Default can a circuit breaker that tripped, worked properly, be damaged inthe process?

Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?

Thank you for any insight, Mark
  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default can a circuit breaker that tripped, worked properly, be damagedin the process?

Mark_Galeck wrote:
Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?


Shouldn't, but as the saying goes "stuff happens".

I'm guessing this maybe was a 240V breaker? The some in "some other
wires" implies one side is shorted, the other not, perhaps, or is that
not a precise description of symptoms.

Replacing certainly sounds in order, check for any signs of collateral
damage from the short at the mounting and neutral bars, etc.

I guess I'll add the obligatory caution -- this wouldn't happen to be an
old FPE (Federal Pacific) breaker/box by any chance?

--
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default can a circuit breaker that tripped, worked properly, be damagedin the process?

On Dec 31, 10:41�am, dpb wrote:
Mark_Galeck wrote:
Hello, �I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!


Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? �Or is something else wrong?


Shouldn't, but as the saying goes "stuff happens".

I'm guessing this maybe was a 240V breaker? �The some in "some other
wires" implies one side is shorted, the other not, perhaps, or is that
not a precise description of symptoms.

Replacing certainly sounds in order, check for any signs of collateral
damage from the short at the mounting and neutral bars, etc.

I guess I'll add the obligatory caution -- this wouldn't happen to be an
old FPE (Federal Pacific) breaker/box by any chance?

--


breakers are designed to do their job, but can go bad. a westinghouse
plant i used to spend a lot of time in found that knock off
westinghouse breakers would either explode or short. i saw a explode
demo once....

these were distribution breakers, just big models of regular home
breakers. i watched them be assembled, it was a interesting place.

I did a repair job saturday and got a nasty shock after being assured
the power was off

I should of done my usual short everything to ground to make certain
circuit was dead...

but to answer your question breakers are designed to trip.

tripping shouldnt damage them

but yes it can happen replace the breaker

are you certain the stuff thats still on is on the breaker in
question?

try a test lamp on the breakers out terminal
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default can a circuit breaker that tripped, worked properly, be damaged in the process?

On Mon, 31 Dec 2007 09:41:38 -0600, dpb wrote:

Mark_Galeck wrote:
Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?


Shouldn't, but as the saying goes "stuff happens".

I'm guessing this maybe was a 240V breaker? The some in "some other
wires" implies one side is shorted, the other not, perhaps, or is that
not a precise description of symptoms.

Replacing certainly sounds in order, check for any signs of collateral
damage from the short at the mounting and neutral bars, etc.

I guess I'll add the obligatory caution -- this wouldn't happen to be an
old FPE (Federal Pacific) breaker/box by any chance?


One way to test the breaker before going out and buying a new one
would be swap wires with another circuit temporally.

I would test a known good circuit to see if the breaker works instead
of testing the bad circuit on a good breaker.


You could have melted some wire insulation when you shorted them
together. (the bang, smoke part)

I would completely unwire what you did and see if the problem clears.

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default can a circuit breaker that tripped, worked properly, be damagedin the process?

Mark_Galeck wrote:
Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?

Thank you for any insight, Mark


Mark
The bad news here is that you may need some special intervention to
protect your home from catastrophic failure of your service equipment
during some future electrical fault.

If you look at the breaker's molded plastic case you will see that it is
marked with a withstand rating. Common ratings are 5,000; 10,000;
22,000; and 45,000 symmetrical amperes. That is the amount of current
the breaker can interrupt without the case rupturing and throwing
burning plastic and molten metal around. At currents well below the
withstand the breaker can fail internally so as to no longer perform
it's function but it would fail in the off condition. It it failed in
such a way that it is still passing current then the withstand rating of
the breaker was exceeded.

Why that is important is that it shows there is enough current available
to the panel's buss bars to exceed the withstand rating of the installed
breakers. You need to have a calculation done by your utilities
engineering department, a fairly sharp master electrician, or an
electrical engineer. If the fault current available to your panels
terminals is indeed higher than the rating of the installed beakers
remedial work needs to be done to protect your home and family from the
real possibility of explosive failure of the existing breakers. The
power utility will sometimes be willing to recommend cost effective
remediation for your situation. If they are not willing to provide that
service then your best recourse is to call in a master electrician to
examine your problem.

Some examples of the kinds of things that can be done is to replace all
of the breakers with breakers recognized for use in that panel that have
a higher withstand rating. Calculation may reveal that only the main
breaker needs to be upgraded. In some installations a fused disconnect
is installed ahead of the panel to limit the fault current to the
existing breakers withstand rating. I know that this is not good news
for you but if you ignore this failure and just replace the failed
breaker then the next fault may turn one of your breakers into a hand
grenade that will not only injure the person who closes it on the fault
but also destroys adjacent breakers and spews burning plastic. Such
failures are rare in homes but they have occurred and the consequences
of such failures are quite dire.
--
Tom Horne


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default can a circuit breaker that tripped, worked properly, be damaged in the process?

On Mon, 31 Dec 2007 07:38:57 -0800 (PST), Mark_Galeck
wrote:

Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?

Thank you for any insight, Mark


Remove the wires from that breaker, put a tester on it and if there is
still voltage, replace the breaker. You could be getting voltage from
some other crossed circuit. Breakers DO go bad and anything can cause
it.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 636
Default can a circuit breaker that tripped, worked properly, be damaged in the process?

Mark_Galeck wrote:
Hello, I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? Or is something else wrong?

Thank you for any insight, Mark


If a tripped circuit breaker is still passing current, it's kinda useless,
isn't it?

Things like this should be designed to fail safe.

I'd contact the manufacturer.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 44
Default can a circuit breaker that tripped, worked properly, be damagedin the process?

On Dec 31 2007, 9:38*am, Mark_Galeck
wrote:
Hello, *I was wiring something and I messed up, as soon as I turned
the heater circuit breaker (to the thing I was wiring) on, there was a
loud bang, smoke and the breaker jumped back to OFF position, that
means, it worked properly, although the part I was wiring, got
damaged. I then disconnected the damaged part.
However, now the circuit breaker appears to "short", that is, even in
the OFF position, some other wires that it controls, are hot!

Can a tripped circuit breaker, get shorted that way in the process, so
that it cannot be turned OFF, and so I should replace the circuit
breaker? *Or is something else wrong?

Thank you for any insight, *Mark


Do yourself a huge favor and call an electrician.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dead circuit with no tripped breaker or fuse [email protected] Home Repair 4 July 20th 07 02:58 PM
When bulb blows, earth leakage circuit breaker is tripped MM UK diy 40 December 16th 06 11:22 AM
Circuit breaker tripped while on vacation, how to get smell out of refrigerator? Dan K Home Repair 9 December 10th 04 04:30 PM
Help -- Power out in one area but circuit breaker not tripped Joseph Meehan Home Repair 0 June 27th 03 02:29 AM


All times are GMT +1. The time now is 03:21 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"