Hi all,

I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?

Thanks,

-JJ

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 625
Default Arc Fault Breaker Problem

The breaker may think it is seeing an arc and thus tripping to prevent a
fire. An oscilloscope (and not a voltmeter) would allow you to see if this
is true. Alternately, the breaker itself may be bad. You would need to
substitute a known good breaker to see if it also trips, thus confirming the
suspicion that there is indeed a dangerous arc condition.

Smarty
wrote in message
oups.com...
Hi all,

I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?

Thanks,

-JJ



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 590
Default Arc Fault Breaker Problem


wrote in message
oups.com...
Hi all,

I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].


Arc fault circuit interrupters look for the signature of an arcing circuit
.... that basically means that they are looking for the higher frequencies
that are generated by arcing. The earliest radio transmitters used a
spark-gap to generate the high frequencies needed.

Like ground-fault breakers, they are subject to falsing. They are fairly
sophisticated devices and can be fooled by nearby lightning strikes, RF
fields, and so on. And they can just simply fail. Yours might have failed.
Try a new one.







  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 557
Default Arc Fault Breaker Problem

On 5 Nov 2006 12:59:35 -0800, "
wrote:

Hi all,

I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?

Thanks,

-JJ



Best case, the breaker is faulty. Worse case, you have an arc. Both
are better than worst of worst, you have an arc, no breaker trip, than
a fire.

Get yourself an electrician to check out the circuit. There is a
reason why the NEC wants bedrooms first [only required] on afci's,
because they do happen most there.

Good luck, and tell us what happened.

later,

tom @ www.WorkAtHomePlans.com

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 376
Default Arc Fault Breaker Problem

Arc fault breakers are also ground fault breakers. Rarely does a
breaker go bad. Far more common are wiring problems. For example,
with higher humidity, a partially conducting wire could be enough to
trip a breaker. A white wire pressed against a safety ground short can
cause strange failures. Only an arc-fault or GFCI breaker would detect
this miswire. If neutral for an arc-faulted circuit was somehow
connected to neutral wire for another circuit, then larger current draw
on that other circuit could trip the arc-fault breaker.

Generally, such tripping is due to a wiring fault. Some of these
faults can be made obvious by applying a large load to each receptacle
to discover where load causes a breaker trip.

wrote:
...
I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?
...


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Arc Fault Breaker Problem

Hello all,

Thanks for your excellent inputs. I had an electrician visit today,
and [of course] everything worked fine after he arrived. [Kind of like
when you visit the doctor and your symptoms vanish for the duration of
the visit...] He did not have the correct breaker type with him - so
he couldn't replace the breaker. We agreed that if it happens again,
he will replace the breaker.

In the mean-time, I might try that heavy load test. I'll keep you all
posted. Thanks again!

-JJ


w_tom wrote:
Arc fault breakers are also ground fault breakers. Rarely does a
breaker go bad. Far more common are wiring problems. For example,
with higher humidity, a partially conducting wire could be enough to
trip a breaker. A white wire pressed against a safety ground short can
cause strange failures. Only an arc-fault or GFCI breaker would detect
this miswire. If neutral for an arc-faulted circuit was somehow
connected to neutral wire for another circuit, then larger current draw
on that other circuit could trip the arc-fault breaker.

Generally, such tripping is due to a wiring fault. Some of these
faults can be made obvious by applying a large load to each receptacle
to discover where load causes a breaker trip.

wrote:
...
I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?
...


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default Arc Fault Breaker Problem

wrote:
Hi all,

I have a spare bedroom that is serviced throughan arc fault breaker.
Over the past several months, the breaker would [once in a great while]
trip. Nothing was running in the room when the breaker would trip.
Typically, the breaker would allow me to reset it. Recently, the
breaker tripped and will not reset. I used an ohm meter and checked
all connections in the bedroom - 6 outlets, light switch and light -
and all seem fine. I even flicked the light switch "on" and measured
17 Ohms at each outlet, indicated no shorts or opens [the lightbulb was
connected across the circuit]. In addition, I measured the resistance
between each neutral and ground, and the resistance is low [less than 1
ohm].

I am not an electrician and I am at a loss. Is it common to have
problems with the breaker itself or is this more likely something I
missed in the wiring?

Thanks,

-JJ


An Arc Fault Breaker includes a thirty milliamp Ground Fault Protection
of Equipment function. With the breaker open remove the neutral
conductor of the circuit from the neutral terminal of the Arc Fault
Circuit Interrupter. Then test between the both current carrying
conductors and ground if any measurable resistance is found you have a
ground fault on the circuit that you will have to find and clear.
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sony TV - Picture Problem Bruce H Electronics Repair 4 October 10th 06 01:30 AM
Household electrical problem Warlock49766 Electronics Repair 6 March 28th 06 06:23 PM
Household electrical problem Warlock49766 Electronics Repair 1 March 27th 06 12:28 AM
Wiring problem A Nony Mous Home Repair 10 May 28th 04 03:00 AM
Problem with retrace lines on EIZO F55S... [email protected] Electronics Repair 2 October 20th 03 01:29 AM


All times are GMT +1. The time now is 06:43 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"