  #1   Report Post  
Posted to alt.home.repair
sglaab
 
Posts: n/a
Default HELP me Split 240 to 120


OK so I think this can be done quite simply I just need to be positive.
I have an unused 240V stove plug (the 3 pronged triangle shaped) I
would like to use this power to hook up a home vacuum system. I want
to split the 240V line into a 120V outlet for the vacuum itself and the
other line for the outlets at each conection (one on each floor) for the
power for the tools & attachments. I believe I can connect the red
white to the outlet for the vacuum in a junction box and the white and
black to a new wire out to the outlets at each connection. OK so far?

The double breaker in the box says 40 on both connected breakers. Are
they both 20A then? Can I leave this together and use this breaker?
Am I OK here. Thanks for the help.


--
sglaab
------------------------------------------------------------------------
sglaab's Profile: http://www.HomeOutfit.com/member.php?userid=277
View this thread: http://www.HomeOutfit.com/showthread.php?t=67382

  #2   Report Post  
Posted to alt.home.repair
RBM
 
Posts: n/a
Default HELP me Split 240 to 120

Your circuit breaker is 40 amps per leg. If you plan to use 12 ga wire,
replace the breaker with 20 amp. Since you mention red, black, and white
wires, I'll assume you have a bare ground or steel cable as a ground, make
sure your new cables are connected to the ground wire or junction box ground
screw




"sglaab" wrote in message
...

OK so I think this can be done quite simply I just need to be positive.
I have an unused 240V stove plug (the 3 pronged triangle shaped) I
would like to use this power to hook up a home vacuum system. I want
to split the 240V line into a 120V outlet for the vacuum itself and the
other line for the outlets at each conection (one on each floor) for the
power for the tools & attachments. I believe I can connect the red
white to the outlet for the vacuum in a junction box and the white and
black to a new wire out to the outlets at each connection. OK so far?

The double breaker in the box says 40 on both connected breakers. Are
they both 20A then? Can I leave this together and use this breaker?
Am I OK here. Thanks for the help.


--
sglaab
------------------------------------------------------------------------
sglaab's Profile: http://www.HomeOutfit.com/member.php?userid=277
View this thread: http://www.HomeOutfit.com/showthread.php?t=67382



  #3   Report Post  
Posted to alt.home.repair
Kevin Ricks
 
Posts: n/a
Default HELP me Split 240 to 120


"sglaab" wrote in message
...

OK so I think this can be done quite simply I just need to be positive.
I have an unused 240V stove plug (the 3 pronged triangle shaped) I
would like to use this power to hook up a home vacuum system. I want
to split the 240V line into a 120V outlet for the vacuum itself and the
other line for the outlets at each conection (one on each floor) for the
power for the tools & attachments. I believe I can connect the red
white to the outlet for the vacuum in a junction box and the white and
black to a new wire out to the outlets at each connection. OK so far?

The double breaker in the box says 40 on both connected breakers. Are
they both 20A then? Can I leave this together and use this breaker?
Am I OK here. Thanks for the help.


No the 40 amp means 40amp on each wire. Since the 2 poles are alternating
(sine wave) you will never have more than 40 amps at the appliance. When one
side is drawing 40 the other side is at 0. When one is at 30 the other is
10 etc.

Does your stove outlet have 4 wires. Red, Black, White, Ground? The ground
may be attached to the box.
If not I would not try to convert it. I would run new wires from the panel.
Some 240V outlets have red, black ground (no neutral). Some have neutral but
no ground. Newer 240V outlets are required to be 4 wire.

In general this is not a good idea. but do this safely you would need to
replace your 40A with a 20 amp double pole. Or two 20 amps breakers with the
handles tied together. (That is if you are using 12 ga wire)
If you did not change the breaker then you would have to keep using the
larger wire (6ga?) on the entire circuit.

A better idea is to make a sub panel at the stove outlet with 2 - 20 amp
breakers there. In that case you would leave the 40 amp breaker in the main
panel. You couldn't do this though if you don't have the 4 wire circuit
with a properly sized ground wire.

Kevin










--
sglaab



  #4   Report Post  
Posted to alt.home.repair
Mark Lloyd
 
Posts: n/a
Default HELP me Split 240 to 120

On Sat, 25 Feb 2006 13:58:14 GMT, "Kevin Ricks"
wrote:


"sglaab" wrote in message
...

OK so I think this can be done quite simply I just need to be positive.
I have an unused 240V stove plug (the 3 pronged triangle shaped) I
would like to use this power to hook up a home vacuum system. I want
to split the 240V line into a 120V outlet for the vacuum itself and the
other line for the outlets at each conection (one on each floor) for the
power for the tools & attachments. I believe I can connect the red
white to the outlet for the vacuum in a junction box and the white and
black to a new wire out to the outlets at each connection. OK so far?

The double breaker in the box says 40 on both connected breakers. Are
they both 20A then? Can I leave this together and use this breaker?
Am I OK here. Thanks for the help.


No the 40 amp means 40amp on each wire. Since the 2 poles are alternating
(sine wave) you will never have more than 40 amps at the appliance. When one
side is drawing 40 the other side is at 0. When one is at 30 the other is
10 etc.


That's not right. The 2 phases are opposite. The peaks occur at the
same time (just opposite polarities). During that time, each side is
drawing 40A. 1/240 second later, each is drawing 0A. The currents will
always be equal and opposite.

It will never total more than 40A because the sides are at opposite
polarities.

Does your stove outlet have 4 wires. Red, Black, White, Ground? The ground
may be attached to the box.
If not I would not try to convert it. I would run new wires from the panel.
Some 240V outlets have red, black ground (no neutral). Some have neutral but
no ground. Newer 240V outlets are required to be 4 wire.


The difference between ground and neutral has to do with current flow.
it you have a dedicated (currently with no load connected) 240V
circuit, how would you know which you have?

In general this is not a good idea. but do this safely you would need to
replace your 40A with a 20 amp double pole. Or two 20 amps breakers with the
handles tied together. (That is if you are using 12 ga wire)
If you did not change the breaker then you would have to keep using the
larger wire (6ga?) on the entire circuit.


You couldn't use 4 (2 for each side) 20A receptacles?

A better idea is to make a sub panel at the stove outlet with 2 - 20 amp
breakers there. In that case you would leave the 40 amp breaker in the main
panel. You couldn't do this though if you don't have the 4 wire circuit
with a properly sized ground wire.

Kevin


I've seen 240V circuits split for holiday lights.










--
sglaab


--
Mark Lloyd
http://notstupid.laughingsquid.com

"Democracy is two wolves and a lamb voting on what
to have for lunch. Liberty is a well armed lamb
contesting the vote." - Benjamin Franklin
  #5   Report Post  
Posted to alt.home.repair
Doug Miller
 
Posts: n/a
Default HELP me Split 240 to 120

In article , Mark Lloyd wrote:
On Sat, 25 Feb 2006 13:58:14 GMT, "Kevin Ricks"
wrote:


In general this is not a good idea. but do this safely you would need to
replace your 40A with a 20 amp double pole. Or two 20 amps breakers with the
handles tied together. (That is if you are using 12 ga wire)
If you did not change the breaker then you would have to keep using the
larger wire (6ga?) on the entire circuit.

You couldn't use 4 (2 for each side) 20A receptacles?


Code violation. Breakers are not permitted to be connected in parallel.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #6   Report Post  
Posted to alt.home.repair
 
Posts: n/a
Default HELP me Split 240 to 120

On Sat, 25 Feb 2006 00:16:20 -0500, sglaab
wrote:


OK so I think this can be done quite simply I just need to be positive.
I have an unused 240V stove plug (the 3 pronged triangle shaped) I
would like to use this power to hook up a home vacuum system. I want
to split the 240V line into a 120V outlet for the vacuum itself and the
other line for the outlets at each conection (one on each floor) for the
power for the tools & attachments. I believe I can connect the red
white to the outlet for the vacuum in a junction box and the white and
black to a new wire out to the outlets at each connection. OK so far?

The double breaker in the box says 40 on both connected breakers. Are
they both 20A then? Can I leave this together and use this breaker?
Am I OK here. Thanks for the help.


Wrap about 600 to 800 feet of insulated wire around your neck and
connect each of the ends to the plug on your vacuum. Put on some well
insulated rubber boots and stand where you dont touch any grounded
metal objects. Grab one of the 240 V wires in your left hand and the
other wire in your right. Turn on the breaker and you will have 120
volts going to the vacuum from the inductance of the coil of wire
around your neck.

Note: You might experience heart failure from doing this, but thats a
small price to pay for progress and technology. Better yet, if you do
survive, you will know you have a strong heart and can save a doctor
bill for cardiac testing.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ductless split A/C system Jason Home Repair 24 July 2nd 05 03:49 PM
How Ductless Split System Dehumidifies a Room? HvacTech2 Home Repair 5 June 15th 05 04:49 PM
tailstock restoration --split clamp removal Steve Koschmann Metalworking 0 February 25th 05 04:04 AM
split system vs ducted reverse cycle. tony Home Repair 0 January 19th 05 09:48 PM
"split" rollers for conveyor needed VITO Metalworking 4 June 8th 04 03:56 PM


All times are GMT +1. The time now is 06:35 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"