Default Heat pump defrost

I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10
Default Heat pump defrost


"Bubba" wrote in message
...
On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:

I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If I
would have kept the heat pump it would have ran me in the poor house paying
for the repairs. I wrote Carrier and complained about their ****ty product.
They or the company that installed it would do nothing to stand behind
their product. I wouldn't have a heat pump if you gave it to me free and
installed it free! They are nothing but a piece of ****! I am very bitter
about the product. You wouldn't believe me if I told you what I have spent
on repairs on my 3 year old unit. I even had a repair insurance policy on it
which ran me $269 a year plus the deductable. That alone ought to tell you
how much confidence they have in their product.
The only place a heat pump might be useful would be in South Florida,
Arizona (Phoenix area south), or Southern Cal.
I don't care what praises other have for a HP.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 408
Default Heat pump defrost

On Feb 6, 9:43*am, wrote:
I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


it's wired wrong
Mark
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10
Default Heat pump defrost


"Bubba" wrote in message
...
On Wed, 6 Feb 2008 12:56:46 -0600, "Dave" wrote:


"Bubba" wrote in message
. ..
On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:

I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.

First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If
I
would have kept the heat pump it would have ran me in the poor house
paying
for the repairs. I wrote Carrier and complained about their ****ty
product.
They or the company that installed it would do nothing to stand behind
their product. I wouldn't have a heat pump if you gave it to me free and
installed it free! They are nothing but a piece of ****! I am very bitter
about the product. You wouldn't believe me if I told you what I have spent
on repairs on my 3 year old unit. I even had a repair insurance policy on
it
which ran me $269 a year plus the deductable. That alone ought to tell
you
how much confidence they have in their product.
The only place a heat pump might be useful would be in South Florida,
Arizona (Phoenix area south), or Southern Cal.
I don't care what praises other have for a HP.


Dave,
What you and the OP had were "parts changers".
Anyone can do that.
I have a high efficiency gas forced air 2 stg variable speed furnace.
Outisde I have a 14 SEER heat pump attached to it.
They both work great. I believe the heat pump has been in 4 yrs now.
Hasnt had a thing happen to it. I had a wonderful
installer...............ME! Thats what I do.
The greatest piece of equipment installed by the worst hack will net
you a horrible piece of crap.
Do your homework next time. Get references and check them out. Get it
installed correctly. Dont look for the cheapest hack out there.
Bubba


Bubba I bought the house new and was told that a Carrier heat pump was the
best on the market. In my opinion it is the best piece of crapp on the
market.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Heat pump defrost

On Feb 6, 2:10*pm, Mark wrote:
On Feb 6, 9:43*am, wrote:

I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


it's wired wrong
Mark


I asked the tech that and he said checked and told me that it is wired
right but could it been wired wrong inside the unit at the factory


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Heat pump defrost

On Feb 6, 3:05*pm, "Blattus Slafaly £ ¥ 0/00 "
wrote:
wrote:
I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


Why would it need to defrost in the winter? You making ice cubes with it.

--
Blattus Slafaly *? 3 * * *7/8


I need it to defrost in the winter because the ice builds up and keeps
the pump from doing its job
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Heat pump defrost

On Feb 6, 7:14*pm, Bubba wrote:
On Wed, 6 Feb 2008 12:56:46 -0600, "Dave" wrote:

"Bubba" wrote in message
.. .
On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:


I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If I
would have kept the heat pump it would have ran me in the poor house paying
for the repairs. I wrote Carrier and complained about their ****ty product.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Heat pump defrost

On Feb 6, 1:56*pm, "Dave" wrote:
"Bubba" wrote in message

...





On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:


I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If I
would have kept the heat pump it would have ran me in the poor house paying
for the repairs. I wrote Carrier and complained about their ****ty product..
They or the company *that installed it would do nothing to stand behind
their product. *I wouldn't have a heat pump if you gave it to me free and
installed it free! They are nothing but a piece of ****! I am very bitter
about the product. You wouldn't believe me if I told you what I have spent
on repairs on my 3 year old unit. I even had a repair insurance policy on it
which ran me $269 a year plus the deductable. *That alone ought to tell you
how much confidence they have in their product.
The only place a heat pump might be useful would be in South Florida,
Arizona *(Phoenix area south), or Southern Cal.
I don't care what praises other have for a HP.- Hide quoted text -

- Show quoted text -


I live in a condo and the only option I have is a heat pump
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 10
Default Heat pump defrost


wrote in message
...
On Feb 6, 1:56 pm, "Dave" wrote:
"Bubba" wrote in message

...





On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:


I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all.
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If
I
would have kept the heat pump it would have ran me in the poor house
paying
for the repairs. I wrote Carrier and complained about their ****ty
product.
They or the company that installed it would do nothing to stand behind
their product. I wouldn't have a heat pump if you gave it to me free and
installed it free! They are nothing but a piece of ****! I am very bitter
about the product. You wouldn't believe me if I told you what I have spent
on repairs on my 3 year old unit. I even had a repair insurance policy on
it
which ran me $269 a year plus the deductable. That alone ought to tell you
how much confidence they have in their product.
The only place a heat pump might be useful would be in South Florida,
Arizona (Phoenix area south), or Southern Cal.
I don't care what praises other have for a HP.- Hide quoted text -

- Show quoted text -


I live in a condo and the only option I have is a heat pump

Go with an electric furnace and A/C unit.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6
Default Heat pump defrost

On Feb 7, 10:43*pm, Bubba wrote:
On Thu, 7 Feb 2008 00:15:10 -0600, "Dave" wrote:

"Bubba" wrote in message
.. .
On Wed, 6 Feb 2008 12:56:46 -0600, "Dave" wrote:


"Bubba" wrote in message
...
On Wed, 6 Feb 2008 06:43:47 -0800 (PST), wrote:


I live in West Chester, Pa., 30 west of Philadelphia. A ARUF018-00A-1
heat pump was installed in my condo about 3 yrs. Ago. I notice that in
the summer if I set the thermostat to a random temperature such as 73
degrees the A/C kicks on and when it reaches 73 degrees the aux heat
kicks on, the compressor kicks on and off every 5 to 10 seconds and
the condenser fan locks out and it seem to go into defrost mode for
about 10 minutes. In the winter the defrost mode does not work at all..
I had the tech service the unit 3 times. The first time he replaced
the thermostat. The second time he added Freon. The third time he
replaced the defrost board and sensor. And after all this it still did
not take care of the problem. Can you help me.


First you need to ask for your money back.
Then you need to find a new service company.
Bubba


I had the same problem with my heat pump that you are having. I had a
Carrier. I took the heat pump out and installed a gas furnace and A/C. If
I
would have kept the heat pump it would have ran me in the poor house
paying
for the repairs. I wrote Carrier and complained about their ****ty
product.
They or the company *that installed it would do nothing to stand behind
their product. *I wouldn't have a heat pump if you gave it to me free and
installed it free! They are nothing but a piece of ****! I am very bitter
about the product. You wouldn't believe me if I told you what I have spent
on repairs on my 3 year old unit. I even had a repair insurance policy on
it
which ran me $269 a year plus the deductable. *That alone ought to tell
you
how much confidence they have in their product.
The only place a heat pump might be useful would be in South Florida,
Arizona *(Phoenix area south), or Southern Cal.
I don't care what praises other have for a HP.


Dave,
What you and the OP had were "parts changers".
Anyone can do that.
I have a high efficiency gas forced air 2 stg variable speed furnace.
Outisde I have a 14 SEER heat pump attached to it.
They both work great. I believe the heat pump has been in 4 yrs now.
Hasnt had a thing happen to it. I had a wonderful
installer...............ME! Thats what I do.
The greatest piece of equipment installed by the worst hack will net
you a horrible piece of crap.
Do your homework next time. Get references and check them out. Get it
installed correctly. Dont look for the cheapest hack out there.
Bubba


Bubba I bought the house new and was told that a Carrier heat pump was the
best on the market. In my opinion it is the best piece of crapp on the
market.


..........and let me guess. You were told that by a Carrier
dealer/builder rep who pushes Carrier equipment because the installing
company gets free trips and perks by selling more and more Carrier
equipment? *Duhhh.
You didnt actually think that the Carrier dealer was going to tell you
that Trane or Lennox or Rheem was the best there is.......did you?
Be that as it may, you are of course entitled to your own opinion.
Bubba- Hide quoted text -

- Show quoted text -


Read my problem, it is not a carrier unit Duhh.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
defrost control board for heat pump wf3h Home Repair 9 September 15th 07 05:39 PM
Heat pump defrost control board and thermostat reversing valve voltage level [email protected] Home Repair 18 May 2nd 06 07:25 AM
Buddy tells me if I have elec heat and a heat pump, I can get a deal with PSE&G... dean Home Repair 3 September 26th 05 04:31 AM
Zoned heat-pump and backup heat strip question Abe Home Repair 2 April 26th 05 01:54 AM
Heat Pump defrost cycle?? Steve Home Repair 2 January 14th 04 03:12 PM


All times are GMT +1. The time now is 05:34 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"