  #1   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 27
Default Chimney liner for oil fired boiler

Dear Readers,

I've a Burnham MPO boiler. I called Burnham, whose technicians
suggest that I take the most conservative approach and line my
existing exterior-wall, clay-lined brick chimney with a stainless
liner to minimize flue condensation.

Should this liner necessarily be insulated as well? Or is the dead
airspace (although somewhat cold due to exterior wall) in the chimney
a sufficient buffer? I know the most conservative answer is to
insulate the liner too, but your experiences would be appreciated as
this insulation would be yet another expense on top of the liner.

Thank you very much for your responses.
-Anthony

  #3   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 4,926
Default Chimney liner for oil fired boiler

On Nov 6, 4:08 am, Don Ocean wrote:
wrote:
Dear Readers,


I've a Burnham MPO boiler. I called Burnham, whose technicians
suggest that I take the most conservative approach and line my
existing exterior-wall, clay-lined brick chimney with a stainless
liner to minimize flue condensation.


Should this liner necessarily be insulated as well? Or is the dead
airspace (although somewhat cold due to exterior wall) in the chimney
a sufficient buffer? I know the most conservative answer is to
insulate the liner too, but your experiences would be appreciated as
this insulation would be yet another expense on top of the liner.


Thank you very much for your responses.
-Anthony


Heh! Heh! Size does matter... ;-)



- Hide quoted text -

- Show quoted text -- Hide quoted text -

- Show quoted text -


If it heats water its a boiler, if it heats air its a furnace, so you
have a boiler from your next post. If its a condensing unit you should
be able to vent through a wall, I dont understand why you need to line
a clay lined chimney unless its falling apart, clay is durable.

  #4   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 26
Default Chimney liner for oil fired boiler




If it heats water its a boiler, if it heats air its a furnace, so you
have a boiler from your next post. If its a condensing unit you should
be able to vent through a wall, I dont understand why you need to line
a clay lined chimney unless its falling apart, clay is durable.


Mortar is not



  #6   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 42
Default Chimney liner for oil fired boiler

ransley wrote:
On Nov 6, 4:08 am, Don Ocean wrote:
wrote:
Dear Readers,
I've a Burnham MPO boiler. I called Burnham, whose technicians
suggest that I take the most conservative approach and line my
existing exterior-wall, clay-lined brick chimney with a stainless
liner to minimize flue condensation.
Should this liner necessarily be insulated as well? Or is the dead
airspace (although somewhat cold due to exterior wall) in the chimney
a sufficient buffer? I know the most conservative answer is to
insulate the liner too, but your experiences would be appreciated as
this insulation would be yet another expense on top of the liner.
Thank you very much for your responses.
-Anthony

Heh! Heh! Size does matter... ;-)



- Hide quoted text -

- Show quoted text -- Hide quoted text -

- Show quoted text -


If it heats water its a boiler, if it heats air its a furnace, so you
have a boiler from your next post. If its a condensing unit you should
be able to vent through a wall, I dont understand why you need to line
a clay lined chimney unless its falling apart, clay is durable.



I say again.. Size does matter. That chimney must be resized to fit the
venting requirements. A liner is one way to downsize for modern
equipment needs. Check your local building authority if you don't
have a code book.

  #7   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 27
Default Chimney liner for oil fired boiler

Check with the Burnham Tech's again, I believe they intemnd for you to use a
double wall stainless flue pipe in the chimney opening. Insulation not
needed.


Just called them again. They expect stack temperatures of below
350F. Considering it's an exterior wall chimney and (I suggested I
may also have a fresh air duct installed in the future), they once
again recommend a stainless liner to prevent condensation from
damaging the existing chimney. As they're not in the liner industry,
they did not want to officially comment on the specific type, although
the individual I spoke with said he's familiar with the single wall
variety.

The double wall stainless liners I'm familiar with would seem like
overkill: they are insulated in between layers and are typically the
type that can be in close proximity to combustibles, like those
metalbestos things. And I do not want to switch to a power vent
situation.

Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there
familiar with or observe a similar stainless chimney liner
installation??

  #8   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 190
Default Chimney liner for oil fired boiler


wrote in message
ps.com...
Check with the Burnham Tech's again, I believe they intemnd for you to
use a
double wall stainless flue pipe in the chimney opening. Insulation not
needed.


Just called them again. They expect stack temperatures of below
350F. Considering it's an exterior wall chimney and (I suggested I
may also have a fresh air duct installed in the future), they once
again recommend a stainless liner to prevent condensation from
damaging the existing chimney. As they're not in the liner industry,
they did not want to officially comment on the specific type, although
the individual I spoke with said he's familiar with the single wall
variety.

The double wall stainless liners I'm familiar with would seem like
overkill: they are insulated in between layers and are typically the
type that can be in close proximity to combustibles, like those
metalbestos things. And I do not want to switch to a power vent
situation.

Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there
familiar with or observe a similar stainless chimney liner
installation??

What does the installation manual say about it??
What do your local codes require??
What did the local building inspector say about it??
What did your insurance company say about it??

We are not here to do your homework for you.


  #9   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 27
Default Chimney liner for oil fired boiler

Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there
familiar with or observe a similar stainless chimney liner
installation??


What does the installation manual say about it??
What do your local codes require??
What did the local building inspector say about it??
What did your insurance company say about it??

We are not here to do your homework for you.- Hide quoted text -

- Show quoted text -


Thanks for the suggestions.
1. Installation manual says use a liner "if condensation is
observed." Per my earlier post, I called the manufacturer and didn't
get too much advice on what type as it's not their product.
2. I didn't think to check the code! Chapt 8 of Mechanical Code of NY
says to use liner that will resist condensate, and is in accordance
with NFPA31. I'll find NFPA31 and see what it says. Hopefully will
provide guidance on insulated vs. non-insulated.
3. Local building inspector cannot (legally) suggest anything beyond
the building code, so I'll need that NFPA31.
4. I didn't check insurance company. Not sure if they'll even
understand what I'm saying. I'll try.

I have two additional thoughts:
1. if flue gas is cooled too much within liner inside chimney, it may
not create sufficient draft up the 25ft tall, exterior wall chimney.
Is there a way I can estimate if I'll have sufficient draft? Reference
would be appreciated.
2. if flue gas is cooled too much and condensation occurs within the
liner, is it such a big deal? It would just drip down, through the
bottom tee, and into the cleanout chamber. In other words, the system
would work as expected, no?

In the meanwhile, any other suggestions or experience is appreciated.

  #10   Report Post  
Posted to alt.home.repair,alt.hvac
Zyp Zyp is offline
external usenet poster
 
Posts: 140
Default Chimney liner for oil fired boiler

wrote:
Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there
familiar with or observe a similar stainless chimney liner
installation??


What does the installation manual say about it??
What do your local codes require??
What did the local building inspector say about it??
What did your insurance company say about it??

We are not here to do your homework for you.- Hide quoted text -

- Show quoted text -


Thanks for the suggestions.
1. Installation manual says use a liner "if condensation is
observed." Per my earlier post, I called the manufacturer and didn't
get too much advice on what type as it's not their product.
2. I didn't think to check the code! Chapt 8 of Mechanical Code of NY
says to use liner that will resist condensate, and is in accordance
with NFPA31. I'll find NFPA31 and see what it says. Hopefully will
provide guidance on insulated vs. non-insulated.
3. Local building inspector cannot (legally) suggest anything beyond
the building code, so I'll need that NFPA31.
4. I didn't check insurance company. Not sure if they'll even
understand what I'm saying. I'll try.

I have two additional thoughts:
1. if flue gas is cooled too much within liner inside chimney, it may
not create sufficient draft up the 25ft tall, exterior wall chimney.
Is there a way I can estimate if I'll have sufficient draft? Reference
would be appreciated.
2. if flue gas is cooled too much and condensation occurs within the
liner, is it such a big deal? It would just drip down, through the
bottom tee, and into the cleanout chamber. In other words, the system
would work as expected, no?

In the meanwhile, any other suggestions or experience is appreciated.


So it doesn't say in the maual to use a flu chimney Type B vent? It doesn't
give you a GAMA guide? Interesting.

--
Zyp




  #11   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 190
Default Chimney liner for oil fired boiler


"Zyp" wrote in message
news
wrote:
Any 3-pass boiler (Buderus, Burnham MPO, etc) experts out there
familiar with or observe a similar stainless chimney liner
installation??

What does the installation manual say about it??
What do your local codes require??
What did the local building inspector say about it??
What did your insurance company say about it??

We are not here to do your homework for you.- Hide quoted text -

- Show quoted text -


Thanks for the suggestions.
1. Installation manual says use a liner "if condensation is
observed." Per my earlier post, I called the manufacturer and didn't
get too much advice on what type as it's not their product.
2. I didn't think to check the code! Chapt 8 of Mechanical Code of NY
says to use liner that will resist condensate, and is in accordance
with NFPA31. I'll find NFPA31 and see what it says. Hopefully will
provide guidance on insulated vs. non-insulated.
3. Local building inspector cannot (legally) suggest anything beyond
the building code, so I'll need that NFPA31.
4. I didn't check insurance company. Not sure if they'll even
understand what I'm saying. I'll try.

I have two additional thoughts:
1. if flue gas is cooled too much within liner inside chimney, it may
not create sufficient draft up the 25ft tall, exterior wall chimney.
Is there a way I can estimate if I'll have sufficient draft? Reference
would be appreciated.
2. if flue gas is cooled too much and condensation occurs within the
liner, is it such a big deal? It would just drip down, through the
bottom tee, and into the cleanout chamber. In other words, the system
would work as expected, no?

In the meanwhile, any other suggestions or experience is appreciated.


So it doesn't say in the maual to use a flu chimney Type B vent? It
doesn't give you a GAMA guide? Interesting.


Whadya want from E-Bay??? You expect to ge the install manuals too? sheesh.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's involved with a chimney liner? dean Home Repair 1 September 27th 05 01:34 AM
Chimney Liner DSegal1027 Home Repair 0 January 21st 05 02:39 AM
Chimney Liner DSegal1027 Home Repair 1 January 19th 05 03:26 AM
Cracked Chimney Liner Billy Home Ownership 2 December 12th 04 12:59 AM
New chimney liner nex barry martin Home Repair 1 October 19th 04 05:27 PM