i am trying to install ARC fault circuite breaker but it keeps tripping
because the neutral wire that's supposed to connect to the ARC fault
breaker is not dedicated but is shared with another non arc-fault
circuite breaker.

Some one told me that both circuit breakers that share the same neutral
wire need to be ARC Fault breaker. Even if this is true, arc fault
breakers are expensive so I hope that there's another way to fix this
problem.

PS I have tried running a neutral wire from the Arc Fault breaker to
the neutral bus and of course the breaker still trips.


Thank you in advance for your help.

  #2   Report Post  
Posted to alt.home.repair
buffalobill
 
Posts: n/a
Default arc fault breaker keeps tripping

"An appliance plug damaged by impact repeatedly caused tripping of the
AFCI until the problem was discovered. When the appliance cord was
replaced, no further tripping of the AFCI occurred.

n A room air conditioner that had developed a defect tripped the AFCI.
The performance of the AFCI was questioned until the offending
appliance was discovered and disconnected. The AFCI continues in
service with no further tripping.

n An AFCI installed in a new building tripped repeatedly until damage
caused by a nail through insulation was discovered and corrected.

n An AFCI installed as a retrofit in an older building tripped as soon
as it was turned on. The installing electrician found the problem with
extensive evidence of arcing in an old lighting fixture.

n Another damaged lamp with line-to-ground arcing was found when an
AFCI was installed in an existing circuit. The AFCI tripped when the
circuit was first energized after the installation.

n An AFCI tripped when retrofitted into an existing circuit.
Examination of the circuit disclosed that wire insulation had burnt
back exposing bare conductors near their connection to a receptacle.
The exposed wires had been arcing through the charred insulation. It
appeared that heat from a loose connection at the receptacle had caused
the wires to burn back.

As you might guess from that list, the greatest number of fires from
electrical causes is in homes ten years old and older where changes
have been made to electrical circuits by various owners and where
insulation is deteriorating with age, use and misuse. However, fires
from electrical arcs are recorded for residences of all ages. Besides,
all homes become older homes. If the protection is not present before
they age, they will remain unprotected as they age."
full story at:
http://www.iaei.org/magazine/03_a/ma...gregmanche.htm

  #4   Report Post  
Posted to alt.home.repair
Steve Kraus
 
Posts: n/a
Default arc fault breaker keeps tripping

How does the AFCI detect arcing if the current is so small (smaller than
the instant trip level of a regular breaker)?
  #5   Report Post  
Posted to alt.home.repair
volts500
 
Posts: n/a
Default arc fault breaker keeps tripping

mcha wrote:

i am trying to install ARC fault circuite breaker but it keeps tripping
because the neutral wire that's supposed to connect to the ARC fault
breaker is not dedicated but is shared with another non arc-fault
circuite breaker.



Some one told me that both circuit breakers that share the same neutral
wire need to be ARC Fault breaker. Even if this is true, arc fault
breakers are expensive so I hope that there's another way to fix this
problem.


Short of discontinuing use of one of the circuits, or running a new
circuit, you need a double pole AFCI breaker.



  #6   Report Post  
Posted to alt.home.repair
Calvin Henry-Cotnam
 
Posts: n/a
Default arc fault breaker keeps tripping

Steve Kraus ) said...

How does the AFCI detect arcing if the current is so small (smaller than
the instant trip level of a regular breaker)?


Arcing can occur between the hot and the neutral or between the hot and
ground. Arcs involve short bursts of high current, and it is this that is
detected for hot to neutral arcs. This would be very difficult to detect
for small levels of current, but true arcs are not small.

HOWEVER, the design of arc fault breakers take the approach that instead
of actually detecting arc current between hot and ground, ANY current
between hot and ground is BAD. By definition, current in the hot that
does not return through the neutral is a ground fault, so by using ground
fault detection, the breaker can trip if current between the hot and
neutral exceeds the GFCI rating.

"Standard" GFCI protection that is required around sinks for instance must
be capable of tripping when this current reaches about 5-6 mA. Many AFCI
breakers detect and trip on ground faults once they exceed 30 mA. Any
imbalance in the current in the hot and the neutral that is greater than
30 mA will cause it to trip because of this ground fault.


So, getting back to the original poster's issue: if the neutral were shared
between two circits on opposite hot legs, then anytime there is some load
on the other circuit, the current in the neutral and the hot on the AFCI
breaker will NOT be equal (or, at least not within 30 mA) and the breaker
will trip.


--
Calvin Henry-Cotnam
"Never ascribe to malice what can equally be explained by incompetence."
- Napoleon
-------------------------------------------------------------------------
NOTE: if replying by email, remove "remove." and ".invalid"

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Circuit Breaker Tripping Bill Home Repair 5 January 30th 06 11:11 PM
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? C5Ya Home Repair 10 August 26th 05 07:34 PM
Hot tub Breaker tripping on 120V connection, 240V works fine Zoner Home Repair 14 August 17th 05 03:22 PM
Tripping Breaker jozep7075 Home Ownership 5 January 14th 05 11:50 PM
breaker tripping barry martin Home Repair 0 June 23rd 03 08:58 PM


All times are GMT +1. The time now is 01:46 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"