Default Furnace BTU output

I currently have a 20 year old Carrier Gas Forced Air furnace model number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.

  #2   Report Post  
Posted to alt.home.repair,alt.hvac
Joe Joe is offline
external usenet poster
 
Posts: 2,837
Default Furnace BTU output

On Oct 5, 12:26 pm, "
wrote:
I currently have a 20 year old Carrier Gas Forced Air furnace model number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.


Probab;y, yes. Do some math...if your old furnace is 80% effcient the
output is 100,000 BTU. If the replacement is 90% or better you have
99,000+ BTU, close enough for practical purposes. HTH

Joe







  #3   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 21
Default Furnace BTU output

I don't know the efficency of the old unit, and neither does the person I
spoke with at Carrier.
The new unit is 80%.
The old one was made in 1985.

J
"Joe" wrote in message
ups.com...
On Oct 5, 12:26 pm, "
wrote:
I currently have a 20 year old Carrier Gas Forced Air furnace model
number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.


Probab;y, yes. Do some math...if your old furnace is 80% effcient the
output is 100,000 BTU. If the replacement is 90% or better you have
99,000+ BTU, close enough for practical purposes. HTH

Joe








  #4   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 4,926
Default Furnace BTU output

On Oct 5, 3:16 pm, ftwhd wrote:
On Fri, 05 Oct 2007 17:26:04 GMT, "

wrote:
I currently have a 20 year old Carrier Gas Forced Air furnace model number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.


An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?


Thanks,


J.


Same or greater huh. Ask the **** wit if hes ever heard of a manual J
then kick his ass out the door and quit cross posting your homeowner
BS to Alt.hvac.


A larger unit will lead to shorter cycles and maybe uneven heat, I cut
my btu 55% on a new unit and finally the house heats evenly. If your
unit just heats on the coldest days of the year it is probably sized
ok, but oversizing is common, also bigger units cost more, more
profit, get a pro that does a load calculation or dont let him in the
door

  #5   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 6,199
Default Furnace BTU output

given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks




  #6   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 190
Default Furnace BTU output


wrote in message
ups.com...
given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks


Is that your final answer??? or do you maybe think you should find out WHERE
he is located. 90+ is great for places where they have 9 months of winter
sports.....OTOH, down here on the Gulf Coast, you need to think 9 months of
cooling and where can I get a small enough furnace to heat with a big enough
blower drive for the A/C.


  #8   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 6,199
Default Furnace BTU output

On Oct 5, 8:51?pm, "Noon-Air" wrote:
wrote in message

ups.com...

given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.


go 90+ go 90+ its worth the extra bucks


Is that your final answer??? or do you maybe think you should find out WHERE
he is located. 90+ is great for places where they have 9 months of winter
sports.....OTOH, down here on the Gulf Coast, you need to think 9 months of
cooling and where can I get a small enough furnace to heat with a big enough
blower drive for the A/C.


good point? where does the person live?

  #9   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


" wrote in message
news:MsuNi.6$j14.1@trnddc06...
I currently have a 20 year old Carrier Gas Forced Air furnace model number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.



Load Calculation, PERIOD!


  #10   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Bubba" wrote in message
...
On Fri, 05 Oct 2007 17:26:04 GMT, "
wrote:

I currently have a 20 year old Carrier Gas Forced Air furnace model

number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110. He
says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.


Sounds like someone doesnt trust someone?
Maybe if he stuck a feather up your ass you would trust him more?
Bubba


Sounds like someone isn't doing a load calc. :-(




  #12   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"ransley" wrote in message
oups.com...
On Oct 5, 3:16 pm, ftwhd wrote:
On Fri, 05 Oct 2007 17:26:04 GMT, "

wrote:
I currently have a 20 year old Carrier Gas Forced Air furnace model

number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on the
label is blank.


An HVAC company wants to replace this with a Carrier model 58STA110.

He
says this will result in the same or greater output as my unit. Is he
correct?


Thanks,


J.


Same or greater huh. Ask the **** wit if hes ever heard of a manual J
then kick his ass out the door and quit cross posting your homeowner
BS to Alt.hvac.


A larger unit will lead to shorter cycles and maybe uneven heat, I cut
my btu 55% on a new unit and finally the house heats evenly. If your
unit just heats on the coldest days of the year it is probably sized
ok, but oversizing is common, also bigger units cost more, more
profit, get a pro that does a load calculation or dont let him in the
door



Thumbs up!


  #13   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


wrote in message
ups.com...
given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks



Heat Pump, Heat Pump, Heat Pump
Dual Fuel, Dual Fuel, Dual Fuel

Where's the OP located?
What's the cost of utilities in their area?

There's a lot of information to be gathered before one could possibly
recommend which would be cheaper to operate in their area.


  #14   Report Post  
Posted to alt.home.repair,alt.hvac
external usenet poster
 
Posts: 6,586
Default Furnace BTU output

kjpro @ usenet.com wrote:
"Tony Hwang" wrote in message
news:ndCNi.5395$hT1.287@pd7urf2no...

wrote:


I don't know the efficency of the old unit, and neither does the person
I spoke with at Carrier.
The new unit is 80%.
The old one was made in 1985.

J
"Joe" wrote in message
groups.com...


On Oct 5, 12:26 pm, "
wrote:


I currently have a 20 year old Carrier Gas Forced Air furnace model
number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on


the

label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110.


He

says this will result in the same or greater output as my unit. Is he
correct?

Thanks,

J.


Probab;y, yes. Do some math...if your old furnace is 80% effcient the
output is 100,000 BTU. If the replacement is 90% or better you have
99,000+ BTU, close enough for practical purposes. HTH

Joe








Hi,
Where do you live?



Why, you looking for a date?
I hear Stormy's available.


Hmmm,
I did not ask you. Local climate and energy cost are a factor in
selecting things like furnace.
  #15   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Tony Hwang" wrote in message
news:2pDNi.5864$hT1.489@pd7urf2no...
kjpro @ usenet.com wrote:
"Tony Hwang" wrote in message
news:ndCNi.5395$hT1.287@pd7urf2no...

wrote:


I don't know the efficency of the old unit, and neither does the person
I spoke with at Carrier.
The new unit is 80%.
The old one was made in 1985.

J
"Joe" wrote in message
groups.com...


On Oct 5, 12:26 pm, "
wrote:


I currently have a 20 year old Carrier Gas Forced Air furnace model
number
58GP125-3 It says the INPUT is 125,100 BTU but the output field on


the

label is blank.

An HVAC company wants to replace this with a Carrier model 58STA110.


He

says this will result in the same or greater output as my unit. Is

he
correct?

Thanks,

J.


Probab;y, yes. Do some math...if your old furnace is 80% effcient the
output is 100,000 BTU. If the replacement is 90% or better you have
99,000+ BTU, close enough for practical purposes. HTH

Joe








Hi,
Where do you live?



Why, you looking for a date?
I hear Stormy's available.


Hmmm,
I did not ask you. Local climate and energy cost are a factor in
selecting things like furnace.



No ****, but that has nothing to do with the OP's original question.




  #16   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:5d6a1$4706ffec$9440c41e$20232
@STARBAND.NET:


wrote in message
ups.com...
given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks



Heat Pump, Heat Pump, Heat Pump
Dual Fuel, Dual Fuel, Dual Fuel

Drunk again?



I see you're still stupid.
I'll make sure to inform you if there's ever a cure.


  #17   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:c8562$4707106d$9440c41e$5316
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:5d6a1$4706ffec$9440c41e$20232
@STARBAND.NET:


wrote in message
ups.com...
given energy cost I wouldnt buy a 80% furnace today and this furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks


Heat Pump, Heat Pump, Heat Pump
Dual Fuel, Dual Fuel, Dual Fuel

Drunk again?



I see you're still stupid.
I'll make sure to inform you if there's ever a cure.

I post and you dance. It never fails does it, drunken monkey boi?



You really need to get a clue.
For once it would be nice, if you posted a FACT.


  #18   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:6ccb6$47071343$9440c41e$5691
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:c8562$4707106d$9440c41e$5316
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:5d6a1$4706ffec$9440c41e$20232
@STARBAND.NET:


wrote in message
ups.com...
given energy cost I wouldnt buy a 80% furnace today and this

furnace
would be a negative at resale time.

go 90+ go 90+ its worth the extra bucks


Heat Pump, Heat Pump, Heat Pump
Dual Fuel, Dual Fuel, Dual Fuel

Drunk again?


I see you're still stupid.
I'll make sure to inform you if there's ever a cure.

I post and you dance. It never fails does it, drunken monkey boi?



You really need to get a clue.
For once it would be nice, if you posted a FACT.

I post and you dance. That's a fact.

I post and you dance. It never fails does it, drunken monkey boi?



You have your **** backwards...
You're the one dancing, you're just too stupid to realize it.
Want another treat?


  #19   Report Post  
Posted to alt.home.repair,alt.hvac
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...


Need another treat?


  #20   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in

:


"Clark" wrote in message
...


Need another treat?

You're the one who needs help son.



Get a clue, you're not very bright.




  #21   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:6fdf9$470ceadf$9440c41e$24684
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in

:


"Clark" wrote in message
...


Need another treat?

You're the one who needs help son.



Get a clue, you're not very bright.

Dance boi, dance. I post, you dance. *It never fails*



Copy and Paste
What a Waste
Of this Internet
They call Space

One day maybe
You'll get a Clue
As one things for sure
I'll always out do You

You're such a twit
Without any Wit
Unlike myself
I know my ****

Please get a life
Before you Die
As your bull****s
Nothing more than a Lie



  #22   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ac004$470ef1bd$9440c41e$1543
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:6fdf9$470ceadf$9440c41e$24684
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in
:


"Clark" wrote in message
...


Need another treat?

You're the one who needs help son.


Get a clue, you're not very bright.

Dance boi, dance. I post, you dance. *It never fails*



Dance boi, dance. I post, you dance. *It never fails*



You're still a Putz.
Looking for another treat?


  #23   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ab2aa$4710fbb9$9440c41e$2736
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ac004$470ef1bd$9440c41e$1543
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:6fdf9$470ceadf$9440c41e$24684
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in
:


"Clark" wrote in message
...


Need another treat?

You're the one who needs help son.


Get a clue, you're not very bright.

Dance boi, dance. I post, you dance. *It never fails*


Dance boi, dance. I post, you dance. *It never fails*



You're still a Putz.
Looking for another treat?

Dance boi, dance. I post, you dance. *It never fails*



What a Putz.
It must suck to be stupid.


  #24   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Furnace BTU output


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ca461$47122bcb$9440c41e$31201
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ab2aa$4710fbb9$9440c41e$2736
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:ac004$470ef1bd$9440c41e$1543
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:6fdf9$470ceadf$9440c41e$24684
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in
:


"Clark" wrote in message
...


Need another treat?

You're the one who needs help son.


Get a clue, you're not very bright.

Dance boi, dance. I post, you dance. *It never fails*


Dance boi, dance. I post, you dance. *It never fails*


You're still a Putz.
Looking for another treat?

Dance boi, dance. I post, you dance. *It never fails*



What a Putz.
It must suck to be stupid.

I know you are correct, I just can't admit it.



You're finally right.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Old Lennox Furnace - Model GH6 100T (maybe thermostat maybe furnace problem) jack Home Repair 5 November 9th 08 02:22 PM
lowering output of furnace? peter Home Repair 9 December 5th 06 05:02 PM
run my oil forced air furnace once a month in the summer to keep the furnace from rusting clickclack Home Repair 7 July 7th 06 10:55 PM
Thick accordion-type furnace filters - can I retrofit furnace for standard? bryanska Home Ownership 1 August 9th 05 09:24 PM
Replacing gas furnace (was New Gas Furnace Time) [email protected] Home Repair 0 February 18th 05 09:31 PM


All times are GMT +1. The time now is 12:29 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"