Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne

  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Simple question on design of electrical subpanels

Yes, that's fine. On a sub panel you don't want the neutral buss to be
bonded to the enclosure


"Wayne Whitney" wrote in message
...
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Simple question on design of electrical subpanels

On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne

  #4   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Simple question on design of electrical subpanels

If you have metallic cables or conduits, their connection to the chassis is
their path to ground


"Wayne Whitney" wrote in message
...
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 100
Default Simple question on design of electrical subpanels

Properly wired "subpanel":

http://www.home-inspect.com/email-images/jan04image.gif

Michael Thomas
Paragon Home Inspections, LLC
Chicago, IL
mdtATparagoninspectsDOT com
eight47-475-5668



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 674
Default Simple question on design of electrical subpanels


"Wayne Whitney" wrote in message
...
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne

The incoming ground wire should terminate at the ground bus, not at the
cabinet itself. Grounding path for the cabinet should be
cabinet-to-bus-to-incoming grounding conductor so the cabinet is not part of
other ground fault current paths.

Don Young


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 118
Default Simple question on design of electrical subpanels

Wayne Whitney wrote:
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne


It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway. If more than one Grounding buss bar is
installed they should be bonded to each other by running a conductor
that is sized for the largest Over Current Protective Device supplying
power to that panel between the buss bars.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 48
Default Simple question on design of electrical subpanels


Wayne Whitney wrote:
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne


Think about this....if that metal enclosure or any metal conduit is not
grounded.....what do you think is going to happen in the event that a
hot wire gets a nick in it...or it comes loose from its
connector....you dont ever want to have that enclosure or any metal
conduit in a situation where it can be hot. Grounding the enclosure and
any metal conduit or raceways makes perfect sense.


Ive had the fire knocked out of me before by a 4 by 4 junction box
before....hot wire loose touching the box.....box wasnt
grounded........thank goodness it wasnt a damp area.

~:

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Simple question on design of electrical subpanels

On 2006-07-14, RBM wrote:

If you have metallic cables or conduits, their connection to the chassis is
their path to ground


Hmm, good point--it is permissible to use some conduit systems as the
EGC in the branch circuits, so then subpanel chassis is part of the
fault current path for those circuits. However, while this may meet
the NEC, I would not consider this to be the best practice. So
perhaps that is the answer to my original question.

Cheers, Wayne



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Simple question on design of electrical subpanels

On 2006-07-15, Tom Horne, Electrician wrote:

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.


It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway.


So it sounds like the setup I describe is NEC compliant but not best
practice? Another poster pointed out that if any branch circuits are
run in metallic conduit and use the conduit as the EGC, then the panel
chassis is part of the fault current path anyway. However, I've run a
separate EGC for the circuits I've run in EMT.

The subpanel I'm using, the Square D QO132L125G, comes with a ground
bar that has no terminals for 1/0 wire and with a single lug bolted to
the chassis for the feeder ground wire. So it seems the
manufacturer's intention is to the chasis as a ground backplane.
Perhaps a better solution would be to replace the single lug with a
double lug (terminology?) and to run an appropriately sized jumper
wire directly to the ground bar?

If more than one Grounding buss bar is installed they should be
bonded to each other by running a conductor that is sized for the
largest Over Current Protective Device supplying power to that panel
between the buss bars.


Do you mean the largest size OCPD for circuits supplied _from_ that
panel, or the size of the feeder circuit OCPD supplying power _to_
that panel? Seems like it should be the former.

Cheers, Wayne

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default Simple question on design of electrical subpanels

Wayne Whitney wrote:
On 2006-07-15, Tom Horne, Electrician wrote:

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway.


So it sounds like the setup I describe is NEC compliant but not best
practice? Another poster pointed out that if any branch circuits are
run in metallic conduit and use the conduit as the EGC, then the panel
chassis is part of the fault current path anyway. However, I've run a
separate EGC for the circuits I've run in EMT.

The subpanel I'm using, the Square D QO132L125G, comes with a ground
bar that has no terminals for 1/0 wire and with a single lug bolted to
the chassis for the feeder ground wire. So it seems the
manufacturer's intention is to the chasis as a ground backplane.
Perhaps a better solution would be to replace the single lug with a
double lug (terminology?) and to run an appropriately sized jumper
wire directly to the ground bar?

If more than one Grounding buss bar is installed they should be
bonded to each other by running a conductor that is sized for the
largest Over Current Protective Device supplying power to that panel
between the buss bars.


Do you mean the largest size OCPD for circuits supplied _from_ that
panel, or the size of the feeder circuit OCPD supplying power _to_
that panel? Seems like it should be the former.

Cheers, Wayne


There are add on lugs available for Square D ground buss bars for many
sizes of wire. Adding one of those to the existing buss bar would be an
elegant solution. Your right I should have said "the largest size OCPD
for circuits supplied _from_ that panel."
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 100
Default Simple question on design of electrical subpanels

Wayne Whitney wrote:
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne


Here 'ya go:

http://ecmweb.com/mag/electric_groun...ing/index.html

Just don't blame me 'cause you just lost half a day - I have to re-read
the whole thing twice a year to keep it all stright myself grin.

Michael Thomas
Paragon Home Inspection, LLC
Chicago, IL
mdtATparagoninspectsDOTcom
eight47-475-5668

  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Simple question on design of electrical subpanels

On 2006-07-16, MDT at Paragon Home Inspections, LLC
wrote:

Here 'ya go: http://ecmweb.com/mag/electric_grounding_vs_bonding/index.html
Just don't blame me 'cause you just lost half a day - I have to re-read
the whole thing twice a year to keep it all stright myself grin.


Thanks, I've actually read those articles once upon a time, at least
the residential parts. I see that Figure 2 of that article actually
shows the chassis of a subpanel as part of an "effective ground-fault
path". So this reinforces the idea that this is NEC compliant,
although perhaps not best practice.

Cheers, Wayne

  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Simple question on design of electrical subpanels

On 2006-07-16, Thomas D. Horne, FF EMT wrote:

There are add on lugs available for Square D ground buss bars for
many sizes of wire. Adding one of those to the existing buss bar
would be an elegant solution.


Ah, thanks for the pointer, that's a good solution. I think I may
have one of those lying around, I didn't understand its purpose when I
received it.

Cheers, Wayne.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Simple Battery question ? Ian Electronics 3 November 25th 05 05:19 PM
Kitchen Design 3D programs, Interior 3D design, Landscape design programs, futa UK diy 0 November 16th 05 10:20 PM
CAX, CAD, CAM, CAE, electronics, EDA, LSI, PCB, FPGA, VHDL, & Other Design CDs ::::::: , updated 03/Feb/2005 futa Metalworking 0 February 5th 05 06:13 PM
Simple question regarding Ceiling tiles and sound? lbbs UK diy 5 March 26th 04 01:36 AM


All times are GMT +1. The time now is 01:29 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"