The A/C at my lake house stopped working and I had a bad repair call.
The tech decided that the circuit board was not working and physically damaged it when he took it out. When I checked out the system I determined that the circuit breaker was the real problem. Any idiot with a volt/ohm meter could see the breaker was bad. I got a new circuit board and installed it myself using the wiring diagram - it was very straightforward, and I replaced the bad breaker. When I turned the system on it worked fine, except I could not turn it off at the thermostat. After some investigation, I found that the thermostat had been completely re-wired, the red on the green, the green on the red and other problems. I suspect that was the result of a visitor to my lake place desperately trying to get the system working. After I rewired the thermostat, the system works properly in terms of the low voltage controls sending out the right voltage on a specific setting, for example the fan comes on when the thermostat is set to " fan on". When you set the compressor to start by moving the control level on the thermostat below the actual temperature, the 24 volt control to the starter relay on the thermostat is activated - but the relay does not close. I have replaced the relay, but that did not solve the problem. I would expect that when the 24 volts gets to the relay terminal, the relay should close, even if it is not hooked up to the compressor, but that does not happen. I have the relay wired properly. I have a Coleman Air handler and a Trane 2.5 ton compressor. Any help would be appreciated. John Funderburgh |
#2
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
|
#3
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
You seem confident that you've wired everything properly. If so, you should
get 24VAC at the contactor when the stat is set properly. If you are getting 24 VAC at the contactor, and it doesn't pull in, the coil is NG. If you're not getting 24VAC at the contactor, check the connections at the air handler, the common and Y terminals may be incorrectly wired. Also check for any time delay circuits built into the system wrote in message oups.com... The A/C at my lake house stopped working and I had a bad repair call. The tech decided that the circuit board was not working and physically damaged it when he took it out. When I checked out the system I determined that the circuit breaker was the real problem. Any idiot with a volt/ohm meter could see the breaker was bad. I got a new circuit board and installed it myself using the wiring diagram - it was very straightforward, and I replaced the bad breaker. When I turned the system on it worked fine, except I could not turn it off at the thermostat. After some investigation, I found that the thermostat had been completely re-wired, the red on the green, the green on the red and other problems. I suspect that was the result of a visitor to my lake place desperately trying to get the system working. After I rewired the thermostat, the system works properly in terms of the low voltage controls sending out the right voltage on a specific setting, for example the fan comes on when the thermostat is set to " fan on". When you set the compressor to start by moving the control level on the thermostat below the actual temperature, the 24 volt control to the starter relay on the thermostat is activated - but the relay does not close. I have replaced the relay, but that did not solve the problem. I would expect that when the 24 volts gets to the relay terminal, the relay should close, even if it is not hooked up to the compressor, but that does not happen. I have the relay wired properly. I have a Coleman Air handler and a Trane 2.5 ton compressor. Any help would be appreciated. John Funderburgh |
#4
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
Yes, I have 24 volts at the relay, and the voltage is activated
properly with the thermostat settings. When I manually operate the relay (push in the contacts) the copressor starts properly. Even of the coil is out, shouldn't the relay close when the 24volts hits it? |
#5
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
I don't know what you mean, by if the coil is out. If you mean the contactor
is out, yes, it should pull in if you apply 24 vac to the coil terminals. This is of course assuming you've got a contactor with 24 volt coil and not 240 volt or 120 volt wrote in message ups.com... Yes, I have 24 volts at the relay, and the voltage is activated properly with the thermostat settings. When I manually operate the relay (push in the contacts) the copressor starts properly. Even of the coil is out, shouldn't the relay close when the 24volts hits it? |
#6
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
|
#7
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
This is a replacement
"CJT" wrote in message ... wrote: Yes, I have 24 volts at the relay, and the voltage is activated properly with the thermostat settings. When I manually operate the relay (push in the contacts) the copressor starts properly. Even of the coil is out, shouldn't the relay close when the 24volts hits it? It sounds like you need a new relay. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#8
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
RBM wrote:
This is a replacement Are you sure you have the correct one, properly wired up? "CJT" wrote in message ... wrote: Yes, I have 24 volts at the relay, and the voltage is activated properly with the thermostat settings. When I manually operate the relay (push in the contacts) the copressor starts properly. Even of the coil is out, shouldn't the relay close when the 24volts hits it? It sounds like you need a new relay. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#9
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
|
#10
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
Is it a 24 VAC coil on the relay? Or did you buy a 110 VAC coil?
-- Christopher A. Young You can't shout down a troll. You have to starve them. .. "Travis Jordan" wrote in message ... wrote: After I rewired the thermostat, the system works properly in terms of the low voltage controls sending out the right voltage on a specific setting, for example the fan comes on when the thermostat is set to " fan on". When you set the compressor to start by moving the control level on the thermostat below the actual temperature, the 24 volt control to the starter relay on the thermostat is activated - but the relay does not close. Got 24VAC at the relay terminals? |
#11
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
Should.... if it's a 24 volt coil. And if you've wired it correctly.
-- Christopher A. Young You can't shout down a troll. You have to starve them. .. wrote in message ups.com... Yes, I have 24 volts at the relay, and the voltage is activated properly with the thermostat settings. When I manually operate the relay (push in the contacts) the copressor starts properly. Even of the coil is out, shouldn't the relay close when the 24volts hits it? |
#12
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
Yes, it is strange. I have the correct relay, it is 24v, it is
identical to the one that was in the system prior to the service call. I have 24vac coming to it, and the thermostat is properly controlling this voltage flow. I can measure the voltage on the control wires disconnected from the relay and it reads about 25vac. When I connect the wires to the relay (and yes, I am confident I am wiring the relay correctly, I made careful note of the hook up before I changed out the relay) the relay does not close and when I check the voltage it reads about half a volt. BTW I really appreciate al the help. John |
#13
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
|
#14
Posted to alt.home.repair
|
|||
|
|||
A/C Compressor Relay will not close
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Chamberlain Garage Door Won't Close | Home Repair | |||
The Mysteries of Close Captioning | Electronics Repair | |||
How close to the edge can dog-holes be located? | Woodworking | |||
Sears Craftman garage door opener won't close anymore | Electronics Repair | |||
How close can electrical sockets be to sinks ? | UK diy |