Default Breaker Panel 220V problem

Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default Breaker Panel 220V problem

On Sun, 6 Jan 2008 12:38:31 -0800 (PST), ronaldo123
wrote:

Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!


Call the power company. Today.

If your readings are correct it sounds like the transformer at the
pole.



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

Yes, it should read 240 volts. You have one dead leg of the 240 volt circuit
coming into the panel. It may be a bad main breaker, or open circuit at the
meter or elsewhere on the utility companies end





"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would get
anything less would be one dead hot leg. When he reads between each hot leg
to ground, he reads the good leg normally and the dead leg he gets a
backfeed reading through any 240 volt appliance that happens to be turned
on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if it
is the power company. I suspect you have a floating neutral and that
needs to be addressed as you cold end up with damaged electronics or even
a fire. (I had a boss once that burned down his photo studio due to one.)

However since I am not sure of exactly what you are measuring and how,
I would suggest asking the power company to come out and make sure their
end is OK first.

Note: If you have or can find an old analog volt meter rather than
that digital, I suspect you will find that those 54 V measurements will
become 0V. In fact if you go now and measure them again you might get
something lower or higher this time. If so that is another indication of
a floating neutral.

"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!


--
Joseph Meehan

Dia 's Muire duit





  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 337
Default Breaker Panel 220V problem

RBM wrote:
If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would get
anything less would be one dead hot leg. When he reads between each hot leg
to ground, he reads the good leg normally and the dead leg he gets a
backfeed reading through any 240 volt appliance that happens to be turned
on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if it
is the power company. I suspect you have a floating neutral and that
needs to be addressed as you cold end up with damaged electronics or even
a fire. (I had a boss once that burned down his photo studio due to one.)

However since I am not sure of exactly what you are measuring and how,
I would suggest asking the power company to come out and make sure their
end is OK first.

Note: If you have or can find an old analog volt meter rather than
that digital, I suspect you will find that those 54 V measurements will
become 0V. In fact if you go now and measure them again you might get
something lower or higher this time. If so that is another indication of
a floating neutral.

"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!

--
Joseph Meehan

Dia 's Muire duit







If it is truly an open hot leg then surely somewhere else in the house
there should be signs of some of the lights not working and some of the
outlets being dead. That is just the way the standard North American
split 240V system works. I won't pretend to know what it is that the OP
is actually measuring or how he is measuring it -- there are just too
many variables involved especially if he is using a DVM.

Personally, I would start measuring at the utility feed and then through
the bus bars and forward but there is no way I will encourage a
non-experienced person to do what I would do. I learned to do much of
this while I was still a teenager and credit my continued breathing to
an abundance of caution.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

You are correct. None of the 240 volt stuff will work, and half of the 120
volt stuff will work
"John McGaw" wrote in message
...
RBM wrote:
If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would get
anything less would be one dead hot leg. When he reads between each hot
leg to ground, he reads the good leg normally and the dead leg he gets a
backfeed reading through any 240 volt appliance that happens to be turned
on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if it
is the power company. I suspect you have a floating neutral and that
needs to be addressed as you cold end up with damaged electronics or
even a fire. (I had a boss once that burned down his photo studio due
to one.)

However since I am not sure of exactly what you are measuring and
how, I would suggest asking the power company to come out and make sure
their end is OK first.

Note: If you have or can find an old analog volt meter rather than
that digital, I suspect you will find that those 54 V measurements will
become 0V. In fact if you go now and measure them again you might get
something lower or higher this time. If so that is another indication
of a floating neutral.

"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!
--
Joseph Meehan

Dia 's Muire duit






If it is truly an open hot leg then surely somewhere else in the house
there should be signs of some of the lights not working and some of the
outlets being dead. That is just the way the standard North American split
240V system works. I won't pretend to know what it is that the OP is
actually measuring or how he is measuring it -- there are just too many
variables involved especially if he is using a DVM.

Personally, I would start measuring at the utility feed and then through
the bus bars and forward but there is no way I will encourage a
non-experienced person to do what I would do. I learned to do much of this
while I was still a teenager and credit my continued breathing to an
abundance of caution.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 337
Default Breaker Panel 220V problem

RBM wrote:
You are correct. None of the 240 volt stuff will work, and half of the 120
volt stuff will work
"John McGaw" wrote in message
...
RBM wrote:
If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would get
anything less would be one dead hot leg. When he reads between each hot
leg to ground, he reads the good leg normally and the dead leg he gets a
backfeed reading through any 240 volt appliance that happens to be turned
on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if it
is the power company. I suspect you have a floating neutral and that
needs to be addressed as you cold end up with damaged electronics or
even a fire. (I had a boss once that burned down his photo studio due
to one.)

However since I am not sure of exactly what you are measuring and
how, I would suggest asking the power company to come out and make sure
their end is OK first.

Note: If you have or can find an old analog volt meter rather than
that digital, I suspect you will find that those 54 V measurements will
become 0V. In fact if you go now and measure them again you might get
something lower or higher this time. If so that is another indication
of a floating neutral.

"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!
--
Joseph Meehan

Dia 's Muire duit




If it is truly an open hot leg then surely somewhere else in the house
there should be signs of some of the lights not working and some of the
outlets being dead. That is just the way the standard North American split
240V system works. I won't pretend to know what it is that the OP is
actually measuring or how he is measuring it -- there are just too many
variables involved especially if he is using a DVM.

Personally, I would start measuring at the utility feed and then through
the bus bars and forward but there is no way I will encourage a
non-experienced person to do what I would do. I learned to do much of this
while I was still a teenager and credit my continued breathing to an
abundance of caution.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com




Actually, I got to thinking about what I wrote and started to wonder if
it is possible to get cross-feeding from one bus through some 240V
device into the other bus without enough odd behavior elsewhere in the
house to notice. I guess it is possible if one wasn't looking for the
symptoms. Probably the best thing to do would be to simply turn off all
of the 240V breakers in the panel to eliminate any potential
cross-feeding. If it was one dead bus then surely some of the lights and
outlets would go dead with all of these breakers turned off.

Has anyone ever seen a half-tripped service main breaker? I haven't, but
I've seen it in a few regular 240V ganged breakers and know that they
can cause some odd things to happen. It might be worthwhile to simply
turn off the main and then turn it back on.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

That's exactly why he's getting a 120 volt reading from the dead leg to
ground. Lights will work on the dead leg through backfeeds through 240 volt
appliances and Edison circuits, (circuits that share a common neutral) but
they won't be full brightness





"John McGaw" wrote in message
. ..
RBM wrote:
You are correct. None of the 240 volt stuff will work, and half of the
120 volt stuff will work
"John McGaw" wrote in message
...
RBM wrote:
If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would
get anything less would be one dead hot leg. When he reads between each
hot leg to ground, he reads the good leg normally and the dead leg he
gets a backfeed reading through any 240 volt appliance that happens to
be turned on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if
it is the power company. I suspect you have a floating neutral and
that needs to be addressed as you cold end up with damaged electronics
or even a fire. (I had a boss once that burned down his photo studio
due to one.)

However since I am not sure of exactly what you are measuring and
how, I would suggest asking the power company to come out and make
sure their end is OK first.

Note: If you have or can find an old analog volt meter rather than
that digital, I suspect you will find that those 54 V measurements
will become 0V. In fact if you go now and measure them again you
might get something lower or higher this time. If so that is another
indication of a floating neutral.

"ronaldo123" wrote in message
...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure each
of the hot wires to the ground it measures 110volts.. is this normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!
--
Joseph Meehan

Dia 's Muire duit




If it is truly an open hot leg then surely somewhere else in the house
there should be signs of some of the lights not working and some of the
outlets being dead. That is just the way the standard North American
split 240V system works. I won't pretend to know what it is that the OP
is actually measuring or how he is measuring it -- there are just too
many variables involved especially if he is using a DVM.

Personally, I would start measuring at the utility feed and then through
the bus bars and forward but there is no way I will encourage a
non-experienced person to do what I would do. I learned to do much of
this while I was still a teenager and credit my continued breathing to
an abundance of caution.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com




Actually, I got to thinking about what I wrote and started to wonder if it
is possible to get cross-feeding from one bus through some 240V device
into the other bus without enough odd behavior elsewhere in the house to
notice. I guess it is possible if one wasn't looking for the symptoms.
Probably the best thing to do would be to simply turn off all of the 240V
breakers in the panel to eliminate any potential cross-feeding. If it was
one dead bus then surely some of the lights and outlets would go dead with
all of these breakers turned off.

Has anyone ever seen a half-tripped service main breaker? I haven't, but
I've seen it in a few regular 240V ganged breakers and know that they can
cause some odd things to happen. It might be worthwhile to simply turn off
the main and then turn it back on.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 636
Default Breaker Panel 220V problem

John McGaw wrote:

Actually, I got to thinking about what I wrote and started to wonder
if it is possible to get cross-feeding from one bus through some 240V
device into the other bus without enough odd behavior elsewhere in the
house to notice. I guess it is possible if one wasn't looking for the
symptoms. Probably the best thing to do would be to simply turn off
all of the 240V breakers in the panel to eliminate any potential
cross-feeding. If it was one dead bus then surely some of the lights
and outlets would go dead with all of these breakers turned off.


I agree. One of his 240V appliances is on - probably the water heater - and
is back-feeding all the 120V circuits on that leg.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 212
Default Breaker Panel 220V problem

Your 120V circuits will each be on one side or the other of the 240V.
Assuming you are able to tell which is which, if you turn off all the
breakers for circuits on one side as well as any 2-pole 240V breakers, what
happens to power on the circuits on the side that remains on?

If the neutral is open then these should be dead as well. But for that to
happen you'd also have to have also a missing or bad ground at the panel or
maybe your ground is ok but the utility's grounding of the neutral on the
secondary side of the transformer could be bad.

However, with a neutral open but a ground that is present but mediocre you
might read proper voltage with nothing turned on and even have satisfactory
operation of a few lights and other small stuff but severe voltage drop
when trying to drive a heavy load.

As the others have said call the utility or a professional electrician ASAP
and be VERY careful about coming into contact with ANYTHING including what
ought to be grounded. If the neutral is open somewhere and grounding
broken or insufficient not only can the neutrals be lethally hot but it's
even possible for the grounds to be hot (less likely with conduits although
possible depending on physical construction but easily possible if the
grounds are just wires within Romex and the like).


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Breaker Panel 220V problem

I had a neighborhood transformer fail once, with wierd readings and
strange symptoms.

one side of transformer fried, still produced a wierd low
voltage...........

real bear to figure out....

call power company, as first step
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

Practically every modern panel is set up with alternating buss, not left
side and right side. The few exceptions are obsolete panels like Pushmatic
and Zinsco





"Steve Kraus" wrote in message
...
Your 120V circuits will each be on one side or the other of the 240V.
Assuming you are able to tell which is which, if you turn off all the
breakers for circuits on one side as well as any 2-pole 240V breakers,
what
happens to power on the circuits on the side that remains on?

If the neutral is open then these should be dead as well. But for that to
happen you'd also have to have also a missing or bad ground at the panel
or
maybe your ground is ok but the utility's grounding of the neutral on the
secondary side of the transformer could be bad.

However, with a neutral open but a ground that is present but mediocre you
might read proper voltage with nothing turned on and even have
satisfactory
operation of a few lights and other small stuff but severe voltage drop
when trying to drive a heavy load.

As the others have said call the utility or a professional electrician
ASAP
and be VERY careful about coming into contact with ANYTHING including what
ought to be grounded. If the neutral is open somewhere and grounding
broken or insufficient not only can the neutrals be lethally hot but it's
even possible for the grounds to be hot (less likely with conduits
although
possible depending on physical construction but easily possible if the
grounds are just wires within Romex and the like).



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Breaker Panel 220V problem

On Jan 6, 2:38 pm, ronaldo123 wrote:

Wow I wasn't expecting these many answers, Thanks ALL!!

The way I measured the hot wires is I turned off the main breaker and
used a digital volt meter, it gives me around 50-58 volts between the
hot wires but each of them gives 110V when I measure against the
neutral wire.
I am having problems with some devices and some lights only turn on
100% if I turn on the oven.
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Breaker Panel 220V problem

That is exactly what happens with one open hot leg. Call an electrician or
your electric utility





"ronaldo123" wrote in message
...
On Jan 6, 2:38 pm, ronaldo123 wrote:

Wow I wasn't expecting these many answers, Thanks ALL!!

The way I measured the hot wires is I turned off the main breaker and
used a digital volt meter, it gives me around 50-58 volts between the
hot wires but each of them gives 110V when I measure against the
neutral wire.
I am having problems with some devices and some lights only turn on
100% if I turn on the oven.



  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Breaker Panel 220V problem


"John McGaw" wrote in message
. ..
RBM wrote:
You are correct. None of the 240 volt stuff will work, and half of the

120
volt stuff will work
"John McGaw" wrote in message
...
RBM wrote:
If he's measuring between the "two hot wires" he should read 240 volts
regardless if his neutral is intact or not. The only reason he would

get
anything less would be one dead hot leg. When he reads between each

hot
leg to ground, he reads the good leg normally and the dead leg he gets

a
backfeed reading through any 240 volt appliance that happens to be

turned
on. Both will give a 120 volt reading.





"Joseph Meehan" wrote in message
...
Since you are getting 110 (should be 120 in most areas) I doubt if

it
is the power company. I suspect you have a floating neutral and that
needs to be addressed as you cold end up with damaged electronics or
even a fire. (I had a boss once that burned down his photo studio

due
to one.)

However since I am not sure of exactly what you are measuring and
how, I would suggest asking the power company to come out and make

sure
their end is OK first.

Note: If you have or can find an old analog volt meter rather

than
that digital, I suspect you will find that those 54 V measurements

will
become 0V. In fact if you go now and measure them again you might

get
something lower or higher this time. If so that is another

indication
of a floating neutral.

"ronaldo123" wrote in message

...
Hi all,

I have problem at home. Recently my oven, water heater, dryer....
stopped working. I tried playing with the breakers but it all seems
to be fine. One curious thing in the panel is that if I measure the
voltage between the 2 hot wires it reads 58volts... if I measure

each
of the hot wires to the ground it measures 110volts.. is this

normal?
Should the voltage between the 2 hotwires measure 220V ?

Thanks!
--
Joseph Meehan

Dia 's Muire duit




If it is truly an open hot leg then surely somewhere else in the house
there should be signs of some of the lights not working and some of the
outlets being dead. That is just the way the standard North American

split
240V system works. I won't pretend to know what it is that the OP is
actually measuring or how he is measuring it -- there are just too many
variables involved especially if he is using a DVM.

Personally, I would start measuring at the utility feed and then

through
the bus bars and forward but there is no way I will encourage a
non-experienced person to do what I would do. I learned to do much of

this
while I was still a teenager and credit my continued breathing to an
abundance of caution.

--
John McGaw
[Knoxville, TN, USA]
http://johnmcgaw.com




Actually, I got to thinking about what I wrote and started to wonder if
it is possible to get cross-feeding from one bus through some 240V
device into the other bus without enough odd behavior elsewhere in the
house to notice. I guess it is possible if one wasn't looking for the
symptoms. Probably the best thing to do would be to simply turn off all
of the 240V breakers in the panel to eliminate any potential
cross-feeding. If it was one dead bus then surely some of the lights and
outlets would go dead with all of these breakers turned off.

Has anyone ever seen a half-tripped service main breaker? I haven't, but
I've seen it in a few regular 240V ganged breakers and know that they
can cause some odd things to happen. It might be worthwhile to simply
turn off the main and then turn it back on.



I saw a half tripped main breaker many years ago. It was a Federal Pacific.
I shut it off and turned it back on again and everything was fine.



  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Breaker Panel 220V problem

On Jan 6, 10:58�pm, ronaldo123 wrote:
On Jan 6, 2:38 pm, ronaldo123 wrote:

Wow I wasn't expecting these many answers, Thanks ALL!!

The way I measured the hot wires is I turned off the main breaker and
used a digital volt meter, it gives me around 50-58 volts between the
hot wires but each of them gives 110V when I measure against the
neutral wire.
I am having problems with some devices and some lights only turn on
100% if I turn on the oven.


its best to not use a digital volt meter when doing home repairs, they
are way too sensitive..........

cheap analog meters are fine, or put a trouble light 50 watt load on
the circuit then check with a digital meter.

a 25 watt light bulb is enough of a load to also let you know whats
up, just connect across connection and see if bulb glows
  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Breaker Panel 220V problem

In article , "Joseph Meehan" wrote:
Since you are getting 110 (should be 120 in most areas) I doubt if it is
the power company. I suspect you have a floating neutral


Nonsense. The two hot legs should always have approximately 240V between them.
The neutral has nothing whatever to do with that.


--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 856
Default Breaker Panel 220V problem

According to RBM :
You are correct. None of the 240 volt stuff will work, and half of the 120
volt stuff will work


Not necessarily. If one leg's connection to the utility is broken,
he could see no 240V devices work, and _all_ of the 120V stuff appear
to work. If a 240V device (like the water heater) is switched on, it'll
backfeed one 120V side into the other.

Ordinarily, you'd expect the lights on the "broken connection side"
to be dim, but if you don't load it up very much, and the 240V device
is large enough (water heater, stove, dryer), the lights may well not
dim noticably at all.

The voltage difference between the two legs at the panel is the
voltage drop across the 240V device.

Simple way to check this stuff out without opening anything up:

1) Cycle the main breaker, and see if things work any better.

2) Turn off _every_ 240V breaker, and see if he loses one half
of the 120V circuits.
--
Chris Lewis,

Age and Treachery will Triumph over Youth and Skill
It's not just anyone who gets a Starship Cruiser class named after them.
  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 212
Default Breaker Panel 220V problem

"RBM" wrote in :

Practically every modern panel is set up with alternating buss, not
left side and right side. The few exceptions are obsolete panels like
Pushmatic and Zinsco


I didn't mean "side" in the literal sense of how the panel is laid out.
We've got one where it's the top group vs. the middle group with mains at
the bottom and 240's that straddle top and middle.

Anyway, looks like he's got one hot side open.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Found something odd in my breaker panel Tater Home Repair 10 October 6th 06 09:57 PM
Breaker Panel....Neutral bus MB Home Repair 12 March 14th 06 06:07 PM
Extending a Breaker Panel. PVR Home Repair 6 September 11th 05 04:38 PM
Breaker panel with main fuses? zxcvbob Home Repair 8 December 18th 04 04:33 AM
OT Ge breaker in Murray panel Dan Caster Metalworking 5 September 9th 03 04:45 PM


All times are GMT +1. The time now is 09:06 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"