Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this cures
the problem temporarily. The problem will go away as soon as the sun is
low enough so the box is in shade. Is this a faulty breaker? I'm not an
electrician, so how much would it be $-wise for an electrician to come
out and fix this? Thanks for any help you could give me in this!

--
mndean

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 479
Default Afternoon sun tripping breaker.

mndean wrote:
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this cures
the problem temporarily. The problem will go away as soon as the sun
is low enough so the box is in shade. Is this a faulty breaker? I'm
not an electrician, so how much would it be $-wise for an electrician
to come out and fix this? Thanks for any help you could give me in
this!


I would appear that the breaker may need to be replaced. This is an
easy job, but if you don't feel comfortable doing it yourself, then having
an electrician do it should be a minimal charge. Note: there is a certain
amount of danger in doing this, so if you are not sure, just have it done.

What is that breaker controlling? Is there something on that circuit
like a A/C unit that could be having problems with the heat? There also
could be a problem with your power coming into your home. If the
transformer feeding your home is too small for the current demands of you
and your neighbors, it may need to be replaced as well. But breakers do go
bad and it does sound like that is your real problem.

--
Joseph Meehan

Dia duit


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default Afternoon sun tripping breaker.


"mndean" wrote in message
oups.com...
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this cures
the problem temporarily. The problem will go away as soon as the sun is
low enough so the box is in shade. Is this a faulty breaker? I'm not an
electrician, so how much would it be $-wise for an electrician to come
out and fix this? Thanks for any help you could give me in this!


I'd do two things. First, I'd replace the breaker. Then, I'd shade the
breaker box.

It is a five minute job, but an electrician is going to have to charge you
at least $75 to come out and do it.

Chances are, a handy neighbor or relative knows how and can help.

Determine the brand and size (amps) of the breaker and buy a replacement
If you've never done this, turn off the power at the main breaker, usually
at the top of the box
Remove the breaker box cover
Loosed the screw holding the wire to the breaker
Remove the breaker. Most snap in place, some have a screw on the buss bar.
Snap in the new one, replace the wire, replace the cover and turn on the
main power


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 46
Default Afternoon sun tripping breaker.


"mndean" wrote in message
oups.com...
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this cures
the problem temporarily. The problem will go away as soon as the sun is
low enough so the box is in shade. Is this a faulty breaker? I'm not an
electrician, so how much would it be $-wise for an electrician to come
out and fix this? Thanks for any help you could give me in this!

--
mndean


When you have a short circuit, a bi-metal link inside the breaker heats up
and then deforms thus flipping the switch off.

Given that most breakers use this thermal mode to trip, excessive heat in
the enclosure can derate the breakers trip point but it should not be as
extreme as you describe. That breaker is obviously defective. The ambient
temp rating of the breaker box is at least 125F.




  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Afternoon sun tripping breaker.


Joseph Meehan wrote:
mndean wrote:
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this cures
the problem temporarily. The problem will go away as soon as the sun
is low enough so the box is in shade. Is this a faulty breaker? I'm
not an electrician, so how much would it be $-wise for an electrician
to come out and fix this? Thanks for any help you could give me in
this!


I would appear that the breaker may need to be replaced. This is an
easy job, but if you don't feel comfortable doing it yourself, then having
an electrician do it should be a minimal charge. Note: there is a certain
amount of danger in doing this, so if you are not sure, just have it done.

What is that breaker controlling? Is there something on that circuit
like a A/C unit that could be having problems with the heat? There also
could be a problem with your power coming into your home. If the
transformer feeding your home is too small for the current demands of you
and your neighbors, it may need to be replaced as well. But breakers do go
bad and it does sound like that is your real problem.

--
Joseph Meehan

Dia duit

Thanks for the advice. The breaker does have an 8000btu room A/C unit
on the circuit. The breaker controls a circuit of outlets that are in
three rooms of the house - it's an old house (1939) and the breaker box
was put in around 1976, and this breaker is an original. This problem
only manifests itself in extreme heat (anything over 95), and the temp
the last two days has averaged 110. I am calling an electrician this
week, but I fear that they may be backed up with work (there are folks
around the city with much worse problems than me).

--
mndean



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 479
Default Afternoon sun tripping breaker.

mndean wrote:
Joseph Meehan wrote:
mndean wrote:
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is
put on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this
cures the problem temporarily. The problem will go away as soon as
the sun is low enough so the box is in shade. Is this a faulty
breaker? I'm not an electrician, so how much would it be $-wise for
an electrician to come out and fix this? Thanks for any help you
could give me in this!


I would appear that the breaker may need to be replaced. This
is an easy job, but if you don't feel comfortable doing it yourself,
then having an electrician do it should be a minimal charge. Note:
there is a certain amount of danger in doing this, so if you are not
sure, just have it done.

What is that breaker controlling? Is there something on that
circuit like a A/C unit that could be having problems with the heat?
There also could be a problem with your power coming into your home.
If the transformer feeding your home is too small for the current
demands of you and your neighbors, it may need to be replaced as
well. But breakers do go bad and it does sound like that is your
real problem.

--
Joseph Meehan

Dia duit

Thanks for the advice. The breaker does have an 8000btu room A/C unit
on the circuit. The breaker controls a circuit of outlets that are in
three rooms of the house - it's an old house (1939) and the breaker
box was put in around 1976, and this breaker is an original. This
problem only manifests itself in extreme heat (anything over 95), and
the temp the last two days has averaged 110. I am calling an
electrician this week, but I fear that they may be backed up with
work (there are folks around the city with much worse problems than
me).


My bet is the breaker needs replaced, likely your tech will have one on
his truck or the AC needs to be replaced, less likely.

--
Joseph Meehan

Dia duit


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Afternoon sun tripping breaker.


Joseph Meehan wrote:
mndean wrote:
Joseph Meehan wrote:
mndean wrote:
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is
put on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this
cures the problem temporarily. The problem will go away as soon as
the sun is low enough so the box is in shade. Is this a faulty
breaker? I'm not an electrician, so how much would it be $-wise for
an electrician to come out and fix this? Thanks for any help you
could give me in this!

I would appear that the breaker may need to be replaced. This
is an easy job, but if you don't feel comfortable doing it yourself,
then having an electrician do it should be a minimal charge. Note:
there is a certain amount of danger in doing this, so if you are not
sure, just have it done.

What is that breaker controlling? Is there something on that
circuit like a A/C unit that could be having problems with the heat?
There also could be a problem with your power coming into your home.
If the transformer feeding your home is too small for the current
demands of you and your neighbors, it may need to be replaced as
well. But breakers do go bad and it does sound like that is your
real problem.

--
Joseph Meehan

Dia duit

Thanks for the advice. The breaker does have an 8000btu room A/C unit
on the circuit. The breaker controls a circuit of outlets that are in
three rooms of the house - it's an old house (1939) and the breaker
box was put in around 1976, and this breaker is an original. This
problem only manifests itself in extreme heat (anything over 95), and
the temp the last two days has averaged 110. I am calling an
electrician this week, but I fear that they may be backed up with
work (there are folks around the city with much worse problems than
me).


My bet is the breaker needs replaced, likely your tech will have one on
his truck or the AC needs to be replaced, less likely.

--
Joseph Meehan

Dia duit


You're probably right, the A/C is only 2 years old and is the least
likely one to cause problems. Thanks again.

--
mndean

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,072
Default Afternoon sun tripping breaker.

"Joseph Meehan" wrote in
:

mndean wrote:
Hi Everyone,.
It seems whenever the temperature gets over 100 degrees or so, a
particular breaker in my house will trip if even a slight load is put
on it. The breaker box is being directly hit by the sun in the
afternoons, and it seems that if I attempt to cool the box, this
cures the problem temporarily. The problem will go away as soon as
the sun is low enough so the box is in shade. Is this a faulty
breaker? I'm not an electrician, so how much would it be $-wise for
an electrician to come out and fix this? Thanks for any help you
could give me in this!


I would appear that the breaker may need to be replaced. This is
an
easy job, but if you don't feel comfortable doing it yourself, then
having an electrician do it should be a minimal charge. Note: there
is a certain amount of danger in doing this, so if you are not sure,
just have it done.

What is that breaker controlling? Is there something on that
circuit
like a A/C unit that could be having problems with the heat? There
also could be a problem with your power coming into your home. If the
transformer feeding your home is too small for the current demands of
you and your neighbors, it may need to be replaced as well. But
breakers do go bad and it does sound like that is your real problem.



This is an easy job, ....


True.

Note: there is a certain amount of danger in doing this,


Yea, like hitting a bus bar with the screwdriver, vaporizing it and
blinding yourself.

Cost (if you do not take 200A jolt):
Screwdriver - $5
Electrician to repair fried box, wires, breakers, etc $500+
Medical bills - $4000
Glasses - minus 400/yr. Credit since you don't need being
blind.


Cost (if you do take 200A jolt):

You'll never know.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Breaker Tripping - But Only Half Robert Stinnett Home Repair 7 May 21st 06 05:24 PM
arc fault breaker keeps tripping [email protected] Home Repair 6 January 15th 06 09:43 AM
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? C5Ya Home Repair 10 August 26th 05 07:34 PM
breaker tripping barry martin Home Repair 0 June 23rd 03 08:58 PM


All times are GMT +1. The time now is 09:27 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"