As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default # of wires per jucntion box -- includes the ground wire?

Len56 wrote:
As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


Yes. (But... )

You don't have to count wires under #14 from a fixture to wires in the box.

A wire originating in and terminating in the same box (ground from green
terminal of an outlet to box ground, for example) doesn't count.

A wire running thru a box w/o splice or tap counts as only one wire
(from which one can deduce the answer to the original question, btw).

And, of course, the limit for #14 would be higher than for #12 (probably
by one altho I didn't check tables).

There are other conditions/adjustments but those are the highlights that
are probably the pertinent ones for the application.

--

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default # of wires per jucntion box -- includes the ground wire?

On 2009-03-17, Len56 wrote:

As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


Each circuit conductor entering the box is counted once. All the EGCs
(ground wires) together count only once.

Cheers, Wayne
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 28
Default # of wires per jucntion box -- includes the ground wire?

Thanks.

"Wayne Whitney" wrote in message
...
On 2009-03-17, Len56 wrote:

As an example, I am looking at a ceiling fan box that says that it is
rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box,
or
is it just the conducting wires (such as the black and white wires)?


Each circuit conductor entering the box is counted once. All the EGCs
(ground wires) together count only once.

Cheers, Wayne


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 238
Default # of wires per jucntion box -- includes the ground wire?

Len56 wrote:
As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


all the bares count as one.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default # of wires per jucntion box -- includes the ground wire?

In article , Wayne Whitney wrote:
On 2009-03-17, Len56 wrote:

As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


Each circuit conductor entering the box is counted once. All the EGCs
(ground wires) together count only once.


Note the distinction: circuit conductors are counted. Fixture conductors (the
leads to a lamp, for example) are not.

Also:
- a conductor that both enters and leaves the box, without being spliced, is
counted only once
- any conductor, no part of which leaves the box, is not counted at all.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default # of wires per jucntion box -- includes the ground wire?

In article , dpb wrote:
Len56 wrote:
As an example, I am looking at a ceiling fan box that says that it is rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box, or
is it just the conducting wires (such as the black and white wires)?


Yes. (But... )

You don't have to count wires under #14 from a fixture to wires in the box.

A wire originating in and terminating in the same box (ground from green
terminal of an outlet to box ground, for example) doesn't count.


Not quite. The rule is "no part of which leaves the box". I grant that it
would be highly unusual, perhaps unique, for a conductor to leave the box in
which it originates and return and be terminated in that same box, but any
such hypothetical conductor that might exist must be counted as two.

A wire running thru a box w/o splice or tap counts as only one wire
(from which one can deduce the answer to the original question, btw).

And, of course, the limit for #14 would be higher than for #12 (probably
by one altho I didn't check tables).


Not necessarily. The OP said the box is marked for up to five #12 conductors,
which means that its capacity is at least 5 * 2.25 cubic inches per conductor,
or 11.25 cubic inches -- but that is *not* big enough for six #14s at 2.00
cubic inches each.

There are other conditions/adjustments but those are the highlights that
are probably the pertinent ones for the application.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default # of wires per jucntion box -- includes the ground wire?


"Doug Miller" wrote in message
...
In article , Wayne Whitney
wrote:
On 2009-03-17, Len56 wrote:

As an example, I am looking at a ceiling fan box that says that it is
rated
for up to five #12 wires.

Does that include the bare ground wires that will be going into the box,
or
is it just the conducting wires (such as the black and white wires)?


Each circuit conductor entering the box is counted once. All the EGCs
(ground wires) together count only once.


Note the distinction: circuit conductors are counted. Fixture conductors
(the
leads to a lamp, for example) are not.




Also:
- a conductor that both enters and leaves the box, without being spliced,
is
counted only once


*Just to clarify the above according to 314.16(B)(1): "Each loop or coil of
unbroken conductor not less than twice the minimum length required for free
conductors in 300.14 shall be counted twice".

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Adding new Circuits to Room Addition... 2 wires or 2 wires + Ground? [email protected] Home Repair 2 March 20th 08 10:58 PM
Bonded ground wires vs. earth ground wire Eigenvector Home Repair 21 December 28th 06 05:31 PM
ground wire extension (anti-static ground) toronado455 Electronics Repair 5 July 18th 06 08:44 AM
Ground Wires In A Plastic Gang Box & Wire Nut Question ? Robert11 Home Repair 7 April 24th 05 08:52 PM
Grounding Of Ground Wires In An Electrical Gang Box (how to handle the green ground wires) Robert11 Home Repair 7 March 8th 05 03:45 PM


All times are GMT +1. The time now is 11:31 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"