Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing

Many local HVAC companies just guess the size of the AC unit and therefore I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.



  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 106
Default AC sizing

Martino wrote:

Many local HVAC companies just guess the size of the AC unit and therefore I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.


First off, you have to use the summer design conditions for your area!
Washington, Seattle-Tacoma airport, Official listed Summer Design is 80
dry bulb & 64 wet bulb, or around a low 41% relative humidity.

Therefore, you are using Summer Design temperatures that are way too high!
Run the above 80-F dry bulb & 64-F wet bulb temps through your manual J
software, then tell us what you get.
How many square footage is your home? Did you figure the heat-gain
correctly?
The ductwork & airflow is critical to efficient operation!
http://www.udarrell.com/proper_cfm_b...syste ms.html

- udarrell

--
WISDOM PRINCIPLED EMPOWERMENT COMMUNICATIONS -
THE REAL POLITICAL ISSUES and PEOPLE EMPOWERMENT
http://www.udarrell.com/
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default AC sizing

On Thu, 8 Feb 2007 07:38:47 -0800, "Martino"
wrote:

Many local HVAC companies just guess the size of the AC unit and therefore I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.




If it's 105 degrees outside, do you really need it to
be 72 inside, or will 82 be good enough?

  #4   Report Post  
Posted to alt.home.repair
DK DK is offline
external usenet poster
 
Posts: 257
Default AC sizing

On Thu, 8 Feb 2007 07:38:47 -0800, "Martino"
wrote:

Many local HVAC companies just guess the size of the AC unit and therefore I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.


Since the standard size residential unit has a max of 5 tons, your
solution is simple. You need two units, a 5 ton and and 2 1/2 ton
unit.

You will find it most economical if you run the highest SEER unit 95
percent of the time and only kick in the other unit when it is
extremely hot and the single unit can't keep up. And you do that by
setting your thermostats appropriately.







  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,392
Default AC sizing

Martino writes:

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think?


It's like politics and elections. The issues are complicated, but all that
complexity reduces to 2 or 3 choices. (Although unlike politicians, one is
usually happy with a choice of air conditioning system.) If your hunch
between one or the other choice is usually right, then it may not be worth
performing a costly analysis. And as your calculations show, the results
depend on some noisy assumptions, so your results are no less noisy than
that, and your hunch may be just as well grounded, especially if you do a
lot of installations, and extra especially if you're replacing an existing
system of known capacity and knew how that performed.

While the Manual J process is sound in physical principles, it also serves
a marketing role. A clever salesman can manipulate assumptions and other
inputs to yield the result he prefers.

Another marketing role was that only "experts" could do it, and any other
competitor was therefore a "hack", but that is becoming less of a working
distinction as the software and publications become available freely on the
Internet, as they should be.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing

This is where my knowledge was (way) off, I guess. The software's Seattle
default summer dry and web b. values were 82 and 66 respectively and I
overwrote the higher one. With 80 and 64 (per your comments) the output is
as follows:

4.14 tons (based on latent + sensible)
5.15 tons (based on 75% sensible capacity)

My house is fairly large (5,700 sq. ft) and has large window areas and a
number of cathedral ceilings. Knowing that many units are 5 tons max (as
one of you also mentioned) I wonder if a 5 tone unit will be adequate.

Thanks for pointing the error

"udarrell" wrote in message
...
Martino wrote:

Many local HVAC companies just guess the size of the AC unit and therefore
I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can
stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.

First off, you have to use the summer design conditions for your area!
Washington, Seattle-Tacoma airport, Official listed Summer Design is 80
dry bulb & 64 wet bulb, or around a low 41% relative humidity.

Therefore, you are using Summer Design temperatures that are way too high!
Run the above 80-F dry bulb & 64-F wet bulb temps through your manual J
software, then tell us what you get.
How many square footage is your home? Did you figure the heat-gain
correctly?
The ductwork & airflow is critical to efficient operation!
http://www.udarrell.com/proper_cfm_b...syste ms.html
- udarrell

--
WISDOM PRINCIPLED EMPOWERMENT COMMUNICATIONS - THE REAL POLITICAL ISSUES
and PEOPLE EMPOWERMENT http://www.udarrell.com/



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing

Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.
Thx

"Goedjn" wrote in message
...
On Thu, 8 Feb 2007 07:38:47 -0800, "Martino"
wrote:

Many local HVAC companies just guess the size of the AC unit and therefore
I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can
stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.




If it's 105 degrees outside, do you really need it to
be 72 inside, or will 82 be good enough?



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default AC sizing


"Martino" wrote in message
...
Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.
Thx


The why not is comfort. To get that much cooling for a week a year, you may
be oversized the rest of the year. Not to mention that operating costs go
up rapidly the greater the differential you are trying to achieve. If you
are in and out frequently, you may also find the differential to be too much
of a change adding to overall discomfort.


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 34
Default AC sizing

I have never lived in a house with an AC that was "too big" but have
been in many with an AC that was too small. Some of them have to run
nearly continuously to struggle to maintain a decent temp. Whatever a
sensible design program comes up with I would round up another half
ton unless I was really really sure it's answer was good enough.

On Thu, 8 Feb 2007 19:21:30 -0800, "Martino"
wrote:

This is where my knowledge was (way) off, I guess. The software's Seattle
default summer dry and web b. values were 82 and 66 respectively and I
overwrote the higher one. With 80 and 64 (per your comments) the output is
as follows:

4.14 tons (based on latent + sensible)
5.15 tons (based on 75% sensible capacity)

My house is fairly large (5,700 sq. ft) and has large window areas and a
number of cathedral ceilings. Knowing that many units are 5 tons max (as
one of you also mentioned) I wonder if a 5 tone unit will be adequate.

Thanks for pointing the error

"udarrell" wrote in message
t...
Martino wrote:

Many local HVAC companies just guess the size of the AC unit and therefore
I
decided to run my new house data through a Manual J compliant software.
Depending on design summer temperature I obtain the following AC size (in
tons) recommendations

Summer Temp Size 1 Size 2
90F 4.76 6.02
95F 5.04 6.46
100F 5.32 6.89
105F 5.61 7.33

The house is being build near Seattle where the max summer temp rarely
exceeds 105F but gets to 100F for a week or so during summer. 90F can
stay
with us for few weeks per summer.

I am a bit confused about two sizing recommendations:

Size 1 is based on sensible and latent heat gain
Size 2 is based on 75% Sensible Capacity

I do not want to oversize my A/C unit but I do not want to significantly
undersize it either. What do you think? Thanks.

First off, you have to use the summer design conditions for your area!
Washington, Seattle-Tacoma airport, Official listed Summer Design is 80
dry bulb & 64 wet bulb, or around a low 41% relative humidity.

Therefore, you are using Summer Design temperatures that are way too high!
Run the above 80-F dry bulb & 64-F wet bulb temps through your manual J
software, then tell us what you get.
How many square footage is your home? Did you figure the heat-gain
correctly?
The ductwork & airflow is critical to efficient operation!
http://www.udarrell.com/proper_cfm_b...syste ms.html
- udarrell

--
WISDOM PRINCIPLED EMPOWERMENT COMMUNICATIONS - THE REAL POLITICAL ISSUES
and PEOPLE EMPOWERMENT http://www.udarrell.com/


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing


"Edwin Pawlowski" wrote in message
...

"Martino" wrote in message
...
Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.
Thx


........... To get that much cooling for a week a year, you may be
oversized the rest of the year. ...............


Seems like a 2-stage unit would take of this situation. Operating at a
low-speed during lower temp periods and kicking into high speed when temp
approaches the max design one.




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default AC sizing


I have never lived in a house with an AC that was "too big" but have
been in many with an AC that was too small. Some of them have to run
nearly continuously to struggle to maintain a decent temp. Whatever a
sensible design program comes up with I would round up another half
ton unless I was really really sure it's answer was good enough.


I thought conventional wisdom was that, if it's running "nearly
continuously", and not "continuously", it's big enough.
The only time an AC unit or heater is too small is if it's
running constantly, and STILL can't keep up, or if you're
after a faster recovery time from setbacks.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default AC sizing

On Thu, 8 Feb 2007 19:24:50 -0800, "Martino"
wrote:
If it's 105 degrees outside, do you really need it to
be 72 inside, or will 82 be good enough?


Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.


Let me rephrase: How much are you willing to pay for the
difference between 72 degrees and 82 degrees, on the
three to six 105 degree days you might encounter per year?

Is that more or less than the price difference for the
next smaller AC unit?
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default AC sizing

If your neighbors have similiar design size homes why not ask ?? Make
friends and learn from their mistakes


  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing

OK. I get the point it's certainly worth considering. Hard to assign the $
value to the comfort but easier to assess if extra $xxx is worth being
comfortable during these few days. In reality over a longer period of time
(even only 10 years) the per very hot day cost might be not that high and
therefore the return on investment might be there. I need to see what the
price diff is between the units and associated costs.
Thx
"Goedjn" wrote in message
...
On Thu, 8 Feb 2007 19:24:50 -0800, "Martino"
wrote:
If it's 105 degrees outside, do you really need it to
be 72 inside, or will 82 be good enough?


Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.


Let me rephrase: How much are you willing to pay for the
difference between 72 degrees and 82 degrees, on the
three to six 105 degree days you might encounter per year?

Is that more or less than the price difference for the
next smaller AC unit?



  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 13
Default AC sizing

The reason I run the analysis is to avoid such a comparison. Different room
arrangements, different insulation, different windows, different equipment
at home, different number of people inside, different ceilings arrangements,
...... - different AC need
wrote in message
oups.com...
If your neighbors have similiar design size homes why not ask ?? Make
friends and learn from their mistakes






  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 106
Default AC sizing

Martino wrote:

The reason I run the analysis is to avoid such a comparison. Different room
arrangements, different insulation, different windows, different equipment
at home, different number of people inside, different ceilings arrangements,
..... - different AC need
wrote in message
roups.com...


If your neighbors have similiar design size homes why not ask ?? Make
friends and learn from their mistakes:

I cool over 900 sq ft in an older home down to 76-F, 50% Relative
Humidity or less, with a Half-Ton or 6,000-BTUH window unit, even at
104-F heat index!
Read how I do it:
http://www.udarrell.com/aircondition...harting.h tml

Do NOT oversize the system! - udarrell

--
WISDOM PRINCIPLED EMPOWERMENT COMMUNICATIONS -
THE REAL POLITICAL ISSUES and PEOPLE EMPOWERMENT
http://www.udarrell.com/
  #17   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default AC sizing

Martino wrote:
OK. I get the point it's certainly worth considering. Hard to assign the $
value to the comfort but easier to assess if extra $xxx is worth being
comfortable during these few days. In reality over a longer period of time
(even only 10 years) the per very hot day cost might be not that high and
therefore the return on investment might be there. I need to see what the
price diff is between the units and associated costs.
Thx


It might even make sense to factor in global warming. Extreme
temperatures will be more common as the planet suffers the impact
of all those SUVs and the destruction of the rain forest.

"Goedjn" wrote in message
...

On Thu, 8 Feb 2007 19:24:50 -0800, "Martino"
wrote:

If it's 105 degrees outside, do you really need it to
be 72 inside, or will 82 be good enough?


Good point but if it is possible to get down to a more comfortable 75F
(which I used for the design param) then why not. Looks that with the
adjusted dry/wet bulb values I will be able to achieve it with a 5 tons
unit.


Let me rephrase: How much are you willing to pay for the
difference between 72 degrees and 82 degrees, on the
three to six 105 degree days you might encounter per year?

Is that more or less than the price difference for the
next smaller AC unit?






--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Duct Sizing Steve Groulx Home Repair 11 October 12th 05 11:11 PM
Duct Sizing [email protected] Home Repair 3 October 12th 05 10:15 PM
Duct Sizing BN Home Repair 2 October 10th 05 12:28 PM
Sizing A/C and Furnace Walter R. Home Repair 7 July 25th 05 02:24 PM
CH Boiler Sizing PoP UK diy 14 November 5th 03 10:40 PM


All times are GMT +1. The time now is 11:34 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"