Can anyone point me towards an Internet resource which gives
information about boiler size to square footage of property for a
domestic CH system? Or alternatively comment on the following?

I visited a property today to investigate the CH system not giving out
enough heat when it gets really cold. One of the things I found
immediately was that the radiators weren't balanced properly (the
return valves were full open on all that I checked), so that's one job
I've got to do.

However, the CH boiler looks like it's well underspecced for the size
of property. It's a Potterton Profile - I didn't think to get the
model number but it just looked too puny to deliver the heat required
for what is a large property - the property has been extended with an
extra floor. Physically it looked like it was the Potterton Profile
40L jobbie:

http://inspiredheating.co.uk/acatalo...FAN_FLUE_.html

If so then it's a 40,000 BTU unit.

What I'd really like to get information on is what size boiler needs
to be installed for a given square footage, if such info is available
anywhere.

Clues anyone?

PoP

  #2   Report Post  
Roger Mills
 
Posts: n/a
Default CH Boiler Sizing


"PoP" wrote in message
...
Can anyone point me towards an Internet resource which gives
information about boiler size to square footage of property for a
domestic CH system? Or alternatively comment on the following?


In order to do a proper job, you need to take account of far more factors
than just the floor area. The wall and roof construction/insulation and the
amount and type of glazing all have a profound effect on the heat losses.

There are various bits of software (such as
http://www.barlo.co.uk/pages/download.cfm) which you can download, which
will do the calcs for you - but they do require some reasonable input data.
Otherwise, its garbage in, garbarge out!

HTH,
Roger



  #3   Report Post  
Andy Hall
 
Posts: n/a
Default CH Boiler Sizing

On Wed, 05 Nov 2003 15:46:16 +0000, PoP
wrote:

Can anyone point me towards an Internet resource which gives
information about boiler size to square footage of property for a
domestic CH system? Or alternatively comment on the following?

I visited a property today to investigate the CH system not giving out
enough heat when it gets really cold. One of the things I found
immediately was that the radiators weren't balanced properly (the
return valves were full open on all that I checked), so that's one job
I've got to do.

However, the CH boiler looks like it's well underspecced for the size
of property. It's a Potterton Profile - I didn't think to get the
model number but it just looked too puny to deliver the heat required
for what is a large property - the property has been extended with an
extra floor. Physically it looked like it was the Potterton Profile
40L jobbie:

http://inspiredheating.co.uk/acatalo...FAN_FLUE_.html

If so then it's a 40,000 BTU unit.

What I'd really like to get information on is what size boiler needs
to be installed for a given square footage, if such info is available
anywhere.

Clues anyone?

PoP


As a quick solution, download one of the heating calculators like the
Myson one. Treat the entire house as one enormous room - i.e. all
room temperatures the same at 21 degrees and use the exterior
dimensions of the house.

You do need to take into account the materials used for walls and
windows (use the areas of those or estimate). There is anything up
to a 5:1 difference in heat loss through walls depending on the
material used, so a guess based on area is going to be wildly
inaccurate. Generally the walls represent the largest heat loss.


Maybe you could do a proper measurement when you balance the
radiators, but a 12kW boiler is likely to be too small for a house of
any size.

In that case a new or an additional one is needed and that renders the
balancing exercise pointless until it's fixed.

..andy

To email, substitute .nospam with .gl
  #4   Report Post  
PoP
 
Posts: n/a
Default CH Boiler Sizing

On Wed, 05 Nov 2003 17:34:40 +0000, Andy Hall
wrote:

In that case a new or an additional one is needed and that renders the
balancing exercise pointless until it's fixed.


Exactly what I told the guy.

Thanks for the additional comments BTW. I think I was just looking for
an answer to "is 40000 BTU too small for a large 4 bed house". It
might have been a better question anyway

Too little beer last night I fear.....

Talking of which, when shall we arrange our next Screwfix sponsored
event?

PoP

  #5   Report Post  
John Stumbles
 
Posts: n/a
Default CH Boiler Sizing

"PoP" wrote in message
...
On Wed, 05 Nov 2003 17:34:40 +0000, Andy Hall
wrote:

In that case a new or an additional one is needed and that renders the
balancing exercise pointless until it's fixed.


Exactly what I told the guy.


Boiler No 6 (or is it 7, I'm losing count :-) coming up? ;-)

Too little beer last night I fear.....

Talking of which, when shall we arrange our next Screwfix sponsored
event?


Heh heh!

--
John Stumbles
-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+-+
-+
Bob the builder / it'll cost yer
Bob the builder / loadsa dosh





  #6   Report Post  
BillR
 
Posts: n/a
Default CH Boiler Sizing

PoP wrote:
On Wed, 05 Nov 2003 17:34:40 +0000, Andy Hall
wrote:

In that case a new or an additional one is needed and that renders
the balancing exercise pointless until it's fixed.


Exactly what I told the guy.

Thanks for the additional comments BTW. I think I was just looking for
an answer to "is 40000 BTU too small for a large 4 bed house". It
might have been a better question anyway

It definitely is too small maybe by a up to a factor of 2.
Could we stick to kW by the way? Its easier to visualise.
e.g. say you have 24kW boiler and 10 rooms thats average 2.4kW /room which
sounds enough in a very crude sense.
12kW just doesn't sound enough does it when looked at this way?


  #7   Report Post  
PoP
 
Posts: n/a
Default CH Boiler Sizing

On Wed, 5 Nov 2003 21:08:19 -0000, "John Stumbles"
] wrote:

Boiler No 6 (or is it 7, I'm losing count :-) coming up? ;-)


I can offer your name if you want. Changing the boiler is not
something I'm going to take on, but flushing the system and refilling
is no problem.

PoP

  #8   Report Post  
PoP
 
Posts: n/a
Default CH Boiler Sizing

On Wed, 5 Nov 2003 21:23:20 -0000, "BillR"
wrote:

Could we stick to kW by the way? Its easier to visualise.


Perhaps someone could kindly advise how to convert BTU to kW?

PoP

  #9   Report Post  
The Natural Philosopher
 
Posts: n/a
Default CH Boiler Sizing

PoP wrote:

Can anyone point me towards an Internet resource which gives
information about boiler size to square footage of property for a
domestic CH system? Or alternatively comment on the following?

I visited a property today to investigate the CH system not giving out
enough heat when it gets really cold. One of the things I found
immediately was that the radiators weren't balanced properly (the
return valves were full open on all that I checked), so that's one job
I've got to do.

However, the CH boiler looks like it's well underspecced for the size
of property. It's a Potterton Profile - I didn't think to get the
model number but it just looked too puny to deliver the heat required
for what is a large property - the property has been extended with an
extra floor. Physically it looked like it was the Potterton Profile
40L jobbie:

http://inspiredheating.co.uk/acatalo...FAN_FLUE_.html

If so then it's a 40,000 BTU unit.

What I'd really like to get information on is what size boiler needs
to be installed for a given square footage, if such info is available
anywhere.

Clues anyone?



It depends ENTIRELY on the standard of insulation.
My plumber (the one who thought pressure came not from teh header tank,
but teh hot water tank) almost refused to install my boiler as he
considered it only big enougjh for a three bed semi. I have (estate
agent spik) a 6 bed cottage.

Its been fine. The house is built to current regs insulation wise.

The actual calcs to size a boiler consist in doing an elemenatl loss
calculation of teh whoole outside of the house, adding in ventilation
losses, gains from south facing windows and walls, working out the heat
you want it and the worst temp the outdie will get to, and coming up
with the number of kilowatts (or BTU/H) needed to heat it.

If its any help, fully insulated house, about 400 sq meter total floor
area, and I am using a 65kBTU/H boiler.

Poorly insulated house - treble that at least.



PoP




  #10   Report Post  
The Natural Philosopher
 
Posts: n/a
Default CH Boiler Sizing

Andy Hall wrote:

On Wed, 05 Nov 2003 15:46:16 +0000, PoP
wrote:


Can anyone point me towards an Internet resource which gives
information about boiler size to square footage of property for a
domestic CH system? Or alternatively comment on the following?

I visited a property today to investigate the CH system not giving out
enough heat when it gets really cold. One of the things I found
immediately was that the radiators weren't balanced properly (the
return valves were full open on all that I checked), so that's one job
I've got to do.

However, the CH boiler looks like it's well underspecced for the size
of property. It's a Potterton Profile - I didn't think to get the
model number but it just looked too puny to deliver the heat required
for what is a large property - the property has been extended with an
extra floor. Physically it looked like it was the Potterton Profile
40L jobbie:

http://inspiredheating.co.uk/acatalo...FAN_FLUE_.html

If so then it's a 40,000 BTU unit.

What I'd really like to get information on is what size boiler needs
to be installed for a given square footage, if such info is available
anywhere.

Clues anyone?

PoP


As a quick solution, download one of the heating calculators like the
Myson one. Treat the entire house as one enormous room - i.e. all
room temperatures the same at 21 degrees and use the exterior
dimensions of the house.

You do need to take into account the materials used for walls and
windows (use the areas of those or estimate). There is anything up
to a 5:1 difference in heat loss through walls depending on the
material used, so a guess based on area is going to be wildly
inaccurate. Generally the walls represent the largest heat loss.


Maybe you could do a proper measurement when you balance the
radiators, but a 12kW boiler is likely to be too small for a house of
any size.



My expenively subcontracted heatloss calculations came up with 10Kw as
peak demand. On a very big house.

I stuck in a bigger boiler than that tho - but its not HUGE. Even at
oeak cold it doesn't run flat out - maybe 50% duty cycle at the worst.


In that case a new or an additional one is needed and that renders the
balancing exercise pointless until it's fixed.



Thats a clue to an emirical way to find out what you need.

Balance the system, and short out the thermostat, and leave the system
running flat out for a few hours. Measure the internal and external
temperature and if the difference is less than 30 degrees celsius, you
need more insulation or a bigger boiler :-)


.andy

To email, substitute .nospam with .gl





  #11   Report Post  
The Natural Philosopher
 
Posts: n/a
Default CH Boiler Sizing

PoP wrote:

On Wed, 05 Nov 2003 17:34:40 +0000, Andy Hall
wrote:


In that case a new or an additional one is needed and that renders the
balancing exercise pointless until it's fixed.


Exactly what I told the guy.

Thanks for the additional comments BTW. I think I was just looking for
an answer to "is 40000 BTU too small for a large 4 bed house". It
might have been a better question anyway



The answer is emphatically NO, its NOT, if its well insulated, and
assuming its not a combi and has to heat three independent showers and a
bath simultaneously.



Too little beer last night I fear.....

Talking of which, when shall we arrange our next Screwfix sponsored
event?

PoP




  #12   Report Post  
The Natural Philosopher
 
Posts: n/a
Default CH Boiler Sizing

BillR wrote:

PoP wrote:

On Wed, 05 Nov 2003 17:34:40 +0000, Andy Hall
wrote:


In that case a new or an additional one is needed and that renders
the balancing exercise pointless until it's fixed.

Exactly what I told the guy.

Thanks for the additional comments BTW. I think I was just looking for
an answer to "is 40000 BTU too small for a large 4 bed house". It
might have been a better question anyway

It definitely is too small maybe by a up to a factor of 2.
Could we stick to kW by the way? Its easier to visualise.
e.g. say you have 24kW boiler and 10 rooms thats average 2.4kW /room which
sounds enough in a very crude sense.
12kW just doesn't sound enough does it when looked at this way?




My kitchen has an aga in it that runs day and night at about 600W. In
winter it has probably 12x50W lights in it burning most of teh time. It
also has U/F heating but I have that bit balanced down to bugger all.
Its 30 square meters of room. Thats 1.2Kw over 30 sq m, or about 40W per
square. The whole house of about 200sq meter was calculated by experts
to need just 10Kw, which is 50W.sq meter.

My U/F heating guide reckoned that a well insulated house needed peak
demands of 50W/sq meter, and a poorly insulated one maybe up to 200W/sq
meter, with 125W/sq meter being a good working average.

Apart from the living rooms, which usually get an open fire in winter,
that level (50w/sq meter) of heating works. Its higher in the bathrooms.
Of course there is a lot of heat from lighting in the winter - probabaly
after dark each room is kicking in another 400W per 30 sq meter room -
so maybe I have up to 65W/sq meter.

Contrast with my old single brick cottage, which used to burn exactly
the same amount of oil as I do now, to heat (badly) four rooms and a porch.

And where a 3Kw fan heater was not adequate to heat a single room.





  #13   Report Post  
BigWallop
 
Posts: n/a
Default CH Boiler Sizing


"PoP" wrote in message
...
On Wed, 5 Nov 2003 21:23:20 -0000, "BillR"
wrote:

Could we stick to kW by the way? Its easier to visualise.


Perhaps someone could kindly advise how to convert BTU to kW?

PoP


http://www.simetric.co.uk/sibtu.htm


  #14   Report Post  
Roger Mills
 
Posts: n/a
Default CH Boiler Sizing


"PoP" wrote in message
...
On Wed, 5 Nov 2003 21:23:20 -0000, "BillR"
wrote:

Could we stick to kW by the way? Its easier to visualise.


Perhaps someone could kindly advise how to convert BTU to kW?

PoP


From memory, 1Kw = approx 3,500 BThU/Hr (but doubtless someone will supply
the exact figure)

Roger


  #15   Report Post  
BigWallop
 
Posts: n/a
Default CH Boiler Sizing


"BigWallop" wrote in message
news

"PoP" wrote in message
...
On Wed, 5 Nov 2003 21:23:20 -0000, "BillR"
wrote:

Could we stick to kW by the way? Its easier to visualise.


Perhaps someone could kindly advise how to convert BTU to kW?

PoP


http://www.simetric.co.uk/sibtu.htm



http://www.ex.ac.uk/cimt/dictunit/ccthcony.htm


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing a boiler David Hearn UK diy 38 November 12th 03 11:10 PM
Boiling boiler Lazy Beetle UK diy 2 October 28th 03 11:30 AM
New boiler operation/settings John UK diy 3 October 27th 03 10:57 PM
Boiler Programmable Thermostat Trips RCD? Rich UK diy 1 September 16th 03 04:23 PM
New Combi boiler GB UK diy 7 September 7th 03 11:34 PM


All times are GMT +1. The time now is 05:12 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"