  #1   Report Post  
Posted to alt.home.repair
bill
 
Posts: n/a
Default gas furnace- what is normal?

Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on
and off while the blower continues to run. Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or is
this typically not normal. not enough air flow...filter, open
registers....thanks bill
  #2   Report Post  
Posted to alt.home.repair
Bert
 
Posts: n/a
Default gas furnace- what is normal?


bill wrote:
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on
and off while the blower continues to run. Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or is
this typically not normal. not enough air flow...filter, open
registers....thanks bill


Mine did that too, but is a diff model Carrier. Was caused by a slug of
water in the draft motor pressure switch tubing.

MikeB

  #3   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default gas furnace- what is normal?


"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on
and off while the blower continues to run.



No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or is
this typically not normal. not enough air flow...filter, open
registers....thanks bill


No one here can tell you. Its being cause by something, and it could be as
simple as a bad limit, or an improperly set gas valve.


  #4   Report Post  
Posted to alt.home.repair
buffalobill
 
Posts: n/a
Default gas furnace- what is normal?

in a working forced air furnace in my basement, the gas burner cycles
on and off while the blower sends the warmed up air to the house until
the thermostst is satisfied.
the main can't usually run 100 percent of the time or the plenum would
get overheated. the system is designed or adjusted at fan in and fan
out settings to deliver that range of heat to your registers.
if your furnace is not operating properly be more specific with the
symptom you have.

  #5   Report Post  
Posted to alt.home.repair
buffalobill
 
Posts: n/a
Default gas furnace- what is normal?

mike b's post reminded me to tell you that we've cleared up a
malfunction more than once, cleaning out the silicone updraft flue
blower motor tube connection with a paperclip.

"Mine did that too, but is a diff model Carrier. Was caused by a slug
of
water in the draft motor pressure switch tubing.

MikeB"



  #6   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default gas furnace- what is normal?


"buffalobill" wrote in message
oups.com...
in a working forced air furnace in my basement, the gas burner cycles
on and off while the blower sends the warmed up air to the house until
the thermostst is satisfied.
the main can't usually run 100 percent of the time or the plenum would
get overheated. the system is designed or adjusted at fan in and fan
out settings to deliver that range of heat to your registers.
if your furnace is not operating properly be more specific with the
symptom you have.


Here is another one, that has a problem, and has no clue he does......

yes..properly INSTALLED units can run 100% of the time like they are
designed to, and never shut the gas off till the thermostat is satisfied.
If they are not, somethings wrong..


  #7   Report Post  
Posted to alt.home.repair
HeatMan
 
Posts: n/a
Default gas furnace- what is normal?


"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on
and off while the blower continues to run.



No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or is
this typically not normal. not enough air flow...filter, open
registers....thanks bill


No one here can tell you. Its being cause by something, and it could be as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second thread
you've mentioned it in...


  #8   Report Post  
Posted to alt.home.repair
bill
 
Posts: n/a
Default gas furnace- what is normal?

I just wanted to know if gas valve cycling is normal while the
thermostst waits to be satisfied. one says no others say yes.???
anyway...i changed a dirty filter and the valve remeined opened during
the complete cycle, which leads me to believe... that gas valve
cycling ( on my model) is NOT normal.......Thanks for your inputs and
discussion. its all helpful.. Bill


On 23 Nov 2005 04:18:12 -0800, "buffalobill"
wrote:

mike b's post reminded me to tell you that we've cleared up a
malfunction more than once, cleaning out the silicone updraft flue
blower motor tube connection with a paperclip.

"Mine did that too, but is a diff model Carrier. Was caused by a slug
of
water in the draft motor pressure switch tubing.

MikeB"


  #9   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default gas furnace- what is normal?


"HeatMan" wrote in message
...

"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on
and off while the blower continues to run.



No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or is
this typically not normal. not enough air flow...filter, open
registers....thanks bill


No one here can tell you. Its being cause by something, and it could be
as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second thread
you've mentioned it in...



Ever seen one with the burn rate set too high?
Can cycle the unit in and out and in and out several times over the course
of a call for heat.


  #10   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default gas furnace- what is normal?


"bill" wrote in message
...
I just wanted to know if gas valve cycling is normal while the
thermostst waits to be satisfied. one says no others say yes.???
anyway...i changed a dirty filter and the valve remeined opened during
the complete cycle, which leads me to believe... that gas valve
cycling ( on my model) is NOT normal.......Thanks for your inputs and
discussion. its all helpful.. Bill




Well, quite simply...its NOT normal on ANY model made in the last 20
years....or any before that if its installed right.
Call for heat from thermostat, valve is open..unless a thermal trips...


On 23 Nov 2005 04:18:12 -0800, "buffalobill"
wrote:

mike b's post reminded me to tell you that we've cleared up a
malfunction more than once, cleaning out the silicone updraft flue
blower motor tube connection with a paperclip.

"Mine did that too, but is a diff model Carrier. Was caused by a slug
of
water in the draft motor pressure switch tubing.

MikeB"






  #11   Report Post  
Posted to alt.home.repair
HeatMan
 
Posts: n/a
Default gas furnace- what is normal?


"CBHVAC" wrote in message
...

"HeatMan" wrote in message
...

"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle

on
and off while the blower continues to run.


No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or

is
this typically not normal. not enough air flow...filter, open
registers....thanks bill

No one here can tell you. Its being cause by something, and it could be
as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second

thread
you've mentioned it in...



Ever seen one with the burn rate set too high?
Can cycle the unit in and out and in and out several times over the course
of a call for heat.



Never seen that.


  #12   Report Post  
Posted to alt.home.repair
CBHVAC
 
Posts: n/a
Default gas furnace- what is normal?


"HeatMan" wrote in message
.. .

"CBHVAC" wrote in message
...

"HeatMan" wrote in message
...

"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle

on
and off while the blower continues to run.


No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle or

is
this typically not normal. not enough air flow...filter, open
registers....thanks bill

No one here can tell you. Its being cause by something, and it could
be
as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second

thread
you've mentioned it in...



Ever seen one with the burn rate set too high?
Can cycle the unit in and out and in and out several times over the
course
of a call for heat.



Never seen that.


On the newer Yorks, Tranes, and Carriers in particular, if you set the gas
valve too high, and dont finalize the heat rise correctly, you can overheat
a limit, that will allow the unit to continue to run, but shuts down the
valve..since its a self resetting Kilxon, when it cools off, it resets the
valve circuit and will fire back up.




  #13   Report Post  
Posted to alt.home.repair
HeatMan
 
Posts: n/a
Default gas furnace- what is normal?


"CBHVAC" wrote in message
...

"HeatMan" wrote in message
.. .

"CBHVAC" wrote in message
...

"HeatMan" wrote in message
...

"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to

cycle
on
and off while the blower continues to run.


No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle

or
is
this typically not normal. not enough air flow...filter, open
registers....thanks bill

No one here can tell you. Its being cause by something, and it could
be
as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second

thread
you've mentioned it in...



Ever seen one with the burn rate set too high?
Can cycle the unit in and out and in and out several times over the
course
of a call for heat.



Never seen that.


On the newer Yorks, Tranes, and Carriers in particular, if you set the gas
valve too high, and dont finalize the heat rise correctly, you can

overheat
a limit, that will allow the unit to continue to run, but shuts down the
valve..since its a self resetting Kilxon, when it cools off, it resets the
valve circuit and will fire back up.


I don't start up those brands any more, but I will remember that...

Thanks.


  #14   Report Post  
Posted to alt.home.repair
Anthony Berlin
 
Posts: n/a
Default gas furnace- what is normal?

It is not brand specific, it applies to any system with a low and high fire
gas valve.




"HeatMan" wrote in message
. ..

"CBHVAC" wrote in message
...

"HeatMan" wrote in message
.. .

"CBHVAC" wrote in message
...

"HeatMan" wrote in message
...

"CBHVAC" wrote in message
...

"bill" wrote in message
...
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to

cycle
on
and off while the blower continues to run.


No.


Its like the high temp
limit switch is closing then reopening (during a cycle where the
thermostst has not been satisfied). should the gas valve cycle

or
is
this typically not normal. not enough air flow...filter, open
registers....thanks bill

No one here can tell you. Its being cause by something, and it

could
be
as
simple as a bad limit, or an improperly set gas valve.



Y'all musta found some funky gas valves lately. This is the second
thread
you've mentioned it in...



Ever seen one with the burn rate set too high?
Can cycle the unit in and out and in and out several times over the
course
of a call for heat.



Never seen that.


On the newer Yorks, Tranes, and Carriers in particular, if you set the

gas
valve too high, and dont finalize the heat rise correctly, you can

overheat
a limit, that will allow the unit to continue to run, but shuts down the
valve..since its a self resetting Kilxon, when it cools off, it resets

the
valve circuit and will fire back up.


I don't start up those brands any more, but I will remember that...

Thanks.




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New high-efficiency gas furnace, old hot water tank - any issues? [email protected] Home Repair 5 August 8th 05 11:04 PM
My Furnace Melted - Preventable? d13f00l Metalworking 10 July 29th 05 12:35 AM
Lennox Furnace Run-on NewGuy Home Repair 7 November 17th 04 05:58 PM
Old Oil Furnace Efficiency Question Vito Cavallo Home Repair 4 November 10th 04 01:07 PM
Furnace Problem...HELP! torque Home Repair 5 January 6th 04 01:24 AM


All times are GMT +1. The time now is 03:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"