arc fault breaker keeps tripping
hello,
i am trying to install ARC fault circuite breaker but it keeps tripping because the neutral wire that's supposed to connect to the ARC fault breaker is not dedicated but is shared with another non arc-fault circuite breaker. Some one told me that both circuit breakers that share the same neutral wire need to be ARC Fault breaker. Even if this is true, arc fault breakers are expensive so I hope that there's another way to fix this problem. PS I have tried running a neutral wire from the Arc Fault breaker to the neutral bus and of course the breaker still trips. Thank you in advance for your help. |
#2
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
"An appliance plug damaged by impact repeatedly caused tripping of the
AFCI until the problem was discovered. When the appliance cord was replaced, no further tripping of the AFCI occurred. n A room air conditioner that had developed a defect tripped the AFCI. The performance of the AFCI was questioned until the offending appliance was discovered and disconnected. The AFCI continues in service with no further tripping. n An AFCI installed in a new building tripped repeatedly until damage caused by a nail through insulation was discovered and corrected. n An AFCI installed as a retrofit in an older building tripped as soon as it was turned on. The installing electrician found the problem with extensive evidence of arcing in an old lighting fixture. n Another damaged lamp with line-to-ground arcing was found when an AFCI was installed in an existing circuit. The AFCI tripped when the circuit was first energized after the installation. n An AFCI tripped when retrofitted into an existing circuit. Examination of the circuit disclosed that wire insulation had burnt back exposing bare conductors near their connection to a receptacle. The exposed wires had been arcing through the charred insulation. It appeared that heat from a loose connection at the receptacle had caused the wires to burn back. As you might guess from that list, the greatest number of fires from electrical causes is in homes ten years old and older where changes have been made to electrical circuits by various owners and where insulation is deteriorating with age, use and misuse. However, fires from electrical arcs are recorded for residences of all ages. Besides, all homes become older homes. If the protection is not present before they age, they will remain unprotected as they age." full story at: http://www.iaei.org/magazine/03_a/ma...gregmanche.htm |
#3
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
|
#4
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
How does the AFCI detect arcing if the current is so small (smaller than
the instant trip level of a regular breaker)? |
#5
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
mcha wrote:
i am trying to install ARC fault circuite breaker but it keeps tripping because the neutral wire that's supposed to connect to the ARC fault breaker is not dedicated but is shared with another non arc-fault circuite breaker. Some one told me that both circuit breakers that share the same neutral wire need to be ARC Fault breaker. Even if this is true, arc fault breakers are expensive so I hope that there's another way to fix this problem. Short of discontinuing use of one of the circuits, or running a new circuit, you need a double pole AFCI breaker. |
#6
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
Steve Kraus ) said...
How does the AFCI detect arcing if the current is so small (smaller than the instant trip level of a regular breaker)? Arcing can occur between the hot and the neutral or between the hot and ground. Arcs involve short bursts of high current, and it is this that is detected for hot to neutral arcs. This would be very difficult to detect for small levels of current, but true arcs are not small. HOWEVER, the design of arc fault breakers take the approach that instead of actually detecting arc current between hot and ground, ANY current between hot and ground is BAD. By definition, current in the hot that does not return through the neutral is a ground fault, so by using ground fault detection, the breaker can trip if current between the hot and neutral exceeds the GFCI rating. "Standard" GFCI protection that is required around sinks for instance must be capable of tripping when this current reaches about 5-6 mA. Many AFCI breakers detect and trip on ground faults once they exceed 30 mA. Any imbalance in the current in the hot and the neutral that is greater than 30 mA will cause it to trip because of this ground fault. So, getting back to the original poster's issue: if the neutral were shared between two circits on opposite hot legs, then anytime there is some load on the other circuit, the current in the neutral and the hot on the AFCI breaker will NOT be equal (or, at least not within 30 mA) and the breaker will trip. -- Calvin Henry-Cotnam "Never ascribe to malice what can equally be explained by incompetence." - Napoleon ------------------------------------------------------------------------- NOTE: if replying by email, remove "remove." and ".invalid" |
#7
Posted to alt.home.repair
|
|||
|
|||
arc fault breaker keeps tripping
If it's TRIPPING, it's on drugs. Take it to a hospital for rehab....
On a serious note, the common neutral may be the cause. Shut off the other circuit that shares that neutral and see if it still trips. If this stops the tripping, run separate neutrals. On 13 Jan 2006 15:12:20 -0800, wrote: hello, i am trying to install ARC fault circuite breaker but it keeps tripping because the neutral wire that's supposed to connect to the ARC fault breaker is not dedicated but is shared with another non arc-fault circuite breaker. Some one told me that both circuit breakers that share the same neutral wire need to be ARC Fault breaker. Even if this is true, arc fault breakers are expensive so I hope that there's another way to fix this problem. PS I have tried running a neutral wire from the Arc Fault breaker to the neutral bus and of course the breaker still trips. Thank you in advance for your help. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||