Default why common trip breakers for 120V circuits?

On 2008-02-03, Terry wrote:

12 guage wire on a 30A breaker a code violation and can be fire
hazard.


This is 98% true. The one exception I know of is for motor loads.
Motors can have a very high startup current, so in a dedicated motor
circuit an alternate arrangement is acceptable, as follows. The motor
itself or a dedicated motor controller or relay provides the
overcurrent (overload) protection. The breaker is just for short
circuit/ground fault protection. The breaker is sized so that it
doesn't trip due to the startup current. So you could end up with a
30 amp breaker on a #12 wire. For further details, see Article 430 of
the NEC.

Cheers, Wayne


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
why common trip breakers for 120V circuits? [email protected] Home Repair 11 February 5th 08 02:59 AM
why common trip breakers for 120V circuits? Wayne Whitney Home Repair 0 February 4th 08 02:24 AM
breakers don't trip, electricity out tysteel Home Repair 27 November 27th 07 05:10 AM
changing 240v trip on circuit breaker to 120v [email protected] Home Repair 4 November 6th 07 04:21 PM
how to 220V-->120V? blurp Home Ownership 6 August 27th 04 07:39 PM


All times are GMT +1. The time now is 08:54 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"