Default Wiring GFCI help

I have a 30+ year old house.
I want to add a GFCI near the kitchen sink

This is what I have to work with
From the breaker box

Red - hot breaker 1
Black - hot breaker 2
White - neutral

Both breakers share the same neutral - they are chained together through
4 outlets

Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)

I tried to install the GFCI in outlet 1, but since it just constantly trips.
When I isolated the white from breaker 2 and was just using breaker 1,
it was ok.

Any suggestions??
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Wiring GFCI help

On Sep 6, 12:29*am, The dude wrote:
I have a 30+ year old house.
I want to add a GFCI near the kitchen sink

This is what I have to work with
*From the breaker box

Red - hot breaker 1
Black - hot breaker 2
White - neutral

Both breakers share the same neutral - they are chained together through
4 outlets

Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)

I tried to install the GFCI in outlet 1, but since it just constantly trips.
When I isolated the white from breaker 2 and was just using breaker 1,
it was ok.

Any suggestions??



The problem is on the "Load" side of the GFI outlet. You attached the
red and neutral going to the next outlet, however the neutral is also
feeding the #3 &4 outlets. Since only the nuetral is GFI Protected,
but not the black wire, it senses a current imbalance and trips. There
are 2 ways to correct this.
1) Run a seperate neutral wire from outlet #1 to outlet #2 ( probably
hard to do if walls are closed) Or maybe easier:
2) Connect GFI on outlet #1, but nothing on Load side, and connect
another GFI on outlet #2 again with nothing on load side. This leaves
the black circuit by itself.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Wiring GFCI help


"The dude" wrote in message
. ..
I have a 30+ year old house.
I want to add a GFCI near the kitchen sink

This is what I have to work with
From the breaker box

Red - hot breaker 1
Black - hot breaker 2
White - neutral

Both breakers share the same neutral - they are chained together through 4
outlets

Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)

I tried to install the GFCI in outlet 1, but since it just constantly
trips.
When I isolated the white from breaker 2 and was just using breaker 1, it
was ok.

Any suggestions??


As Mikepier suggested, don't connect anything to the load side of any GFCI.
You have an Edison circuit, which makes things a little more complicated.
Wherever you want a GFCI outlet, remove the existing outlet, splice the
neutral wires together with a pigtail to the GFCI and if there is more than
one hot wire on the existing outlet, splice them together also with a
pigtail to the new GFCI


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 54
Default Wiring GFCI help

Mikepier wrote:
On Sep 6, 12:29 am, The dude wrote:
I have a 30+ year old house.
I want to add a GFCI near the kitchen sink

This is what I have to work with
From the breaker box

Red - hot breaker 1
Black - hot breaker 2
White - neutral

Both breakers share the same neutral - they are chained together through
4 outlets

Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)

I tried to install the GFCI in outlet 1, but since it just constantly trips.
When I isolated the white from breaker 2 and was just using breaker 1,
it was ok.

Any suggestions??



The problem is on the "Load" side of the GFI outlet. You attached the
red and neutral going to the next outlet, however the neutral is also
feeding the #3 &4 outlets. Since only the nuetral is GFI Protected,
but not the black wire, it senses a current imbalance and trips. There
are 2 ways to correct this.
1) Run a seperate neutral wire from outlet #1 to outlet #2 ( probably
hard to do if walls are closed) Or maybe easier:
2) Connect GFI on outlet #1, but nothing on Load side, and connect
another GFI on outlet #2 again with nothing on load side. This leaves
the black circuit by itself.


I cannot run a second neutral wire.

So I just need to buy another GFCI for #2.
What do you mean by not using the load side?
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Wiring GFCI help

On Sep 6, 9:44*am, The dude wrote:
Mikepier wrote:
On Sep 6, 12:29 am, The dude wrote:
I have a 30+ year old house.
I want to add a GFCI near the kitchen sink


This is what I have to work with
*From the breaker box


Red - hot breaker 1
Black - hot breaker 2
White - neutral


Both breakers share the same neutral - they are chained together through
4 outlets


Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)


I tried to install the GFCI in outlet 1, but since it just constantly trips.
When I isolated the white from breaker 2 and was just using breaker 1,
it was ok.


Any suggestions??


The problem is on the "Load" side of the GFI outlet. You *attached the
red and neutral going to the next outlet, however the neutral is also
feeding the #3 &4 outlets. Since only the nuetral *is GFI Protected,
but not the black wire, it senses a current imbalance and trips. There
are 2 ways to correct this.
1) Run a seperate neutral wire from outlet #1 to outlet #2 ( probably
hard to do if walls are closed) Or maybe easier:
2) Connect GFI on outlet #1, but nothing on Load side, *and connect
another GFI on outlet #2 again with nothing on load side. This leaves
the black circuit by itself.


I cannot run a second neutral wire.

So I just need to buy another GFCI for #2.
What do you mean by not using the load side?- Hide quoted text -

- Show quoted text -



The load side of a GFCI is used when you want that GFCI to not only
protect that outlet, but also other outlets. The other outlets are
connected to the load side of the one GFCI.

The easiest solution to your Edison circuit problem is to just use two
GFCIs in the two outlets and NOT use the load side.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Wiring GFCI help

So I just need to buy another GFCI for #2.
What do you mean by not using the load side?- Hide quoted text -

- Show quoted text -


If you look on the back of a GFI outlet, the top terminals are labeled
"LINE" and the bottom terminals are labeled "LOAD".
The incoming feed goes to "LINE", then usually to feed another
circuit, you connect the outgoing feed to "LOAD". This means any
outlet downstream is protected. So if the GFI tripped, the downstream
outlets would be dead also.
However your situation is different. You have to basically install the
GFI's as stand alone outlets, not feeding other outlets.
But continue feeding the other outlets by just wire nutting in the box.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 54
Default Wiring GFCI help

wrote:
On Sep 6, 9:44 am, The dude wrote:
Mikepier wrote:
On Sep 6, 12:29 am, The dude wrote:
I have a 30+ year old house.
I want to add a GFCI near the kitchen sink
This is what I have to work with
From the breaker box
Red - hot breaker 1
Black - hot breaker 2
White - neutral
Both breakers share the same neutral - they are chained together through
4 outlets
Red Outlet 1 (needs GFCI)
Red Outlet 2 (needs GFCI)
Black Outlet 3 (needs nothing)
Black Outlet 4 (needs nothing)
I tried to install the GFCI in outlet 1, but since it just constantly trips.
When I isolated the white from breaker 2 and was just using breaker 1,
it was ok.
Any suggestions??
The problem is on the "Load" side of the GFI outlet. You attached the
red and neutral going to the next outlet, however the neutral is also
feeding the #3 &4 outlets. Since only the nuetral is GFI Protected,
but not the black wire, it senses a current imbalance and trips. There
are 2 ways to correct this.
1) Run a seperate neutral wire from outlet #1 to outlet #2 ( probably
hard to do if walls are closed) Or maybe easier:
2) Connect GFI on outlet #1, but nothing on Load side, and connect
another GFI on outlet #2 again with nothing on load side. This leaves
the black circuit by itself.

I cannot run a second neutral wire.

So I just need to buy another GFCI for #2.
What do you mean by not using the load side?- Hide quoted text -

- Show quoted text -



The load side of a GFCI is used when you want that GFCI to not only
protect that outlet, but also other outlets. The other outlets are
connected to the load side of the one GFCI.

The easiest solution to your Edison circuit problem is to just use two
GFCIs in the two outlets and NOT use the load side.


OK

I see now.

Thanks
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 54
Default Wiring GFCI help

Mikepier wrote:
So I just need to buy another GFCI for #2.
What do you mean by not using the load side?- Hide quoted text -

- Show quoted text -


If you look on the back of a GFI outlet, the top terminals are labeled
"LINE" and the bottom terminals are labeled "LOAD".
The incoming feed goes to "LINE", then usually to feed another
circuit, you connect the outgoing feed to "LOAD". This means any
outlet downstream is protected. So if the GFI tripped, the downstream
outlets would be dead also.
However your situation is different. You have to basically install the
GFI's as stand alone outlets, not feeding other outlets.
But continue feeding the other outlets by just wire nutting in the box.



I installed these as stand alone outlets.
Everyyhing works perfect now
Thanks
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Wiring GFCI help

So you have more protected outlets using less GFCIs

--
Mikey S.
"Blattus Slafaly" wrote in message
Why would you ever ever want downstream outlets dead too?




  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Wiring GFCI help

On Sep 7, 8:34*am, Blattus Slafaly
wrote:
Mikepier wrote:
So I just need to buy another GFCI for #2.
What do you mean by not using the load side?- Hide quoted text -


- Show quoted text -


If you look on the back of a GFI outlet, the top terminals are labeled
"LINE" and the bottom terminals are labeled "LOAD".
The incoming feed goes to "LINE", then usually to feed another
circuit, you connect the outgoing feed to "LOAD". This means any
outlet downstream is protected. So if the GFI tripped, the downstream
outlets would be dead also. *\


Why would you ever ever want downstream outlets dead too?

However your situation is different. You have to basically install the
GFI's as stand alone outlets, not feeding other outlets.
But continue feeding the other outlets by just wire nutting in the box.


--
Blattus Slafaly *? 3 * * *7/8


Why would you ever ever want downstream outlets dead too?

I have 3 receptacles in my garage. The "first" is a GFCI, the other 2
are on the load side.

I can use any (or all) receptacle and have protection at each one.

In my basement bathroom, I have a light fixture over the shower stall.
It is on the load side of the GFCI, just in case...


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Wiring GFCI help


In my basement bathroom, I have a light fixture over the shower stall.
It is on the load side of the GFCI, just in case...- Hide quoted text -


Actually I think it is required by code that any light or fan inside
the shower must be on a GFI.

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 193
Default Wiring GFCI help

Mikepier wrote:
In my basement bathroom, I have a light fixture over the shower stall.
It is on the load side of the GFCI, just in case...- Hide quoted text -


Actually I think it is required by code that any light or fan inside
the shower must be on a GFI.


Yes I believe it is.

What I meant was just to show another reason for using the load side of
the GFCI. The "just in case" was the reason - just in case someone comes
in contact with the fixture (and it's hot, etc.)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI breakers for Al wiring [email protected] Home Repair 47 May 16th 07 04:43 PM
GFCI breakers for Al wiring Kristen Caldwell Electronics Repair 9 April 17th 07 10:21 PM
GFCI wiring procedure dclutch Home Repair 22 January 13th 07 01:54 AM
GFCI Outlet Wiring Question Alan Home Repair 7 August 7th 05 05:42 PM
wiring question -- switch to GFCI? fnord Home Repair 4 February 7th 05 11:21 PM


All times are GMT +1. The time now is 09:44 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"