Hi all,
I'm quite confident wiring some baseboards that I need to install... they're 240V, various sizes. What I'm not sure of is how to have multiple baseboards on the same circuit? Can I do it with a 2-conductor wire (as both conductors are "hot")? I've been scouring the net looking for a diagram of the circuit from... say... breaker--baseboard#1--baseboard#2--baseboard#3 I assume also that multiple thermostats could be wired in before each heater to control that specific heater independantly from others on the circuit.. (or alternatively have one thermostat at the beginning of the circuit that would then limit all heaters on the circuit. Any help greatly appreciated!! Sincerely, Chris |
#3
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
|
#4
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
My two cents. Might also want to ensure you figure in the length of wire
to be used. There is some resistance (power loss) for longer runs. wrote: Hi all, I'm quite confident wiring some baseboards that I need to install... they're 240V, various sizes. What I'm not sure of is how to have multiple baseboards on the same circuit? Can I do it with a 2-conductor wire (as both conductors are "hot")? I've been scouring the net looking for a diagram of the circuit from... say... breaker--baseboard#1--baseboard#2--baseboard#3 I assume also that multiple thermostats could be wired in before each heater to control that specific heater independantly from others on the circuit.. (or alternatively have one thermostat at the beginning of the circuit that would then limit all heaters on the circuit. Any help greatly appreciated!! Sincerely, Chris |
#5
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
wrote in message ups.com... Hi all, I'm quite confident wiring some baseboards that I need to install... they're 240V, various sizes. What I'm not sure of is how to have multiple baseboards on the same circuit? Can I do it with a 2-conductor wire (as both conductors are "hot")? It is easy enough to wire, but bear in mind that the breaker and all the associated wire must be large enough to carry the current required by three heaters. Unless they are tiny, that is a problem. My cottage had three 15a baseboards with #12 wire and a 50a breaker. It also had a 23a water heater on #12 with a 30a breaker. Amazing it didn't burn down in the 35 years it was like that. |
#6
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
You have to calculate the total load you want on each circuit, then use
cables large enough to carry that load. Typically you would run the feed from the breaker box to a wall thermostat location, daisy chain the feed to another wall thermostat location, on and on until you've use up the capacity of the feed. From each wall thermostat location you would run the cables to the heaters controlled by those thermostats wrote in message ups.com... Hi all, I'm quite confident wiring some baseboards that I need to install... they're 240V, various sizes. What I'm not sure of is how to have multiple baseboards on the same circuit? Can I do it with a 2-conductor wire (as both conductors are "hot")? I've been scouring the net looking for a diagram of the circuit from... say... breaker--baseboard#1--baseboard#2--baseboard#3 I assume also that multiple thermostats could be wired in before each heater to control that specific heater independantly from others on the circuit.. (or alternatively have one thermostat at the beginning of the circuit that would then limit all heaters on the circuit. Any help greatly appreciated!! Sincerely, Chris |
#7
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
|
#8
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
Hi all,
Thank you very much for your responses. No disrespect taken... I appreciate all your help and your sound advice. I'll give you some more details on what I've got going so far. Hopefully that will both allow you to help me out a little more and ease any concerns. I have a large supply of standard 12/2 wiring with bare ground (so max 20A, 16A being "common sense") ... which is why I asked. If required I would certainly purchase 3 conductor if I have to, but the cost of copper these days is so prohibitive, I was hoping to use what I have on hand. Apparently the new electrical code coming into force (at least here in BC, Canada) actually allows 100% load on the wire, that said, every professional I have talked to is still abiding by the 80% rule, which just seems like good common sense to me. So that's what I'll do. I'm just trying to plan out my circuits before I start seriously feeding wire.... so here are two examples, is something like this doable? Circuit #1: Living Room: 2500W - room stat Bathroom #1: 500W - stat-on-heater Bathroom #2: 500W - stat-on-heater 3500W = 14.5A (240V) or 15.9A (220V) Circuit #2: Dining Room: 1500W room stat Kitchen: 1000W room stat Bedroom: 1000W - room stat 3500W = 14.5A (240V) or 15.9A (220V) Those loads should keep me in an acceptable range... obviously below code. My question centers more around actual wiring. Is there any benefit in terms of load sharing / wear to series vs. parallel? Do I use the connections on both ends of the heaters (they have identical connections on both ends for convenience) to "pass through", or simply connect them through wirenuts on the same end. And as for the question of efficiency, we looked at all the options when replacing our oil furnace and baseboard was the only realistic and affordable option for us. (heat-pump, retrofit too expensive... gas, price too volatile + retrofit... radiant floor -- inappropriate softwood flooring) Also, considering 100% of the energy you put into an electric baseboard gets turned into heat, it's actually *more* effecient than oil, gas, or wood furnaces in terms of energy use. The actual effective heat you get out of it comes down to the efficiency of your house as a whole, which affects all heating systems equally. Baseboard gives us both ease of installation/expansion, cheap long-term energy (BC has cheapest power in North America), virtually nil maintenance costs, and flexibility to turn off unused portions of the house. |
#9
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
Hi all,
Thank you very much for your responses. No disrespect taken... I appreciate all your help and your sound advice. I'll give you some more details on what I've got going so far. Hopefully that will both allow you to help me out a little more and ease any concerns. I have a large supply of standard 12/2 wiring with bare ground (so max 20A, 16A being "common sense") ... which is why I asked. If required I would certainly purchase 3 conductor if I have to, but the cost of copper these days is so prohibitive, I was hoping to use what I have on hand. Apparently the new electrical code coming into force (at least here in BC, Canada) actually allows 100% load on the wire, that said, every professional I have talked to is still abiding by the 80% rule, which just seems like good common sense to me. So that's what I'll do. I'm just trying to plan out my circuits before I start seriously feeding wire.... so here are two examples, is something like this doable? Circuit #1: Living Room: 2500W - room stat Bathroom #1: 500W - stat-on-heater Bathroom #2: 500W - stat-on-heater 3500W = 14.5A (240V) or 15.9A (220V) Circuit #2: Dining Room: 1500W room stat Kitchen: 1000W room stat Bedroom: 1000W - room stat 3500W = 14.5A (240V) or 15.9A (220V) Those loads should keep me in an acceptable range... obviously below code. My question centers more around actual wiring. Is there any benefit in terms of load sharing / wear to series vs. parallel? Do I use the connections on both ends of the heaters (they have identical connections on both ends for convenience) to "pass through", or simply connect them through wirenuts on the same end. And as for the question of efficiency, we looked at all the options when replacing our oil furnace and baseboard was the only realistic and affordable option for us. (heat-pump, retrofit too expensive... gas, price too volatile + retrofit... radiant floor -- inappropriate softwood flooring) Also, considering 100% of the energy you put into an electric baseboard gets turned into heat, it's actually *more* effecient than oil, gas, or wood furnaces in terms of energy use. The actual effective heat you get out of it comes down to the efficiency of your house as a whole, which affects all heating systems equally. Baseboard gives us both ease of installation/expansion, cheap long-term energy (BC has cheapest power in North America), virtually nil maintenance costs, and flexibility to turn off unused portions of the house. I guess it depends on if your costs for electricity is cheaper than cost of gas it would be cheaper for electric, we have a 85% efficiency furnace, uses pvc pipe for chimney and outside air intake, so i would say that most of the gas (propane) is being turned into heat. our electrical costs here are not as bad as they neighboring state but still cost prohibitive to run all baseboard heating for main source of heating. i imagine that 80% of wire load with all units connectd in series works, cant see why you would put individual thermostats on heaters in the same room though. Different rooms to create custom heating zones seems almost a no-brainer if you got the hardware. |
#10
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
You never put the baseboard units in series, always in parallel. and the
heaters have wiring boxes on both ends just so you have a choice where to run the feed. You leave one end wire nutted together. If you are connecting more than one heater together, run both feed in and feed out cables into one junction box on the heater and parallel them along with the heater conductors, then jump to the next heater. Also, there would be absolutely no reason to run three conductor cable, 12/2 gives you 240 volts + ground, which is all you need wrote in message ps.com... Hi all, Thank you very much for your responses. No disrespect taken... I appreciate all your help and your sound advice. I'll give you some more details on what I've got going so far. Hopefully that will both allow you to help me out a little more and ease any concerns. I have a large supply of standard 12/2 wiring with bare ground (so max 20A, 16A being "common sense") ... which is why I asked. If required I would certainly purchase 3 conductor if I have to, but the cost of copper these days is so prohibitive, I was hoping to use what I have on hand. Apparently the new electrical code coming into force (at least here in BC, Canada) actually allows 100% load on the wire, that said, every professional I have talked to is still abiding by the 80% rule, which just seems like good common sense to me. So that's what I'll do. I'm just trying to plan out my circuits before I start seriously feeding wire.... so here are two examples, is something like this doable? Circuit #1: Living Room: 2500W - room stat Bathroom #1: 500W - stat-on-heater Bathroom #2: 500W - stat-on-heater 3500W = 14.5A (240V) or 15.9A (220V) Circuit #2: Dining Room: 1500W room stat Kitchen: 1000W room stat Bedroom: 1000W - room stat 3500W = 14.5A (240V) or 15.9A (220V) Those loads should keep me in an acceptable range... obviously below code. My question centers more around actual wiring. Is there any benefit in terms of load sharing / wear to series vs. parallel? Do I use the connections on both ends of the heaters (they have identical connections on both ends for convenience) to "pass through", or simply connect them through wirenuts on the same end. And as for the question of efficiency, we looked at all the options when replacing our oil furnace and baseboard was the only realistic and affordable option for us. (heat-pump, retrofit too expensive... gas, price too volatile + retrofit... radiant floor -- inappropriate softwood flooring) Also, considering 100% of the energy you put into an electric baseboard gets turned into heat, it's actually *more* effecient than oil, gas, or wood furnaces in terms of energy use. The actual effective heat you get out of it comes down to the efficiency of your house as a whole, which affects all heating systems equally. Baseboard gives us both ease of installation/expansion, cheap long-term energy (BC has cheapest power in North America), virtually nil maintenance costs, and flexibility to turn off unused portions of the house. |
#11
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
excellent that is exactly what i needed to know
thanks! Chris RBM (remove this) wrote: You never put the baseboard units in series, always in parallel. and the heaters have wiring boxes on both ends just so you have a choice where to run the feed. You leave one end wire nutted together. If you are connecting more than one heater together, run both feed in and feed out cables into one junction box on the heater and parallel them along with the heater conductors, then jump to the next heater. Also, there would be absolutely no reason to run three conductor cable, 12/2 gives you 240 volts + ground, which is all you need wrote in message ps.com... Hi all, Thank you very much for your responses. No disrespect taken... I appreciate all your help and your sound advice. I'll give you some more details on what I've got going so far. Hopefully that will both allow you to help me out a little more and ease any concerns. I have a large supply of standard 12/2 wiring with bare ground (so max 20A, 16A being "common sense") ... which is why I asked. If required I would certainly purchase 3 conductor if I have to, but the cost of copper these days is so prohibitive, I was hoping to use what I have on hand. Apparently the new electrical code coming into force (at least here in BC, Canada) actually allows 100% load on the wire, that said, every professional I have talked to is still abiding by the 80% rule, which just seems like good common sense to me. So that's what I'll do. I'm just trying to plan out my circuits before I start seriously feeding wire.... so here are two examples, is something like this doable? Circuit #1: Living Room: 2500W - room stat Bathroom #1: 500W - stat-on-heater Bathroom #2: 500W - stat-on-heater 3500W = 14.5A (240V) or 15.9A (220V) Circuit #2: Dining Room: 1500W room stat Kitchen: 1000W room stat Bedroom: 1000W - room stat 3500W = 14.5A (240V) or 15.9A (220V) Those loads should keep me in an acceptable range... obviously below code. My question centers more around actual wiring. Is there any benefit in terms of load sharing / wear to series vs. parallel? Do I use the connections on both ends of the heaters (they have identical connections on both ends for convenience) to "pass through", or simply connect them through wirenuts on the same end. And as for the question of efficiency, we looked at all the options when replacing our oil furnace and baseboard was the only realistic and affordable option for us. (heat-pump, retrofit too expensive... gas, price too volatile + retrofit... radiant floor -- inappropriate softwood flooring) Also, considering 100% of the energy you put into an electric baseboard gets turned into heat, it's actually *more* effecient than oil, gas, or wood furnaces in terms of energy use. The actual effective heat you get out of it comes down to the efficiency of your house as a whole, which affects all heating systems equally. Baseboard gives us both ease of installation/expansion, cheap long-term energy (BC has cheapest power in North America), virtually nil maintenance costs, and flexibility to turn off unused portions of the house. |
#12
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
Whats the OPs cost per KWH?
Around here its about a dime costs a fortune to heat with electric. |
#13
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
wrote in message ups.com... Whats the OPs cost per KWH? Around here its about a dime costs a fortune to heat with electric. Wish I could pay a dime. Her in CT, it is about 16¢ |
#14
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
As of my current bill, BC Hydro (it's a government-owned company) the
residential rate is: $0.06330 /kW.h ... and that's after a rate hike of I think 5% last year. so 6.3c "Canadian"... not sure if exchange rates make that much of a difference when you're talking cents :+) Chris Edwin Pawlowski wrote: wrote in message ups.com... Whats the OPs cost per KWH? Around here its about a dime costs a fortune to heat with electric. Wish I could pay a dime. Her in CT, it is about 16¢ |
#16
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
On 25 Sep 2006 20:17:38 -0700, "terry"
wrote: wrote: Besides, unless you've got your own power-station, resistive electric heaters are about the most wasteful way to heat a house. Care to expand on that? Electric heaters turn all the the electricity they consume into heat. So it then comes down to how much does electricity the cost in comparsion to other 'fuels'. We have used electric baseboards for the last 36 years. Maintenance costs have been virtually nil; no heaters have burnt out or needed replacement. Whereas if we had used fuel oil, or propane etc. there would have been furnace repairs, chimney flue cleaning etc. So just curious as to why baseboard heaters are 'wasteful'? Terry You didn't consider where that electricity comes from, and how it gets from there to your heaters.. -- 90 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "The government of the United States is not, in any sense, founded on the Christian religion." -- George Washington |
#17
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
wrote in message ups.com... Hi all, I'm quite confident wiring some baseboards that I need to install... they're 240V, various sizes. What I'm not sure of is how to have multiple baseboards on the same circuit? As others have stated, if the wire size (and thermostat capacity) sufficient for the total load there isn't a problem. Two wire (plus ground) can and is normally used. Check the installation instructions for the baseboard heaters. They may tell you EXACTLY how to wire several heaters in "multiple." Among other "got yas" is the insulation temperature ratings of the wire. But, for example, the instructions will tell you whether the heater housing is considered a conduit for wiring purposes or do you have to run the wires for the several units in the wall or below the floor. Pays to read and understand the installtion instruction before you buy the heaters. |
#18
Posted to alt.home.repair
|
|||
|
|||
Wiring multiple baseboard heaters
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Hydronic elecric baseboard heater vs standard electric baseboard heater | Home Repair | |||
Baseboard Heaters | Home Repair | |||
is venting your dryer to the house O.K in winter? | Home Repair | |||
peculiar wiring in residential switch box? | Home Repair | |||
connecting aluminum to copper wiring | Home Repair |