gas furnace- what is normal?
Carrier Gas furnace model 58PAV090. What is the normal heating
sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill |
#2
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
bill wrote: Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill Mine did that too, but is a diff model Carrier. Was caused by a slug of water in the draft motor pressure switch tubing. MikeB |
#3
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. |
#4
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
in a working forced air furnace in my basement, the gas burner cycles
on and off while the blower sends the warmed up air to the house until the thermostst is satisfied. the main can't usually run 100 percent of the time or the plenum would get overheated. the system is designed or adjusted at fan in and fan out settings to deliver that range of heat to your registers. if your furnace is not operating properly be more specific with the symptom you have. |
#5
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
mike b's post reminded me to tell you that we've cleared up a
malfunction more than once, cleaning out the silicone updraft flue blower motor tube connection with a paperclip. "Mine did that too, but is a diff model Carrier. Was caused by a slug of water in the draft motor pressure switch tubing. MikeB" |
#6
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"buffalobill" wrote in message oups.com... in a working forced air furnace in my basement, the gas burner cycles on and off while the blower sends the warmed up air to the house until the thermostst is satisfied. the main can't usually run 100 percent of the time or the plenum would get overheated. the system is designed or adjusted at fan in and fan out settings to deliver that range of heat to your registers. if your furnace is not operating properly be more specific with the symptom you have. Here is another one, that has a problem, and has no clue he does...... yes..properly INSTALLED units can run 100% of the time like they are designed to, and never shut the gas off till the thermostat is satisfied. If they are not, somethings wrong.. |
#7
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... |
#8
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
I just wanted to know if gas valve cycling is normal while the
thermostst waits to be satisfied. one says no others say yes.??? anyway...i changed a dirty filter and the valve remeined opened during the complete cycle, which leads me to believe... that gas valve cycling ( on my model) is NOT normal.......Thanks for your inputs and discussion. its all helpful.. Bill On 23 Nov 2005 04:18:12 -0800, "buffalobill" wrote: mike b's post reminded me to tell you that we've cleared up a malfunction more than once, cleaning out the silicone updraft flue blower motor tube connection with a paperclip. "Mine did that too, but is a diff model Carrier. Was caused by a slug of water in the draft motor pressure switch tubing. MikeB" |
#9
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"HeatMan" wrote in message ... "CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... Ever seen one with the burn rate set too high? Can cycle the unit in and out and in and out several times over the course of a call for heat. |
#10
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"bill" wrote in message ... I just wanted to know if gas valve cycling is normal while the thermostst waits to be satisfied. one says no others say yes.??? anyway...i changed a dirty filter and the valve remeined opened during the complete cycle, which leads me to believe... that gas valve cycling ( on my model) is NOT normal.......Thanks for your inputs and discussion. its all helpful.. Bill Well, quite simply...its NOT normal on ANY model made in the last 20 years....or any before that if its installed right. Call for heat from thermostat, valve is open..unless a thermal trips... On 23 Nov 2005 04:18:12 -0800, "buffalobill" wrote: mike b's post reminded me to tell you that we've cleared up a malfunction more than once, cleaning out the silicone updraft flue blower motor tube connection with a paperclip. "Mine did that too, but is a diff model Carrier. Was caused by a slug of water in the draft motor pressure switch tubing. MikeB" |
#11
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"CBHVAC" wrote in message ... "HeatMan" wrote in message ... "CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... Ever seen one with the burn rate set too high? Can cycle the unit in and out and in and out several times over the course of a call for heat. Never seen that. |
#12
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"HeatMan" wrote in message .. . "CBHVAC" wrote in message ... "HeatMan" wrote in message ... "CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... Ever seen one with the burn rate set too high? Can cycle the unit in and out and in and out several times over the course of a call for heat. Never seen that. On the newer Yorks, Tranes, and Carriers in particular, if you set the gas valve too high, and dont finalize the heat rise correctly, you can overheat a limit, that will allow the unit to continue to run, but shuts down the valve..since its a self resetting Kilxon, when it cools off, it resets the valve circuit and will fire back up. |
#13
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
"CBHVAC" wrote in message ... "HeatMan" wrote in message .. . "CBHVAC" wrote in message ... "HeatMan" wrote in message ... "CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... Ever seen one with the burn rate set too high? Can cycle the unit in and out and in and out several times over the course of a call for heat. Never seen that. On the newer Yorks, Tranes, and Carriers in particular, if you set the gas valve too high, and dont finalize the heat rise correctly, you can overheat a limit, that will allow the unit to continue to run, but shuts down the valve..since its a self resetting Kilxon, when it cools off, it resets the valve circuit and will fire back up. I don't start up those brands any more, but I will remember that... Thanks. |
#14
Posted to alt.home.repair
|
|||
|
|||
gas furnace- what is normal?
It is not brand specific, it applies to any system with a low and high fire
gas valve. "HeatMan" wrote in message . .. "CBHVAC" wrote in message ... "HeatMan" wrote in message .. . "CBHVAC" wrote in message ... "HeatMan" wrote in message ... "CBHVAC" wrote in message ... "bill" wrote in message ... Carrier Gas furnace model 58PAV090. What is the normal heating sequence? during the heat cycle, is it normal for the gas to cycle on and off while the blower continues to run. No. Its like the high temp limit switch is closing then reopening (during a cycle where the thermostst has not been satisfied). should the gas valve cycle or is this typically not normal. not enough air flow...filter, open registers....thanks bill No one here can tell you. Its being cause by something, and it could be as simple as a bad limit, or an improperly set gas valve. Y'all musta found some funky gas valves lately. This is the second thread you've mentioned it in... Ever seen one with the burn rate set too high? Can cycle the unit in and out and in and out several times over the course of a call for heat. Never seen that. On the newer Yorks, Tranes, and Carriers in particular, if you set the gas valve too high, and dont finalize the heat rise correctly, you can overheat a limit, that will allow the unit to continue to run, but shuts down the valve..since its a self resetting Kilxon, when it cools off, it resets the valve circuit and will fire back up. I don't start up those brands any more, but I will remember that... Thanks. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
New high-efficiency gas furnace, old hot water tank - any issues? | Home Repair | |||
My Furnace Melted - Preventable? | Metalworking | |||
Lennox Furnace Run-on | Home Repair | |||
Old Oil Furnace Efficiency Question | Home Repair | |||
Furnace Problem...HELP! | Home Repair |