I'm in the planning stages of a switch to hydronic heat for my home
which will replace my existing forced air heat. The system will
include a mix of radiant panels and staple-up under-floor tubing. The
heat source for this system will be my current Takagi T-KD20 tankless
water heater. It is rated for 20 to 185 MBTU input and 85% efficient.

The conceptual problem I'm running into is this: If, for instance, I
wanted to heat my master bedroom and bath on one zone, the calculated
sensible loss is 6,032 BTU/hr. If this were the only zone running, it
would come in significantly under the 17,000 BTU minimum (20,000 BTU *
85% efficiency = 17,000 BTU) the Takagi can put out. Wouldn't I run
into a thermal runaway situation? If there's more heat going into a
system than what is coming out it would seem so. Am I missing
something? Do each of my zones have to emit at least 17,000 BTU to
prevent this situation?

I've thought about adding a 20 to 40 gallon storage tank to the design
and a three way valve controlled by an aquastat. While each zone is
calling for heat the circulator(s) would run and, only if the water
temp in the system was below a certain threshold, would the flow be
routed through the Takagi.

I've seen some prefab plumbing designed for the application using a
thermostatic mixing valve offered by some online vendors. I have two
problems with that design though. First, I'm going to need water temps
approaching 180 degrees in order to get enough output in the coldest
winter months to meet the loss. Second, with a mixing valve it would
seem those kits are just bouncing back and forth between the hysteresis
of the flow sensors in the tankless heater. I would guess that would
cause frequent cycling of the tankless. That's where my storage tank,
three way valve and aquastat idea came from - similar concept to the
thermostatic mixing valve but extended cycle period.

Anyone have any thoughts?

Thanks in advance!

Stan

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 554
Default Hydronic loop sizing

I dont think the pipe can take more than around 115, you dont want 180f
under the floors. Your heater can put out 185000 btu but to just heat
water for hydromic it might only use 50000 btu. You need to research
this with the vendors and reading.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Hydronic loop sizing

I dont think the pipe can take more than around 115, you dont want 180f

By "the pipe" I'm guessing you're referring to PEX. Standard PEX (ASTM
877/876) can take 180 deg at 100 psi. PEX-AL-PEX (ASTM 1281) can take
180 deg at 125 psi. My 180 degree max is based upon the rating for the
radiant panels (which generally use copper pipe, not PEX). But none
the less, the issue of my target temperature was not what I was asking
about. The design temperature is irrelevant - or rather only relevant
for the density values used in calculations. This is a heat-in vs.
heat-out situation.

under the floors. Your heater can put out 185000 btu but to just heat
water for hydromic it might only use 50000 btu. You need to research
this with the vendors and reading.


Believe me, I've done plenty of research. If I wanted to be told to
"do more research" I would have posted this in alt.hvac! :-)

To "show my work" so to speak, using the 6,032 BTU/hr loop mentioned
above, if I design it with a 180 deg entering temp, and 20 deg nominal
temp drop, it would need to flow 0.62 gal/min. That is actually below
the Takagi's turn on threshold of 0.75 gal/min. If I go with 1.0
gal/min I get a resulting drop of 12.4 degrees. When the water returns
to the heater, if it is getting 17,000 BTU minimum (I'm assuming that
rating is in BTU/hr) put back into it, the resulting temp increase
would be 34 degrees, thus an exit temp of about 201 degrees. If this
cycle simply continues there would be thermal runaway.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 151
Default Hydronic loop sizing

wrote:
I'm in the planning stages of a switch to hydronic heat for my home
which will replace my existing forced air heat. The system will
include a mix of radiant panels and staple-up under-floor tubing. The
heat source for this system will be my current Takagi T-KD20 tankless
water heater. It is rated for 20 to 185 MBTU input and 85% efficient.

The conceptual problem I'm running into is this: If, for instance, I
wanted to heat my master bedroom and bath on one zone, the calculated
sensible loss is 6,032 BTU/hr. If this were the only zone running, it
would come in significantly under the 17,000 BTU minimum (20,000 BTU *
85% efficiency = 17,000 BTU) the Takagi can put out. Wouldn't I run
into a thermal runaway situation? If there's more heat going into a
system than what is coming out it would seem so. Am I missing
something? Do each of my zones have to emit at least 17,000 BTU to
prevent this situation?

I've thought about adding a 20 to 40 gallon storage tank to the design
and a three way valve controlled by an aquastat. While each zone is
calling for heat the circulator(s) would run and, only if the water
temp in the system was below a certain threshold, would the flow be
routed through the Takagi.

I've seen some prefab plumbing designed for the application using a
thermostatic mixing valve offered by some online vendors. I have two
problems with that design though. First, I'm going to need water temps
approaching 180 degrees in order to get enough output in the coldest
winter months to meet the loss. Second, with a mixing valve it would
seem those kits are just bouncing back and forth between the hysteresis
of the flow sensors in the tankless heater. I would guess that would
cause frequent cycling of the tankless. That's where my storage tank,
three way valve and aquastat idea came from - similar concept to the
thermostatic mixing valve but extended cycle period.

Anyone have any thoughts?

Thanks in advance!

Stan


As noted you need more info, study more.

When you run hot water through any kind of 'radiator' its temperature
drops, losing its heat to the air. If it cannot lose its heat, the water
simply stays hot, the boiler[wh whatever] will only heat it to the set
point then it will shut off.

Again, not being rude, I installed radiant tubing, but had a pro do the
design. I know enough to know that you do not know enough yet. Yet.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default Hydronic loop sizing


wrote in message
To "show my work" so to speak, using the 6,032 BTU/hr loop mentioned
above, if I design it with a 180 deg entering temp, and 20 deg nominal
temp drop, it would need to flow 0.62 gal/min. That is actually below
the Takagi's turn on threshold of 0.75 gal/min. If I go with 1.0
gal/min I get a resulting drop of 12.4 degrees. When the water returns
to the heater, if it is getting 17,000 BTU minimum (I'm assuming that
rating is in BTU/hr) put back into it, the resulting temp increase
would be 34 degrees, thus an exit temp of about 201 degrees. If this
cycle simply continues there would be thermal runaway.


I think your work needs work. Why would there be a thermal runaway? Does
the Takagi not have an aquastat to cycle it off if heat is not needed? If
not, it is the wrong appliance to use for a heater.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 554
Default Hydronic loop sizing

Even for you to consider 180f input is crazy, Think Cooking your feet
unless your in bed. I also wonder why you are doing this, you can get a
94% efficient furnace Vs your 85% takagi, a Vsdc blower motor that will
consume on low less than your planned pump. Can the 3/4 or 1" output
handle the gpm you need to pump through the house, If you think you will
need 180f something in your plan is wrong, radiant heat is to be under
115f, not cook you at high temps, to consider that 180 is the Max
rating as you say, well that is the maximum and not wise to continualy
stress the pipe, even if you wanted cooked feet for dinner. Do you have
pets, because unless they live on the furniture all day and night they
will be dead in a short time

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 193
Default Hydronic loop sizing

wrote:
I dont think the pipe can take more than around 115, you dont want 180f


By "the pipe" I'm guessing you're referring to PEX. Standard PEX (ASTM
877/876) can take 180 deg at 100 psi. PEX-AL-PEX (ASTM 1281) can take
180 deg at 125 psi. My 180 degree max is based upon the rating for the
radiant panels (which generally use copper pipe, not PEX). But none
the less, the issue of my target temperature was not what I was asking
about. The design temperature is irrelevant - or rather only relevant
for the density values used in calculations. This is a heat-in vs.
heat-out situation.


under the floors. Your heater can put out 185000 btu but to just heat
water for hydromic it might only use 50000 btu. You need to research
this with the vendors and reading.


Believe me, I've done plenty of research. If I wanted to be told to
"do more research" I would have posted this in alt.hvac! :-)

To "show my work" so to speak, using the 6,032 BTU/hr loop mentioned
above, if I design it with a 180 deg entering temp, and 20 deg nominal
temp drop, it would need to flow 0.62 gal/min. That is actually below
the Takagi's turn on threshold of 0.75 gal/min. If I go with 1.0
gal/min I get a resulting drop of 12.4 degrees. When the water returns
to the heater, if it is getting 17,000 BTU minimum (I'm assuming that
rating is in BTU/hr) put back into it, the resulting temp increase
would be 34 degrees, thus an exit temp of about 201 degrees. If this
cycle simply continues there would be thermal runaway.


I am looking at a website right now that is heating the slab with 83F
input water. The exit temp of the water is about 71F. Flow rate thru
each zone is about 3GPM. Total flow rate is about 9GPM. Slab temp is in
the upper 60s with outside air temp at 31F. The heat source is putting
roughly 30,000BTUH into the slab

The owner's manual for the Tagaki tankless that I am reading now says
that it will monitor the temperature of the water it outputs and adjust
the burners to LIMIT the output water temp to 120F. You can set the
output temp to be as low as 105F.

Seems to me that setting the flow rate thru the radiant loop to 3GPM,
and setting the tagaki to 105F, the Tagaki will intermittently fire to
keep its output temp near 105F, until your slab temp sensor turns off
the circulator pump. Even setting the temp to 120F, the factory
setting, will accomplish the same goal.

After all, you really want your slab temp near 70F, not 90F. Restaurants
in Korea put a shot of hot water thru the slab where you sit down. This
ONLY warms up the slab to the upper 70s, and then it cools as you sit there.

I agree with your critics, you have focussed on the heater
characteristics without considering the safety factors built into the
heater. You have focussed on the characteristics of the radiant loop
without considering the characteristics of the loop circulator pumps.

You need to expand your view!!!




180F temps are POSSIBLE out of the tagaki, but the unit would be
defective if it permitted such a thing to occur
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 554
Default Hydronic loop sizing

But is the Takagis flow rate, or gpm enough. It has a 3/4 or maybe 1"
piping, My Bosch Ng Tankless is 3/4, Boilers are not that small, my
boiler is 2" output- input pipe

I lived with Radiant heat, never were the floors Hot as you think is
necessary. Never should they be hot. But if you are trying to save on
utilities you wont.

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default Hydronic loop sizing

We're getting ready to build a new detached shop and we're going to "tube
up" the slab for radiant heat. Could you give me the links to the sites you
are looking at? I need an online supplier for the tubing and as much
education as possible. We are going to do this ourselves. Hopefully we'll
drive it with solar panels in the future.

--
Steve Barker



"Robert Gammon" wrote in message
t...
wrote:
I am looking at a website right now that is heating the slab with 83F
input water. The exit temp of the water is about 71F. Flow rate thru each
zone is about 3GPM. Total flow rate is about 9GPM. Slab temp is in the
upper 60s with outside air temp at 31F. The heat source is putting
roughly 30,000BTUH into the slab

The owner's manual for the Tagaki tankless that I am reading now says that
it will monitor the temperature of the water it outputs and adjust the
burners to LIMIT the output water temp to 120F. You can set the output
temp to be as low as 105F.

Seems to me that setting the flow rate thru the radiant loop to 3GPM, and
setting the tagaki to 105F, the Tagaki will intermittently fire to keep
its output temp near 105F, until your slab temp sensor turns off the
circulator pump. Even setting the temp to 120F, the factory setting, will
accomplish the same goal.

After all, you really want your slab temp near 70F, not 90F. Restaurants
in Korea put a shot of hot water thru the slab where you sit down. This
ONLY warms up the slab to the upper 70s, and then it cools as you sit
there.

I agree with your critics, you have focussed on the heater characteristics
without considering the safety factors built into the heater. You have
focussed on the characteristics of the radiant loop without considering
the characteristics of the loop circulator pumps.

You need to expand your view!!!




180F temps are POSSIBLE out of the tagaki, but the unit would be defective
if it permitted such a thing to occur



  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 193
Default Hydronic loop sizing

Steve Barker LT wrote:
We're getting ready to build a new detached shop and we're going to "tube
up" the slab for radiant heat. Could you give me the links to the sites you
are looking at? I need an online supplier for the tubing and as much
education as possible. We are going to do this ourselves. Hopefully we'll
drive it with solar panels in the future.


www.ourcoolhouse.com

Radiant loop is powered by a ground source heat pump

The issue with solar is daytime use only. Detached shop OK. Maybe not
out there every day. Probably not out there before sun up, and probably
back to the house before or shortly after sun down.

Be sure to check out insolation rates for where you live and size the
number of collectors to be able to meet a target 70F approx slab temp in
winter.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 193
Default Hydronic loop sizing

Robert Gammon wrote:
Steve Barker LT wrote:
We're getting ready to build a new detached shop and we're going to
"tube up" the slab for radiant heat. Could you give me the links to
the sites you are looking at? I need an online supplier for the
tubing and as much education as possible. We are going to do this
ourselves. Hopefully we'll drive it with solar panels in the future.


www.ourcoolhouse.com

Radiant loop is powered by a ground source heat pump

The issue with solar is daytime use only. Detached shop OK. Maybe not
out there every day. Probably not out there before sun up, and
probably back to the house before or shortly after sun down.

Be sure to check out insolation rates for where you live and size the
number of collectors to be able to meet a target 70F approx slab temp
in winter.

and to the OP

The Tagaki is likely to fire for 30 seconds to get the water temp up to
120F and then shutoff while you continue to circulate the water.
After 30 to 90 seconds of circulation, the water temp has dropped low
enough that the Tagaki will fire again. Remember the Tagaki detects
BOTH flow and temperature of its outlet water.

Keep in mind that the circulator pump will want to move the water much
faster than 1 GPM.

You will use ALOT of gas to do this, even though Tagaki does document
the application in their guide.

As a radiant heat source, I think a tankless will work better as the
heat source for driveway deicing than for keeping your slab warm.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default Hydronic loop sizing

Thanks for the info. We're not trying to heat the place per se, but just
enough to keep the slab above freezing as to prevent heaving and cracking.
It'll just be a storage shed / occasional truck work type shop for private
use.

--
Steve Barker




"Robert Gammon" wrote in message
et...
Steve Barker LT wrote:
We're getting ready to build a new detached shop and we're going to "tube
up" the slab for radiant heat. Could you give me the links to the sites
you are looking at? I need an online supplier for the tubing and as much
education as possible. We are going to do this ourselves. Hopefully
we'll drive it with solar panels in the future.


www.ourcoolhouse.com

Radiant loop is powered by a ground source heat pump

The issue with solar is daytime use only. Detached shop OK. Maybe not out
there every day. Probably not out there before sun up, and probably back
to the house before or shortly after sun down.

Be sure to check out insolation rates for where you live and size the
number of collectors to be able to meet a target 70F approx slab temp in
winter.



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Hydronic loop sizing


The Tagaki is likely to fire for 30 seconds to get the water temp up to
120F and then shutoff while you continue to circulate the water.
After 30 to 90 seconds of circulation, the water temp has dropped low
enough that the Tagaki will fire again. Remember the Tagaki detects
BOTH flow and temperature of its outlet water.

....

You will use ALOT of gas to do this, even though Tagaki does document
the application in their guide.


That's exactly the type of info I was looking for. Thanks! I though
it may work like that, but needed confirmation.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rope knot making a loop. Perry Templeton Home Repair 11 September 30th 06 08:30 PM
hydronic heater is on in summer John Smith Home Repair 1 July 24th 06 12:55 PM
DIY TEK compensation loop for R7844 Tod Treganowan Electronics Repair 3 April 22nd 06 02:30 PM
Audio amp earth loop? Gareth Magennis Electronics Repair 5 November 3rd 04 10:57 AM
Central Heating Question - Heating Loop Murdo MacKenzie UK diy 2 May 17th 04 02:42 PM


All times are GMT +1. The time now is 04:53 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"