The A/C at my lake house stopped working and I had a bad repair call.
The tech decided that the circuit board was not working and physically
damaged it when he took it out. When I checked out the system I
determined that the circuit breaker was the real problem. Any idiot
with a volt/ohm meter could see the breaker was bad.

I got a new circuit board and installed it myself using the wiring
diagram - it was very straightforward, and I replaced the bad
breaker. When I turned the system on it worked fine, except I could
not turn it off at the thermostat.

After some investigation, I found that the thermostat had been
completely re-wired, the red on the green, the green on the red and
other problems. I suspect that was the result of a visitor to my lake
place desperately trying to get the system working.

After I rewired the thermostat, the system works properly in terms of
the low voltage controls sending out the right voltage on a specific
setting, for example the fan comes on when the thermostat is set to "
fan on". When you set the compressor to start by moving the control
level on the thermostat below the actual temperature, the 24 volt
control to the starter relay on the thermostat is activated - but the
relay does not close. I have replaced the relay, but that did not
solve the problem. I would expect that when the 24 volts gets to the
relay terminal, the relay should close, even if it is not hooked up to
the compressor, but that does not happen. I have the relay wired
properly. I have a Coleman Air handler and a Trane 2.5 ton compressor.

Any help would be appreciated.

John Funderburgh

  #3   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default A/C Compressor Relay will not close

You seem confident that you've wired everything properly. If so, you should
get 24VAC at the contactor when the stat is set properly. If you are getting
24 VAC at the contactor, and it doesn't pull in, the coil is NG. If you're
not getting 24VAC at the contactor, check the connections at the air
handler, the common and Y terminals may be incorrectly wired. Also check for
any time delay circuits built into the system



wrote in message
oups.com...
The A/C at my lake house stopped working and I had a bad repair call.
The tech decided that the circuit board was not working and physically
damaged it when he took it out. When I checked out the system I
determined that the circuit breaker was the real problem. Any idiot
with a volt/ohm meter could see the breaker was bad.

I got a new circuit board and installed it myself using the wiring
diagram - it was very straightforward, and I replaced the bad
breaker. When I turned the system on it worked fine, except I could
not turn it off at the thermostat.

After some investigation, I found that the thermostat had been
completely re-wired, the red on the green, the green on the red and
other problems. I suspect that was the result of a visitor to my lake
place desperately trying to get the system working.

After I rewired the thermostat, the system works properly in terms of
the low voltage controls sending out the right voltage on a specific
setting, for example the fan comes on when the thermostat is set to "
fan on". When you set the compressor to start by moving the control
level on the thermostat below the actual temperature, the 24 volt
control to the starter relay on the thermostat is activated - but the
relay does not close. I have replaced the relay, but that did not
solve the problem. I would expect that when the 24 volts gets to the
relay terminal, the relay should close, even if it is not hooked up to
the compressor, but that does not happen. I have the relay wired
properly. I have a Coleman Air handler and a Trane 2.5 ton compressor.

Any help would be appreciated.

John Funderburgh



  #4   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default A/C Compressor Relay will not close

Yes, I have 24 volts at the relay, and the voltage is activated
properly with the thermostat settings. When I manually operate the
relay (push in the contacts) the copressor starts properly.

Even of the coil is out, shouldn't the relay close when the 24volts
hits it?

  #5   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default A/C Compressor Relay will not close

I don't know what you mean, by if the coil is out. If you mean the contactor
is out, yes, it should pull in if you apply 24 vac to the coil terminals.
This is of course assuming you've got a contactor with 24 volt coil and not
240 volt or 120 volt



wrote in message
ups.com...
Yes, I have 24 volts at the relay, and the voltage is activated
properly with the thermostat settings. When I manually operate the
relay (push in the contacts) the copressor starts properly.

Even of the coil is out, shouldn't the relay close when the 24volts
hits it?





  #8   Report Post  
Posted to alt.home.repair
CJT
 
Posts: n/a
Default A/C Compressor Relay will not close

RBM wrote:

This is a replacement


Are you sure you have the correct one, properly wired up?


"CJT" wrote in message
...

wrote:


Yes, I have 24 volts at the relay, and the voltage is activated
properly with the thermostat settings. When I manually operate the
relay (push in the contacts) the copressor starts properly.

Even of the coil is out, shouldn't the relay close when the 24volts
hits it?


It sounds like you need a new relay.

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .






--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #10   Report Post  
Posted to alt.home.repair
Stormin Mormon
 
Posts: n/a
Default A/C Compressor Relay will not close

Is it a 24 VAC coil on the relay? Or did you buy a 110 VAC coil?

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Travis Jordan" wrote in message
...
wrote:
After I rewired the thermostat, the system works properly in terms

of
the low voltage controls sending out the right voltage on a specific
setting, for example the fan comes on when the thermostat is set to

"
fan on". When you set the compressor to start by moving the control
level on the thermostat below the actual temperature, the 24 volt
control to the starter relay on the thermostat is activated - but

the
relay does not close.


Got 24VAC at the relay terminals?





  #11   Report Post  
Posted to alt.home.repair
Stormin Mormon
 
Posts: n/a
Default A/C Compressor Relay will not close

Should.... if it's a 24 volt coil. And if you've wired it correctly.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

wrote in message
ups.com...
Yes, I have 24 volts at the relay, and the voltage is activated
properly with the thermostat settings. When I manually operate the
relay (push in the contacts) the copressor starts properly.

Even of the coil is out, shouldn't the relay close when the 24volts
hits it?


  #12   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default A/C Compressor Relay will not close

Yes, it is strange. I have the correct relay, it is 24v, it is
identical to the one that was in the system prior to the service call.
I have 24vac coming to it, and the thermostat is properly controlling
this voltage flow. I can measure the voltage on the control wires
disconnected from the relay and it reads about 25vac. When I connect
the wires to the relay (and yes, I am confident I am wiring the relay
correctly, I made careful note of the hook up before I changed out the
relay) the relay does not close and when I check the voltage it reads
about half a volt.

BTW I really appreciate al the help.

John

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chamberlain Garage Door Won't Close Ed Home Repair 9 October 20th 14 09:06 PM
The Mysteries of Close Captioning Ron Electronics Repair 10 October 12th 05 08:02 PM
How close to the edge can dog-holes be located? BillyBob Woodworking 13 April 30th 05 02:09 PM
Sears Craftman garage door opener won't close anymore Duane Electronics Repair 2 June 15th 04 01:57 AM
How close can electrical sockets be to sinks ? LOZ34 UK diy 4 August 24th 03 11:17 AM


All times are GMT +1. The time now is 01:11 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"