Troubleshooting Electrical Outlet
What would be the next step in testing an innoperable electrical
outlet? All the outlets connected to one circuit breaker do not work. I've replaced the circuit breaker and outlets, but still nothing. what should be done next |
#2
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
There are several logical steps available for someone with limited
troubleshooting skills. 1) Replace all the wiring 2) Learn how to troubleshoot 3) Find someone who knows how to troubleshoot wrote in message oups.com... What would be the next step in testing an innoperable electrical outlet? All the outlets connected to one circuit breaker do not work. I've replaced the circuit breaker and outlets, but still nothing. what should be done next |
#3
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
If all of the outlets on the entire circuit are dead, you need to find the
break in the cable between the panel and the first outlet or run a new cable wrote in message oups.com... What would be the next step in testing an innoperable electrical outlet? All the outlets connected to one circuit breaker do not work. I've replaced the circuit breaker and outlets, but still nothing. what should be done next |
#4
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
How are you determining the outlets are "dead?"
How did you know which breaker to change? Has there been any rewiring lately? Did the outlets EVER work? Do you have a multimeter or an ohmmeter? I think a little more info would bein order here. IFF you've replaced the right breaker, and done so properly, then the problem is going to be an open wire someplace between the breaker and the first "dead" outlet in the line. HTH, Pop wrote in message oups.com... : What would be the next step in testing an innoperable electrical : outlet? : All the outlets connected to one circuit breaker do not work. : I've replaced the circuit breaker and outlets, but still nothing. : what should be done next : |
#5
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
wrote in message oups.com... What would be the next step in testing an innoperable electrical outlet? All the outlets connected to one circuit breaker do not work. I've replaced the circuit breaker and outlets, but still nothing. what should be done next Is there a voltage drop across the breaker?...If so, it is open....good luck, Mac |
#6
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
I had some lights plugged into them which worked at one point, but now
do not work they work when plugged into an outlet in another room. there is a breaker designated for the room that the outlets are in no rewiring has been done recently i have a multimeter, A voltage test reveals .4 volts across the outlet plugs Pop wrote: How are you determining the outlets are "dead?" How did you know which breaker to change? Has there been any rewiring lately? Did the outlets EVER work? Do you have a multimeter or an ohmmeter? I think a little more info would bein order here. IFF you've replaced the right breaker, and done so properly, then the problem is going to be an open wire someplace between the breaker and the first "dead" outlet in the line. HTH, Pop wrote in message oups.com... : What would be the next step in testing an innoperable electrical : outlet? : All the outlets connected to one circuit breaker do not work. : I've replaced the circuit breaker and outlets, but still nothing. : what should be done next : |
#7
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
The first step is to ensure you are actually working on the correct
wiring. Labels in the breaker box are not reliable (just my opinion) . You may pick up stray current on your meter. First check that the breaker is working. Multimeter from breaker connection to neutral. I would ensure the breaker is off and do a continuity test for the wiring to the first box. You can do this single handed by joining the wires at the box with a nut and testing at the breaker box. A non-contact voltage sensor is a worthwhile investment. About $10 and will alert you to hot wiring without actually touching the bare wires. If you are not comfortable with doing this stuff call an electrician. |
#8
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
Set your multimeter to read AC volts. Remove all the cover plates from
the non-working outlets and test each terminal to the other within the receptacle, and each to ground (the metal box and the ground screw). If you don't find any that read 120V then your problem is a break in the wire or the breaker. If you have a main breaker you can throw that, yank the suspect breaker, and test it for continuity in open and closed positions. If you don't feel confident doing this and/or don't know what you're doing then call a professional; he'll solve it in a few minutes. Mike |
#9
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
|
#10
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
Lots of good advice already given. Another thing to consider is that there
may be another outlet, receptacle or light, wired between the ones you have checked and the breaker box. It could be located in another nearby room. Replacing breakers or outlets without first locating the fault is not a good idea. Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Don Young wrote in message oups.com... Set your multimeter to read AC volts. Remove all the cover plates from the non-working outlets and test each terminal to the other within the receptacle, and each to ground (the metal box and the ground screw). If you don't find any that read 120V then your problem is a break in the wire or the breaker. If you have a main breaker you can throw that, yank the suspect breaker, and test it for continuity in open and closed positions. If you don't feel confident doing this and/or don't know what you're doing then call a professional; he'll solve it in a few minutes. Mike |
#11
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
Don Young wrote:
Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. Mike |
#12
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
|
#13
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
|
#15
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
Keith Williams wrote:
In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. Hi, That's why I still have an old Simpson 260 analog multi meter. Also have Fluke DVM, Tek 'scope, etc. Tony |
#16
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
In article .com,
says... Keith Williams wrote: In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. -- Keith I love my non contact tester, I think it's a GC. I have noticed one thing and that is you can get a false positive if you're holding the tester and near or standing on an extension cord. I guess it capacitively couples to the voltage source. Still better than a false negative :). Indeed. I'm pretty careful even with the NC tester. A false- negative could ruin one's day. -- Keith |
#17
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
In article EtBsf.92824$2k.40435@pd7tw1no,
says... Keith Williams wrote: In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. Hi, That's why I still have an old Simpson 260 analog multi meter. I never really liked the '260s, certainly not enough to buy one. The light bulb may be more accurate. ;-) Also have Fluke DVM, Tek 'scope, etc. A scope for an AC line? ;-) I have a couple of Fluke (77?) multimeters left (some have sprouted legs) and a bunch of Harbor Freight $2.99 specials. The latter gets loaned out these days. ;-) -- Keith |
#18
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
"Keith Williams" wrote in message T... In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. -- Keith Hi Keith, Good advice as usual....I am assuming you are the same Keith that posts over at alt.engineering.electrical. Hope you had a great Christmas season and all is well out here in Central Florida....Mac |
#19
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
"Steve" wrote in message ... wrote: Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters can give misleading readings due to their high input impedance. Capacitive coupling from adjacent wires can cause so-called "ghost voltages" to appear in wires that are not connected to a power source. A low-impedance voltage tester, such as a test light or a Wiggy, will draw enough current to eliminate these "ghost voltages." -- -- Steve Buy good multimeters (Fluke works) and many nightmares disappear. I have many from my previous life/occupation and they have served me well. The cheap ones will ultimately lead you astray and are not worth the "powder to blow them up"....Happy New Year to All....Mac |
#20
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
In article ,
lid says... "Keith Williams" wrote in message T... In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. -- Keith Hi Keith, Good advice as usual....I am assuming you are the same Keith that posts over at alt.engineering.electrical. Yep, the same. I've noticed you back around the Usenet for a while. ;-) Hope you had a great Christmas season and all is well out here in Central Florida....Mac Great holiday here! We've been visiting my mother (92YO) In Central Illinois for the last week and are on our way back tomorrow and Friday. Long drive (1100mi.). ugh -- Keith |
#21
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
Ross Mac wrote:
Buy good multimeters (Fluke works) and many nightmares disappear. This is generally good advice but won't solve the problem of "ghost voltage" measurements. High input impedance is, for most purposes, a desirable characteristic in a meter to keep from loading the circuit under test. However, low impedance is needed to determine whether a power circuit is really energized or just capacitively coupled to an adjoining wire. This is one job where a relatively inexpensive electrical tester can outperform an expensive meter. (I am not talking about the $2.99 Harbor Freight meter here, but testers such as Klein's Wiggy, Ideal's Vol-Con, or Fluke's 7-600.) -- -- Steve |
#22
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
"Steve" wrote in message ... Ross Mac wrote: Buy good multimeters (Fluke works) and many nightmares disappear. This is generally good advice but won't solve the problem of "ghost voltage" measurements. High input impedance is, for most purposes, a desirable characteristic in a meter to keep from loading the circuit under test. However, low impedance is needed to determine whether a power circuit is really energized or just capacitively coupled to an adjoining wire. True! This is one job where a relatively inexpensive electrical tester can outperform an expensive meter. Also true! (I am not talking about the $2.99 Harbor Freight meter here, True, and that's a relief! So many posts about that meter/door stop. I usually pay more than $2.99 for a good set of test leads. but testers such as Klein's Wiggy, Ideal's Vol-Con, or Fluke's 7-600.) Good suggestion.....Mac -- -- Steve |
#23
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
"Keith Williams" wrote in message T... In article , lid says... "Keith Williams" wrote in message T... In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. -- Keith Hi Keith, Good advice as usual....I am assuming you are the same Keith that posts over at alt.engineering.electrical. Yep, the same. I've noticed you back around the Usenet for a while. ;-) Hope you had a great Christmas season and all is well out here in Central Florida....Mac Great holiday here! We've been visiting my mother (92YO) In Central Illinois for the last week and are on our way back tomorrow and Friday. Long drive (1100mi.). ugh -- Keith Hi Keith, I'll have to shoot you an email....been busy with the biz I purchased back in March and finally have more time for Usenet....Yup...retirement is over and I don't miss it.....Ross And for the other readers....that was early retirement and does not equal old.... :)....Ross....well, not that old! |
#24
Posted to alt.home.repair
|
|||
|
|||
Troubleshooting Electrical Outlet
In article ,
lid says... "Keith Williams" wrote in message T... In article , lid says... "Keith Williams" wrote in message T... In article .com, says... Don Young wrote: Troubleshooting with a digital voltmeter is also not a good idea; a test lamp is much better. Why isn't a multimeter a good idea? He's measuring volts, not current, so it won't blow the meter. Digital multimeters have a very high input impedance and can read high values on open circuits because of the capacitive coupling between wires. A test lamp is a low impedance device so any capacitive coupling becomes insignificant. If you really need to know what the voltage is, use both (load the circuit and read with the meter). A test lamp is a good idea. He could also pick up one of those outlet testers for a few dollars. A "three-light tester" should be in everyone's toolbox. Another tool I've found to be quite valuable is a non-contact voltage probe. -- Keith Hi Keith, Good advice as usual....I am assuming you are the same Keith that posts over at alt.engineering.electrical. Yep, the same. I've noticed you back around the Usenet for a while. ;-) Hope you had a great Christmas season and all is well out here in Central Florida....Mac Great holiday here! We've been visiting my mother (92YO) In Central Illinois for the last week and are on our way back tomorrow and Friday. Long drive (1100mi.). ugh -- Keith Hi Keith, I'll have to shoot you an email....been busy with the biz I purchased back in March and finally have more time for Usenet....Yup...retirement is over and I don't miss it.....Ross Damn! Don't tell me that! I wanna get out as soon as possible ('06?). Do drop a line when you get a chance. And for the other readers....that was early retirement and does not equal old.... :)....Ross....well, not that old! Uh, me too! ;-) Have a merry new year! -- Keith |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Strange Electrical outlet | Home Repair | |||
FS Six 20A outlet shop electrical panel, each outlet protected | Metalworking | |||
FS Six 20A outlet shop electrical panel, each outlet protected | Home Repair | |||
FS Six 20A outlet shop electrical panel, each outlet protected | Woodworking | |||
electrical outlet problem | Home Repair |