Wayne Whitney July 14th 06 10:35 PM

Simple question on design of electrical subpanels
 
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne


RBM July 15th 06 12:05 AM

Simple question on design of electrical subpanels
 
Yes, that's fine. On a sub panel you don't want the neutral buss to be
bonded to the enclosure


"Wayne Whitney" wrote in message
...
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne




Wayne Whitney July 15th 06 12:08 AM

Simple question on design of electrical subpanels
 
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne


RBM July 15th 06 12:41 AM

Simple question on design of electrical subpanels
 
If you have metallic cables or conduits, their connection to the chassis is
their path to ground


"Wayne Whitney" wrote in message
...
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne




MDT at Paragon Home Inspections, LLC July 15th 06 01:54 AM

Simple question on design of electrical subpanels
 
Properly wired "subpanel":

http://www.home-inspect.com/email-images/jan04image.gif

Michael Thomas
Paragon Home Inspections, LLC
Chicago, IL
mdtATparagoninspectsDOT com
eight47-475-5668


Don Young July 15th 06 03:48 AM

Simple question on design of electrical subpanels
 

"Wayne Whitney" wrote in message
...
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne

The incoming ground wire should terminate at the ground bus, not at the
cabinet itself. Grounding path for the cabinet should be
cabinet-to-bus-to-incoming grounding conductor so the cabinet is not part of
other ground fault current paths.

Don Young



Tom Horne, Electrician July 15th 06 04:35 AM

Simple question on design of electrical subpanels
 
Wayne Whitney wrote:
Hello,

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

Thanks, Wayne


It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway. If more than one Grounding buss bar is
installed they should be bonded to each other by running a conductor
that is sized for the largest Over Current Protective Device supplying
power to that panel between the buss bars.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison

[email protected] July 15th 06 08:42 AM

Simple question on design of electrical subpanels
 

Wayne Whitney wrote:
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne


Think about this....if that metal enclosure or any metal conduit is not
grounded.....what do you think is going to happen in the event that a
hot wire gets a nick in it...or it comes loose from its
connector....you dont ever want to have that enclosure or any metal
conduit in a situation where it can be hot. Grounding the enclosure and
any metal conduit or raceways makes perfect sense.


Ive had the fire knocked out of me before by a 4 by 4 junction box
before....hot wire loose touching the box.....box wasnt
grounded........thank goodness it wasnt a damp area.

~:


Wayne Whitney July 16th 06 02:14 AM

Simple question on design of electrical subpanels
 
On 2006-07-15, wrote:

Think about this....if that metal enclosure or any metal conduit is not
grounded....


I think my original question must not have been clear, of course you
have to ground the subpanel chassis. The question is whether it is OK
to use the subpanel chassis as part of the fault current path for the
circuit served by the subpanel.

Wayne

Wayne Whitney July 16th 06 02:18 AM

Simple question on design of electrical subpanels
 
On 2006-07-14, RBM wrote:

If you have metallic cables or conduits, their connection to the chassis is
their path to ground


Hmm, good point--it is permissible to use some conduit systems as the
EGC in the branch circuits, so then subpanel chassis is part of the
fault current path for those circuits. However, while this may meet
the NEC, I would not consider this to be the best practice. So
perhaps that is the answer to my original question.

Cheers, Wayne


Wayne Whitney July 16th 06 02:28 AM

Simple question on design of electrical subpanels
 
On 2006-07-15, Tom Horne, Electrician wrote:

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.


It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway.


So it sounds like the setup I describe is NEC compliant but not best
practice? Another poster pointed out that if any branch circuits are
run in metallic conduit and use the conduit as the EGC, then the panel
chassis is part of the fault current path anyway. However, I've run a
separate EGC for the circuits I've run in EMT.

The subpanel I'm using, the Square D QO132L125G, comes with a ground
bar that has no terminals for 1/0 wire and with a single lug bolted to
the chassis for the feeder ground wire. So it seems the
manufacturer's intention is to the chasis as a ground backplane.
Perhaps a better solution would be to replace the single lug with a
double lug (terminology?) and to run an appropriately sized jumper
wire directly to the ground bar?

If more than one Grounding buss bar is installed they should be
bonded to each other by running a conductor that is sized for the
largest Over Current Protective Device supplying power to that panel
between the buss bars.


Do you mean the largest size OCPD for circuits supplied _from_ that
panel, or the size of the feeder circuit OCPD supplying power _to_
that panel? Seems like it should be the former.

Cheers, Wayne


Thomas D. Horne, FF EMT July 16th 06 03:04 AM

Simple question on design of electrical subpanels
 
Wayne Whitney wrote:
On 2006-07-15, Tom Horne, Electrician wrote:

Is it standard for a residential electrical subpanel to use its
chassis as a ground backplane? I.e. the ground from the incoming
4-wire feed terminates at a lug bolted to the back of the panel, and
the ground bar is also just bolted to the back of the panel.

It would be better practice to have all Equipment Grounding Conductors
terminate to the Grounding buss bar so as to avoid using the cabinet as
a fault current pathway.


So it sounds like the setup I describe is NEC compliant but not best
practice? Another poster pointed out that if any branch circuits are
run in metallic conduit and use the conduit as the EGC, then the panel
chassis is part of the fault current path anyway. However, I've run a
separate EGC for the circuits I've run in EMT.

The subpanel I'm using, the Square D QO132L125G, comes with a ground
bar that has no terminals for 1/0 wire and with a single lug bolted to
the chassis for the feeder ground wire. So it seems the
manufacturer's intention is to the chasis as a ground backplane.
Perhaps a better solution would be to replace the single lug with a
double lug (terminology?) and to run an appropriately sized jumper
wire directly to the ground bar?

If more than one Grounding buss bar is installed they should be
bonded to each other by running a conductor that is sized for the
largest Over Current Protective Device supplying power to that panel
between the buss bars.


Do you mean the largest size OCPD for circuits supplied _from_ that
panel, or the size of the feeder circuit OCPD supplying power _to_
that panel? Seems like it should be the former.

Cheers, Wayne


There are add on lugs available for Square D ground buss bars for many
sizes of wire. Adding one of those to the existing buss bar would be an
elegant solution. Your right I should have said "the largest size OCPD
for circuits supplied _from_ that panel."
--
Tom Horne

Well we aren't no thin blue heroes and yet we aren't no blackguards to.
We're just working men and woman most remarkable like you.

MDT at Paragon Home Inspections, LLC July 16th 06 06:24 PM

Simple question on design of electrical subpanels
 
Wayne Whitney wrote:
On 2006-07-14, RBM wrote:

Yes, that's fine. On a sub panel you don't want the neutral buss to
be bonded to the enclosure.


Thanks, I understand the part about the neutral buss being kept
separate from the ground buss in subpanels. And obviously the
subpanel chassis needs to be tied to the equipment ground. I was just
surprised to the subpanel chassis as part of the fault current path
for all the circuits served by the subpanel. That's fine?

Thanks, Wayne


Here 'ya go:

http://ecmweb.com/mag/electric_groun...ing/index.html

Just don't blame me 'cause you just lost half a day - I have to re-read
the whole thing twice a year to keep it all stright myself grin.

Michael Thomas
Paragon Home Inspection, LLC
Chicago, IL
mdtATparagoninspectsDOTcom
eight47-475-5668


Wayne Whitney July 16th 06 06:48 PM

Simple question on design of electrical subpanels
 
On 2006-07-16, MDT at Paragon Home Inspections, LLC
wrote:

Here 'ya go: http://ecmweb.com/mag/electric_grounding_vs_bonding/index.html
Just don't blame me 'cause you just lost half a day - I have to re-read
the whole thing twice a year to keep it all stright myself grin.


Thanks, I've actually read those articles once upon a time, at least
the residential parts. I see that Figure 2 of that article actually
shows the chassis of a subpanel as part of an "effective ground-fault
path". So this reinforces the idea that this is NEC compliant,
although perhaps not best practice.

Cheers, Wayne


Wayne Whitney July 16th 06 06:49 PM

Simple question on design of electrical subpanels
 
On 2006-07-16, Thomas D. Horne, FF EMT wrote:

There are add on lugs available for Square D ground buss bars for
many sizes of wire. Adding one of those to the existing buss bar
would be an elegant solution.


Ah, thanks for the pointer, that's a good solution. I think I may
have one of those lying around, I didn't understand its purpose when I
received it.

Cheers, Wayne.