A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been plagued
by computer power supply failures. The supplies fail when apparently many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components. This
has happened to 8 supplies so far. A visible blue flash has been witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS regulator
board floats above chassis potential. Apparently a large potential differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from repeated
arc overs are evindent (the arc that makes it fail is not the 1st time it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors and
getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS





  #2   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
GregS
 
Posts: n/a
Default Computer room static blowing server power supplies

In article , "T" wrote:
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been plagued
by computer power supply failures. The supplies fail when apparently many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components. This
has happened to 8 supplies so far. A visible blue flash has been witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS regulator
board floats above chassis potential. Apparently a large potential differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from repeated
arc overs are evindent (the arc that makes it fail is not the 1st time it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors and
getting past the MOVs to build a potential on the boards.


It sounds like your UPS's should take care of everything.
I woulds have the UPS's checked out. I would have building electricians
check things out. I would have installed whole circuit transient protection
at the breaker box feeding the room.

greg
  #3   Report Post  
Posted to sci.electronics.repair
Eric H
 
Posts: n/a
Default Computer room static blowing server power supplies


"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been
plagued by computer power supply failures. The supplies fail when
apparently many tens of thousands of volts jump from inside the PS around
the switching regulators to the chassis of the supply taking out all the
components. This has happened to 8 supplies so far. A visible blue flash
has been witnessed several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still
happening. The computers are various brands and varoious ages, from 1 week
old to 5 years old. The probelm began occuring 2 months ago. The data
center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via
the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the chassis.
Burn marks from repeated arc overs are evindent (the arc that makes it
fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors
and getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS





I have had this problem before. The servers on site were blowing power
supplies intermittently and corrupting the data on the HDD. After lots of
parts swaps, softeware rebuilds etc the situation was getting extremely
serious. I was called in to investigate.
The site had a large UPS installed. Measuring the voltage with my digital
meter I found the supply varying from approx 198v to 224v over a period of 1
hour. The UPS was isolated but the readings were very similar.
I temporarily installed a mains analyser and when I returned a few days
later, after looking at the printout was amazed to find that the power was
fluctuating between 210v ~ 380v. It should be 220v.

I had a qualified electrician check out the site but he could find no fault.
I then called out the electricity board who discovered an intermittent open
circuit earth in the buildings 3 phase 415v power supply.

This was traced to a connection outside the building underground. After
repair we had no more problems.



  #4   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Ban
 
Posts: n/a
Default Computer room static blowing server power supplies

T wrote:
A raised floor server room with 6 servers, fiber optic patch panels,
large control system cabinets and large UPS system, has been recently
been plagued by computer power supply failures. The supplies fail
when apparently many tens of thousands of volts jump from inside the
PS around the switching regulators to the chassis of the supply
taking out all the components. This has happened to 8 supplies so
far. A visible blue flash has been witnessed several times by
pewrsons in the room.
The servers so far affected are all sitting on the raised computer
center floor. What ususally happens seems to be when a person enters
the 12x20ft room or gets near a server a large snap is heard and the
server is on the backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the
bldg steel, raised floor structure, etc to try to stop this. Its
still happening. The computers are various brands and varoious ages,
from 1 week old to 5 years old. The probelm began occuring 2 months
ago. The data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the
chassis. Burn marks from repeated arc overs are evindent (the arc
that makes it fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these
conductors and getting past the MOVs to build a potential on the
boards.

Any ideas would be appreciated.
TJS


Put a humidifier inside the room, the air is too dry and static electricity
builds up.
--
ciao Ban
Apricale, Italy


  #5   Report Post  
Posted to sci.electronics.repair
Eric H
 
Posts: n/a
Default Computer room static blowing server power supplies


"Ban" wrote in message
...
T wrote:
A raised floor server room with 6 servers, fiber optic patch panels,
large control system cabinets and large UPS system, has been recently
been plagued by computer power supply failures. The supplies fail
when apparently many tens of thousands of volts jump from inside the
PS around the switching regulators to the chassis of the supply
taking out all the components. This has happened to 8 supplies so
far. A visible blue flash has been witnessed several times by
pewrsons in the room.
The servers so far affected are all sitting on the raised computer
center floor. What ususally happens seems to be when a person enters
the 12x20ft room or gets near a server a large snap is heard and the
server is on the backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the
bldg steel, raised floor structure, etc to try to stop this. Its
still happening. The computers are various brands and varoious ages,
from 1 week old to 5 years old. The probelm began occuring 2 months
ago. The data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the
chassis. Burn marks from repeated arc overs are evindent (the arc
that makes it fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these
conductors and getting past the MOVs to build a potential on the
boards.

Any ideas would be appreciated.
TJS


Put a humidifier inside the room, the air is too dry and static
electricity builds up.
--
ciao Ban
Apricale, Italy

********! Load of crap. Some static charge that must be to crack over with
a blue flash. Come on now!




  #6   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
T
 
Posts: n/a
Default Computer room static blowing server power supplies

This was th 1st thing we fixed. The RH was 15%, we raised it to 45% (its
winter). The adjacent control rrom is around 15% .
TJS

"Ban" wrote in message
...
T wrote:
A raised floor server room with 6 servers, fiber optic patch panels,
large control system cabinets and large UPS system, has been recently
been plagued by computer power supply failures. The supplies fail
when apparently many tens of thousands of volts jump from inside the
PS around the switching regulators to the chassis of the supply
taking out all the components. This has happened to 8 supplies so
far. A visible blue flash has been witnessed several times by
pewrsons in the room.
The servers so far affected are all sitting on the raised computer
center floor. What ususally happens seems to be when a person enters
the 12x20ft room or gets near a server a large snap is heard and the
server is on the backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the
bldg steel, raised floor structure, etc to try to stop this. Its
still happening. The computers are various brands and varoious ages,
from 1 week old to 5 years old. The probelm began occuring 2 months
ago. The data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the
chassis. Burn marks from repeated arc overs are evindent (the arc
that makes it fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these
conductors and getting past the MOVs to build a potential on the
boards.

Any ideas would be appreciated.
TJS


Put a humidifier inside the room, the air is too dry and static
electricity builds up.
--
ciao Ban
Apricale, Italy



  #7   Report Post  
Posted to sci.electronics.repair
T
 
Posts: n/a
Default Computer room static blowing server power supplies

Good info, (you must be in europe, 220v!) I will test the UPS circuitry. I
think I need to find a 'sensor' to detect the charge build up on the boards.
Somehow if the supply voltage is not the nominal 120vac and is instead
180vac or so, somehow the regulators are developing tremendous voltages on
the circuit board to jump those gaps.

"Eric H" wrote in message
...

"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been
plagued by computer power supply failures. The supplies fail when
apparently many tens of thousands of volts jump from inside the PS around
the switching regulators to the chassis of the supply taking out all the
components. This has happened to 8 supplies so far. A visible blue flash
has been witnessed several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still
happening. The computers are various brands and varoious ages, from 1
week old to 5 years old. The probelm began occuring 2 months ago. The
data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the chassis.
Burn marks from repeated arc overs are evindent (the arc that makes it
fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors
and getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS





I have had this problem before. The servers on site were blowing power
supplies intermittently and corrupting the data on the HDD. After lots of
parts swaps, softeware rebuilds etc the situation was getting extremely
serious. I was called in to investigate.
The site had a large UPS installed. Measuring the voltage with my digital
meter I found the supply varying from approx 198v to 224v over a period of
1 hour. The UPS was isolated but the readings were very similar.
I temporarily installed a mains analyser and when I returned a few days
later, after looking at the printout was amazed to find that the power was
fluctuating between 210v ~ 380v. It should be 220v.

I had a qualified electrician check out the site but he could find no
fault. I then called out the electricity board who discovered an
intermittent open circuit earth in the buildings 3 phase 415v power
supply.

This was traced to a connection outside the building underground. After
repair we had no more problems.





  #8   Report Post  
Posted to sci.electronics.repair
GregS
 
Posts: n/a
Default Computer room static blowing server power supplies

In article , "T" wrote:
Good info, (you must be in europe, 220v!) I will test the UPS circuitry. I
think I need to find a 'sensor' to detect the charge build up on the boards.
Somehow if the supply voltage is not the nominal 120vac and is instead
180vac or so, somehow the regulators are developing tremendous voltages on
the circuit board to jump those gaps.


I don't think you need a sensor. That blue flash is good enough. Perhaps the exact
point is no known. Regardless, monitor the voltage feeding the supplies, and
the UPS input, and the voltages between ground and neutral.
greg


"Eric H" wrote in message
...

"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been
plagued by computer power supply failures. The supplies fail when
apparently many tens of thousands of volts jump from inside the PS around
the switching regulators to the chassis of the supply taking out all the
components. This has happened to 8 supplies so far. A visible blue flash
has been witnessed several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still
happening. The computers are various brands and varoious ages, from 1
week old to 5 years old. The probelm began occuring 2 months ago. The
data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the chassis.
Burn marks from repeated arc overs are evindent (the arc that makes it
fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors
and getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS





I have had this problem before. The servers on site were blowing power
supplies intermittently and corrupting the data on the HDD. After lots of
parts swaps, softeware rebuilds etc the situation was getting extremely
serious. I was called in to investigate.
The site had a large UPS installed. Measuring the voltage with my digital
meter I found the supply varying from approx 198v to 224v over a period of
1 hour. The UPS was isolated but the readings were very similar.
I temporarily installed a mains analyser and when I returned a few days
later, after looking at the printout was amazed to find that the power was
fluctuating between 210v ~ 380v. It should be 220v.

I had a qualified electrician check out the site but he could find no
fault. I then called out the electricity board who discovered an
intermittent open circuit earth in the buildings 3 phase 415v power
supply.

This was traced to a connection outside the building underground. After
repair we had no more problems.





  #9   Report Post  
Posted to sci.electronics.repair
Eric H
 
Posts: n/a
Default Computer room static blowing server power supplies


"T" wrote in message
...
Good info, (you must be in europe, 220v!) I will test the UPS circuitry. I
think I need to find a 'sensor' to detect the charge build up on the
boards. Somehow if the supply voltage is not the nominal 120vac and is
instead 180vac or so, somehow the regulators are developing tremendous
voltages on the circuit board to jump those gaps.

"Eric H" wrote in message
...

"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels,
large control system cabinets and large UPS system, has been recently
been plagued by computer power supply failures. The supplies fail when
apparently many tens of thousands of volts jump from inside the PS around
the switching regulators to the chassis of the supply taking out all the
components. This has happened to 8 supplies so far. A visible blue flash
has been witnessed several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer
center floor. What ususally happens seems to be when a person enters the
12x20ft room or gets near a server a large snap is heard and the server
is on the backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still
happening. The computers are various brands and varoious ages, from 1
week old to 5 years old. The probelm began occuring 2 months ago. The
data center was built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside of the power supplies. I am thinking about the common power
source, via the power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS
regulator board floats above chassis potential. Apparently a large
potential differnce is building. It jumps a 1 inch gap to the chassis.
Burn marks from repeated arc overs are evindent (the arc that makes it
fail is not the 1st time it occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors
and getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS





I have had this problem before. The servers on site were blowing power
supplies intermittently and corrupting the data on the HDD. After lots of
parts swaps, softeware rebuilds etc the situation was getting extremely
serious. I was called in to investigate.
The site had a large UPS installed. Measuring the voltage with my
digital meter I found the supply varying from approx 198v to 224v over a
period of 1 hour. The UPS was isolated but the readings were very
similar.
I temporarily installed a mains analyser and when I returned a few days
later, after looking at the printout was amazed to find that the power
was fluctuating between 210v ~ 380v. It should be 220v.

I had a qualified electrician check out the site but he could find no
fault. I then called out the electricity board who discovered an
intermittent open circuit earth in the buildings 3 phase 415v power
supply.

This was traced to a connection outside the building underground. After
repair we had no more problems.


Measure the mains input with a Digital meter to check if it is within
specification for your country.

Then hire a mains analyser for a few days to monitor the supply. I presume
you have 3 phase supplies going into the building as we do in the UK. your
problem appears to be a mains supply problem.


  #10   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair
 
Posts: n/a
Default Computer room static blowing server power supplies

T wrote:
[...]

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

[...]
Any ideas would be appreciated.
TJS


A near identical situation was cured simply by spraying the carpet
tiles in the computer room and access corridor, with anti static
solution.
john



  #11   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair
T
 
Posts: n/a
Default Computer room static blowing server power supplies

We have ordered some conductive matting for walking on. Waiting for it while
supplies are failing!

wrote in message
oups.com...
T wrote:
[...]

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

[...]
Any ideas would be appreciated.
TJS


A near identical situation was cured simply by spraying the carpet
tiles in the computer room and access corridor, with anti static
solution.
john



  #12   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair
T
 
Posts: n/a
Default Computer room static blowing server power supplies

My technicians have been testing the grounds to the steel and they are
intact. We have a new fiber pull coming into the room just today via and
existing conduit. The failures have been occuring for almost 2 months but
much more frequently these last 2 weeks.



"petrus bitbyter" wrote in message
l.nl...



Is ground still connected to good old earth? You'll have to check to be
sure. Suppose the metal of the floor and installation has been grounded
carefully but you'll have to check this too. An open ground connection may
be the cause of you problems. Especially an open connection that is closed
again by someone entering the room.

On all PCs and servers I know, the secondary of the power supply has been
connected to the enclosure which in turn is grounded. So I assume the
spark
jumps from the primary of the power supply the the chassis. Looks like
neutral and hot are floating which means that the neutral has not been
connected to ground, at least not properly. (Don't know where neutral
should
be grounded in your place.)

There are other possibillities. Did someone install a badly insulated neon
sign near you? Some other renovation maybe? Something else I can't even
imagine but not very likely. I'm pretty sure something is not grounded
properly anymore, but what?

petrus bitbyter






  #13   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair
Michael A. Terrell
 
Posts: n/a
Default Computer room static blowing server power supplies

T wrote:

My technicians have been testing the grounds to the steel and they are
intact. We have a new fiber pull coming into the room just today via and
existing conduit. The failures have been occuring for almost 2 months but
much more frequently these last 2 weeks.


I would have the electrical system inspected. The power transformer
for the building may not be properly grounded. The ground rod or wiring
may be damaged, leaving the transformer floating above ground.


--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
  #14   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
TJS
 
Posts: n/a
Default Computer room static blowing server power supplies

An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our case
then the blue flash is just a 120/170p-p vac arc to ground, and not a static
discharge.

We are looking at replacing our floor tiles with the modern ultra low static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been

plagued
by computer power supply failures. The supplies fail when apparently many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components.

This
has happened to 8 supplies so far. A visible blue flash has been witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still

happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via

the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS

regulator
board floats above chassis potential. Apparently a large potential

differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from

repeated
arc overs are evindent (the arc that makes it fail is not the 1st time it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors

and
getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS







  #15   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Bennett Price
 
Posts: n/a
Default Computer room static blowing server power supplies

Is the air conditioning overhead supply or raised floor supply?

TJS wrote:
An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our case
then the blue flash is just a 120/170p-p vac arc to ground, and not a static
discharge.

We are looking at replacing our floor tiles with the modern ultra low static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been

plagued
by computer power supply failures. The supplies fail when apparently many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components.

This
has happened to 8 supplies so far. A visible blue flash has been witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still

happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via

the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS

regulator
board floats above chassis potential. Apparently a large potential

differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from

repeated
arc overs are evindent (the arc that makes it fail is not the 1st time it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors

and
getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS









  #16   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Franc Zabkar
 
Posts: n/a
Default Computer room static blowing server power supplies

On Wed, 05 Apr 2006 12:59:59 GMT, "TJS" put finger to
keyboard and composed:

An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our case
then the blue flash is just a 120/170p-p vac arc to ground, and not a static
discharge.

We are looking at replacing our floor tiles with the modern ultra low static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


What are the chances of zinc whiskers causing *exactly* the same fault
in *8* PSUs?

- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.
  #17   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
T
 
Posts: n/a
Default Computer room static blowing server power supplies

I'm skeptical about zinc whiskers and the white paper does come from a
cleaning service company, enough said. But still it is a consideration


"Franc Zabkar" wrote in message
...
On Wed, 05 Apr 2006 12:59:59 GMT, "TJS" put finger to
keyboard and composed:

An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels
are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our
case
then the blue flash is just a 120/170p-p vac arc to ground, and not a
static
discharge.

We are looking at replacing our floor tiles with the modern ultra low
static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


What are the chances of zinc whiskers causing *exactly* the same fault
in *8* PSUs?

- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.



  #18   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
T
 
Posts: n/a
Default Computer room static blowing server power supplies

AC is from overhead

"Bennett Price" wrote in message
m...
Is the air conditioning overhead supply or raised floor supply?

TJS wrote:
An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels
are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper
http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our
case
then the blue flash is just a 120/170p-p vac arc to ground, and not a
static
discharge.

We are looking at replacing our floor tiles with the modern ultra low
static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that
about
the time the problems began

TJS


"T" wrote in message
...
A raised floor server room with 6 servers, fiber optic patch panels,
large
control system cabinets and large UPS system, has been recently been

plagued
by computer power supply failures. The supplies fail when apparently
many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components.

This
has happened to 8 supplies so far. A visible blue flash has been
witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer
center
floor. What ususally happens seems to be when a person enters the
12x20ft
room or gets near a server a large snap is heard and the server is on
the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still

happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the
inside
of the power supplies. I am thinking about the common power source, via

the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS

regulator
board floats above chassis potential. Apparently a large potential

differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from

repeated
arc overs are evindent (the arc that makes it fail is not the 1st time
it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors

and
getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS







  #19   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Franc Zabkar
 
Posts: n/a
Default Computer room static blowing server power supplies

On Wed, 5 Apr 2006 22:05:11 -0400, "T" put finger to
keyboard and composed:

I'm skeptical about zinc whiskers and the white paper does come from a
cleaning service company, enough said. But still it is a consideration


I wonder why the arc jumps a 1" gap between the chopper and the
chassis. Why not the much smaller (?) gap on the underside of the PCB?

- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.
  #20   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
GregS
 
Posts: n/a
Default Computer room static blowing server power supplies

In article , wrote:
On Wed, 05 Apr 2006 12:59:59 GMT, "TJS" put finger to
keyboard and composed:

An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper
http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our case
then the blue flash is just a 120/170p-p vac arc to ground, and not a static
discharge.

We are looking at replacing our floor tiles with the modern ultra low static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


What are the chances of zinc whiskers causing *exactly* the same fault
in *8* PSUs?


Identical or different?


  #21   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
James Sweet
 
Posts: n/a
Default Computer room static blowing server power supplies

T wrote:
A raised floor server room with 6 servers, fiber optic patch panels, large
control system cabinets and large UPS system, has been recently been plagued
by computer power supply failures. The supplies fail when apparently many
tens of thousands of volts jump from inside the PS around the switching
regulators to the chassis of the supply taking out all the components. This
has happened to 8 supplies so far. A visible blue flash has been witnessed
several times by pewrsons in the room.

The servers so far affected are all sitting on the raised computer center
floor. What ususally happens seems to be when a person enters the 12x20ft
room or gets near a server a large snap is heard and the server is on the
backup redundant PS, if it has not already failed.

We have been adding grounding bonding from all computer case to the bldg
steel, raised floor structure, etc to try to stop this. Its still happening.
The computers are various brands and varoious ages, from 1 week old to 5
years old. The probelm began occuring 2 months ago. The data center was
built 12 years ago.

We are at a loss to figure out how the charge is building up on the inside
of the power supplies. I am thinking about the common power source, via the
power cords Hot, Neutral and Ground conductor.

The green wire should be bonded to the PC case. Apparently the PS regulator
board floats above chassis potential. Apparently a large potential differnce
is building. It jumps a 1 inch gap to the chassis. Burn marks from repeated
arc overs are evindent (the arc that makes it fail is not the 1st time it
occurs!)

The Hot and Nuetral..how could a charge be coming in on these conductors and
getting past the MOVs to build a potential on the boards.


Any ideas would be appreciated.
TJS







I think static is highly unlikely as the cause here. My guess would be
overvoltage on the line, transients, or inadequate cooling.
  #22   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Rich The Newsgroup Wacko
 
Posts: n/a
Default Computer room static blowing server power supplies

On Tue, 04 Apr 2006 16:41:57 -0400, T wrote:
....
potential differnce is building. It jumps a 1 inch gap to the chassis.
Burn marks from repeated arc overs are evindent (the arc that makes it
fail is not the 1st time it occurs!)

Any ideas would be appreciated.


Call an exorcist. ;-)
--
Cheers!
Rich
------
"If you find for your verse there's no call,
And you can't afford paper at all,
For the true poet born,
However forlorn,
There is always the lavat'ry wall."

  #23   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Rich Grise
 
Posts: n/a
Default Computer room static blowing server power supplies

On Wed, 05 Apr 2006 12:59:59 +0000, TJS wrote:

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began


Well, skeptical is good, but usually when troubleshooting, the first
question is, "What changed?"

This is a no-brainer. Start looking through your contract with the floor
installer, to see if you can have him eat the cost of replacing the killer
tile.

Good Luck!
Rich


  #24   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Rich Grise
 
Posts: n/a
Default Computer room static blowing server power supplies

On Thu, 06 Apr 2006 08:05:33 +1000, Franc Zabkar wrote:

On Wed, 05 Apr 2006 12:59:59 GMT, "TJS" put finger to
keyboard and composed:

An update; We are investigating "zinc whiskers" phenomina as a possible
cause. The zinc filaments are produced from the plywood core floor panels
supported by the zinc electrocoted support structure. When floor panels are
lifted or disturbed the conductive dust can get into the power supply and
lead to shorts between the modern closely spaced SMT devices.
See here for a white paper http://www.dataclean.com/pdf/zincwhiskers3.pdf

The failures/arcs in our supplies have all arced from the 120vac chopper
regulator collector to the PS case. If the zinc whisker problem is our case
then the blue flash is just a 120/170p-p vac arc to ground, and not a static
discharge.

We are looking at replacing our floor tiles with the modern ultra low static
floor tiles.

I'm a little skeptical that this is the problem, but it is true that 2
months ago we pulled floor tiles to look for fiber conduits and that about
the time the problems began

TJS


What are the chances of zinc whiskers causing *exactly* the same fault
in *8* PSUs?


Pretty good, considering that the tiles are the only thing that changed.

I probably wouldn't say, "zinc whiskers", but I'm pretty sure that, except
for galvanizing garbage cans, zinc is AWFUL! It gets all over everything.
I once worked at a place where they had to scrap a $100,000.00 (or so)
Ultra-High-Vacuum bell jar because someone had installed brass connectors -
the zinc outgassed, and contaminated the whole thing.

Maybe you could leach the zinc out of your tile by washing it down with
muriatic acid. ;-) [1]

I've also seen an installation where a bunch of boxes running off 277V
lighting power started arcing, and the only conductive thing in the room
was the dust from the desert setting, which could very well have been
conductive - it was only about 100 miles from Great Salt Lake. We fixed
it by putting furnace filters on top of all of the boxes, which the idiot
designer had put all of the intake air vents on the top of. =:-O

It was a pretty sweet TDY[2], though - $1000.00/week plus per diem plus
expenses plus airplane ticket plus car rental. ;-)

Good Luck!
Rich
[1] That's a joke, by the way. If you do use muriatic acid on zinc, be
sure that you're in a very very well-ventilated place, because it makes
hydrogen gas. But then, you could use the zinc chloride for sunscreen;
just mix it with yogurt. ;-)
[2] Temporary DutY



  #25   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Rich Grise, but drunk
 
Posts: n/a
Default Computer room static blowing server power supplies

On Thu, 06 Apr 2006 16:42:35 +1000, Franc Zabkar wrote:

On Wed, 5 Apr 2006 22:05:11 -0400, "T" put finger to
keyboard and composed:

I'm skeptical about zinc whiskers and the white paper does come from a
cleaning service company, enough said. But still it is a consideration


I wonder why the arc jumps a 1" gap between the chopper and the
chassis. Why not the much smaller (?) gap on the underside of the PCB?

- Franc Zabkar


Poltergeists.

Cheers!
Rich
--
-----BEGIN GEEK CODE BLOCK-----
Version: 3.1
GAT(E P) dpu s: a++ C++@ P+ L+++ !E W+ N++ o? K? w-- !O !M !V PS+++
PE Y+ PGP- t 5+++)-; X- R- tv+ b+ DI+++++ D-? G e+$ h+ r-- z+
------END GEEK CODE BLOCK------



  #26   Report Post  
Posted to sci.electronics.basics,sci.electronics.equipment,sci.electronics.repair,sci.engr.electrical
Franc Zabkar
 
Posts: n/a
Default Computer room static blowing server power supplies

On Fri, 07 Apr 2006 22:56:16 GMT, Rich Grise
put finger to keyboard and composed:

What are the chances of zinc whiskers causing *exactly* the same fault
in *8* PSUs?


Pretty good, considering that the tiles are the only thing that changed.


The OP states that "the failures/arcs in our supplies have all arced
from the 120vac chopper regulator collector to the PS case."

I would have thought that zinc whiskers would result in random faults.

- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cooling Server Room Richard Conway UK diy 13 July 3rd 05 10:15 PM
pc power supply failure? Al Electronics Repair 9 January 23rd 05 11:15 PM
OT Guns more Guns Cliff Metalworking 519 December 12th 04 05:52 AM
Heat banks (again!) Dave UK diy 148 September 6th 04 08:45 PM


All times are GMT +1. The time now is 02:52 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"