Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#41
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
"Doug Miller" wrote in message ... In article , cayoung61- says... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? First, I'd replace the dangerous and illegal [for this use] 12-2 cable with 12-3, with the red and black wires connected to a two-pole 240V breaker. Then I'd wire the space heater across the black and white, and the hair dryer across the red and white. That's 15A in the black wire, 14A in the red wire, and (15A - 14A) = 1A in the white wire. If you don't understand how that works, and why it's safe, and why the setup you described is not ... then you oughta stop offering electrical advice. I'll second what Doug said. I make no claims to be an electrician, and know just enough to be dangerous. But in any wiring or other repair, I don't go by what will 'be safe for me, because I know how it is set up.' I go by what will be safe for any guests, or for the next owner of the place. A wiring setup can easily be in place for 50+ years or more. Are you gonna be around that long, to make sure everyone knows about your 'good enough' shortcut? Spend the few extra bucks, wire it to code or better, and never have to worry about it again. If nothing else, when it comes time for you or your heirs to sell, the buyer's inspector will likely catch it anyway, and you'll have to pay more to redo the work at that point. aem sends... |
#42
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
wrote:
On Sun, 08 Jan 2006 00:13:46 GMT, "Tom Horne, Electrician" wrote: "Stormin Mormon" wrote in message m... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message gy.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. -- Regards, Doug Miller (alphageek at milmac dot com) Sounds like Stormy fell asleep in Basic Electricity 101 or even junior high Science class... Steve Scott wrote: Actually he's right on this one. This fails code on two points. You can't have a ground act as a current carrying wire. You can't run two circuits off one neutral. You used to but it hasn't met code in some time. On Sat, 07 Jan 2006 17:16:19 GMT, "Oscar_Lives" wrote: Article 100 Definitions. Dear Tom The Electrician : PAY SOME ****ING ATTENTION !!! No one asked for a ****ing description of basic theory, the point is the rig Mormy described is dangerous, illegal, and either suicidal or homicidal depending on who exactly he plans to kill with his little experiments in household wiring. Sincerely, Paul The Licensed Master Electrician. Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system. It is a little like running one twelve volt bulb and two six volt bulbs from two six volt batteries connected in series. I can ground the common point of the two batteries to make the example even more representative. If I want to run a six volt load I connect it across only one battery by applying it between the outer end and common point of either battery. If I want to run a twelve volt load I connect it to the outer ends of both batteries. For this arrangement to work the batteries must be connected in series with one batteries negative connected to the other batteries positive. If the two batteries are connected with both positive poles or both negative poles together than the voltage across the non common ends of the two batteries is zero. The original Edison circuits had DC on them but instead of batteries they had two DC generators running in series with their common point grounded. Originally used to reduce voltage drop in distribution Edison circuits continue to be used today as a labor and materials conservation technique. DC batteries arranged in Edison arrays are still used to supply single phase emergency lighting panels in older buildings. When the power fails the contactor supplying AC 208/120 single phase power to those panels drops out and connects the three conductors of the single phase feeder to 120 two volt wet cells connected in series and grounded at the common point between batteries sixty and sixty one. That leaves 120 volts between each ungrounded conductor and the neutral and 240 volts between the two ungrounded conductors. Paul You might take your own advise. Steve Scott, the poster I was replying to, said You can't run two circuits off one neutral. You used to but it hasn't met code in some time. I was correcting that bad information. You can in fact run two or three circuits of of a single neutral. I could understand your being so upset if I had only quoted the OPs question but I also quoted the misstatement that I was responding to so get a grip. Take a chill pill. -- Tom Horne Well we aren't no thin blue heroes and yet we aren't no blackguards to. We're just working men and woman most remarkable like you. |
#43
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
Mark Lloyd wrote:
On Sun, 08 Jan 2006 00:22:33 GMT, "Tom Horne, Electrician" wrote: Mark Lloyd wrote: On Sat, 07 Jan 2006 15:46:40 GMT, "Stormin Mormon" wrote: Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. That's 1A in the neutral if they're on opposite phases. However, how are you going to make sure noone ever moves a breaker wrong, butting I guess you figured out that last word was supposed to be "putting". Spelling checkers can do bad stuff like that. them on the same phase and making it 29A? How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message y.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. Any feeder or branch circuit that supplies loads that are connected to two or three ungrounded conductors must be protected by common trip breakers or breakers equipped with listed handle ties. To disarrange the circuit you would have to move at least one of the conductors to a different breaker rather than just moving the breaker and that isn't very likely. That's what I wanted to know. I have a shared neutral circuit in my house that's working OK now (different phases). I need to fix the breakers. The breakers only need fixing if the circuit supplies loads that are not line to neutral or if the circuit supplies both ungrounded conductors to devices mounted on the same yoke or strap. A qualified person is supposed to know that three and four wire circuits must be supplied from different voltages or phases. Any person who does not understand multi wire branch circuits has absolutely no business removing the cover from a panel cabinet. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#44
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
On Sun, 08 Jan 2006 16:33:16 GMT, "Thomas D. Horne, FF EMT"
wrote: wrote: On Sun, 08 Jan 2006 00:13:46 GMT, "Tom Horne, Electrician" wrote: "Stormin Mormon" wrote in message om... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message igy.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. -- Regards, Doug Miller (alphageek at milmac dot com) Sounds like Stormy fell asleep in Basic Electricity 101 or even junior high Science class... Steve Scott wrote: Actually he's right on this one. This fails code on two points. You can't have a ground act as a current carrying wire. You can't run two circuits off one neutral. You used to but it hasn't met code in some time. On Sat, 07 Jan 2006 17:16:19 GMT, "Oscar_Lives" wrote: Article 100 Definitions. Dear Tom The Electrician : PAY SOME ****ING ATTENTION !!! No one asked for a ****ing description of basic theory, the point is the rig Mormy described is dangerous, illegal, and either suicidal or homicidal depending on who exactly he plans to kill with his little experiments in household wiring. Sincerely, Paul The Licensed Master Electrician. Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system. It is a little like running one twelve volt bulb and two six volt bulbs from two six volt batteries connected in series. I can ground the common point of the two batteries to make the example even more representative. If I want to run a six volt load I connect it across only one battery by applying it between the outer end and common point of either battery. If I want to run a twelve volt load I connect it to the outer ends of both batteries. For this arrangement to work the batteries must be connected in series with one batteries negative connected to the other batteries positive. If the two batteries are connected with both positive poles or both negative poles together than the voltage across the non common ends of the two batteries is zero. The original Edison circuits had DC on them but instead of batteries they had two DC generators running in series with their common point grounded. Originally used to reduce voltage drop in distribution Edison circuits continue to be used today as a labor and materials conservation technique. DC batteries arranged in Edison arrays are still used to supply single phase emergency lighting panels in older buildings. When the power fails the contactor supplying AC 208/120 single phase power to those panels drops out and connects the three conductors of the single phase feeder to 120 two volt wet cells connected in series and grounded at the common point between batteries sixty and sixty one. That leaves 120 volts between each ungrounded conductor and the neutral and 240 volts between the two ungrounded conductors. Paul You might take your own advise. Steve Scott, the poster I was replying to, said You can't run two circuits off one neutral. You used to but it hasn't met code in some time. I was correcting that bad information. You can in fact run two or three circuits of of a single neutral. I could understand your being so upset if I had only quoted the OPs question but I also quoted the misstatement that I was responding to so get a grip. Take a chill pill. OK, my bad. :-) -- Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
#45
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
Steve Scott wrote: Actually he's right on this one. This fails code on two points. You can't have a ground act as a current carrying wire. What about those adapters that convert the 220 for an electric stove into 110 for the electrical side of a gas stove (lights, timer, clock, ignitor, etc...? Aren't they using the ground in that way? |
#46
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
On Sun, 08 Jan 2006 16:39:07 GMT, "Tom Horne, Electrician"
wrote: Mark Lloyd wrote: On Sun, 08 Jan 2006 00:22:33 GMT, "Tom Horne, Electrician" wrote: Mark Lloyd wrote: On Sat, 07 Jan 2006 15:46:40 GMT, "Stormin Mormon" wrote: Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. That's 1A in the neutral if they're on opposite phases. However, how are you going to make sure noone ever moves a breaker wrong, butting I guess you figured out that last word was supposed to be "putting". Spelling checkers can do bad stuff like that. them on the same phase and making it 29A? How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message gy.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. Any feeder or branch circuit that supplies loads that are connected to two or three ungrounded conductors must be protected by common trip breakers or breakers equipped with listed handle ties. To disarrange the circuit you would have to move at least one of the conductors to a different breaker rather than just moving the breaker and that isn't very likely. That's what I wanted to know. I have a shared neutral circuit in my house that's working OK now (different phases). I need to fix the breakers. The breakers only need fixing if the circuit supplies loads that are not line to neutral or if the circuit supplies both ungrounded conductors to devices mounted on the same yoke or strap. A qualified person is supposed to know that three and four wire circuits must be supplied from different voltages or phases. Any person who does not understand multi wire branch circuits has absolutely no business removing the cover from a panel cabinet. Something still needs to be fixed. There is no way to tell from looking at the panel, that different phases are required. As I said in another pose, it shouldn't be too hard to rewire an outlet, eliminating the (shared neutral) situation. I'll do that. -- Mark Lloyd http://notstupid.laughingsquid.com "Democracy is two wolves and a lamb voting on what to have for lunch. Liberty is a well armed lamb contesting the vote." - Benjamin Franklin |
#47
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
“However it is my experience that those who believe it to be overkill just
don't understand why it was written the way it is.” I have a strong suspicion that a considerable amount of it was for “Turf Protection” for Electrical Contractors and Union Installers. There are several things I did not mention in the previous post about “This is enough to show that you should not attempt this installation yourself”. One of the new houses I wired from scratch happened to be one of the very first in our area to have a fully grounded system. The “Professional” electricians were not yet installing fully grounded systems. Where would I get the idea to do such a thing? From my Handy-Dandy Sears “Home Wiring Simplified”, or some such title, hand book. Also for those who reacted so hysterically about “ungrounded” neutral wire, in this molded plastic wire, typical of much or most today, that particular wire is actually as well insulated as the conductors, it just does not have a separate sleeve with the sleeved conductors then having thinner body insulation. Might want to check the construction of 6 Ga. and larger wire of not too long ago, what comprised the Neutral. Never heard of any problem with it. By the way, does everyone here feel it is necessary to post complete messages that are being responded too? Walt Conner |
#48
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
WConner wrote:
"However it is my experience that those who believe it to be overkill just don't understand why it was written the way it is." I have a strong suspicion that a considerable amount of it was for "Turf Protection" for Electrical Contractors and Union Installers. You can suspect what you want, but from my experience, every rule, including those that on first look sound suspicious have very good sound safety and electrical reasons for being there. I repeat my opinion that ignoring any part of the code is foolish. -- Joseph Meehan Dia duit |
#49
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
That's a fascinating approach. I can see that working. Didn't even think of
that -- effectively making a 220 volt space heater / hair dryer. Neat technique! -- Christopher A. Young You can't shout down a troll. You have to starve them. .. "Doug Miller" wrote in message ... In article , cayoung61- says... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? First, I'd replace the dangerous and illegal [for this use] 12-2 cable with 12-3, with the red and black wires connected to a two-pole 240V breaker. Then I'd wire the space heater across the black and white, and the hair dryer across the red and white. That's 15A in the black wire, 14A in the red wire, and (15A - 14A) = 1A in the white wire. If you don't understand how that works, and why it's safe, and why the setup you described is not ... then you oughta stop offering electrical advice. |
#50
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
"Steve Scott" wrote in message ... On Sun, 08 Jan 2006 16:33:16 GMT, "Thomas D. Horne, FF EMT" wrote: wrote: On Sun, 08 Jan 2006 00:13:46 GMT, "Tom Horne, Electrician" wrote: "Stormin Mormon" wrote in message om... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message igy.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. -- Regards, Doug Miller (alphageek at milmac dot com) Sounds like Stormy fell asleep in Basic Electricity 101 or even junior high Science class... Steve Scott wrote: Actually he's right on this one. This fails code on two points. You can't have a ground act as a current carrying wire. You can't run two circuits off one neutral. You used to but it hasn't met code in some time. On Sat, 07 Jan 2006 17:16:19 GMT, "Oscar_Lives" wrote: Article 100 Definitions. Dear Tom The Electrician : PAY SOME ****ING ATTENTION !!! No one asked for a ****ing description of basic theory, the point is the rig Mormy described is dangerous, illegal, and either suicidal or homicidal depending on who exactly he plans to kill with his little experiments in household wiring. Sincerely, Paul The Licensed Master Electrician. Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system. It is a little like running one twelve volt bulb and two six volt bulbs from two six volt batteries connected in series. I can ground the common point of the two batteries to make the example even more representative. If I want to run a six volt load I connect it across only one battery by applying it between the outer end and common point of either battery. If I want to run a twelve volt load I connect it to the outer ends of both batteries. For this arrangement to work the batteries must be connected in series with one batteries negative connected to the other batteries positive. If the two batteries are connected with both positive poles or both negative poles together than the voltage across the non common ends of the two batteries is zero. The original Edison circuits had DC on them but instead of batteries they had two DC generators running in series with their common point grounded. Originally used to reduce voltage drop in distribution Edison circuits continue to be used today as a labor and materials conservation technique. DC batteries arranged in Edison arrays are still used to supply single phase emergency lighting panels in older buildings. When the power fails the contactor supplying AC 208/120 single phase power to those panels drops out and connects the three conductors of the single phase feeder to 120 two volt wet cells connected in series and grounded at the common point between batteries sixty and sixty one. That leaves 120 volts between each ungrounded conductor and the neutral and 240 volts between the two ungrounded conductors. Paul You might take your own advise. Steve Scott, the poster I was replying to, said You can't run two circuits off one neutral. You used to but it hasn't met code in some time. I was correcting that bad information. You can in fact run two or three circuits of of a single neutral. I could understand your being so upset if I had only quoted the OPs question but I also quoted the misstatement that I was responding to so get a grip. Take a chill pill. Tom, yes you can run 2 or a hundred circuits off a single neutral. Does it meet the NEC? No, but feel free to wire your home in any fashion you desire. Steve, Local codes may vary, but suggest first start with reading NEC 210-4(b) before making any comments regarding NEC noncompliance. A fairly good discussion can be found here : http://www.inspect-ny.com/electric/multiwir.htm Assuming a balanced load and opposite "hot legs", no current flows within the neutral conductor.....and even in the case where one side has no connected load, the current carried by the neutral won't rise above what is being drawn by the individual feeder. -- SVL |
#51
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
"Stormin Mormon" wrote in message
. com... Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message digy.com... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. -- Regards, Doug Miller (alphageek at milmac dot com) Sounds like Stormy fell asleep in Basic Electricity 101 or even junior high Science class... Steve Scott wrote: Actually he's right on this one. This fails code on two points. You can't have a ground act as a current carrying wire. You can't run two circuits off one neutral. You used to but it hasn't met code in some time. On Sat, 07 Jan 2006 17:16:19 GMT, "Oscar_Lives" wrote: Article 100 Definitions. Dear Tom The Electrician : PAY SOME ****ING ATTENTION !!! No one asked for a ****ing description of basic theory, the point is the rig Mormy described is dangerous, illegal, and either suicidal or homicidal depending on who exactly he plans to kill with his little experiments in household wiring. Sincerely, Paul The Licensed Master Electrician. Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system. It is a little like running one twelve volt bulb and two six volt bulbs from two six volt batteries connected in series. I can ground the common point of the two batteries to make the example even more representative. If I want to run a six volt load I connect it across only one battery by applying it between the outer end and common point of either battery. If I want to run a twelve volt load I connect it to the outer ends of both batteries. For this arrangement to work the batteries must be connected in series with one batteries negative connected to the other batteries positive. If the two batteries are connected with both positive poles or both negative poles together than the voltage across the non common ends of the two batteries is zero. The original Edison circuits had DC on them but instead of batteries they had two DC generators running in series with their common point grounded. Originally used to reduce voltage drop in distribution Edison circuits continue to be used today as a labor and materials conservation technique. DC batteries arranged in Edison arrays are still used to supply single phase emergency lighting panels in older buildings. When the power fails the contactor supplying AC 208/120 single phase power to those panels drops out and connects the three conductors of the single phase feeder to 120 two volt wet cells connected in series and grounded at the common point between batteries sixty and sixty one. That leaves 120 volts between each ungrounded conductor and the neutral and 240 volts between the two ungrounded conductors. Paul You might take your own advise. Steve Scott, the poster I was replying to, said You can't run two circuits off one neutral. You used to but it hasn't met code in some time. I was correcting that bad information. You can in fact run two or three circuits of of a single neutral. I could understand your being so upset if I had only quoted the OPs question but I also quoted the misstatement that I was responding to so get a grip. Take a chill pill. Steve Scott wrote: Tom, yes you can run 2 or a hundred circuits off a single neutral. Does it meet the NEC? No, but feel free to wire your home in any fashion you desire. Steve You keep making the assertion that multi wire branch circuits in which two or three ungrounded conductors share a neutral violates code. Would you please quote chapter and verse to back up your position. If you read my previous posting that is quoted above you will see that I have provided the quote from the US National Electric Code (NEC) to back up my assertion that this is a permitted practice. I expect you to do the same. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#52
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
In article Aliwf.16920$v84.189@trnddc06, "WConner" wrote:
“However it is my experience that those who believe it to be overkill just don't understand why it was written the way it is.” I have a strong suspicion that a considerable amount of it was for “Turf Protection” for Electrical Contractors and Union Installers. The National Electrical Code is published by the National Fire Protection Association. That should tell you something about the motives of its authors. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#53
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
In article , "Stormin Mormon" wrote:
That's a fascinating approach. I can see that working. Didn't even think of that -- effectively making a 220 volt space heater / hair dryer. Neat technique! Ummm.... no. It's clear you still don't understand. As I suggested before, Google on "Edison circuit" and learn something new. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#54
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
|
#56
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
I have a strong suspicion that a considerable amount of it was for “Turf
Protection” for Electrical Contractors and Union Installers. The National Electrical Code is published by the National Fire Protection Association. That should tell you something about the motives of its authors. Who published the Code has nothing what-so-ever to do with who lobbied to have certain "Turf Protection" included. Now for all you people who are running around frantically waving your CODE books, I am sure the next time you step into your car or truck and head down the highway, you will remember there is a code involved here also. Part of this code is posted on signs along the way and read - SPEED LIMIT 20, 35, 50, 55. etc, MPH. If you are running 56 MPH in 55 zone, you are breaking the code. Ignoring the code may lead to arrest, personal injury or death. To quote someone here - "The code is there for a reason, a very good reason. Ignoring it because the danger is not understood, is foolish and dangerous" anyone recognize this? Walt Conner Over and Out |
#57
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
Steve You keep making the assertion that multi wire branch circuits in which two or three ungrounded conductors share a neutral violates code. Would you please quote chapter and verse to back up your position. If you read my previous posting that is quoted above you will see that I have provided the quote from the US National Electric Code (NEC) to back up my assertion that this is a permitted practice. I expect you to do the same. It is not only permitted practice, but done in nearly every home in this country. At your service, you have only ONE neutral returning. Neutrals have to be properly sized, by trained electricians who can make sure they balance correctly, but it's common. A Neutral should NEVER, EVER be a non-insulated conductor in your home. It's carrying 120 V (or whatever) and the same current as the wire coming from your breaker. 3 wire systems with equal loads on both hots (but supplied out-of-phase of each other) will 'cancel' current out.. but it's not a given and imbalances routinely occur... which present hazardous current on the neutral. A Neutral should NEVER, EVER be grounded ANYWHERE but at the panel where it enters your property (called a service entrance). Doing otherwise exposes you to electrocution and fire hazards. Jake |
#58
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
|
#59
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
On Tue, 10 Jan 2006 15:55:16 GMT, "Thomas D. Horne, FF EMT"
wrote: wrote: On Mon, 09 Jan 2006 21:30:45 GMT, AZ Nomad wrote: There may be enough of a voltage difference that grounding the neutral may present a fire hazard. A fire hazard, let's not get silly here. 250.32 DOES allow a 3 wire feed to a remote building. That is a fact. The issue is whether it is insulated or not. Bear in mind it is connected to grounding electrodes at BOTH ends along with the equipment grounding system at the far end.. I will not say it is legal but I also can't put my finger on the hazard. In addition to my bread work as an electrician I also crawl down long snotty hallways looking for other peoples children at 0dark30. Say WHAT ????? In other words I am a volunteer firefighter / rescuer. Whew ! For a second there I thought you were admitting to being a pervert ! :-) -- Click here every day to feed an animal that needs you today !!! http://www.theanimalrescuesite.com/ Paul ( pjm @ pobox . com ) - remove spaces to email me 'Some days, it's just not worth chewing through the restraints.' 'With sufficient thrust, pigs fly just fine.' HVAC/R program for Palm PDA's Free demo now available online http://pmilligan.net/palm/ |
#60
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
Jake wrote:
A Neutral should NEVER, EVER be grounded ANYWHERE but at the panel where it enters your property (called a service entrance). Doing otherwise exposes you to electrocution and fire hazards. One of the ways to wire a feeder to a garage, or other separate building, is to run hots and a neutral and connect the neutral to a grounding electrode (ground rod) at the garage (similar to a service entrance). 2005NEC 250.32B2 bud-- |
#61
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
|
#62
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
wrote in message ... On Tue, 10 Jan 2006 15:55:16 GMT, "Thomas D. Horne, FF EMT" wrote: wrote: On Mon, 09 Jan 2006 21:30:45 GMT, AZ Nomad wrote: There may be enough of a voltage difference that grounding the neutral may present a fire hazard. A fire hazard, let's not get silly here. 250.32 DOES allow a 3 wire feed to a remote building. That is a fact. The issue is whether it is insulated or not. Bear in mind it is connected to grounding electrodes at BOTH ends along with the equipment grounding system at the far end.. I will not say it is legal but I also can't put my finger on the hazard. In addition to my bread work as an electrician I also crawl down long snotty hallways looking for other peoples children at 0dark30. Say WHAT ????? In other words I am a volunteer firefighter / rescuer. Whew ! For a second there I thought you were admitting to being a pervert ! :-) Yup... One should NEVER admit to THAT !!!! G -- SVL |
#63
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
Just TRY to sell that house, home inspectors love stuff like that
|
#64
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
|
#65
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
wrote:
Just TRY to sell that house, home inspectors love stuff like that They love houses wired to the National Electrical Code? bud-- No houses with shortcuts..... home inspectors love finding them, and buyers really enjoy running the price down. do it right the first time, its safer, and elminates long term hassles |
#66
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
wrote:
Just TRY to sell that house, home inspectors love stuff like that They love houses wired to the National Electrical Code? bud-- No houses with shortcuts..... home inspectors love finding them, and buyers really enjoy running the price down. do it right the first time, its safer, and elminates long term hassles |
#67
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
|
#68
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
The Tom Horne wrote:
wrote: On Tue, 10 Jan 2006 15:55:16 GMT, "Thomas D. Horne, FF EMT" wrote: In addition to my bread work as an electrician I also crawl down long snotty hallways looking for other peoples children at 0dark30. Then you know about the NEC proposal process. If you want to make 3 wire feeders illegal, write a proposal, see what they say. What led you to the conclusion that I "want to make 3 wire feeders illegal?" -- Tom Horne Because that's Greg. :-) |
#69
Posted to alt.home.repair
|
|||
|
|||
110v line to 220v line?
WConner posted for all of us...
I don't top post - see either inline or at bottom. "I am not sure about your grounding idea either. " I think if you check your house wiring, you will find it is grounded this way, if you have a house built within the last 30 years or so at least. "You forgot zoned heat piping and an underground tunnel so he never has to go outside. LOL" ditto Most likely the existing wire will be used for lighting circuit and a new line run. For those talking about how "cheap wire is" have you priced 10-3 w/ground direct burial wire lately? It will take a season or two to re-establish a nice lawn over the trench also. Now for the "black tape, etc" comment, do you run two black wires to/from your wall switches? Since you break the black, this is what you should do, right? Better check to see all of yours are that way. I wasn't very clear, the thought was to come from a new 220V breaker. The problem is the neutral would not have individual insulation, but would be insulated within the bundle, which in the case of the neutral, shouldn't make that much difference. Thanks, Walt Conner Walt, you ask a question (which has been asked & answered SOOOO many times) didn't do ANY research get good answers then argue with them and will do it the way you want. Go away. -- My boss said I was dumb and apathetic. I said I don't know and I don't care... Tekkie |
#70
Posted to alt.home.repair,alt.hvac
|
|||
|
|||
110v line to 220v line?
using a transformer for the 110 would be safer but cost more
what's you life worth On Sat, 07 Jan 2006 17:16:19 GMT, "Oscar_Lives" wrote: "Stormin Mormon" wrote in message .. . Well, supposing I'm running a space heater (15 amps) on the black wire and the bare wire. And running a hair dryer (14 amps) on the white wire and the bare wire. That's 29amps in a bare piece of 12 ga. How would you wire it differently? -- Christopher A. Young You can't shout down a troll. You have to starve them. . "Doug Miller" wrote in message m... In article , "Stormin Mormon" wrote: With two hots and one neutral, you'd be possible to overheat the neutral in a big way. Not if they're connected properly. -- Regards, Doug Miller (alphageek at milmac dot com) Sounds like Stormy fell asleep in Basic Electricity 101 or even junior high Science class... |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Using only one 110v feed from a 220v pair on a remote grounded motor. | Home Repair | |||
McCulloch Strimmer Line | UK diy | |||
Problem with wiring for new second phone line | Home Repair | |||
Telephone Line 1/ 2 | Home Repair | |||
Telephone Line Problems | Home Repair |