I am about to add electric baseboard heat to a finished attic space in a
house that I own.

The wiring diagrams in a book that I have and on the Internet show to create
a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going
from the heater to the thermostat. I assume that means that at the panel
box there would be a double breaker to create the 220/240-volt, and that the
white wire would be coded at the panel and at the heater to be black. But,
that seems a little strange to me.

Is that how it is supposed to be done, or is it better or more correct to
run 12/3 as the feed and use the black and red wires as the hot wires?


  #2   Report Post  
Posted to alt.home.repair
N8N N8N is offline
external usenet poster
 
Posts: 1,192
Default Wiring electric baseboard heaters

On Feb 19, 10:32*am, "RonABC" wrote:
I am about to add electric baseboard heat to a finished attic space in a
house that I own.

The wiring diagrams in a book that I have and on the Internet show to create
a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going
from the heater to the thermostat. *I assume that means that at the panel
box there would be a double breaker to create the 220/240-volt, and that the
white wire would be coded at the panel and at the heater to be black. *But,
that seems a little strange to me.

Is that how it is supposed to be done, or is it better or more correct to
run 12/3 as the feed and use the black and red wires as the hot wires?


No, because there is no need for a neutral for a 240V heater. Just
extra expense and more wires in your boxes.

I'm curious why you'd need 12/3 from the heater to the thermostat?
Are you using electronic thermostats? Typically the 240 just goes
from the panel to the thermostat and then from the thermostat to the
heater.

nate
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Wiring electric baseboard heaters


"RonABC" wrote in message
...
I am about to add electric baseboard heat to a finished attic space in a
house that I own.

The wiring diagrams in a book that I have and on the Internet show to
create a 220/240-volt system using a 12/2 feed up to the heater(s), with
12/3 going from the heater to the thermostat. I assume that means that at
the panel box there would be a double breaker to create the 220/240-volt,
and that the white wire would be coded at the panel and at the heater to
be black. But, that seems a little strange to me.

Is that how it is supposed to be done, or is it better or more correct to
run 12/3 as the feed and use the black and red wires as the hot wires?
I would do as Nate suggested, run the 12/2g from the panel to the line
voltage thermostat, then off the load side of a line voltage double pole
thermostat, run a 12/2g to the heaters



  #4   Report Post  
Posted to alt.home.repair
EXT EXT is offline
external usenet poster
 
Posts: 1,661
Default Wiring electric baseboard heaters

RBM wrote:
"RonABC" wrote in message
...
I am about to add electric baseboard heat to a finished attic space
in a house that I own.

The wiring diagrams in a book that I have and on the Internet show
to create a 220/240-volt system using a 12/2 feed up to the
heater(s), with 12/3 going from the heater to the thermostat. I
assume that means that at the panel box there would be a double
breaker to create the 220/240-volt, and that the white wire would
be coded at the panel and at the heater to be black. But, that
seems a little strange to me. Is that how it is supposed to be done, or
is it better or more
correct to run 12/3 as the feed and use the black and red wires as
the hot wires? I would do as Nate suggested, run the 12/2g from the
panel to the
line voltage thermostat, then off the load side of a line voltage
double pole thermostat, run a 12/2g to the heaters


There is a special 12/2 made for 220v heaters, the outer jacket is red and
the wires inside are colored red and black with a ground. It is acceptable
to run regular 12/2 cable but the white wire must be recolored with most any
color except white, gray or green.

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

N8N wrote:

I'm curious why you'd need 12/3 from the heater to the thermostat?
Are you using electronic thermostats? Typically the 240 just goes
from the panel to the thermostat and then from the thermostat to the
heater.


I'll have to check the wiring diagram again to be sure I read it correctly.
It's in a Black and Decker wiring book that I have at the house (page 171, I
think), and I thought I remembered seeing 12/3 going to the thermostat which
was between two heater units. Maybe it's because the diagram I was looking
at showed the thermostat between the two heater units, or maybe I just plain
read it wrong, or I am not correctly rembering what I saw. I'll post back
later today when I look at the book again.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

EXT wrote:

There is a special 12/2 made for 220v heaters, the outer jacket is
red and the wires inside are colored red and black with a ground. It
is acceptable to run regular 12/2 cable but the white wire must be
recolored with most any color except white, gray or green.


That's interesting. I've never seen that, but I'll look for it.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

Also, I just found the following forum on this topic:

Page 1 of the thread:

http://www.ridgidforum.com/forum/sho...b8953& t=9489



Page 2 of the thread:



http://www.ridgidforum.com/forum/sho...?t=9489&page=2




  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Wiring electric baseboard heaters


"RonABC" wrote in message
...
Also, I just found the following forum on this topic:

Page 1 of the thread:

http://www.ridgidforum.com/forum/sho...b8953& t=9489



Page 2 of the thread:



http://www.ridgidforum.com/forum/sho...?t=9489&page=2



Just follow the instruction of qrocking, in page 2, and be sure to do your
load calculation to determine the total amperage of the heaters. Typical
electric heat thermostats are rated for 22 amps



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

RBM wrote:
"RonABC" wrote in message
...
Also, I just found the following forum on this topic:

Page 1 of the thread:

http://www.ridgidforum.com/forum/sho...b8953& t=9489



Page 2 of the thread:



http://www.ridgidforum.com/forum/sho...?t=9489&page=2



Just follow the instruction of qrocking, in page 2, and be sure to
do your load calculation to determine the total amperage of the
heaters. Typical electric heat thermostats are rated for 22 amps


Thanks. Will do.

The free and generous help that you and others provide on this forum is
awesome!


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,447
Default Wiring electric baseboard heaters

On Feb 19, 12:32*pm, "RonABC" wrote:
I am about to add electric baseboard heat to a finished attic space in a
house that I own.

The wiring diagrams in a book that I have and on the Internet show to create
a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going
from the heater to the thermostat. *I assume that means that at the panel
box there would be a double breaker to create the 220/240-volt, and that the
white wire would be coded at the panel and at the heater to be black. *But,
that seems a little strange to me.

Is that how it is supposed to be done, or is it better or more correct to
run 12/3 as the feed and use the black and red wires as the hot wires?


Assuming your thermostats are 230 volt 'line voltage type' ?????

Also don't know why you need 3 conductor; either from panel to
thermostat or thermostat to heater!

More normal (and exactly how this house 1970 is wired) is 12-2 red/
black (with a bare ground conductor of course).

Black/white can be used provided the white is colored or taped (red
nail polish will do) to identify that it is hot (not neutral!).

You are correct, the red and black are connected through a double-pole
circuit breaker for #12 AWG that's a 20 amp DP breaker. Don't forget
the ground connection at each point also. For 230 there is no neutral.
Use standard wiring practice; insurance companies (both for property
and life insurance) can be picky!!!!!!!

With some (double pole thermostats) both red and black connect
'through' the thermostat. Most of my original ones do so.

But I have one or two that are single pole; in that case the black
goes through the thermostat and the red is connected straight through.

Make sure you thoroughly understand how the thermostat must be wired
also that they are the correct type. There have been cases where
people have hooked up low voltage thermostats to 230 volt line voltage
and blown the sh** out of them. In one case starting a small fire!

Low voltage thermostats are commonly used to control the low voltage
controls of furnaces etc. Or they can, using extra hardware (control
relays) control line voltage heaters. That then becomes a matter of
why use relays, where to mount them and how to get low voltage wire
from them to the 'low voltage thermostats'! Different discussion
altogether.

BTW we have found electric baseboard heaters and line voltage
thermostats very reliable. Since 1970 we have less than $100 in
maintenance. Two thermostats and one circuit breaker.

Any doubts get advice/help. In this area we have had three fatalities
(all children!) and a total of 3 fires all blamed on electrical
problems prior to Feb 15th, this year of 2009!

No matter what heating is used do not let people sleep in areas
without escape routes; whether that is basements or attics etc. Equip
(for only a few dollars) any new areas with smoke detectors.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 238
Default Wiring electric baseboard heaters

RonABC wrote:
I am about to add electric baseboard heat to a finished attic space in a
house that I own.

The wiring diagrams in a book that I have and on the Internet show to create
a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going
from the heater to the thermostat. I assume that means that at the panel
box there would be a double breaker to create the 220/240-volt, and that the
white wire would be coded at the panel and at the heater to be black. But,
that seems a little strange to me.

Is that how it is supposed to be done, or is it better or more correct to
run 12/3 as the feed and use the black and red wires as the hot wires?


white marked black is fine.

s
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

Thanks. That's all very good advice.

I did have it wrong when I thought I saw something about needing 3-wire in
the circuit. I looked again at the wiring diagram and I had read it wrong.


terry wrote:
On Feb 19, 12:32 pm, "RonABC" wrote:
I am about to add electric baseboard heat to a finished attic space
in a house that I own.

The wiring diagrams in a book that I have and on the Internet show
to create a 220/240-volt system using a 12/2 feed up to the
heater(s), with 12/3 going from the heater to the thermostat. I
assume that means that at the panel box there would be a double
breaker to create the 220/240-volt, and that the white wire would be
coded at the panel and at the heater to be black. But, that seems a
little strange to me.

Is that how it is supposed to be done, or is it better or more
correct to run 12/3 as the feed and use the black and red wires as
the hot wires?


Assuming your thermostats are 230 volt 'line voltage type' ?????

Also don't know why you need 3 conductor; either from panel to
thermostat or thermostat to heater!

More normal (and exactly how this house 1970 is wired) is 12-2 red/
black (with a bare ground conductor of course).

Black/white can be used provided the white is colored or taped (red
nail polish will do) to identify that it is hot (not neutral!).

You are correct, the red and black are connected through a double-pole
circuit breaker for #12 AWG that's a 20 amp DP breaker. Don't forget
the ground connection at each point also. For 230 there is no neutral.
Use standard wiring practice; insurance companies (both for property
and life insurance) can be picky!!!!!!!

With some (double pole thermostats) both red and black connect
'through' the thermostat. Most of my original ones do so.

But I have one or two that are single pole; in that case the black
goes through the thermostat and the red is connected straight through.

Make sure you thoroughly understand how the thermostat must be wired
also that they are the correct type. There have been cases where
people have hooked up low voltage thermostats to 230 volt line voltage
and blown the sh** out of them. In one case starting a small fire!

Low voltage thermostats are commonly used to control the low voltage
controls of furnaces etc. Or they can, using extra hardware (control
relays) control line voltage heaters. That then becomes a matter of
why use relays, where to mount them and how to get low voltage wire
from them to the 'low voltage thermostats'! Different discussion
altogether.

BTW we have found electric baseboard heaters and line voltage
thermostats very reliable. Since 1970 we have less than $100 in
maintenance. Two thermostats and one circuit breaker.

Any doubts get advice/help. In this area we have had three fatalities
(all children!) and a total of 3 fires all blamed on electrical
problems prior to Feb 15th, this year of 2009!

No matter what heating is used do not let people sleep in areas
without escape routes; whether that is basements or attics etc. Equip
(for only a few dollars) any new areas with smoke detectors.



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 65
Default Wiring electric baseboard heaters

N8N wrote:

I'm curious why you'd need 12/3 from the heater to the thermostat?
Are you using electronic thermostats? Typically the 240 just goes
from the panel to the thermostat and then from the thermostat to the
heater.


Thanks. My mistake. I checked the wiring diagram again and what I thought
I remembered seeing was not correct. It does show all 2-wire and no 3-wire.
I had briefly noticed red and black wires in the circuit and I was thinking
that meant 3-wire. But, upon looking more carefully, I see now that the red
and black wires were just the thermostat wire colors.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric baseboard heaters safe? [email protected] Home Repair 8 May 25th 07 05:58 AM
Electric Baseboard Heaters Scot Home Repair 1 October 28th 06 03:39 PM
Wiring multiple baseboard heaters [email protected] Home Repair 17 September 27th 06 02:38 AM
Electric baseboard heaters Remi Home Repair 7 September 19th 06 02:53 AM
Replacing Thermosats for Intertherm Electric Hot Water Baseboard Heaters Mike Home Repair 6 January 12th 05 02:53 AM


All times are GMT +1. The time now is 06:38 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"