Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
I had run a 12/3 w.g 220v circuit to my attic, and then branched into
two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#2
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
"emichael" wrote in message
ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#3
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
thanks.
hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#4
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
You are correct that you can't share a neutral between the two breakers. You
need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#5
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
It's fine, just make sure your common neutral connections are pigtailed and
not dependent on the receptacles "e michael brandt" wrote in message link.net... thanks. hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#6
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
These are for window AirConditioners, and happen to be right next to hot
water radiators, which I figured are as likely to be as good a ground as a faucet in a bathroom. Do you see any reason that I cannot simply use the ganged 220v breaker like I had it before (ignoring the AFCI for now.) That way both circuits are tripped when either one is overloaded. emichael RBM wrote: You are correct that you can't share a neutral between the two breakers. You need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#7
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
Not a problem
"e michael brandt" wrote in message hlink.net... These are for window AirConditioners, and happen to be right next to hot water radiators, which I figured are as likely to be as good a ground as a faucet in a bathroom. Do you see any reason that I cannot simply use the ganged 220v breaker like I had it before (ignoring the AFCI for now.) That way both circuits are tripped when either one is overloaded. emichael RBM wrote: You are correct that you can't share a neutral between the two breakers. You need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#8
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
They are in fact pigtailed, btu why is it okay to have current in one
circuit in the romex ? Is that not a hazard to someone who thinks the power is off by having thrown one breaker? And altho you are saying it IS legal to have two unganged breakers, is it not okay (or even better) to do it with a ganged 220 v breaker like I had it before and like the first inspector passed on? emichael RBM wrote: It's fine, just make sure your common neutral connections are pigtailed and not dependent on the receptacles "e michael brandt" wrote in message link.net... thanks. hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#9
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
thanks.
emichael RBM wrote: It's fine, just make sure your common neutral connections are pigtailed and not dependent on the receptacles "e michael brandt" wrote in message link.net... thanks. hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#10
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
thanks so much.
btw, in the future if I decide to use my now useless AFCIs in two new kitchen circuits, would a GFCI be needed at the outlets? Or are AFCIs doing both jobs according to code? emichael RBM wrote: Not a problem "e michael brandt" wrote in message hlink.net... These are for window AirConditioners, and happen to be right next to hot water radiators, which I figured are as likely to be as good a ground as a faucet in a bathroom. Do you see any reason that I cannot simply use the ganged 220v breaker like I had it before (ignoring the AFCI for now.) That way both circuits are tripped when either one is overloaded. emichael RBM wrote: You are correct that you can't share a neutral between the two breakers. You need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#11
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
You actually have two separate circuits. With circuit A off, all the outlets
etc attached are dead. With circuit B off, all those outlets are dead. The only problem or danger is in unsplicing the common neutral. By connecting the two circuits to a double pole breaker, you eliminate that possible danger as well. I don't recall code on when a double pole is required for Edison circuits, but I believe if outlets in one box are connected to both live legs, you're required to use a double pole breaker "e michael brandt" wrote in message link.net... They are in fact pigtailed, btu why is it okay to have current in one circuit in the romex ? Is that not a hazard to someone who thinks the power is off by having thrown one breaker? And altho you are saying it IS legal to have two unganged breakers, is it not okay (or even better) to do it with a ganged 220 v breaker like I had it before and like the first inspector passed on? emichael RBM wrote: It's fine, just make sure your common neutral connections are pigtailed and not dependent on the receptacles "e michael brandt" wrote in message link.net... thanks. hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#12
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
AFCI's are for bedrooms only, kitchen's require GFCI's for all counter
outlets "e michael brandt" wrote in message link.net... thanks so much. btw, in the future if I decide to use my now useless AFCIs in two new kitchen circuits, would a GFCI be needed at the outlets? Or are AFCIs doing both jobs according to code? emichael RBM wrote: Not a problem "e michael brandt" wrote in message hlink.net... These are for window AirConditioners, and happen to be right next to hot water radiators, which I figured are as likely to be as good a ground as a faucet in a bathroom. Do you see any reason that I cannot simply use the ganged 220v breaker like I had it before (ignoring the AFCI for now.) That way both circuits are tripped when either one is overloaded. emichael RBM wrote: You are correct that you can't share a neutral between the two breakers. You need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#13
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
On 16 Sep 2006 14:53:09 -0700, "emichael" wrote:
I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#14
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
I understand. thanks.
emichael RBM wrote: You actually have two separate circuits. With circuit A off, all the outlets etc attached are dead. With circuit B off, all those outlets are dead. The only problem or danger is in unsplicing the common neutral. By connecting the two circuits to a double pole breaker, you eliminate that possible danger as well. I don't recall code on when a double pole is required for Edison circuits, but I believe if outlets in one box are connected to both live legs, you're required to use a double pole breaker "e michael brandt" wrote in message link.net... They are in fact pigtailed, btu why is it okay to have current in one circuit in the romex ? Is that not a hazard to someone who thinks the power is off by having thrown one breaker? And altho you are saying it IS legal to have two unganged breakers, is it not okay (or even better) to do it with a ganged 220 v breaker like I had it before and like the first inspector passed on? emichael RBM wrote: It's fine, just make sure your common neutral connections are pigtailed and not dependent on the receptacles "e michael brandt" wrote in message link.net... thanks. hmm, then I just have to remove the afci breakers and revert to a standard breaker I guess. Was the HomeDepot fellow right that this should have two unganged breakers, one for each circuit? That would make me nervous - if one trips or is turned off, there is still current in that calbe on the other circuit. emichael peter wrote: "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? AFCI contains a 30mA GFCI. You cannot use GFCI with a shared neutral. It wants to see equal current on the neutral and the hot. With a shared neutral, there is no way to make it work. Like you said, the GFCI (within the AFCI) is confused. If you want AFCI, you need to have two 12/2 circuits. In the future perhaps someone would make AFCI receptacles you can installed in the bedroom, or double AFCI breaker specifically for shared neutral ciruit. |
#15
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
okay thanks.
emichael RBM wrote: AFCI's are for bedrooms only, kitchen's require GFCI's for all counter outlets "e michael brandt" wrote in message link.net... thanks so much. btw, in the future if I decide to use my now useless AFCIs in two new kitchen circuits, would a GFCI be needed at the outlets? Or are AFCIs doing both jobs according to code? emichael RBM wrote: Not a problem "e michael brandt" wrote in message hlink.net... These are for window AirConditioners, and happen to be right next to hot water radiators, which I figured are as likely to be as good a ground as a faucet in a bathroom. Do you see any reason that I cannot simply use the ganged 220v breaker like I had it before (ignoring the AFCI for now.) That way both circuits are tripped when either one is overloaded. emichael RBM wrote: You are correct that you can't share a neutral between the two breakers. You need to run separate two wire circuits to the bedrooms. Why are you installing GFCI outlets in bedrooms? "emichael" wrote in message ups.com... I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb |
#16
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
I appreciate your comments. Understand though that all this started due
to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#17
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
Dude! Wiring is no hobby and you don't know what you are doing, so hire
a licensed Electrical Contractor. Put your family up in a Hotel until you get someone qualified to check out your "Cluster F" of a job. You will burn down your home if you try hard enough! e michael brandt wrote: I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#18
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
"e michael brandt" wrote in message
link.net... btw, in the future if I decide to use my now useless AFCIs in two new kitchen circuits, would a GFCI be needed at the outlets? Or are AFCIs doing both jobs according to code? The GFCI inside the AFCI trips at 30mA. It is meant to protect equipments, not human. I believe this GFCI is an unpublicized feature of AFCI. Therefore you still need to install a regular GFCI, which trips at 5mA. In the future there will be combination AFCI/GFCI (trips at 5mA). This is puzzling to me. If they have a built-in 30mA GFCI, it should cost very little to make it trip at 5mA, and they can sell it for more. BTW, current AFCI only detects parallel fault (e.g. an intermitent short circuit). They will be required to detect series arc as well (intermittent open circuit) eventually. |
#19
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
"RBM" rbm2(remove wrote in message ... You actually have two separate circuits. With circuit A off, all the outlets etc attached are dead. With circuit B off, all those outlets are dead. The only problem or danger is in unsplicing the common neutral. By connecting the two circuits to a double pole breaker, you eliminate that possible danger as well. I don't recall code on when a double pole is required for Edison circuits, but I believe if outlets in one box are connected to both live legs, you're required to use a double pole breaker Linked breakers required only on the same yoke (strap), not just in the same box. NEC 210.4 B (2005) (B) Devices or Equipment. Where a multiwire branch circuit supplies more than one device or equipment on the same yoke, a means shall be provided to disconnect simultaneously all ungrounded conductors supplying those devices or equipment at the point where the branch circuit originates. |
#20
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
Sounds logical to me. Thanks.
emichael Paul A wrote: "RBM" rbm2(remove wrote in message ... You actually have two separate circuits. With circuit A off, all the outlets etc attached are dead. With circuit B off, all those outlets are dead. The only problem or danger is in unsplicing the common neutral. By connecting the two circuits to a double pole breaker, you eliminate that possible danger as well. I don't recall code on when a double pole is required for Edison circuits, but I believe if outlets in one box are connected to both live legs, you're required to use a double pole breaker Linked breakers required only on the same yoke (strap), not just in the same box. NEC 210.4 B (2005) (B) Devices or Equipment. Where a multiwire branch circuit supplies more than one device or equipment on the same yoke, a means shall be provided to disconnect simultaneously all ungrounded conductors supplying those devices or equipment at the point where the branch circuit originates. |
#21
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
Thanks for letting me know the details of these GFCIs.
emichael peter wrote: "e michael brandt" wrote in message link.net... btw, in the future if I decide to use my now useless AFCIs in two new kitchen circuits, would a GFCI be needed at the outlets? Or are AFCIs doing both jobs according to code? The GFCI inside the AFCI trips at 30mA. It is meant to protect equipments, not human. I believe this GFCI is an unpublicized feature of AFCI. Therefore you still need to install a regular GFCI, which trips at 5mA. In the future there will be combination AFCI/GFCI (trips at 5mA). This is puzzling to me. If they have a built-in 30mA GFCI, it should cost very little to make it trip at 5mA, and they can sell it for more. BTW, current AFCI only detects parallel fault (e.g. an intermitent short circuit). They will be required to detect series arc as well (intermittent open circuit) eventually. |
#22
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
e michael brandt wrote:
I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom You can buy 12/2+2 with ground cable for the purpose of supplying two AFCI protected circuits in one cable run. Both Square D and Cutler Hammer offer two pole common neutral AFCIs but the price is very high. You will only find them through an electrical supply house. General Electric's version can be seen at http://www.arcadvisor.com/afci.html. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#23
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
I had read that such cable was to be available. I , but did not know it
was already on the market. This is good info for the future, but unfortunately the horse is out of this barn. After running the cable (this one and others) up to the attic, I filled the chase with blown insulation and foam so there is no longer any way to run cable easily. What i really need now is AFCIs that go into the outlet box. Are they on the near horizon that you know of? emichael Tom Horne, Electrician wrote: e michael brandt wrote: I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom You can buy 12/2+2 with ground cable for the purpose of supplying two AFCI protected circuits in one cable run. Both Square D and Cutler Hammer offer two pole common neutral AFCIs but the price is very high. You will only find them through an electrical supply house. General Electric's version can be seen at http://www.arcadvisor.com/afci.html. |
#24
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
On Sun, 17 Sep 2006 00:50:10 GMT, e michael brandt
wrote: I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael This is not a how-to, but to get you familar with how maybe an electrician can help you. 1. Order an expensive double-pole AFCI breaker for your current wiring method and panel. or 2. Pull the orginal wire(12/3) down into a small load center, then installed AFCI's in that load center then feed you bedrooms. or 3. Tape to the end of the 12/3 some 12/2/2 and pull. The 12/3 might feed back to your panel and then you will have the correct wire and do a normal AFCI installation. or 4. A combination of these listed, or other ideas. See? The idea is that you NEED a qualified electrician to help, and home inspectors only evaluate overall work, they don't tell YOU (or who does the work) how to do their job, it is their (or YOU) responsiblity. Good luck, and please tell us what happens in follow-ups. later, tom @ www.WorkAtHomePlans.com Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#25
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
Tom, you are indeed great. i am thrilled to learn that there are
actually double pole AFCI's, designed for shared neutrals like mine! Altho pricey, that is the way to go. A simple solution. thanks so much. emichael Tom The Great wrote: On Sun, 17 Sep 2006 00:50:10 GMT, e michael brandt wrote: I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael This is not a how-to, but to get you familar with how maybe an electrician can help you. 1. Order an expensive double-pole AFCI breaker for your current wiring method and panel. or 2. Pull the orginal wire(12/3) down into a small load center, then installed AFCI's in that load center then feed you bedrooms. or 3. Tape to the end of the 12/3 some 12/2/2 and pull. The 12/3 might feed back to your panel and then you will have the correct wire and do a normal AFCI installation. or 4. A combination of these listed, or other ideas. See? The idea is that you NEED a qualified electrician to help, and home inspectors only evaluate overall work, they don't tell YOU (or who does the work) how to do their job, it is their (or YOU) responsiblity. Good luck, and please tell us what happens in follow-ups. later, tom @ www.WorkAtHomePlans.com Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#26
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
On Sun, 17 Sep 2006 22:09:30 GMT, e michael brandt
wrote: Tom, you are indeed great. i am thrilled to learn that there are actually double pole AFCI's, designed for shared neutrals like mine! Altho pricey, that is the way to go. A simple solution. thanks so much. emichael Like baby pigeons, I've never seen a double pole AFCI, but I guess they exist from practicle need, and people told me so. Good luck, do a quick google search with information of what type of panel you have. Good luck, but I stand by the suggestion you get a licensed/qualified electricion going forward. later, tom @ www.BlankHelp.com Tom The Great wrote: On Sun, 17 Sep 2006 00:50:10 GMT, e michael brandt wrote: I appreciate your comments. Understand though that all this started due to misdirection from the electrical inspector! He was surely correct that AFCIs are required in bedrooms, but failed to put that fact together with the common ground issue. He should either have told me a) I must bite the bullet and re-run a circuit to one room, abandoning one leg of my 12/3 OR acknowledge that the first inspector passed my 220v ganged breaker and left things as they were. Instead he told me to install AFCIs where it seems they can not physically work. emichael This is not a how-to, but to get you familar with how maybe an electrician can help you. 1. Order an expensive double-pole AFCI breaker for your current wiring method and panel. or 2. Pull the orginal wire(12/3) down into a small load center, then installed AFCI's in that load center then feed you bedrooms. or 3. Tape to the end of the 12/3 some 12/2/2 and pull. The 12/3 might feed back to your panel and then you will have the correct wire and do a normal AFCI installation. or 4. A combination of these listed, or other ideas. See? The idea is that you NEED a qualified electrician to help, and home inspectors only evaluate overall work, they don't tell YOU (or who does the work) how to do their job, it is their (or YOU) responsiblity. Good luck, and please tell us what happens in follow-ups. later, tom @ www.WorkAtHomePlans.com Tom The Great wrote: On 16 Sep 2006 14:53:09 -0700, "emichael" wrote: I had run a 12/3 w.g 220v circuit to my attic, and then branched into two 12/2 w.g to run 110v to each of two separate GFCI-protected wall outlets. Originally I had a ganged double pole 20a 220v breaker supplying this paired circuit, and all was well. And the electrical inspector was content. But then a different electrical inspector told me that instead i needed to have AFCI breakers in the breaker box, since these outlets are in bedrooms. So, I bought two 20a AFCIs (I could find no double pole 220v AFCIs and the guy at HomeDepot said with this situation they should have been on two separate breakers anyway.) Well, now the AFCIs trip (both of them simultaneously) whenever there is any load on either circuit. My guess is that because there is a shared neutral, the AFCIs are getting confused. But I am also wondering if the problem might be because there are GFCIs at each outlet. Can GFCIs and AFCIs cooexist okay? If so, then is there a way to use AFCIs in this situation? Thanks for your help. emichaelb No offense, but reading some of the replies, you need to leave this group, and get yourself a licensed and insured electrician, before you kill someone. Or worse, void your home insurance policy! later, tom |
#27
Posted to alt.home.repair
|
|||
|
|||
AFCIs on a 220v circuit, sort of
According to e michael brandt :
Sounds logical to me. Thanks. [That only applies to the NEC. The CEC _requires_ tied breakers on shared neutral circuits, period.] But that's irrelevant. The original issue is NOT whether the breakers are tied together, but because they share a neutral. You _cannot_ feed a shared neutral circuit with two separate AFCI's or GFCI's. It just don't work. Code or not. You either have to split the neutral (run another cable), OR, install the AFCI's AFTER the circuit splits to the bedrooms. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Electrical question: a gfci AND a lighting circuit | Home Repair | |||
7.5hp 3 phase, 440v to 220v. Am I wiring this up right? | Metalworking | |||
20-amp outlet, 15-amp circuit, builder BSing me??? | Home Repair | |||
Electric circuit breaker | Home Repair | |||
Case of the unknown circuit | UK diy |