In fixing my pool skimmer plumbing I had to remove about a 12"x18" area of
my concrete pool deck. The deck is a 4" thick concrete slab, then a layer
of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went below
the slab, I believe one end of it goes to the exterior wall of the house
where there is a switch and an outlet, and the other end go to a planter
area twenty feet away where there is a conduit coming out with a few
outlets, used for exterior lighting. There are several planter areas around
the pool deck, all with electrical outlets coming out of the ground.

Problem is, the rigid conduit these wires are in, is badly corroded, the
area where I opened up near the skimmer, the conduit was corroded so badly
when I poked it with a stick it broke like a twig, exposing the red wire
inside. I suspect it's the same with all four wires that ran underground to
get power to the planter areas and may be the submerged pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in the
planter areas where it could get water from the sprinklers, but it's not
practical to rip up my entire concrete pool deck just to redo it.

Is there a practical solution?

Thanks,

MC


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Below grade electrical wiring

It sounds like you have buried EMT and not galv pipe. There is no practical
way to repair it, although the fact that the wires are wet is not an issue.
Even wires in a galvanized pipe underground will be wet and in contact with
the pipe and ground, etc. I would just make sure the conductors are
protected by ground fault devices on the house side, this way if the
insulation on the wires failed, you would be protected. You would also want
to be sure that there is a separate ground wire in the conduit, and that the
conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area of
my concrete pool deck. The deck is a 4" thick concrete slab, then a layer
of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went below
the slab, I believe one end of it goes to the exterior wall of the house
where there is a switch and an outlet, and the other end go to a planter
area twenty feet away where there is a conduit coming out with a few
outlets, used for exterior lighting. There are several planter areas
around the pool deck, all with electrical outlets coming out of the
ground.

Problem is, the rigid conduit these wires are in, is badly corroded, the
area where I opened up near the skimmer, the conduit was corroded so badly
when I poked it with a stick it broke like a twig, exposing the red wire
inside. I suspect it's the same with all four wires that ran underground
to get power to the planter areas and may be the submerged pool light as
well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but it's
not practical to rip up my entire concrete pool deck just to redo it.

Is there a practical solution?

Thanks,

MC



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 664
Default Below grade electrical wiring

Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...
It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet and
in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of the
house where there is a switch and an outlet, and the other end go to a
planter area twenty feet away where there is a conduit coming out with a
few outlets, used for exterior lighting. There are several planter areas
around the pool deck, all with electrical outlets coming out of the
ground.

Problem is, the rigid conduit these wires are in, is badly corroded, the
area where I opened up near the skimmer, the conduit was corroded so
badly when I poked it with a stick it broke like a twig, exposing the red
wire inside. I suspect it's the same with all four wires that ran
underground to get power to the planter areas and may be the submerged
pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but it's
not practical to rip up my entire concrete pool deck just to redo it.

Is there a practical solution?

Thanks,

MC





  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Below grade electrical wiring

On Jan 5, 9:57�am, "MiamiCuse" wrote:
Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message

...



It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet and
in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground


"MiamiCuse" wrote in message
. ..
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. �The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.


While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of the
house where there is a switch and an outlet, and the other end go to a
planter area twenty feet away where there is a conduit coming out with a
few outlets, used for exterior lighting. �There are several planter areas
around the pool deck, all with electrical outlets coming out of the
ground.


Problem is, the rigid conduit these wires are in, is badly corroded, the
area where I opened up near the skimmer, the conduit was corroded so
badly when I poked it with a stick it broke like a twig, exposing the red
wire inside. �I suspect it's the same with all four wires that ran
underground to get power to the planter areas and may be the submerged
pool light as well.


Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but it's
not practical to rip up my entire concrete pool deck just to redo it.


Is there a practical solution?


Thanks,


MC- Hide quoted text -


- Show quoted text -


if that the only wire in the conduit? how old is the pool?

safety rules have changed a lot. between age and needed safety
upgrades you may have a large project started
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Below grade electrical wiring

If the conduit only has one red and one white wire, and no others, yes, you
have no ground wire


"MiamiCuse" wrote in message
...
Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...
It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet and
in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of the
house where there is a switch and an outlet, and the other end go to a
planter area twenty feet away where there is a conduit coming out with a
few outlets, used for exterior lighting. There are several planter
areas around the pool deck, all with electrical outlets coming out of
the ground.

Problem is, the rigid conduit these wires are in, is badly corroded, the
area where I opened up near the skimmer, the conduit was corroded so
badly when I poked it with a stick it broke like a twig, exposing the
red wire inside. I suspect it's the same with all four wires that ran
underground to get power to the planter areas and may be the submerged
pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but it's
not practical to rip up my entire concrete pool deck just to redo it.

Is there a practical solution?

Thanks,

MC









  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 664
Default Below grade electrical wiring


wrote in message
...
On Jan 5, 9:57?am, "MiamiCuse" wrote:
Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message

...



It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet
and
in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground


"MiamiCuse" wrote in message
. ..
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. ?The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.


While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of
the
house where there is a switch and an outlet, and the other end go to a
planter area twenty feet away where there is a conduit coming out with
a
few outlets, used for exterior lighting. ?There are several planter
areas
around the pool deck, all with electrical outlets coming out of the
ground.


Problem is, the rigid conduit these wires are in, is badly corroded,
the
area where I opened up near the skimmer, the conduit was corroded so
badly when I poked it with a stick it broke like a twig, exposing the
red
wire inside. ?I suspect it's the same with all four wires that ran
underground to get power to the planter areas and may be the submerged
pool light as well.


Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but
it's
not practical to rip up my entire concrete pool deck just to redo it.


Is there a practical solution?


Thanks,


MC- Hide quoted text -


- Show quoted text -


if that the only wire in the conduit? how old is the pool?

safety rules have changed a lot. between age and needed safety
upgrades you may have a large project started


pool was built in 1972.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 664
Default Below grade electrical wiring

The conduit has a single red wire, no white wire or any other wire.
Strange...

"RBM" wrote in message
...
If the conduit only has one red and one white wire, and no others, yes,
you have no ground wire


"MiamiCuse" wrote in message
...
Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...
It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet
and in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...
In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of
the house where there is a switch and an outlet, and the other end go
to a planter area twenty feet away where there is a conduit coming out
with a few outlets, used for exterior lighting. There are several
planter areas around the pool deck, all with electrical outlets coming
out of the ground.

Problem is, the rigid conduit these wires are in, is badly corroded,
the area where I opened up near the skimmer, the conduit was corroded
so badly when I poked it with a stick it broke like a twig, exposing
the red wire inside. I suspect it's the same with all four wires that
ran underground to get power to the planter areas and may be the
submerged pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but
it's not practical to rip up my entire concrete pool deck just to redo
it.

Is there a practical solution?

Thanks,

MC









  #8   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Below grade electrical wiring

MiamiCuse wrote:
The conduit has a single red wire, no white wire or any other wire.

....

Where does it come from and go again?

What is it hooked to and what other connection(s) is/are on whatever
that device(s) is/are?

This a low-voltage lighting circuit by chance?

--

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 261
Default Below grade electrical wiring

MiamiCuse wrote:

The conduit has a single red wire, no white wire or any other wire.
Strange...

"RBM" wrote in message
...

If the conduit only has one red and one white wire, and no others, yes,
you have no ground wire


"MiamiCuse" wrote in message
...

Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...

It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet
and in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...

In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of
the house where there is a switch and an outlet, and the other end go
to a planter area twenty feet away where there is a conduit coming out
with a few outlets, used for exterior lighting. There are several
planter areas around the pool deck, all with electrical outlets coming
out of the ground.

Problem is, the rigid conduit these wires are in, is badly corroded,
the area where I opened up near the skimmer, the conduit was corroded
so badly when I poked it with a stick it broke like a twig, exposing
the red wire inside. I suspect it's the same with all four wires that
ran underground to get power to the planter areas and may be the
submerged pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but
it's not practical to rip up my entire concrete pool deck just to redo
it.

Is there a practical solution?

Thanks,

MC


Do you have a sprinkler system?


--
Robert Allison
Rimshot, Inc.
Georgetown, TX
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Below grade electrical wiring

One conductor doesn't get you very far, unless it is possibly a bonding
conductor. The rebar in the concrete pool deck must be bonded together. If
it is, it will be #8 gauge. Is it definitely an insulated (Red) conductor?


"MiamiCuse" wrote in message
news
The conduit has a single red wire, no white wire or any other wire.
Strange...

"RBM" wrote in message
...
If the conduit only has one red and one white wire, and no others, yes,
you have no ground wire


"MiamiCuse" wrote in message
...
Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...
It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet
and in contact with the pipe and ground, etc. I would just make sure
the conductors are protected by ground fault devices on the house side,
this way if the insulation on the wires failed, you would be protected.
You would also want to be sure that there is a separate ground wire in
the conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
...
In fixing my pool skimmer plumbing I had to remove about a 12"x18"
area of my concrete pool deck. The deck is a 4" thick concrete slab,
then a layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of
the house where there is a switch and an outlet, and the other end go
to a planter area twenty feet away where there is a conduit coming out
with a few outlets, used for exterior lighting. There are several
planter areas around the pool deck, all with electrical outlets coming
out of the ground.

Problem is, the rigid conduit these wires are in, is badly corroded,
the area where I opened up near the skimmer, the conduit was corroded
so badly when I poked it with a stick it broke like a twig, exposing
the red wire inside. I suspect it's the same with all four wires that
ran underground to get power to the planter areas and may be the
submerged pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing,
in the planter areas where it could get water from the sprinklers, but
it's not practical to rip up my entire concrete pool deck just to redo
it.

Is there a practical solution?

Thanks,

MC













  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,009
Default Below grade electrical wiring


"MiamiCuse" wrote

While fixing the plumbing, I noticed an electrical conduit that went below
the slab, I believe one end of it goes to the exterior wall of the house
where there is a switch and an outlet, and the other end go to a planter
area twenty feet away where there is a conduit coming out with a few

(snip- Corroded conduit)

Is there a practical solution?


I think so. If the line is unsafe, have it capped off at the house first.
Danger now gone. Next, look and see if it would be easier to just ignore
the old conduit and run a new one with newest safety grade. It wouldnt have
to follow the same lines as the old so might not involve as much under the
pool deck digging to lay it. Depending on the design of your pool deck, it
*might* even be possible to go ontop without creating a trip hazard?


  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,963
Default Below grade electrical wiring

On Sat, 05 Jan 2008 17:34:51 GMT, Robert Allison
wrote:

MiamiCuse wrote:

The conduit has a single red wire, no white wire or any other wire.
Strange...

"RBM" wrote in message
...

If the conduit only has one red and one white wire, and no others, yes,
you have no ground wire


"MiamiCuse" wrote in message
...

Thanks, there is only one red wire inside the conduit, does this mean I
don't have a proper ground wire?

"RBM" wrote in message
...

It sounds like you have buried EMT and not galv pipe. There is no
practical way to repair it, although the fact that the wires are wet is
not an issue. Even wires in a galvanized pipe underground will be wet
and in contact with the pipe and ground, etc. I would just make sure the
conductors are protected by ground fault devices on the house side, this
way if the insulation on the wires failed, you would be protected. You
would also want to be sure that there is a separate ground wire in the
conduit, and that the conduit is not used as an equipment ground



"MiamiCuse" wrote in message
m...

In fixing my pool skimmer plumbing I had to remove about a 12"x18" area
of my concrete pool deck. The deck is a 4" thick concrete slab, then a
layer of 3/4" tile on top.

While fixing the plumbing, I noticed an electrical conduit that went
below the slab, I believe one end of it goes to the exterior wall of
the house where there is a switch and an outlet, and the other end go
to a planter area twenty feet away where there is a conduit coming out
with a few outlets, used for exterior lighting. There are several
planter areas around the pool deck, all with electrical outlets coming
out of the ground.

Problem is, the rigid conduit these wires are in, is badly corroded,
the area where I opened up near the skimmer, the conduit was corroded
so badly when I poked it with a stick it broke like a twig, exposing
the red wire inside. I suspect it's the same with all four wires that
ran underground to get power to the planter areas and may be the
submerged pool light as well.

Something tells me it's not safe to have exposed hot wires like this
underground especially where it may be wet - near the pool plumbing, in
the planter areas where it could get water from the sprinklers, but
it's not practical to rip up my entire concrete pool deck just to redo
it.

Is there a practical solution?

Thanks,

MC


Do you have a sprinkler system?


That's what I was thinking of when I read "red wire". My sprinkler
system (installed in 1998) has red wires going to each valve, and
white for common. These wires are not in conduit, but buried with the
pipes.
--
Mark Lloyd
http://notstupid.laughingsquid.com

"DISCLAIMER If you find a posting or message
from me offensive, inappropriate, or disruptive,
please ignore it. If you don't know how to
ignore a posting, complain to me and I will
demonstrate."
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hy-Grade Hy Grade Steel Roofing Roof Company WARNING [email protected] Home Repair 7 September 7th 19 09:14 PM
Help with Electrical Wiring ,please travelingart Home Repair 4 October 13th 07 11:01 PM
Electrical Wiring [email protected] UK diy 4 October 6th 07 10:03 PM
Electrical Wiring Help! [email protected] Home Repair 18 January 16th 07 12:06 AM
Hy-Grade Hy Grade Steel Roofing Roof Company W A R N I N G [email protected] Home Ownership 1 June 13th 06 06:36 PM


All times are GMT +1. The time now is 09:15 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"