Hi all. I need help understanding some parts of the NEC as they
pertain to my sevice feed and sub panels.

I had my service loop replaced recently from an old 60 amp service
that fed 2 55 amp sub panels directly from a fused disconnect at the
meter.

The new service loop is 200 amps. The existing feed lines, etc to the
subpanels were kept in place and fed via 55 amp breakers, removing the
old fused disconnect.

The electrician installed a 200 amp breaker panel with main lugs only
(No main breaker). He said something about "As long as there are not
any 100 amp feeds to subpanels, a main breaker is not required".

The electrical inspector passed the install with no problems.

Is this correct?

Also, on my subpanels, there is no "Main" breaker either. They are old
screw-buss fuse panels with lugs only. If I replace them, are they
REQUIRED to have a Main Breaker on the sub-panel?

I have a copy of the NEC, but I'm a little lost on these details.

THANKS!
-A
  #2   Report Post  
Posted to alt.home.repair
Joe Joe is offline
external usenet poster
 
Posts: 2,837
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 12:48*pm, Guy Noir wrote:
Hi all. I need help understanding some parts of the NEC as they
pertain to my sevice feed and sub panels.

I had my service loop replaced recently from an old 60 amp service
that fed 2 55 amp sub panels directly from a fused disconnect at the
meter.

The new service loop is 200 amps. The existing feed lines, etc to the
subpanels were kept in place and fed via 55 amp breakers, removing the
old fused disconnect.

The electrician installed a 200 amp breaker panel with main lugs only
(No main breaker). He said something about "As long as there are not
any 100 amp feeds to subpanels, a main breaker is not required".

The electrical inspector passed the install with no problems.

Is this correct?

Also, on my subpanels, there is no "Main" breaker either. They are old
screw-buss fuse panels with lugs only. If I replace them, are they
REQUIRED to have a Main Breaker on the sub-panel?

I have a copy of the NEC, but I'm a little lost on these details.

THANKS!
-A


The final arbiter is your building inspector. If he passed it, there's
no code violation. For possible changes, let the building code people
answer the question. From a common sense standpoint if you get rid of
fuses you need some replacement circuit protection which is in the
NEC, just not obvious. Better answers can be found in wiring methods
books that make the NEC legalese less obscure. Good luck.

Joe
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 1:14*pm, Joe wrote:
On Mar 31, 12:48*pm, Guy Noir wrote:





Hi all. I need help understanding some parts of the NEC as they
pertain to my sevice feed and sub panels.


I had my service loop replaced recently from an old 60 amp service
that fed 2 55 amp sub panels directly from a fused disconnect at the
meter.


The new service loop is 200 amps. The existing feed lines, etc to the
subpanels were kept in place and fed via 55 amp breakers, removing the
old fused disconnect.


The electrician installed a 200 amp breaker panel with main lugs only
(No main breaker). He said something about "As long as there are not
any 100 amp feeds to subpanels, a main breaker is not required".


The electrical inspector passed the install with no problems.


Is this correct?


Also, on my subpanels, there is no "Main" breaker either. They are old
screw-buss fuse panels with lugs only. If I replace them, are they
REQUIRED to have a Main Breaker on the sub-panel?


I have a copy of the NEC, but I'm a little lost on these details.


THANKS!
-A


The final arbiter is your building inspector. If he passed it, there's
no code violation. For possible changes, let the building code people
answer the question. From a common sense standpoint if you get rid of
fuses you need some replacement circuit protection which is in the
NEC,


Sure, the fuse disconnect from the meter was replaced by circuit
breakers, but the sub panels themselves have no main, lugs only. So
the circuit goes from the main panel breaker to the sub lug only.
Just curious if the replacements subs need mains or main lugs are fine
as a replacement....

Thanks for the feedback.

-A

just not obvious. Better answers can be found in wiring methods
books that make the NEC legalese less obscure. Good luck.

Joe- Hide quoted text -

- Show quoted text -


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 4:57*pm, wrote:
On Mon, 31 Mar 2008 10:48:28 -0700 (PDT), Guy Noir





wrote:
Hi all. I need help understanding some parts of the NEC as they
pertain to my sevice feed and sub panels.


I had my service loop replaced recently from an old 60 amp service
that fed 2 55 amp sub panels directly from a fused disconnect at the
meter.


The new service loop is 200 amps. The existing feed lines, etc to the
subpanels were kept in place and fed via 55 amp breakers, removing the
old fused disconnect.


The electrician installed a 200 amp breaker panel with main lugs only
(No main breaker). He said something about "As long as there are not
any 100 amp feeds to subpanels, a main breaker is not required".


The electrical inspector passed the install with no problems.


Is this correct?


Also, on my subpanels, there is no "Main" breaker either. They are old
screw-buss fuse panels with lugs only. If I replace them, are they
REQUIRED to have a Main Breaker on the sub-panel?


I have a copy of the NEC, but I'm a little lost on these details.


THANKS!
-A


Your 200a panel is not a lighting and appliance panel since the branch
circuits do not originate there. You are limited to 6 disconnects in
there. It could be for feeders to your fuse panels or you could add a
couple big loads directly to the panel. Just remember total needs to
be six or less. As long as your sub-panels are individually protected
at the feed end they don't need a "main" in the panel.- Hide quoted text -

- Show quoted text -


Thanks for the info. That was very helpful! I hooked my Central Air/
Electric furnace direct to the 200A panel as well as my feeders to the
subs. I'll make sure to keep it at or under 6!
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 655
Default Main Panel and Sub Panel questions and the NEC

So, using this line of thinking, the building inspector(s) are gods and can
never make a mistake?


s


"Joe" wrote in message
...
On Mar 31, 12:48 pm, Guy Noir wrote:

The final arbiter is your building inspector. If he passed it, there's
no code violation.

Joe




  #6   Report Post  
Posted to alt.home.repair
Joe Joe is offline
external usenet poster
 
Posts: 2,837
Default Main Panel and Sub Panel questions and the NEC

On Mar 31, 4:57*pm, "S. Barker" wrote:
So, using this line of thinking, the building inspector(s) are gods and can
never make a mistake?


You totally missed the point, which is: You can't fight City Hall. And
also, in many years of dealing with building inspection I have had
valuable help from many very knowledgeable folks. That's the way it is
in small midwest towns, so YMMV. Of course we all make mistakes,
including inspection staff, but IMO there's more grief from badly
written codes than personnel supervising compliance.
Cheers,

Joe
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel to main panel wiring in converting multi-family to single family dwelling [email protected] Home Repair 6 November 10th 06 02:18 AM
OT security system main panel Karl Townsend Metalworking 4 September 11th 05 09:48 PM
Main Panel alive with breakers off? Walter R. Home Repair 3 August 6th 05 01:09 AM
Breaker panel with main fuses? zxcvbob Home Repair 8 December 18th 04 04:33 AM
Is main panel surge protection worth it? Jeffrey J. Kosowsky Home Repair 11 October 28th 04 11:20 AM


All times are GMT +1. The time now is 02:57 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"