GFCI Question "take two"
Imagine a hypothetical situation where you have a load center for a Spa,
wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful |
#2
|
|||
|
|||
I don't mean to sound like a smart ass but your description doesn't sound
accurate. Like I said previously, you DON'T drive ground rods to protect a tub or the related equipment. You also don't connect the neutral from a GFCI breaker to something it is not protecting. If it is a straight 240 volt heater, it doesn't use a neutral so you don't have one to connect. It does however sound like you may have a defective GFCI breaker wrote in message t... Imagine a hypothetical situation where you have a load center for a Spa, wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful |
#3
|
|||
|
|||
RBM
You aren't ! On the ground rod thing. This is an older house, And without measuring Impeadence to ground from my current service Gound connection to cold water connection, I just added a ground rod, bonded it to service panel. The spa is also bonded to this ground in the service panel. on the breaker. I guess I could go buy another breaker but I would like too test this one . I think what you might be saying is that if the breaker was functioning correctly it should trip (GFCI trip button) without having anything landed on the neutral lug of the breaker. The 30 I have would not trip with or without the breaker supplied neutral was landed on neutral bus. I just assumed that is why it didn't work. thanks. "RBM" rbm2(remove wrote in message news I don't mean to sound like a smart ass but your description doesn't sound accurate. Like I said previously, you DON'T drive ground rods to protect a tub or the related equipment. You also don't connect the neutral from a GFCI breaker to something it is not protecting. If it is a straight 240 volt heater, it doesn't use a neutral so you don't have one to connect. It does however sound like you may have a defective GFCI breaker wrote in message t... Imagine a hypothetical situation where you have a load center for a Spa, wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful |
#4
|
|||
|
|||
Your grounds are ultimately tied back to the same location, your service
panel. You don't want to create any additional paths from the tub. It will be grounded fine by the ground wire in your feeder. That breaker should trip with or without a neutral connected to the load. I think it's defective. If you bought it at HD it has a much higher chance of being defective in my opinion wrote in message t... RBM You aren't ! On the ground rod thing. This is an older house, And without measuring Impeadence to ground from my current service Gound connection to cold water connection, I just added a ground rod, bonded it to service panel. The spa is also bonded to this ground in the service panel. on the breaker. I guess I could go buy another breaker but I would like too test this one . I think what you might be saying is that if the breaker was functioning correctly it should trip (GFCI trip button) without having anything landed on the neutral lug of the breaker. The 30 I have would not trip with or without the breaker supplied neutral was landed on neutral bus. I just assumed that is why it didn't work. thanks. "RBM" rbm2(remove wrote in message news I don't mean to sound like a smart ass but your description doesn't sound accurate. Like I said previously, you DON'T drive ground rods to protect a tub or the related equipment. You also don't connect the neutral from a GFCI breaker to something it is not protecting. If it is a straight 240 volt heater, it doesn't use a neutral so you don't have one to connect. It does however sound like you may have a defective GFCI breaker wrote in message t... Imagine a hypothetical situation where you have a load center for a Spa, wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful |
#5
|
|||
|
|||
wrote in message t... Imagine a hypothetical situation where you have a load center for a Spa, wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, Personally I would want the whole thing to shut down not just individual circuits. ( not a code requirement ) The last spa I worked on had a landing area for the incomming feeders and we protected the whole thing at the panel with a gfci. Every time I have seen multipule gfci's used it was either problematic or coordination was impossible. (not speaking about adjustable breakers, just residential ) I ran a #6 bond wire even though not required. Call me paranoid. no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use Why would you want to do this? GFCI's measure imbalances in a circuit. Why would you want to combine circuits? See above the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water What is the age of the home? Did your panel have an ground installed already? (probably if cica ~1968 and newer) Were there 2 bare copper wires in the panel? For an supplemental ground to be effective it needs to be installed out of the sphere of grounding. example, ground rod 8 feet long so the second ground rod would be installed a mininum of 8 feet way. If installed closer then the new ground rod is not as effective as it could be. I assume you used the same size wire as the water bond for you service. ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful My suggestion is to protect the panel with a GFCI and use regular breakers for the other loads. AND seek local professional help. Hypothetically you have a situation brewing here. |
#6
|
|||
|
|||
Personally I would want the whole thing to shut down not just individual
circuits. ( not a code requirement ) I agree. I'm not trying to cut corners, just dealing with primary panel breaker space and cost of new 60 amp GFCI. What is the age of the home? Did your panel have an ground installed already? (probably if cica ~1968 and newer) Were there 2 bare copper wires in the panel? For an supplemental ground to be effective it needs to be installed out of the sphere of grounding. example, ground rod 8 feet long so the second ground rod would be installed a mininum of 8 feet way. '66. One cold water ground. More than 8 feet away. I think Bud and RBM answered my question. I'm at least going to buy a new 30 amp 2-pole GFCI and probably a new 60 and replace other two at load center. Another reason I want to go with a new 30 amp is this spa (used) came with this configuration factory. Thanks for your input. "SQLit" wrote in message ... wrote in message t... Imagine a hypothetical situation where you have a load center for a Spa, wherein it contains a 2-pole 30 amp GFCI breaker (for heater) and a 20 amp 2-pole GFCI breaker. The 2-20 amp can be tripped (from a short circuit) independently of the other, Personally I would want the whole thing to shut down not just individual circuits. ( not a code requirement ) The last spa I worked on had a landing area for the incomming feeders and we protected the whole thing at the panel with a gfci. Every time I have seen multipule gfci's used it was either problematic or coordination was impossible. (not speaking about adjustable breakers, just residential ) I ran a #6 bond wire even though not required. Call me paranoid. no trip bar connecting them, but when you hit the GFCI trip button they both trip. This breaker operates the 110v loads like the blower/light/ozanator etc. I've seen where, on some installations, instead of having individual GFCI breakers, The 60 amp main is GFCI. In this case since there is no 220v neutral load from the heater, should I use Why would you want to do this? GFCI's measure imbalances in a circuit. Why would you want to combine circuits? See above the neutral load from the 110v stuff to hook to the 30 amp 220v GFCI. To be on the safe side I drove a new ground rod to compliment the cold water What is the age of the home? Did your panel have an ground installed already? (probably if cica ~1968 and newer) Were there 2 bare copper wires in the panel? For an supplemental ground to be effective it needs to be installed out of the sphere of grounding. example, ground rod 8 feet long so the second ground rod would be installed a mininum of 8 feet way. If installed closer then the new ground rod is not as effective as it could be. I assume you used the same size wire as the water bond for you service. ground and bonded it back to my service panel. I know there was life and hot tubs before GFCI, I just want to get the opinion of someone who knows. No offense Todd H. (my smart-ass young poster) but this is not you. I appreciate the Yellow pages advise but it wasn't really helpful My suggestion is to protect the panel with a GFCI and use regular breakers for the other loads. AND seek local professional help. Hypothetically you have a situation brewing here. |
#7
|
|||
|
|||
|
#8
|
|||
|
|||
If think the breakers aren't tripping correctly on ground fault you could kludge a temporary 110V outlet to each hot-pole with the neutral to the load side neutral for that breaker and use a commonly available GFCI tester in the 110V kludged outlet. The kludged outlet also requires a ground for a GFCI tester to work. Note there are a number of requirements for a hot tub (US-NEC). Without looking it up, what comes to mind is: no outlets within 5' special requirements for lights within 5' and over that area exposed metal within 5' that could be energized to be bonded disconnect within-sight-of but over 5' away (for maintenance - subpanel would work) GFCI outlet between 5 and 10' away if outside no wires overhead (may extend to side) Bud-- |