The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is unobstructed
and also flowing water.

This is a Carrier unit of unknown vintage, and it was installed with the
access panel less than a foot from the basement wall, presumably because the
refrigerant connections are right below the panel, and it's a direct shot
from there to the outdoor unit. Whatever, it was a real pleasure taking the
panel off and getting it back on.

Could not see much with the access panel off because of the restricted view,
but I did see that the copper drain line was covered with water droplets.
The drain runs from the "front" of the evaporator housing to the back where
the drain hose connects. Thus the drain line runs through the inlet air
plenum.

Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in it; from the factory
it appears. What is the purpose of this second drain connection? It
connects to the same reservoir as the other drain, but a fair amount of
water came out of it when I took the plug out.

I'm guessing that the condensate tray could have a leak in it, but I don't
see any easy way of accessing it short of cutting a hole in the housing. I
don't know what these trays are made of or if they are are prone to rusting
out.

Alternatively, I'm wondering if the uninsulated drain line, which has cold
condensate flowing through it, is condensing the humidity of the incoming
air and that is what is leaking out of the nearby joint between the
evaporator housing and the furnace housing that it's mounted on. That's
where the water is showing up when the unit is operating. The existing
drain line has a trap in it so there is no air flow through it.

My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose on the
presently unused drain so that there will be no flow in the uninsulated
section and no condensation on its outside surface.

What do you suggest?

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 147
Default Air conditioner condensate leakage

Silver Surfer wrote:
The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is
unobstructed and also flowing water.

This is a Carrier unit of unknown vintage, and it was installed with
the access panel less than a foot from the basement wall, presumably
because the refrigerant connections are right below the panel, and
it's a direct shot from there to the outdoor unit. Whatever, it was
a real pleasure taking the panel off and getting it back on.

Could not see much with the access panel off because of the
restricted view, but I did see that the copper drain line was covered
with water droplets. The drain runs from the "front" of the
evaporator housing to the back where the drain hose connects. Thus
the drain line runs through the inlet air plenum.

Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in
it; from the factory it appears. What is the purpose of this second
drain connection? It connects to the same reservoir as the other
drain, but a fair amount of water came out of it when I took the plug
out.
I'm guessing that the condensate tray could have a leak in it, but I
don't see any easy way of accessing it short of cutting a hole in the
housing. I don't know what these trays are made of or if they are
are prone to rusting out.

Alternatively, I'm wondering if the uninsulated drain line, which has
cold condensate flowing through it, is condensing the humidity of the
incoming air and that is what is leaking out of the nearby joint
between the evaporator housing and the furnace housing that it's
mounted on. That's where the water is showing up when the unit is
operating. The existing drain line has a trap in it so there is no
air flow through it.
My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose
on the presently unused drain so that there will be no flow in the
uninsulated section and no condensation on its outside surface.

What do you suggest?


You may have a condensate pan that has a leak maybe due to rusting.
Sometimes they can be replaced but a new evaporator coil may be needed.
The unwrapped drain line maybe the problem but if it is part of the problem
then it most likely it would have leaked from the beginning when the system
was installed..

--
Moe Jones
http://www.MoeJones.info


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,447
Default Air conditioner condensate leakage

On Aug 12, 12:25*pm, "Moe Jones" wrote:
Silver Surfer wrote:
The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is
unobstructed and also flowing water.


This is a Carrier unit of unknown vintage, and it was installed with
the access panel less than a foot from the basement wall, presumably
because the refrigerant connections are right below the panel, and
it's a direct shot from there to the outdoor unit. *Whatever, it was
a real pleasure taking the panel off and getting it back on.


Could not see much with the access panel off because of the
restricted view, but I did see that the copper drain line was covered
with water droplets. The drain runs from the "front" of the
evaporator housing to the back where the drain hose connects. *Thus
the drain line runs through the inlet air plenum.


Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in
it; from the factory it appears. *What is the purpose of this second
drain connection? *It connects to the same reservoir as the other
drain, but a fair amount of water came out of it when I took the plug
out.
I'm guessing that the condensate tray could have a leak in it, but I
don't see any easy way of accessing it short of cutting a hole in the
housing. *I don't know what these trays are made of or if they are
are prone to rusting out.


Alternatively, I'm wondering if the uninsulated drain line, which has
cold condensate flowing through it, is condensing the humidity of the
incoming air and that is what is leaking out of the nearby joint
between the evaporator housing and the furnace housing that it's
mounted on. *That's where the water is showing up when the unit is
operating. *The existing drain line has a trap in it so there is no
air flow through it.
My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose
on the presently unused drain so that there will be no flow in the
uninsulated section and no condensation on its outside surface.


What do you suggest?


You may have a condensate pan that has a leak maybe due to rusting.
Sometimes they can be replaced but a new evaporator coil may be needed.
The unwrapped drain line maybe the problem but if it is part of the problem
then it most likely it would have leaked from the beginning when the system
was installed..

--
Moe Joneshttp://www.MoeJones.info- Hide quoted text -

- Show quoted text -


Unless only noticeable when the weather is exceptionally humid and
moisture in incoming outside air IS condensing on the cool condensate
pipe as suggested.
The climate is changing you know!
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Air conditioner condensate leakage

On Aug 12, 10:25*am, "Moe Jones" wrote:
Silver Surfer wrote:
The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is
unobstructed and also flowing water.


This is a Carrier unit of unknown vintage, and it was installed with
the access panel less than a foot from the basement wall, presumably
because the refrigerant connections are right below the panel, and
it's a direct shot from there to the outdoor unit. *Whatever, it was
a real pleasure taking the panel off and getting it back on.


Could not see much with the access panel off because of the
restricted view, but I did see that the copper drain line was covered
with water droplets. The drain runs from the "front" of the
evaporator housing to the back where the drain hose connects. *Thus
the drain line runs through the inlet air plenum.


Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in
it; from the factory it appears. *What is the purpose of this second
drain connection? *It connects to the same reservoir as the other
drain, but a fair amount of water came out of it when I took the plug
out.
I'm guessing that the condensate tray could have a leak in it, but I
don't see any easy way of accessing it short of cutting a hole in the
housing. *I don't know what these trays are made of or if they are
are prone to rusting out.


Alternatively, I'm wondering if the uninsulated drain line, which has
cold condensate flowing through it, is condensing the humidity of the
incoming air and that is what is leaking out of the nearby joint
between the evaporator housing and the furnace housing that it's
mounted on. *That's where the water is showing up when the unit is
operating. *The existing drain line has a trap in it so there is no
air flow through it.
My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose
on the presently unused drain so that there will be no flow in the
uninsulated section and no condensation on its outside surface.


What do you suggest?


You may have a condensate pan that has a leak maybe due to rusting.
Sometimes they can be replaced but a new evaporator coil may be needed.
The unwrapped drain line maybe the problem but if it is part of the problem
then it most likely it would have leaked from the beginning when the system
was installed..

--
Moe Joneshttp://www.MoeJones.info- Hide quoted text -

- Show quoted text -


Some units have a second backup drain pipe in case the first one gets
blocked. The fact that a lot of water ran out when you opened it
suggests that the actual drain line is at least partially blocked and
not flowing freely, or there would be very little water to run out.
  #5   Report Post  
Posted to alt.home.repair
mm mm is offline
external usenet poster
 
Posts: 7,824
Default Air conditioner condensate leakage

On Mon, 11 Aug 2008 21:44:36 -0400, "Silver Surfer"
wrote:

The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is unobstructed
and also flowing water.

This is a Carrier unit of unknown vintage, and it was installed with the


I had water on the floor, also with a Carrier, from 1975.

FWIW, my outside unit is directly opposite the inside unit.

Everything worked fine for the first 5 or 10 years I lived here, plus
I suppose the 4 years the other guy did.

Then it started going on the floor and not into the sump.

I took off the plastic drain pipe, and blew through it with my lungs.
Twenty feet but it didn't seem clogged. Still I ran faucet water
through it to flush it out, and the water came out full blast. Put it
back together and it didn't work any better.

I cut open the plenum to look inside. Not a lot of water, but I
probably hadn't been running the AC for days or weeks before that.

Everythign looked ok inside.

I may have done other thigns but this is what worked. The plastic
pipe came out an inch, then turned down for 3 or 4 inches, then
sideways to the wall a couple feet**, then down to the floor 4 feet,
then along the wall 6 feet, then sideways to the sump 2 feet, and down
an inch.

**This piece was horizontal, not uphill.

All I did was rearrange the pipes so instead of going down 3 inches,
it goes down 2 feet before it turns sideways, same distance to the
wallk and then down 2 more feet or so to make 4 feet total.

Now it works fine. It's hard enough to understand why it works
better now than it did, but even harder to understand why it worked
fine for 15 years and then didnt' work anymore.


I"m going to post and send you a copy. If the comcast people are
reading, Hi, guys!


access panel less than a foot from the basement wall, presumably because the
refrigerant connections are right below the panel, and it's a direct shot
from there to the outdoor unit. Whatever, it was a real pleasure taking the
panel off and getting it back on.

Could not see much with the access panel off because of the restricted view,
but I did see that the copper drain line was covered with water droplets.
The drain runs from the "front" of the evaporator housing to the back where
the drain hose connects. Thus the drain line runs through the inlet air
plenum.

Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in it; from the factory
it appears. What is the purpose of this second drain connection? It
connects to the same reservoir as the other drain, but a fair amount of
water came out of it when I took the plug out.

I'm guessing that the condensate tray could have a leak in it, but I don't
see any easy way of accessing it short of cutting a hole in the housing. I
don't know what these trays are made of or if they are are prone to rusting
out.

Alternatively, I'm wondering if the uninsulated drain line, which has cold
condensate flowing through it, is condensing the humidity of the incoming
air and that is what is leaking out of the nearby joint between the
evaporator housing and the furnace housing that it's mounted on. That's
where the water is showing up when the unit is operating. The existing
drain line has a trap in it so there is no air flow through it.

My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose on the
presently unused drain so that there will be no flow in the uninsulated
section and no condensation on its outside surface.

What do you suggest?




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 23
Default Air conditioner condensate leakage

Mr. mm,

Thanks for that valuable information. I will give your fix a try this
coming weekend.

"mm" wrote in message
...
On Mon, 11 Aug 2008 21:44:36 -0400, "Silver Surfer"
wrote:

The evaporator coil for a friend's central air conditioning is leaking
condensate on the basement floor; however, the drain line is unobstructed
and also flowing water.

This is a Carrier unit of unknown vintage, and it was installed with the


I had water on the floor, also with a Carrier, from 1975.

FWIW, my outside unit is directly opposite the inside unit.

Everything worked fine for the first 5 or 10 years I lived here, plus
I suppose the 4 years the other guy did.

Then it started going on the floor and not into the sump.

I took off the plastic drain pipe, and blew through it with my lungs.
Twenty feet but it didn't seem clogged. Still I ran faucet water
through it to flush it out, and the water came out full blast. Put it
back together and it didn't work any better.

I cut open the plenum to look inside. Not a lot of water, but I
probably hadn't been running the AC for days or weeks before that.

Everythign looked ok inside.

I may have done other thigns but this is what worked. The plastic
pipe came out an inch, then turned down for 3 or 4 inches, then
sideways to the wall a couple feet**, then down to the floor 4 feet,
then along the wall 6 feet, then sideways to the sump 2 feet, and down
an inch.

**This piece was horizontal, not uphill.

All I did was rearrange the pipes so instead of going down 3 inches,
it goes down 2 feet before it turns sideways, same distance to the
wallk and then down 2 more feet or so to make 4 feet total.

Now it works fine. It's hard enough to understand why it works
better now than it did, but even harder to understand why it worked
fine for 15 years and then didnt' work anymore.


I"m going to post and send you a copy. If the comcast people are
reading, Hi, guys!


access panel less than a foot from the basement wall, presumably because
the
refrigerant connections are right below the panel, and it's a direct shot
from there to the outdoor unit. Whatever, it was a real pleasure taking
the
panel off and getting it back on.

Could not see much with the access panel off because of the restricted
view,
but I did see that the copper drain line was covered with water droplets.
The drain runs from the "front" of the evaporator housing to the back
where
the drain hose connects. Thus the drain line runs through the inlet air
plenum.

Noticed a small cover on one corner of the evaporator housing. Behind the
cover was a very short drain pipe with a rubber plug in it; from the
factory
it appears. What is the purpose of this second drain connection? It
connects to the same reservoir as the other drain, but a fair amount of
water came out of it when I took the plug out.

I'm guessing that the condensate tray could have a leak in it, but I don't
see any easy way of accessing it short of cutting a hole in the housing.
I
don't know what these trays are made of or if they are are prone to
rusting
out.

Alternatively, I'm wondering if the uninsulated drain line, which has cold
condensate flowing through it, is condensing the humidity of the incoming
air and that is what is leaking out of the nearby joint between the
evaporator housing and the furnace housing that it's mounted on. That's
where the water is showing up when the unit is operating. The existing
drain line has a trap in it so there is no air flow through it.

My first thought is to put insulation on the drain pipe inside the
evaporator housing, but it will be exceptionally difficult to reach. My
second thought is to plug the present drain and install the hose on the
presently unused drain so that there will be no flow in the uninsulated
section and no condensation on its outside surface.

What do you suggest?



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Snowblower And Oil Leakage ? Robert11 Home Repair 0 April 16th 08 12:42 PM
Cathode / Heater leakage. N Cook Electronics Repair 3 December 27th 07 03:00 PM
garden hose leakage SeaKan Home Repair 9 April 16th 06 07:32 PM
Cleaning UPS battery leakage Ryan Underwood Electronics Repair 2 August 31st 05 09:54 PM
ouch! 25v dc leakage to DVD case The Real Andy Electronics Repair 4 June 29th 04 09:35 AM


All times are GMT +1. The time now is 05:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"