Default GFCI question

Hello Group.

I have a problem with a GFCI tripping every time I turn on my shop
fan. This line has a 40" shop fan (on a wall switch) and three
outlets. I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. It was wired
by a licensed electrician and worked fine for ten years. What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? Any advice?

Thanks.

unklerichie
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default GFCI question


wrote in message
...
Hello Group.

I have a problem with a GFCI tripping every time I turn on my shop
fan. This line has a 40" shop fan (on a wall switch) and three
outlets. I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. It was wired
by a licensed electrician and worked fine for ten years. What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? Any advice?



Since the breaker is not tripping it can probably be removed from the
equation. Plug the fan into another GFI in another part of the house or
replace the GFI that you are now using and see what happens in either case.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default GFCI question

On Aug 22, 10:02*pm, "John Grabowski" wrote:
wrote in message

...

Hello Group.


I have a problem with a GFCI tripping every time I turn on my shop
fan. *This line has a 40" shop fan (on a wall switch) and three
outlets. *I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. *It was wired
by a licensed electrician and worked fine for ten years. *What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? *Any advice?


Since the breaker is not tripping it can probably be removed from the
equation. *Plug the fan into another GFI in another part of the house or
replace the GFI that you are now using and see what happens in either case.


The fan is wired to a switch through the wall. I can't plug it in
somewhere else. I'm betting you're correct about the GFI. I'll
replace it tomorrow.

Many thanks, John.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 627
Default GFCI question

The GFI is probably working just fine and doing its job. These detect when
there is a short to ground. Electric motors have all sorts of exposed wires
inside and dust can get in there and cause a little short to ground.

Try blowing out the fan motor with compressed air or having the motor
serviced.


wrote in message
Hello Group.

I have a problem with a GFCI tripping every time I turn on my shop
fan. This line has a 40" shop fan (on a wall switch) and three
outlets. I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. It was wired
by a licensed electrician and worked fine for ten years. What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? Any advice?

Thanks.

unklerichie



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 289
Default GFCI question

On Aug 23, 8:32*am, "Bill" wrote:
The GFI is probably working just fine and doing its job. These detect when
there is a short to ground. Electric motors have all sorts of exposed wires
inside and dust can get in there and cause a little short to ground.

Try blowing out the fan motor with compressed air or having the motor
serviced.



wrote in message
Hello Group.


I have a problem with a GFCI tripping every time I turn on my shop
fan. *This line has a 40" shop fan (on a wall switch) and three
outlets. *I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. *It was wired
by a licensed electrician and worked fine for ten years. *What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? *Any advice?


Thanks.


unklerichie- Hide quoted text -


- Show quoted text -


Blowing out a motor with compressed air is a quick way to be buying
it's replacement.

Soft paint brush and a vacuum , and yes you sometimes have to open the
thing up.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 460
Default GFCI question

OH PLEEEEEASE....... I've been blowing motors out for 40+ years and have
NEVER damaged one yet. You'll do more damage poking a vacuum nozzle or
paint brush in there.

s


"beecrofter" wrote in message
...

Blowing out a motor with compressed air is a quick way to be buying
it's replacement.

Soft paint brush and a vacuum , and yes you sometimes have to open the
thing up.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 460
Default GFCI question

Replace it with a standard outlet and the problem will go away.

s


wrote in message
...

The fan is wired to a switch through the wall. I can't plug it in
somewhere else. I'm betting you're correct about the GFI. I'll
replace it tomorrow.

Many thanks, John.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 679
Default GFCI question

Hello Group.

I have a problem with a GFCI tripping every time I turn on my shop
fan. This line has a 40" shop fan (on a wall switch) and three
outlets. I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. It was wired
by a licensed electrician and worked fine for ten years. What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? Any advice?

Thanks.

unklerichie


A 40" fan has to have a pretty good sized motor and takes several
seconds for it to come up to speed. Everything being reactive, while it
is starting, it is creating reverse EMF (electro-motive-force) which,
during that time, is making the current in the two feed wires go out of
phase with each other. THAT can pop a GFCI; they just don't work well
with large inductive loads like electric motors.

Please let us know if changing out the GFI helps anything because IMO it
won't, but I'd be pleased to be wrong.

Also, if the insides of the fan are dirty, dusty, full of fuzz and
coated with whatever from the air, that can cause small currents to flow
from the hot to the earth ground which might also trip a GFCI.

It sounds like the fan gets turning pretty good before the GFI pops, so
you could, JUST IN THIS ONE CASE, try starting the fan, when the GFI
pops, quickly reset it and see if the fan will continue to start up.
If it still pops, you could try VERY CAREFULLY (ELECTRICITY CAN
*KILL* YOU) TRY shorting around the GFCI with a lead until the fan gets
running. Then remove the bypass; If the fan continues to run, there is
there is no problem with the fan. \
But if the GFCI pops, then there is definitely a probelen with the
fan or the wiring to it.

I'd use a little Radio Shack clip lead to do the shorting across the
GFCI (from input/source side to load side, NOT load to load!).
Kill the breaker, put the clip leads on, have somoeone turn on the
breaker, carefully remove the clip lead by the insulated handles, and
see if the fan keeps going. If so, it's 99% going to be EMF issues
which most any GFCI will pop on.
Note: If the GFCI should pop while the clip leads are attached, it
means one of them is not getting a good connection; kill power, clean
the area you want to attach it to, and try again.

DONE WRONG, THIS CAN BE VERY DANGEROUS! NEVER TOUCH ANYTHING ELECTRICAL
OR ANY METAL NEAR THE ELECTRICAL PART WHILE THE BREAKER IS ON! If you
aren't experienced around electricity see if you can find an
experienced buddy to do these things for you; it might be the best
advice.

BTW, GFCI's are down in cost these days and there ARE some that are made
for higher loads than the standard 15 amps, although they cost more.

HTH


  #9   Report Post  
Posted to alt.home.repair
M Q M Q is offline
external usenet poster
 
Posts: 257
Default GFCI question



TWayne wrote:

....

A 40" fan has to have a pretty good sized motor and takes several
seconds for it to come up to speed. Everything being reactive, while it
is starting, it is creating reverse EMF (electro-motive-force) which,
during that time, is making the current in the two feed wires go out of
phase with each other.

B.S. Unless you have a very big reservoir for electrons, the current
on the two feed wires will not be "out of phase".
A large capacitor to ground would be such a reservoir, but that is
a ground fault, and the GFCI should trip for that.

....
If it still pops, you could try VERY CAREFULLY (ELECTRICITY CAN
*KILL* YOU) TRY shorting around the GFCI with a lead until the fan gets
running. Then remove the bypass; If the fan continues to run, there is
there is no problem with the fan.

Not necessarily. There may be both mechanical and electrical
differences in the motor during acceleration that could cause
a ground fault during acceleration. OP didn't mention whether
this motor had a centrifugal switch controlling the start winding.

Most likely you have a ground fault in the motor.
It may be solid or it may be intermittent.
Have you tried measuring the resistance from hot to ground
for the motor?

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default GFCI question

The problem is something leaking power. Changing a socket won't make power
leak go away.

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"Steve Barker DLT" wrote in message
...
Replace it with a standard outlet and the problem will go away.

s


wrote in message
...

The fan is wired to a switch through the wall. I can't plug it in
somewhere else. I'm betting you're correct about the GFI. I'll
replace it tomorrow.

Many thanks, John.





  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10,530
Default GFCI question

The way you tell what the problem is. Notice when the GFCI trips. If the
GFCI trips consistenly with one appliance other, then the problem is with
the appliance. For example, if one appliance consistently runs for a couple
seconds and then trips the GFCI, you can be fairly sure that one appliance
has a power leak.

A standard socket might keep the appliance running, but won't be as safe.
It's unlikely anyone will be shocked by a 40 inch shop fan, especially if
the fan is properly grounded. So, a non GFCI socket may be a work around for
you.

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


wrote in message
...
Hello Group.

I have a problem with a GFCI tripping every time I turn on my shop
fan. This line has a 40" shop fan (on a wall switch) and three
outlets. I can use the outlets fine, but when I turn on the fan, it
runs for about ten seconds and then it trips the GFCI. It was wired
by a licensed electrician and worked fine for ten years. What is the
best way to figure out what's bad, the fan motor, the GFCI, or maybe
the breaker? Any advice?

Thanks.

unklerichie


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 679
Default GFCI question

TWayne wrote:

...

A 40" fan has to have a pretty good sized motor and takes several
seconds for it to come up to speed. Everything being reactive,
while it is starting, it is creating reverse EMF
(electro-motive-force) which, during that time, is making the
current in the two feed wires go out of phase with each other.

B.S. Unless you have a very big reservoir for electrons, the current
on the two feed wires will not be "out of phase".
A large capacitor to ground would be such a reservoir, but that is
a ground fault, and the GFCI should trip for that.

...
If it still pops, you could try VERY CAREFULLY (ELECTRICITY CAN
*KILL* YOU) TRY shorting around the GFCI with a lead until the fan
gets running. Then remove the bypass; If the fan continues to run,
there is there is no problem with the fan.

Not necessarily. There may be both mechanical and electrical
differences in the motor during acceleration that could cause
a ground fault during acceleration. OP didn't mention whether
this motor had a centrifugal switch controlling the start winding.

Most likely you have a ground fault in the motor.
It may be solid or it may be intermittent.
Have you tried measuring the resistance from hot to ground
for the motor?


Since Neutral and Ground are tied together back in the breaker box,
that's not going to prove anything without disconnecting the wires and
even then without a voltage to break down the gap it likely wouldn't
show anything but the resistance part of the fan motor.
I wouldn't even bother with that; it'll measure near zero, only a few
ohms to a hundred or so depending on the fan motor coils.


  #13   Report Post  
Posted to alt.home.repair
M Q M Q is offline
external usenet poster
 
Posts: 257
Default GFCI question

TWayne wrote:

....
Most likely you have a ground fault in the motor.
It may be solid or it may be intermittent.
Have you tried measuring the resistance from hot to ground
for the motor?



Since Neutral and Ground are tied together back in the breaker box,
that's not going to prove anything without disconnecting the wires and
even then without a voltage to break down the gap it likely wouldn't
show anything but the resistance part of the fan motor.
I wouldn't even bother with that; it'll measure near zero, only a few
ohms to a hundred or so depending on the fan motor coils.


Of course you disconnect the motor before measuring!

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI question DB Home Repair 6 March 30th 07 10:48 PM
Another GFCI Question [email protected] Home Repair 12 June 23rd 06 11:33 PM
GFCI Question Robert Tamlyn Home Repair 2 August 8th 05 01:15 PM
GFCI Question "take two" Home Repair 7 August 2nd 05 07:49 PM
gfci question sligo Home Repair 4 July 2nd 05 04:37 AM


All times are GMT +1. The time now is 02:34 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"