I've been reading deja articles for hours on separate days - but I
would like some quick advice if possible. I'll try to keep the story
short.

Moved into a condo; very old Lennox upflow heating/2-ton air
conditioning unit. 900 sq ft open space (no bedrooms/doors)

The air that comes out of the registers is _somewhat_ cold - but not
cold as I like it to be. As a result, I can only maintain the indoors
temperature at about 78, no lower. I would like to get down to 70 if
possible (outside temp 80-95).

It appears that the previous owner did not have an air filter where the
air got sucked in by the fan... so I put in a new filter. Due to the
way the unit is positioned (basically inside a closet) - I'm not sure
if having a filter is causing a problem by possibly restricting intake
of air.

There is no icing on the pipes at the outside condenser unit as I can
see. The alum fins on the condenser unit looks ok, free of debris. I
had a guy come out and fill it with a pound of R22, he said it was low.
I did notice some improvement, I can go down to about 76 now, but
still I would like to go down further to 70. Am I asking the unit too
much?

What else can I check to narrow down the issue. From reading some
posts, how do I check evap coils (this coil is different than the
condenser right?) & condensor/coil water drain (not sure where this is
located)?

I realize that the AC guy is supposed to be doing this stuff for me,
but to make a long story short I do not get to choose who comes by to
diagnose the unit. In the event I do have to shell out money, I would
like to be informed.

Thanks for any suggestions.

  #2   Report Post  
~^Johnny^~
 
Posts: n/a
Default

-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1

On 27 Jul 2005 19:13:57 -0700, wrote:

I've been reading deja articles for hours on separate days - but I
would like some quick advice if possible. I'll try to keep the
story short.

Moved into a condo; very old Lennox upflow heating/2-ton air
conditioning unit. 900 sq ft open space (no bedrooms/doors)

The air that comes out of the registers is _somewhat_ cold - but not
cold as I like it to be. As a result, I can only maintain the
indoors temperature at about 78, no lower. I would like to get down
to 70 if possible (outside temp 80-95).

It appears that the previous owner did not have an air filter where
the air got sucked in by the fan... so I put in a new filter. Due
to the way the unit is positioned (basically inside a closet) - I'm
not sure if having a filter is causing a problem by possibly
restricting intake of air.

There is no icing on the pipes at the outside condenser unit as I
can see. The alum fins on the condenser unit looks ok, free of
debris. I had a guy come out and fill it with a pound of R22, he
said it was low.
I did notice some improvement, I can go down to about 76 now, but
still I would like to go down further to 70. Am I asking the unit
too much?

What else can I check to narrow down the issue. From reading some
posts, how do I check evap coils (this coil is different than the
condenser right?) & condensor/coil water drain (not sure where this
is located)?

I realize that the AC guy is supposed to be doing this stuff for me,
but to make a long story short I do not get to choose who comes by
to diagnose the unit. In the event I do have to shell out money, I
would like to be informed.

Thanks for any suggestions.



With a severe shortage of refrigerant, the low side can run in a
partial vacuum. If there is a leak on the low side, air and
moisture could have been drawn in when it was running low on
refrigerant. Without fixing the leak and evacuating the system prior
to adding refrigerant, the air and moisture wreaks havoc with the
system.

You might not be able to choose which tech the contractor sends out,
but you certainly can and should choose a different contractor!





-----BEGIN PGP SIGNATURE-----
Version: PGP 7.1

iQA/AwUBQuhLjAIk7T39FC4ZEQL7FgCg+2NgDNe6nRUj010/JeYqMp2vPoEAnjFb
gsGPKp8Os+0lF8KWs9MQJ3i3
=9AhI
-----END PGP SIGNATURE-----

--
-john
wide-open at throttle dot info
  #3   Report Post  
papaya
 
Posts: n/a
Default

try evacuating for 1 hour and recharging the CORRECT manufacture's
recommended amount of virgin R-22 freon

also, comb out all mashed-in places on condenser coil and evaporator coil

with unit off, clean condenser with 1/2 Alki-Foam, and 1/2 water mix
leave on 5 minutes, rinse with hose
http://www.virginiakmp.com/Spec/AKF1.pdf





wrote in message
oups.com...
I've been reading deja articles for hours on separate days - but I
would like some quick advice if possible. I'll try to keep the story
short.

Moved into a condo; very old Lennox upflow heating/2-ton air
conditioning unit. 900 sq ft open space (no bedrooms/doors)

The air that comes out of the registers is _somewhat_ cold - but not
cold as I like it to be. As a result, I can only maintain the indoors
temperature at about 78, no lower. I would like to get down to 70 if
possible (outside temp 80-95).

It appears that the previous owner did not have an air filter where the
air got sucked in by the fan... so I put in a new filter. Due to the
way the unit is positioned (basically inside a closet) - I'm not sure
if having a filter is causing a problem by possibly restricting intake
of air.

There is no icing on the pipes at the outside condenser unit as I can
see. The alum fins on the condenser unit looks ok, free of debris. I
had a guy come out and fill it with a pound of R22, he said it was low.
I did notice some improvement, I can go down to about 76 now, but
still I would like to go down further to 70. Am I asking the unit too
much?

What else can I check to narrow down the issue. From reading some
posts, how do I check evap coils (this coil is different than the
condenser right?) & condensor/coil water drain (not sure where this is
located)?

I realize that the AC guy is supposed to be doing this stuff for me,
but to make a long story short I do not get to choose who comes by to
diagnose the unit. In the event I do have to shell out money, I would
like to be informed.

Thanks for any suggestions.



  #4   Report Post  
meirman
 
Posts: n/a
Default

In alt.home.repair on Thu, 28 Jul 2005 03:02:58 -0400 "papaya"
posted:


also, comb out all mashed-in places on condenser coil and evaporator coil


I've tried that with what we call a butter knife, an all-metal knife
with a slightly serrated blade that isn't sharp enough to cut meat.

And also a small screwdriver iirc.

And I bought a fin comb, and tried that too. One with several sides
for different numbers of fins per inch.

It still seems to take forever. Is their a trick?

Should I use some sort of lubricant? What?

thanks..


Meirman
--
If emailing, please let me know whether
or not you are posting the same letter.
Change domain to erols.com, if necessary.
  #5   Report Post  
udarrell
 
Posts: n/a
Default

wrote:

I've been reading deja articles for hours on separate days - but I
would like some quick advice if possible. I'll try to keep the story
short.

Moved into a condo; very old Lennox upflow heating/2-ton air
conditioning unit. 900 sq ft open space (no bedrooms/doors)

The air that comes out of the registers is _somewhat_ cold - but not
cold as I like it to be. As a result, I can only maintain the indoors
temperature at about 78, no lower. I would like to get down to 70 if
possible (outside temp 80-95).

It appears that the previous owner did not have an air filter where the
air got sucked in by the fan... so I put in a new filter. Due to the
way the unit is positioned (basically inside a closet) - I'm not sure
if having a filter is causing a problem by possibly restricting intake
of air.


How much space is below the furnace closet floor?
Lack of Return Air Grille Area could very well be restricting the
airflow to & through the cooling coil!

Check thoroughly for hot air leaks from the attic down through the wall
petitions to under the air handler!
These are common problems I have found over the years of servicing A/C
systems.
If you have room put large return air filter grilles along the sides
under the furnace closet floor, do so.
This will allow you to have more open air return area for the lint
loading of filters. (See Linked page.)
If you can use the other return filter grilles, if airflow is then not
adequate, remove the furnace filter.


There is no icing on the pipes at the outside condenser unit as I can
see. The alum fins on the condenser unit looks ok, free of debris. I
had a guy come out and fill it with a pound of R22, he said it was low.
I did notice some improvement, I can go down to about 76 now, but
still I would like to go down further to 70. Am I asking the unit too
much?

What else can I check to narrow down the issue. From reading some
posts, how do I check evap coils (this coil is different than the
condenser right?) & condensor/coil water drain (not sure where this is
located)?

I realize that the AC guy is supposed to be doing this stuff for me,
but to make a long story short I do not get to choose who comes by to
diagnose the unit. In the event I do have to shell out money, I would
like to be informed. Thanks for any suggestions


Well, if your "Design Conditions" are similar to mine": 88-dry bulb,
73-wet bulb , around 49% Relative Humidity, then "a mere half ton
6,000-Btu/hr" window shaker with a floor fan setup like mine would get
you to 76-F and to 50% RH even on high humidity days. Your unit is
2-tons or 24,000-Btu/hr, 4 times the capacity of mine!
http://www.udarrell.com/aircondition...harting.h tml


What do you want to bet that your 2-tonner is not getting anywhere near
2-tons of heat transfer from the indoor air to the outdoors!
Also, it must not be reducing the humidity sufficiently or you would
feel very comfortable at 76-F.

My 6,000-Btu/hr Whirlpool remote control room A/C only cost around
$130.00 and cools well within the comfort zone around 920 sq. ft. on the
hottest days imaginable, 112 Heat Index days! Am I a happy camper, you
bet I am!

With the power disconnected check the blower wheel blades; if they are
filled with lint then the evaporator coil is plugged and insulated too.
No system should be charged with refrigerant until it is confirmed that
the evaporator has an optimal heatload being absorbed by it!

The condenser may appear to be clean to you, but could be blocked
between the fins and/or the fins cold be insulated by wrong cleaning
methods such as using oil based detergents when it was cleaned in the
past. (It is very old!) Both coils should be thoroughly cleaned with a
good coil cleaner; the evaporator should be thoroughly cleaned with a
good evaporator cleaner.

Only then, should the system charge be balanced:
http://www.udarrell.com/ac-trouble-s...ubcooling.html

Leave all, these jobs to a good tech! - udarrell

--
Factors in the Correct Sizing of Residential Air Conditioning Systems -
Recommended Procedures for Proper Duct Sizing of Residential Air Conditioning Systems
http://www.udarrell.com/proper_cfm_b...syste ms.html


  #6   Report Post  
Black Adder
 
Posts: n/a
Default

If there has been no filter in your unit then for sure the evap coil is
dirty. That being said, it does not explain the lack of cooling on the
lineset or the air coming out of registers. You need a competent tech
to come and check the whole system over. Could very well be a leak on
an old system on the other hand techs who just "throw in a pound of
freon" because they don't know any better are not helping the
situation. Also the advice to " vacuum the system down and weigh in the
charge" is useless unless you can find out where the system is leaking.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moth Ball Smell in Central Air Conditioner FB Home Repair 30 July 16th 05 04:32 PM
New Central Heating and Cooling [email protected] Home Repair 9 May 6th 05 02:19 AM
Central Air Zones Beartums Home Repair 15 March 14th 05 09:29 PM
Sears For Central Air Conditioner KJ1 Home Repair 18 June 14th 04 05:26 AM
Central A/C cooling fine but humidity seems high D- Home Repair 6 July 3rd 03 08:40 PM


All times are GMT +1. The time now is 02:22 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"