Default Correct sizing of a/c?

With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C is
getting old and I want to replace it with a new one. If this one is sized
correctly I will know what size to look for .

Thank you
--
Walter
www.rationality.net
-


  #2   Report Post  
Joseph Meehan
 
Posts: n/a
Default

Walter R. wrote:
With the outside air at 90 and a RH of 50%, the inside temp at 80,
with a differential of 1.5 degrees, my A/C is on for 30 minutes and
off for 40 minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C
is getting old and I want to replace it with a new one. If this one
is sized correctly I will know what size to look for .

Thank you


Correctly sizing an A/C requires a number of measurements including
insulation windows etc. A local HVAC man can do the calculation for you
(it's called a manual calculation) and advise you of your options.



--
Joseph Meehan

Dia duit


  #3   Report Post  
Tekkie®
 
Posts: n/a
Default

Walter R. posted for all of us...
I don't top post - see either inline or at bottom.

With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C is
getting old and I want to replace it with a new one. If this one is sized
correctly I will know what size to look for .

Thank you

Maybe
--

Tekkie
  #4   Report Post  
Greg O
 
Posts: n/a
Default


"Walter R." wrote in message
...
With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C is
getting old and I want to replace it with a new one. If this one is sized
correctly I will know what size to look for .

Thank you
--
Walter
www.rationality.net
-


Looks to me to be a bit over sized. A Manual J is the only accurate way to
know for sure, anything else is a guess!
My AC runs constantly at 95 degrees and it will maintain a indoor temp of
74. Sized right on in my book!
Greg


  #5   Report Post  
TURTLE
 
Posts: n/a
Default


"Greg O" wrote in message
...

"Walter R." wrote in message
...
With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C is
getting old and I want to replace it with a new one. If this one is sized
correctly I will know what size to look for .

Thank you
--
Walter
www.rationality.net
-


Looks to me to be a bit over sized. A Manual J is the only accurate way to
know for sure, anything else is a guess!
My AC runs constantly at 95 degrees and it will maintain a indoor temp of 74.
Sized right on in my book!
Greg


This is Turtle.

I can keep 70ºF indoors with it 107ºF outdoors. Now it will run about 100% of
the time during the day lite hours. The Manual J said 3.25 tons and I upped to
3.5 tons. That 1/4 ton would make the difference at 107ºF outdoors these days.
Also that 1/4 ton hurts me on a 85ºF outdoor temp with not enough of run time. i
then installed a humidistat to override and keep a 55% RH or below.

TURTLE




  #6   Report Post  
 
Posts: n/a
Default

"Walter R." wrote:

With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly? I would like to know because the A/C is
getting old and I want to replace it with a new one. If this one is sized
correctly I will know what size to look for .

Thank you
--
Walter
www.rationality.net
-


You might want to poke around the web sites of a few mfgs to see if they have
calculators.

Lou


  #7   Report Post  
Stretch
 
Posts: n/a
Default

Turtle,

1/4 ton oversized should not hurt. In the old days we figured up to
25% oversized was OK. Now it is recommended to oversize no more than
15%. Of course, you are sometimes limited by available sizes.


Walter,

If the conditions stated by you are design conditions for your area,
you are WAY oversized! When you are at design conditions, inside and
outside, your unit should run constantle or nearly constantly.

Stretch

  #8   Report Post  
Vic Dura
 
Posts: n/a
Default

On Tue, 26 Jul 2005 01:07:24 GMT, in alt.home.repair Correct
sizing of a/c? "Walter R." wrote:

With the outside air at 90 and a RH of 50%, the inside temp at 80, with a
differential of 1.5 degrees, my A/C is on for 30 minutes and off for 40
minutes.

Is this 3t A/C sized correctly?


IMO, yes.

--
To reply to me directly, remove the CLUTTER from my email address.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stainless barbed insert adapter sizing?? Loren Amelang Metalworking 3 July 19th 05 09:51 PM
How to verify the correct functioning of a varible speed air handler [email protected] Home Repair 0 January 13th 05 07:25 PM
Help sizing a pressure tank Ed in Florida Home Repair 8 April 7th 04 11:12 PM
Sizing electrical wall boxes. volts500 Home Repair 4 July 5th 03 06:13 PM
Gas Weedeater not working when tank is on bottom (correct cutting position) Patch Home Repair 0 July 2nd 03 07:42 PM


All times are GMT +1. The time now is 10:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"