transformer is for safety. A grounded isolation transformer is for"noise" reduction on the line and elimination of ground loop currents and floating grounds. |
#26
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
In article , Chip C wrote:
I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. Not "in some places" -- anywhere that has adopted the U.S. National Electrical Code. Not "at some time" -- always. Not "was ok" -- still is ok. The NEC specifically permits the use of metal conduit of various types to be used as the equipment grounding conductor. Bare or green wires are not necessary. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. Not if it's properly grounded, it doesn't. |
#27
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
In article ,
The Daring Dufas wrote: I guess they didn't want any stray electric currents affecting the multi million dollar Cray Super Computer. TDD Free association, probably my favorite quote of all time: "I used a #2 pencil and a quadrille pad." (Seymour Cray's response to "What kind of computer did you use to design the Cray supercomputer?") |
#28
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Tue, 18 Aug 2009 15:15:22 GMT, (Doug Miller)
wrote: In article , wrote: On Wed, 19 Aug 2009 03:48:21 GMT, (Doug Miller) wrote: In article , Chip C wrote: I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. Not "in some places" -- anywhere that has adopted the U.S. National Electrical Code. Not "at some time" -- always. Not "was ok" -- still is ok. The NEC specifically permits the use of metal conduit of various types to be used as the equipment grounding conductor. Bare or green wires are not necessary. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. Not if it's properly grounded, it doesn't. "proerly grounded" and EMT as ground is an oxymoron. Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. |
#29
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
A couple generations ago, colored outlets have to move to
the back of the hospital, please. -- Christopher A. Young Learn more about Jesus www.lds.org .. |
#30
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On 8/19/2009 8:47 PM spake thus:
On Tue, 18 Aug 2009 15:15:22 GMT, (Doug Miller) wrote: In article , wrote: On Wed, 19 Aug 2009 03:48:21 GMT, (Doug Miller) wrote: In article , Chip C wrote: I believe that audio and signal processing equipment might benefit from them, since in some places (at some time) I hear was ok to use the metallic conduit as the circuit's ground, and not pull a bare or green wire. Not "in some places" -- anywhere that has adopted the U.S. National Electrical Code. Not "at some time" -- always. Not "was ok" -- still is ok. The NEC specifically permits the use of metal conduit of various types to be used as the equipment grounding conductor. Bare or green wires are not necessary. The conduit picks up a lot of noise, so it causes problems for equipment that uses the ground as a signal reference level. Not if it's properly grounded, it doesn't. "proerly grounded" and EMT as ground is an oxymoron. Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. -- Found--the gene that causes belief in genetic determinism |
#31
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
|
#32
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
On Thu, 20 Aug 2009 11:19:14 -0700, David Nebenzahl
wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. The problem is, the NEC allows either one to be used as a ground - and the "dimple" is NOT a safe ground. The compression connector, wrench tite - perhaps. |
#33
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
David Nebenzahl wrote:
On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. Chuckle. At work, on certain data circuits, they braze or epoxy the joints on the conduit, done with compression fittings. Before they pull the copper or fiber, of course. Of course, a ground path isn't what they are after. -- aem sends... |
#34
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
aemeijers wrote:
David Nebenzahl wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. Chuckle. At work, on certain data circuits, they braze or epoxy the joints on the conduit, done with compression fittings. Before they pull the copper or fiber, of course. Of course, a ground path isn't what they are after. -- aem sends... do they also happen to have walls covered with sheets of copper soldered together? I've worked in some places like that... nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#35
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
Nate Nagel wrote:
aemeijers wrote: David Nebenzahl wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. Chuckle. At work, on certain data circuits, they braze or epoxy the joints on the conduit, done with compression fittings. Before they pull the copper or fiber, of course. Of course, a ground path isn't what they are after. -- aem sends... do they also happen to have walls covered with sheets of copper soldered together? I've worked in some places like that... nate Nah, the hardware itself is shielded now. But there are some storage rooms in the dungeon, now used for other things, that are covered with expanded metal mesh over the concrete block, and in the plastered ceiling. There is one room that I suspect has the sort of wallpaper you describe, but thankfully I'm not allowed in there. The paperwork to be allowed in the room in front of that room, and use the hardware there, was bad enough. -- aem sends... |
#36
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
aemeijers wrote:
Nate Nagel wrote: aemeijers wrote: David Nebenzahl wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. Chuckle. At work, on certain data circuits, they braze or epoxy the joints on the conduit, done with compression fittings. Before they pull the copper or fiber, of course. Of course, a ground path isn't what they are after. -- aem sends... do they also happen to have walls covered with sheets of copper soldered together? I've worked in some places like that... nate Nah, the hardware itself is shielded now. But there are some storage rooms in the dungeon, now used for other things, that are covered with expanded metal mesh over the concrete block, and in the plastered ceiling. There is one room that I suspect has the sort of wallpaper you describe, but thankfully I'm not allowed in there. The paperwork to be allowed in the room in front of that room, and use the hardware there, was bad enough. -- aem sends... y'know, now that I think about it, once upon a time expanded metal mesh was used for lath for plasterwork. I know my high school was constructed that way; not sure why they spec'd plaster and not drywall as it was built in 1972 or 1973 I believe. Wouldn't that play holy hell with radio reception? Obviously people weren't trying to listen to the radio or watch TV inside a high school, but I'm sure quite a few homes were built like this as well... nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#37
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
Nate Nagel wrote:
aemeijers wrote: Nate Nagel wrote: aemeijers wrote: David Nebenzahl wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. Chuckle. At work, on certain data circuits, they braze or epoxy the joints on the conduit, done with compression fittings. Before they pull the copper or fiber, of course. Of course, a ground path isn't what they are after. -- aem sends... do they also happen to have walls covered with sheets of copper soldered together? I've worked in some places like that... nate Nah, the hardware itself is shielded now. But there are some storage rooms in the dungeon, now used for other things, that are covered with expanded metal mesh over the concrete block, and in the plastered ceiling. There is one room that I suspect has the sort of wallpaper you describe, but thankfully I'm not allowed in there. The paperwork to be allowed in the room in front of that room, and use the hardware there, was bad enough. -- aem sends... y'know, now that I think about it, once upon a time expanded metal mesh was used for lath for plasterwork. I know my high school was constructed that way; not sure why they spec'd plaster and not drywall as it was built in 1972 or 1973 I believe. Wouldn't that play holy hell with radio reception? Obviously people weren't trying to listen to the radio or watch TV inside a high school, but I'm sure quite a few homes were built like this as well... nate No, the wall mesh in these rooms was obvious RF sheilding. You could see where there used to be a mesh door to complete the cage. I guess they figured floor didn't need shielding, since that part of building was well below grade, with no sewers and such below it. -- aem sends... |
#38
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
wrote:
On Thu, 20 Aug 2009 11:19:14 -0700, David Nebenzahl wrote: On 8/20/2009 11:05 AM spake thus: On Thu, 20 Aug 2009 10:56:39 -0700, David Nebenzahl wrote: Not according to publishers of the NEC, it isn't. "The equipment grounding conductor ... shall be one or more ... of the following: ... Electrical metallic tubing...." [2008 NEC, Article 250.118] I imagine they know a little more about it than you do. EMT in a dry location - OK. But with humidity, and particularly humidty and vibration, the integrity of the ground suffers in a short time. I would never depend on the EMT for a safety ground. This seems to be analogous to backstabbed connections vs. screw-terminal connections: allowed by the NEC, but not as good a technique. Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. That is true if you use a green wire ground too. Workmanship is the key to any installation. Most of the industrial jobs I inspected specified compression connectors wrench tight. That is a pretty solid ground path. They still pulled a green wire most of the time. Yes. I forgot to mention that when I run conduit, I much prefer the compression connectors to the "make-a-dimple-in-the-tubing-with-a-screw" ones, which always seem a bit on the cheesy side to me. The problem is, the NEC allows either one to be used as a ground - and the "dimple" is NOT a safe ground. The compression connector, wrench tite - perhaps. I'm sure the code making panel will be interested - submit a code change proposal. Be sure to include pictures of the dead bodies - it is very effective. On the other hand, the code panels are not likely to make changes based only on opinion. "Dimple" is not a good description, as there were also fittings that used a compression tool to create a "dimple". (They still allowed?) In addition to using compression fittings you can use non-diecast fittings (not sure what they are called). They are a lot better connection on set-screw fittings. Or compression non-diecast fittings. -- bud-- |
#39
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
aemeijers | 2009-08-20 | 10:39:27 PM wrote:
do they also happen to have walls covered with sheets of copper soldered together? I've worked in some places like that... Nah, the hardware itself is shielded now. But there are some storage rooms in the dungeon, now used for other things, that are covered with expanded metal mesh over the concrete block, and in the plastered ceiling. There is one room that I suspect has the sort of wallpaper you describe, but thankfully I'm not allowed in there. The paperwork to be allowed in the room in front of that room, and use the hardware there, was bad enough. y'know, now that I think about it, once upon a time expanded metal mesh was used for lath for plasterwork. I know my high school was constructed that way; not sure why they spec'd plaster and not drywall as it was built in 1972 or 1973 I believe. Wouldn't that play holy hell with radio reception? Obviously people weren't trying to listen to the radio or watch TV inside a high school, but I'm sure quite a few homes were built like this as well... No, the wall mesh in these rooms was obvious RF sheilding. You could see where there used to be a mesh door to complete the cage. I guess they figured floor didn't need shielding, since that part of building was well below grade, with no sewers and such below it. I once watched the construction of a Tempest-class area: * Commercial metal studs * One layer of metal-coated 5/8" wallboard on each side, metal out * Tape seams with metal tape * Another layer of metal-coated wallboard, seams shifted four feet * Tape seams with metal tape * One layer of regular wallboard for the finish surface * Speakers to play music inside the walls * Motion detectors to detect motion inside the walls They did the ceiling after the walls closed in, so I didn't get to see what happened there, but I'm sure it was equally impressive. -- Steve Bell New Life Home Improvement Arlington, TX USA |
#40
Posted to alt.home.repair
|
|||
|
|||
Colored Electrical Outlets
Think about it: with EMT, all it takes is one loose screw somewhere in the line to sever, or at least seriously degrade, the ground connection. So long as there is any kind of "connection" a fault will start an arc that will "trip" the CB. I was installing some foil insulation on a wall with a outlet box. The foil just brushed against the hot wire and FLASH, POP the breaker tripped. I guess the foil had been grounded by another outlet's plaster ears. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
220 electrical outlets? | Woodworking | |||
electrical outlets | Home Repair | |||
Ungrounded Electrical outlets | Home Repair | |||
No boxes behind electrical outlets | Home Repair | |||
Question about red electrical outlets | Home Repair |