My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default zoned hot water system problem


"RayV" wrote in message

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)


Why? You have three zone valves and three circulators. The individual
circulator for the zone should be doing the ork.


Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly.


Was this a single zone system that was converted to a multi-zone system?
Sounds crazy to have a main circulator plus the individual zones. Could
also be the zone valves are not operating properly. Have you checked to be
sure they are closed?
..

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Should be one way or the other. Any thermostat calling for heat would start
the pump and open the valve for that zone. My house has two pumps, one for
each zone. The thermostat starts the pump for that zone only and heats
that zone only. The boiler is controlled by an aquastat that starts the
burner when the water temperature gets below the set point.


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default zoned hot water system problem


Edwin Pawlowski wrote:
"RayV" wrote in message

Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)


Why? You have three zone valves and three circulators. The individual
circulator for the zone should be doing the ork.

System doesn't have any zone valves. Flo-control valves are supposed
to stop 'gravity circulation'.
http://www.bellgossett.com/Press/BG-flocontrol.asp

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly.


Was this a single zone system that was converted to a multi-zone system?


Looks like it to me.

Sounds crazy to have a main circulator plus the individual zones. Could
also be the zone valves are not operating properly. Have you checked to be
sure they are closed?


Again, no zone valves just the flo-control 'gravity flow' preventers.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Should be one way or the other. Any thermostat calling for heat would start
the pump and open the valve for that zone. My house has two pumps, one for
each zone. The thermostat starts the pump for that zone only and heats
that zone only. The boiler is controlled by an aquastat that starts the
burner when the water temperature gets below the set point.


I'm guessing the _main_ circulator pump is left-over from before the
system was zoned. My previous house had only one pump and three zone
valves and always worked fine. The pump was on the cold side of the
boiler. I think whoever did the zone work did not set up the system
properly. From what I read about these flo-control valves they will
allow flow with a minimal amount of pressure just not gravity flow from
rising hot water.

  #4   Report Post  
Posted to alt.home.repair
Sev Sev is offline
external usenet poster
 
Posts: 160
Default zoned hot water system problem


RayV wrote:

I'm guessing the _main_ circulator pump is left-over from before the
system was zoned. My previous house had only one pump and three zone
valves and always worked fine. The pump was on the cold side of the
boiler. I think whoever did the zone work did not set up the system
properly. From what I read about these flo-control valves they will
allow flow with a minimal amount of pressure just not gravity flow from
rising hot water.


Unless I'm misunderstanding, aren't they designed to prevent backflow,
but allow flow from pumps, which appears to be the problem? When
circulator(s) are running, they are indeed allowing forward flow of
water through entire system. I think you need zone valves. As you say,
appears to be retrofitted system by someone who didn't quite know what
they were doing. Don't know how large the loops are, but main and zone
circulators seem redundant, though don't see why that should be a
problem(doesn't appear to be excessive electrical load at present),
once zone valves are put in.

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default zoned hot water system problem


Sev wrote:

Unless I'm misunderstanding, aren't they designed to prevent backflow,
but allow flow from pumps, which appears to be the problem? When
circulator(s) are running, they are indeed allowing forward flow of
water through entire system. I think you need zone valves. As you say,
appears to be retrofitted system by someone who didn't quite know what
they were doing. Don't know how large the loops are, but main and zone
circulators seem redundant, though don't see why that should be a
problem(doesn't appear to be excessive electrical load at present),
once zone valves are put in.


You got it right. If you look at this page about halfway down they
show these valves installed after the zone pumps.
http://www.bellgossett.com/homeowner...ntrolvalve.asp
I think the reason his are allowing flow all of the time is 'main' pump
is on the return side of the bolier and forcing all three flo-control
valves open even though the zone pump isn't on.

I'm thinking of disconnecting the main circulator and then running each
zone to see if that cures the problem. Although having the pumps on
the outlet side of the boiler _could_ lead to a boiler overheat more
easily than if the pump was on the inlet side.

If it were my house I would disconnect the zone pumps and install zone
valves and run it for a season just using the main pump. If all went
well I would pull the zone pumps and have three spares.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default zoned hot water system problem


"RayV" wrote in message

Again, no zone valves just the flo-control 'gravity flow' preventers.


Again, check to see that they are operating properly. Mine have an
adjustment thumb screw on the top of them.


I'm guessing the _main_ circulator pump is left-over from before the
system was zoned.


Sure sounds that way. The main pump would have enough force to get water
past the flo-controls.




  #7   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default zoned hot water system problem

Like Ed said, you either use circulators and flow controls or circulators
with zone valves and no flow controls. When you buy the boiler, it comes
with one circulator mounted on it, if you need more zones, you usually
remove that one and build or buy a manifold and mount them all together. So
you have a total of 4 zones, and I'm assuming 4 thermostats and relays. What
concerns me is what is controlling the boiler? Ed mentions an aquastat
maintaining his boiler temperature, some boilers maintain temperature and
some are wired for cold start, which means each zone control would turn on
its circulator and fire the boiler as well. What do you have for domestic
hot water? If it's a coil built into the boiler, you will have a triple
aquastat relay mounted on the boiler to maintain temperature, but if not,
you may have issues with the original circulator becoming energized when any
of the others come on.



"RayV" wrote in message
ups.com...
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8
Default zoned hot water system problem

061031 0950 - Edwin Pawlowski posted:


"RayV" wrote in message

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)


Why? You have three zone valves and three circulators. The individual
circulator for the zone should be doing the ork.


Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly.


Was this a single zone system that was converted to a multi-zone system?
Sounds crazy to have a main circulator plus the individual zones. Could
also be the zone valves are not operating properly. Have you checked to be
sure they are closed?
.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Should be one way or the other. Any thermostat calling for heat would start
the pump and open the valve for that zone. My house has two pumps, one for
each zone. The thermostat starts the pump for that zone only and heats
that zone only. The boiler is controlled by an aquastat that starts the
burner when the water temperature gets below the set point.


I don't understand the multiple circulating pumps. If there is a manifold
with zone valves, when a zone thermostat calls for heat, the zone valve will
open, and that turns on the circulating pump. Only that zone will get the
hot water. The same for the other zone. The circulating pump won't shut
off until all the zone valves are closed.

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default zoned hot water system problem


RBM (remove this) wrote:
Like Ed said, you either use circulators and flow controls or circulators
with zone valves and no flow controls. When you buy the boiler, it comes
with one circulator mounted on it, if you need more zones, you usually
remove that one and build or buy a manifold and mount them all together. So
you have a total of 4 zones, and I'm assuming 4 thermostats and relays. What
concerns me is what is controlling the boiler? Ed mentions an aquastat
maintaining his boiler temperature, some boilers maintain temperature and
some are wired for cold start, which means each zone control would turn on
its circulator and fire the boiler as well. What do you have for domestic
hot water?


Separate water heater.

If it's a coil built into the boiler, you will have a triple
aquastat relay mounted on the boiler to maintain temperature, but if not,
you may have issues with the original circulator becoming energized when any
of the others come on.

This is exactly what is happening, every time an individual zone calls
for heat the 'main' circulator pump kicks on with the boiler as well as
the zone pump. The pressure from the main circulator is enough to lift
the flo-control valves off their seats in every zone.

The biggest problem is my BIL makes Tim 'the tool man' Taylor look like
Tommy Silva. So I can't try things like disconnect the main circulator
and let it run for a few days. I told him several times after I
changed the zone pump and refilled the system to check the pressure a
couple times a day for a few days. He still hasn't checked it (he
forgot).
I'm thinking there are three options:
1-Have him buy three zone valves and replace the flo-control valves
with zone valves and leave everything else alone.

2-Put in the zone valves and disconnect the three zone pumps to see if
the single circulator pump can move enough water. If it works then
remove the zone circulators in the spring.

3-Tell him to call in a heating guy who will sell him some fancy
interconnected thermostats with ambient temperature probes along with
with cyclonic self-equalizing pumps. Oh yeah and a new boiler since
the old one isn't up to the task of properly heating the house
efficiently.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RayV wrote:
RBM (remove this) wrote:
Like Ed said, you either use circulators and flow controls or circulators
with zone valves and no flow controls. When you buy the boiler, it comes
with one circulator mounted on it, if you need more zones, you usually
remove that one and build or buy a manifold and mount them all together. So
you have a total of 4 zones, and I'm assuming 4 thermostats and relays. What
concerns me is what is controlling the boiler? Ed mentions an aquastat
maintaining his boiler temperature, some boilers maintain temperature and
some are wired for cold start, which means each zone control would turn on
its circulator and fire the boiler as well. What do you have for domestic
hot water?


Separate water heater.

If it's a coil built into the boiler, you will have a triple
aquastat relay mounted on the boiler to maintain temperature, but if not,
you may have issues with the original circulator becoming energized when any
of the others come on.

This is exactly what is happening, every time an individual zone calls
for heat the 'main' circulator pump kicks on with the boiler as well as
the zone pump. The pressure from the main circulator is enough to lift
the flo-control valves off their seats in every zone.

The biggest problem is my BIL makes Tim 'the tool man' Taylor look like
Tommy Silva. So I can't try things like disconnect the main circulator
and let it run for a few days. I told him several times after I
changed the zone pump and refilled the system to check the pressure a
couple times a day for a few days. He still hasn't checked it (he
forgot).
I'm thinking there are three options:
1-Have him buy three zone valves and replace the flo-control valves
with zone valves and leave everything else alone.

2-Put in the zone valves and disconnect the three zone pumps to see if
the single circulator pump can move enough water. If it works then
remove the zone circulators in the spring.

3-Tell him to call in a heating guy who will sell him some fancy
interconnected thermostats with ambient temperature probes along with
with cyclonic self-equalizing pumps. Oh yeah and a new boiler since
the old one isn't up to the task of properly heating the house
efficiently.


Ray, Did you check to make sure that the top nut of the check valve
was closed tight? Most times people forget to tighten this nut. If
not tight, it will allow for the hot water to enter into the other zone
causing ghost heating.

Paul



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default zoned hot water system problem


wrote:

Ray, Did you check to make sure that the top nut of the check valve
was closed tight? Most times people forget to tighten this nut. If
not tight, it will allow for the hot water to enter into the other zone
causing ghost heating.

Paul


Yes. After I replaced the pump I fully opened (bypassed) the
flo-control valves and ran all of the circulator pumps to hopefully
flush any dirt from the seats and get the air moving. Then I closed
all of the flo-control valves. They were all closed when I got there
and hadn't been touched in years if ever.

  #12   Report Post  
Posted to alt.home.repair
Sev Sev is offline
external usenet poster
 
Posts: 160
Default zoned hot water system problem


RayV wrote:

This is exactly what is happening, every time an individual zone calls
for heat the 'main' circulator pump kicks on with the boiler as well as
the zone pump. The pressure from the main circulator is enough to lift
the flo-control valves off their seats in every zone.

The biggest problem is my BIL makes Tim 'the tool man' Taylor look like
Tommy Silva. So I can't try things like disconnect the main circulator
and let it run for a few days.


Hmmm. I was just about to suggest exactly that- that the fix might be
as simple as unscrewing the wire nut that secures the hot wire for the
main circulator...

  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RayV wrote:
wrote:

Ray, Did you check to make sure that the top nut of the check valve
was closed tight? Most times people forget to tighten this nut. If
not tight, it will allow for the hot water to enter into the other zone
causing ghost heating.

Paul


Yes. After I replaced the pump I fully opened (bypassed) the
flo-control valves and ran all of the circulator pumps to hopefully
flush any dirt from the seats and get the air moving. Then I closed
all of the flo-control valves. They were all closed when I got there
and hadn't been touched in years if ever.


Well, then if they are tight and have been there for awhile and you
are getting ghost heating you may want to try and replace one of the
check valves. There really isn't much to forced hot water system.

Paul

  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default zoned hot water system problem

In article .com, "RayV" wrote:

wrote:
RayV wrote:

Yes. After I replaced the pump I fully opened (bypassed) the
flo-control valves and ran all of the circulator pumps to hopefully
flush any dirt from the seats and get the air moving. Then I closed
all of the flo-control valves. They were all closed when I got there
and hadn't been touched in years if ever.


Well, then if they are tight and have been there for awhile and you
are getting ghost heating you may want to try and replace one of the
check valves. There really isn't much to forced hot water system.


I was thinking about trying that but all three flo-control valves are
allowing flow no matter which of the zones is calling for heat. That
would mean all three of them have failed or are stuck, he also told me
that he has always gotten heat everywhere in the house since he moved
in 8 years ago. This has to be an incorrect zone job done for the
previous owner.

So just turn off the main circulator and be done with it. That's the problem.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #17   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default zoned hot water system problem

As Doug and Sev said, disconnect the wire to the "main" circulator and see
what happens. If the problem stops and this main circulator is not part of a
manifold, but instead, is inline in the return, I'd remove it altogether



"RayV" wrote in message
ups.com...
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?



  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RBM (remove this) wrote:
As Doug and Sev said, disconnect the wire to the "main" circulator and see
what happens. If the problem stops and this main circulator is not part of a
manifold, but instead, is inline in the return, I'd remove it altogether



"RayV" wrote in message
ups.com...
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Sorry....Disagree!! If you are NOT using zone valves then you need a
circ for each zone...PERIOD. If your using zone valves then one circ
wil work as long as you have the proper controller for the zone vavles.
How else are you going to get the hot water to each zone when there is
a call for heat by the thermostat? In my house I have two zones. I
choose to plumb my heating system with individual circulators because I
don't like zone valves. I have a Taco 503 controller that turns on
each individual circ when each thermostat calls for heat. In a basic
hot water boiler setup the only component that will prevent "Ghost
Heating" into a zone that is NOT calling for heat is a check
valve.....PERIOD.

So, don't remove the circ. I would make sure that the valves are
working properly. You should be able to open up the valve without
removing it completely form the system. Now, if your still confused on
this issue all you have to do is call a professional. They will figure
it out for you.

-paul

  #19   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default zoned hot water system problem

Another possibility is that the "main" circulator is not pulling in the same
direction as the three on the manifold


wrote in message
ups.com...

RBM (remove this) wrote:
As Doug and Sev said, disconnect the wire to the "main" circulator and
see
what happens. If the problem stops and this main circulator is not part
of a
manifold, but instead, is inline in the return, I'd remove it altogether



"RayV" wrote in message
ups.com...
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Sorry....Disagree!! If you are NOT using zone valves then you need a
circ for each zone...PERIOD. If your using zone valves then one circ
wil work as long as you have the proper controller for the zone vavles.
How else are you going to get the hot water to each zone when there is
a call for heat by the thermostat? In my house I have two zones. I
choose to plumb my heating system with individual circulators because I
don't like zone valves. I have a Taco 503 controller that turns on
each individual circ when each thermostat calls for heat. In a basic
hot water boiler setup the only component that will prevent "Ghost
Heating" into a zone that is NOT calling for heat is a check
valve.....PERIOD.

So, don't remove the circ. I would make sure that the valves are
working properly. You should be able to open up the valve without
removing it completely form the system. Now, if your still confused on
this issue all you have to do is call a professional. They will figure
it out for you.

-paul



  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RBM remove this wrote:
Another possibility is that the "main" circulator is not pulling in the same
direction as the three on the manifold




Good point!!! LOL, wouldn't that be a kick in the A*S. He should make
sure that the arrow on the circ is pointing in the proper
direction......Didn't even think of that.



  #22   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RayV wrote:
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


RayV, After all of the suggestions made and what you have tried do you
have a fix? I'm curious to what fixed this problem and I'm sure the
others in the group would like to hear what the solution was.

-paul

  #23   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 831
Default zoned hot water system problem


wrote:
RayV wrote:
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


RayV, After all of the suggestions made and what you have tried do you
have a fix? I'm curious to what fixed this problem and I'm sure the
others in the group would like to hear what the solution was.

-paul


I also posted this in alt.hvac and the predominate (reasonable) opinion
there and here is the main circulator pump on the inlet side of the
boiler is not needed in conjunction with the zone pumps. I suspect the
system would be fine with one pump and zone valves. The top floor
might not get as much flow if all 3 zones are calling at the same time
but the lower zones would eventually shut off.

This weekend I will go over and disconnect the wires to the 'main'
circulator and run each zone and see what happens. Worst that can
happen is I have to reconnect it.

If that doesn't work maybe I'll have him call in an HVAC guy for an
opinion. I could install zone valves for him and the parts would be
less than $400 (plus $30 for a bottle of vodka).

I'll post a followup after I try disconnecting the main pump.

  #24   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 24
Default zoned hot water system problem


RayV wrote:
wrote:
RayV wrote:
My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


RayV, After all of the suggestions made and what you have tried do you
have a fix? I'm curious to what fixed this problem and I'm sure the
others in the group would like to hear what the solution was.

-paul


I also posted this in alt.hvac and the predominate (reasonable) opinion
there and here is the main circulator pump on the inlet side of the
boiler is not needed in conjunction with the zone pumps. I suspect the
system would be fine with one pump and zone valves. The top floor
might not get as much flow if all 3 zones are calling at the same time
but the lower zones would eventually shut off.

This weekend I will go over and disconnect the wires to the 'main'
circulator and run each zone and see what happens. Worst that can
happen is I have to reconnect it.

If that doesn't work maybe I'll have him call in an HVAC guy for an
opinion. I could install zone valves for him and the parts would be
less than $400 (plus $30 for a bottle of vodka).

I'll post a followup after I try disconnecting the main pump.


Sounds like I misunderstood you. Are you saying that there are
circulators for each zone and then another circulator for all zones
which you call the main pump? If this is the case, then yes I agree
with you. I would disconnect the main circulator and try the heat.

-paul

  #26   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default zoned hot water system problem

RayV posted for all of us...

My BIL called me over to help him fix a leaking circulator pump on his
system which was an easy swap and fixed the leak. But he still has a
big problem with his system, here's the current setup:

Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump

The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.

Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?


Asked and answered MANY times! Sorry, you lose, buh bye, bring in the next
player Johnny.
--
Tekkie Don't bother to thank me, I do this as a public service.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
cottage water system problem mike-k Home Repair 3 May 1st 06 01:23 AM
How to protect your skin & hair to water infection nitin Home Repair 1 March 26th 06 08:46 PM
Brown's gas?? T.Alan Kraus Metalworking 16 December 9th 05 07:36 AM
need hot water FAST PV Home Repair 38 January 30th 04 01:15 AM
Water system problem BigWallop UK diy 2 August 8th 03 11:12 AM


All times are GMT +1. The time now is 09:24 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"