Wiring electric baseboard heaters
I am about to add electric baseboard heat to a finished attic space in a
house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? |
#2
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
On Feb 19, 10:32*am, "RonABC" wrote:
I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. *I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. *But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? No, because there is no need for a neutral for a 240V heater. Just extra expense and more wires in your boxes. I'm curious why you'd need 12/3 from the heater to the thermostat? Are you using electronic thermostats? Typically the 240 just goes from the panel to the thermostat and then from the thermostat to the heater. nate |
#3
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
"RonABC" wrote in message ... I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? I would do as Nate suggested, run the 12/2g from the panel to the line voltage thermostat, then off the load side of a line voltage double pole thermostat, run a 12/2g to the heaters |
#4
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
RBM wrote:
"RonABC" wrote in message ... I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? I would do as Nate suggested, run the 12/2g from the panel to the line voltage thermostat, then off the load side of a line voltage double pole thermostat, run a 12/2g to the heaters There is a special 12/2 made for 220v heaters, the outer jacket is red and the wires inside are colored red and black with a ground. It is acceptable to run regular 12/2 cable but the white wire must be recolored with most any color except white, gray or green. |
#5
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
N8N wrote:
I'm curious why you'd need 12/3 from the heater to the thermostat? Are you using electronic thermostats? Typically the 240 just goes from the panel to the thermostat and then from the thermostat to the heater. I'll have to check the wiring diagram again to be sure I read it correctly. It's in a Black and Decker wiring book that I have at the house (page 171, I think), and I thought I remembered seeing 12/3 going to the thermostat which was between two heater units. Maybe it's because the diagram I was looking at showed the thermostat between the two heater units, or maybe I just plain read it wrong, or I am not correctly rembering what I saw. I'll post back later today when I look at the book again. |
#6
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
EXT wrote:
There is a special 12/2 made for 220v heaters, the outer jacket is red and the wires inside are colored red and black with a ground. It is acceptable to run regular 12/2 cable but the white wire must be recolored with most any color except white, gray or green. That's interesting. I've never seen that, but I'll look for it. |
#7
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
Also, I just found the following forum on this topic:
Page 1 of the thread: http://www.ridgidforum.com/forum/sho...b8953& t=9489 Page 2 of the thread: http://www.ridgidforum.com/forum/sho...?t=9489&page=2 |
#8
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
"RonABC" wrote in message ... Also, I just found the following forum on this topic: Page 1 of the thread: http://www.ridgidforum.com/forum/sho...b8953& t=9489 Page 2 of the thread: http://www.ridgidforum.com/forum/sho...?t=9489&page=2 Just follow the instruction of qrocking, in page 2, and be sure to do your load calculation to determine the total amperage of the heaters. Typical electric heat thermostats are rated for 22 amps |
#9
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
RBM wrote:
"RonABC" wrote in message ... Also, I just found the following forum on this topic: Page 1 of the thread: http://www.ridgidforum.com/forum/sho...b8953& t=9489 Page 2 of the thread: http://www.ridgidforum.com/forum/sho...?t=9489&page=2 Just follow the instruction of qrocking, in page 2, and be sure to do your load calculation to determine the total amperage of the heaters. Typical electric heat thermostats are rated for 22 amps Thanks. Will do. The free and generous help that you and others provide on this forum is awesome! |
#10
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
On Feb 19, 12:32*pm, "RonABC" wrote:
I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. *I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. *But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? Assuming your thermostats are 230 volt 'line voltage type' ????? Also don't know why you need 3 conductor; either from panel to thermostat or thermostat to heater! More normal (and exactly how this house 1970 is wired) is 12-2 red/ black (with a bare ground conductor of course). Black/white can be used provided the white is colored or taped (red nail polish will do) to identify that it is hot (not neutral!). You are correct, the red and black are connected through a double-pole circuit breaker for #12 AWG that's a 20 amp DP breaker. Don't forget the ground connection at each point also. For 230 there is no neutral. Use standard wiring practice; insurance companies (both for property and life insurance) can be picky!!!!!!! With some (double pole thermostats) both red and black connect 'through' the thermostat. Most of my original ones do so. But I have one or two that are single pole; in that case the black goes through the thermostat and the red is connected straight through. Make sure you thoroughly understand how the thermostat must be wired also that they are the correct type. There have been cases where people have hooked up low voltage thermostats to 230 volt line voltage and blown the sh** out of them. In one case starting a small fire! Low voltage thermostats are commonly used to control the low voltage controls of furnaces etc. Or they can, using extra hardware (control relays) control line voltage heaters. That then becomes a matter of why use relays, where to mount them and how to get low voltage wire from them to the 'low voltage thermostats'! Different discussion altogether. BTW we have found electric baseboard heaters and line voltage thermostats very reliable. Since 1970 we have less than $100 in maintenance. Two thermostats and one circuit breaker. Any doubts get advice/help. In this area we have had three fatalities (all children!) and a total of 3 fires all blamed on electrical problems prior to Feb 15th, this year of 2009! No matter what heating is used do not let people sleep in areas without escape routes; whether that is basements or attics etc. Equip (for only a few dollars) any new areas with smoke detectors. |
#11
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
RonABC wrote:
I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? white marked black is fine. s |
#12
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
Thanks. That's all very good advice.
I did have it wrong when I thought I saw something about needing 3-wire in the circuit. I looked again at the wiring diagram and I had read it wrong. terry wrote: On Feb 19, 12:32 pm, "RonABC" wrote: I am about to add electric baseboard heat to a finished attic space in a house that I own. The wiring diagrams in a book that I have and on the Internet show to create a 220/240-volt system using a 12/2 feed up to the heater(s), with 12/3 going from the heater to the thermostat. I assume that means that at the panel box there would be a double breaker to create the 220/240-volt, and that the white wire would be coded at the panel and at the heater to be black. But, that seems a little strange to me. Is that how it is supposed to be done, or is it better or more correct to run 12/3 as the feed and use the black and red wires as the hot wires? Assuming your thermostats are 230 volt 'line voltage type' ????? Also don't know why you need 3 conductor; either from panel to thermostat or thermostat to heater! More normal (and exactly how this house 1970 is wired) is 12-2 red/ black (with a bare ground conductor of course). Black/white can be used provided the white is colored or taped (red nail polish will do) to identify that it is hot (not neutral!). You are correct, the red and black are connected through a double-pole circuit breaker for #12 AWG that's a 20 amp DP breaker. Don't forget the ground connection at each point also. For 230 there is no neutral. Use standard wiring practice; insurance companies (both for property and life insurance) can be picky!!!!!!! With some (double pole thermostats) both red and black connect 'through' the thermostat. Most of my original ones do so. But I have one or two that are single pole; in that case the black goes through the thermostat and the red is connected straight through. Make sure you thoroughly understand how the thermostat must be wired also that they are the correct type. There have been cases where people have hooked up low voltage thermostats to 230 volt line voltage and blown the sh** out of them. In one case starting a small fire! Low voltage thermostats are commonly used to control the low voltage controls of furnaces etc. Or they can, using extra hardware (control relays) control line voltage heaters. That then becomes a matter of why use relays, where to mount them and how to get low voltage wire from them to the 'low voltage thermostats'! Different discussion altogether. BTW we have found electric baseboard heaters and line voltage thermostats very reliable. Since 1970 we have less than $100 in maintenance. Two thermostats and one circuit breaker. Any doubts get advice/help. In this area we have had three fatalities (all children!) and a total of 3 fires all blamed on electrical problems prior to Feb 15th, this year of 2009! No matter what heating is used do not let people sleep in areas without escape routes; whether that is basements or attics etc. Equip (for only a few dollars) any new areas with smoke detectors. |
#13
Posted to alt.home.repair
|
|||
|
|||
Wiring electric baseboard heaters
N8N wrote:
I'm curious why you'd need 12/3 from the heater to the thermostat? Are you using electronic thermostats? Typically the 240 just goes from the panel to the thermostat and then from the thermostat to the heater. Thanks. My mistake. I checked the wiring diagram again and what I thought I remembered seeing was not correct. It does show all 2-wire and no 3-wire. I had briefly noticed red and black wires in the circuit and I was thinking that meant 3-wire. But, upon looking more carefully, I see now that the red and black wires were just the thermostat wire colors. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Electric baseboard heaters safe? | Home Repair | |||
Electric Baseboard Heaters | Home Repair | |||
Wiring multiple baseboard heaters | Home Repair | |||
Electric baseboard heaters | Home Repair | |||
Replacing Thermosats for Intertherm Electric Hot Water Baseboard Heaters | Home Repair |