  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 52
Default Furnace safety switch question

I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.
  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Furnace safety switch question

You do want an emergency switch for the furnace. It may be possible that
another switch was installed at a different location? There should be one on
or at the furnace and another outside of a room that the furnace is enclosed
in or if it's in an open basement, you may find one at an entrance to the
basement. If it needs to be connected , you can break into the circuit at
the disconnect that's near the furnace. It should be connected in series
with the other switch, so both must be on to power the furnace


"46erjoe" wrote in message
...
I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 52
Default Furnace safety switch question

On Sun, 3 Dec 2006 19:08:15 -0500, "RBM" rbm2(remove
wrotF:

You do want an emergency switch for the furnace. It may be possible that
another switch was installed at a different location? There should be one on
or at the furnace and another outside of a room that the furnace is enclosed
in or if it's in an open basement, you may find one at an entrance to the
basement. If it needs to be connected , you can break into the circuit at
the disconnect that's near the furnace. It should be connected in series
with the other switch, so both must be on to power the furnace


There is a switch a few feet from the furnace, right at the power
entry point. Aside from that, there is no other switch.

Again, I find it hard that this would be overlooked, especially if
somebody took the time to write on the wire what it was for.

Hmmmm




"46erjoe" wrote in message
.. .
I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.



  #4   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Furnace safety switch question

Kinda makes you wonder what else you should be looking at



"46erjoe" wrote in message
news
On Sun, 3 Dec 2006 19:08:15 -0500, "RBM" rbm2(remove
wrotF:

You do want an emergency switch for the furnace. It may be possible that
another switch was installed at a different location? There should be one
on
or at the furnace and another outside of a room that the furnace is
enclosed
in or if it's in an open basement, you may find one at an entrance to the
basement. If it needs to be connected , you can break into the circuit at
the disconnect that's near the furnace. It should be connected in series
with the other switch, so both must be on to power the furnace


There is a switch a few feet from the furnace, right at the power
entry point. Aside from that, there is no other switch.

Again, I find it hard that this would be overlooked, especially if
somebody took the time to write on the wire what it was for.

Hmmmm




"46erjoe" wrote in message
. ..
I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.





  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 233
Default Furnace safety switch question

On Mon, 04 Dec 2006 00:00:00 GMT, 46erjoe
wrote:

I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.

Can't you get hold of the seller? If no longer local, get the real
estate agent stirred up about a possible safety element.

Worst come to worst, is there some kind of municipal oversight
that can help you answer the q?




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,469
Default Furnace safety switch question

aspasia spake thus:

On Mon, 04 Dec 2006 00:00:00 GMT, 46erjoe
wrote:

I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?


Can't you get hold of the seller? If no longer local, get the real
estate agent stirred up about a possible safety element.

Worst come to worst, is there some kind of municipal oversight
that can help you answer the q?


Wrong approach, I'd say: at this stage of the game, I don't think
stirring up the local authorities and bringing an adverse inspection
situation down on their head is what the O.P. wants or needs.

If anything, the services of an electrician would be helpful. They might
not charge much (or anything) to come out and look at your setup and
tell you what's what. As someone else here says, it's not rocket
surgery. And not likely the house is going to burn down in the meantime.


--
Just as McDonald's is where you go when you're hungry but don't really
care about the quality of your food, Wikipedia is where you go when
you're curious but don't really care about the quality of your knowledge.

- Matthew White's WikiWatch (http://users.erols.com/mwhite28/wikiwoo.htm)
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,079
Default Furnace safety switch question


"46erjoe" wrote in message
...
I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.


You said 4 years old, so I presume there was a previous owner.

I find it hard to believe the previous owner would have missed that.
Assuming that is what the switch is for, there's no way of knowing that by
the way, unless you could get the previous owner to confirm that.

If it were my furnace, I'd have it inspected thoroughly and ask about the
cost to have the switch installed assuming there isn't another one already
hooked up elsewhere. 14/2 is pretty thin gauge wire, so it sounds right for
a shutoff switch. The builder may have just changed his/her/it mind while
locating the switch and put the functioning one elsewhere.

Mine's right next to the furnace, probably not the best place for it if
there was an emergency.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 557
Default Furnace safety switch question

On Mon, 04 Dec 2006 00:00:00 GMT, 46erjoe
wrote:

I just bought a new home in NE Pa. It's about 4 years old. Just inside
the kitchen coming in from the door of the attached garage is an
on/off switch with a bright red cover plate. I'm assuming it's the
safety switch for the furnace to turn it off in an emergency. The
furnace is gas/ho****er.

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.

Was this an oversight on the part of the builder/electrician? Or did
it suddenly become a non-code item? I find it hard to believe than an
inspector would miss it.

If this must be hooked up, how do I go about doing it? Just finish the
run to the power near the furnace and splice it in so that power runs
to the furnace only when the switch is turned on and the circuit is
complete?

Or just forget the whole thing?

Thanks.



I too live in Pa, ABE area. I was told that some local communities
want 'emergency' 'service' switches relocated to right next to the
furnaces. One, the NEC requires a in-sight switch, and two, home
owners have blown up their homes flipping the switch. They smell gas,
and rather than leave and call the fire dept, they hit the switch, and
boom.

Just saying what I've been told.

later,

tom @ www.Consolidated-Loans.info


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,185
Default Furnace safety switch question

46erjoe wrote:

When the furnace is running and I flip the switch, nothing happens.
The furnace keeps running. I checked in the basement and just below
where the switchplate is located, exiting from the corner of the base
stud plate is about 10 feet of coiled 14/2 wire just hanging there. On
it in ink is written "furn safety". But it's not connected to
anything.


Around here the breaker itself can serve as the furnace switch, as long
as it's between the furnace and the exit.

Would that apply to your case?

Chris
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default Furnace safety switch question

On Mon, 04 Dec 2006 00:41:49 GMT, 46erjoe
wrote:

On Sun, 3 Dec 2006 19:08:15 -0500, "RBM" rbm2(remove
wrotF:

You do want an emergency switch for the furnace. It may be possible that
another switch was installed at a different location? There should be one on
or at the furnace and another outside of a room that the furnace is enclosed
in or if it's in an open basement, you may find one at an entrance to the
basement. If it needs to be connected , you can break into the circuit at
the disconnect that's near the furnace. It should be connected in series
with the other switch, so both must be on to power the furnace


There is a switch a few feet from the furnace, right at the power
entry point. Aside from that, there is no other switch.

Again, I find it hard that this would be overlooked, especially if
somebody took the time to write on the wire what it was for.


All it takes is a scheduling conflict, so that the person
who normally does the job sends a lackey instead.




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lennox furnace--is this a safety switch or a circuit breaker? C. Raniac Home Repair 4 February 26th 19 08:14 PM
Trouble with Baso pilot safety switch Henry Home Repair 8 October 7th 06 03:35 AM
Pilot safety switch chronic failure Jim Home Repair 2 March 12th 06 02:09 PM
Furnace Question - master switch vs thermostat joe Home Repair 2 January 23rd 05 04:30 PM
Delta Drill Press Safety Switch firstjois Woodworking 17 September 5th 04 07:20 PM


All times are GMT +1. The time now is 08:27 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"