Finished wiring the wood-shop area. All in conduit, 12 quadplex wall outlets, and four fluorescent lights on three way switches. Also a 220V feed to the air compressor. New sub-panel in wood shop is fed by an other sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp breaker feeding the wood shop sub panel. All wiring within conduit is #12 except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would go to the breaker, turn it on and check the outlet with a clamp lamp and then turn off the breaker for further work. When I was installing the outlet group # 11, the wires shifted withing the conduit and the hot wire in # 12 touched the metal box. (Yes, I didn't cap the wires while I was working, I simply bent them out of each other's way. Stupid) Anyway, the question is "why did the 50 amp breaker feeding my sup panel break instead of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same thing happened. I dislodged the safety shield on the belt, the fan blade could not turn and ergo the motor drew too many amps on start-up. Again, instead of the 30 amp circuit feeding the compressor breaking, it's the 50 amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose everything and am left in the dark. Have to get a flashlight, go outside one building and into another to access the other side of the wall.

All comments and advise appreciated.

Ivan Vegvary
  #2   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,710
Default electrical question (wood shop)

Ivan Vegvary wrote:


Is the 50 amp breaker simply too sensitive?


It sounds like that's exactly the case. Since it's used, it may have been
tripped many times in its past life, which does change its sensativity.

--

-Mike-



  #3   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,648
Default electrical question (wood shop)

Ivan Vegvary wrote in
:

[...]
Anyway, the question is "why did the 50 amp breaker feeding my
sup panel break instead of the 20 amp breaker withing the sub
panel"?

[...]
Is the 50 amp breaker simply too sensitive?


Well, it's *more* sensitive, anyway. That doesn't mean, necessarily, that it's *too* sensitive (i.e.
more sensitive than it's supposed to be). It could be that way by design.
  #4   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 511
Default electrical question (wood shop)

On 8/31/2012 11:21 AM, Doug Miller wrote:
Ivan wrote in
:

[...]
Anyway, the question is "why did the 50 amp breaker feeding my
sup panel break instead of the 20 amp breaker withing the sub
panel"?

[...]
Is the 50 amp breaker simply too sensitive?


Well, it's *more* sensitive, anyway. That doesn't mean, necessarily, that it's *too* sensitive (i.e.
more sensitive than it's supposed to be). It could be that way by design.



Although I don't have Doug's electrical expertise, I was thinking that
the surge was just that, a surge. It's wasn't like the turning the flow
from a water faucet from low to high. It was more like turning the
flow from low to "Niagara Falls"!

CB'ers supposedly handle motor start-up better than fuses(don't they?),
clearly due to a delay. I think it's built into the mechanics of the
CB'er. Maybe this delay is a measurable feature of the 2 CB'ers involved?
  #5   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,710
Default electrical question (wood shop)

Bill wrote:


Although I don't have Doug's electrical expertise, I was thinking that
the surge was just that, a surge. It's wasn't like the turning the
flow from a water faucet from low to high. It was more like turning
the flow from low to "Niagara Falls"!


Not so bad an analogy, but it does not address the real question - why did
the 50A breaker trip and not the 20A. Keep working on it Bill - though
admitedly, it is a bit of speculation after the fact like this.


CB'ers supposedly handle motor start-up better than fuses(don't
they?), clearly due to a delay. I think it's built into the
mechanics of the CB'er. Maybe this delay is a measurable feature of
the 2 CB'ers involved?


Actually, slow blow fuses can perform better than breakers when it comes to
start up current. The operative word is "can". As far as the "measurable
feature of 2 CB's involved" - not even sure what that means, but the short
answer is... likely, no.

--

-Mike-





  #6   Report Post  
Posted to rec.woodworking
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical question (wood shop)

On 8/31/2012 12:06 PM, Mike Marlow wrote:
....

... As far as the "measurable
feature of 2 CB's involved" - not even sure what that means, ...


Circuit breakers have time response curves, too; there are ones
specifically for motor applications as well just as "slo-blo" fuses.

It's possible one of OPs is but it'll be knowable by looking at the
actual manufacturer's part no's...

As for tripping a 50A breaker ahead of a 20A when the short is on that
20A circuit--that ain't the way it should operate, no.

I'd suspect the 50A is the culprit here--check that it's not warm to
touch when operating normally; they will fail w/ age and that's often a
clue.

--
  #7   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 12,155
Default electrical question (wood shop)

On 8/31/2012 12:06 PM, Mike Marlow wrote:
Bill wrote:


Although I don't have Doug's electrical expertise, I was thinking that
the surge was just that, a surge. It's wasn't like the turning the
flow from a water faucet from low to high. It was more like turning
the flow from low to "Niagara Falls"!


Not so bad an analogy, but it does not address the real question - why did
the 50A breaker trip and not the 20A. Keep working on it Bill - though
admitedly, it is a bit of speculation after the fact like this.


CB'ers supposedly handle motor start-up better than fuses(don't
they?), clearly due to a delay. I think it's built into the
mechanics of the CB'er. Maybe this delay is a measurable feature of
the 2 CB'ers involved?


Actually, slow blow fuses can perform better than breakers when it comes to
start up current. The operative word is "can". As far as the "measurable
feature of 2 CB's involved" - not even sure what that means, but the short
answer is... likely, no.


We have a new home and had a problem with a breaker, it clearly was
rated high enough to perform the task. The electrician that came out to
replace the breaker indicated that the typical modern breaker is
designed to blow up at up to 20% below the rating. BS or not, this is
not the first time I have heard this.

In my old shop I was running a compressor and freezer on the same
circuit. If I added my router and fan the 15 amp breaker would some
times trip. In the new house on a 20 amp dedicated circuit the breaker
often tripped with only the compressor and freezer. So now the freezer
runs on a separate 15 amp circuit and the compressor and drum sander run
on the 20 amp. No more problems.
  #8   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,377
Default electrical question (wood shop)

Leon lcb11211@swbelldotnet writes:

We have a new home and had a problem with a breaker, it clearly was
rated high enough to perform the task. The electrician that came out to
replace the breaker indicated that the typical modern breaker is
designed to blow up at up to 20% below the rating. BS or not, this is
not the first time I have heard this.


IIRC, the code requires that a circuit be loaded to no more than 80%
ampacity, derated by temperature and raceway loading.

As for the OP, if the 50 is upstream of the 20, and the 50 blows
first on a dead short, the 20 should be replaced ASAP.

scott

  #9   Report Post  
Posted to rec.woodworking
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical question (wood shop)

On 8/31/2012 1:16 PM, Scott Lurndal wrote:
....

As for the OP, if the 50 is upstream of the 20, and the 50 blows
first on a dead short, the 20 should be replaced ASAP.

....

Excepting (unless he mistyped) the 20A is supposedly a brand new breaker
while the 50A is used. I'm suspecting the 50A (or something else isn't
kosher that's totally impossible to diagnose from here).

--
  #10   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,710
Default electrical question (wood shop)

dpb wrote:
On 8/31/2012 1:16 PM, Scott Lurndal wrote:
...

As for the OP, if the 50 is upstream of the 20, and the 50 blows
first on a dead short, the 20 should be replaced ASAP.

...

Excepting (unless he mistyped) the 20A is supposedly a brand new
breaker while the 50A is used. I'm suspecting the 50A (or something
else isn't kosher that's totally impossible to diagnose from here).


Not to mention that if I recall correctly, there were more than on sub panel
breakers that exhibited this same symptom - so, both of them passed the
current to the sub-panel feed. That would seem to point to the sub-panel
feed.

--

-Mike-





  #11   Report Post  
Posted to rec.woodworking
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical question (wood shop)

On 8/31/2012 1:02 PM, Leon wrote:
....

We have a new home and had a problem with a breaker, it clearly was
rated high enough to perform the task. The electrician that came out to
replace the breaker indicated that the typical modern breaker is
designed to blow up at up to 20% below the rating. BS or not, this is
not the first time I have heard this.

....

You can always go to manufacturer datasheets and see...eg,

http://products.schneider-electric.us/support/technical-library/?event=detail&oid=0900892680117fff&cat=0b008926800 fd695

--
  #12   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 12,155
Default electrical question (wood shop)

On 8/31/2012 1:16 PM, Scott Lurndal wrote:
Leon lcb11211@swbelldotnet writes:

We have a new home and had a problem with a breaker, it clearly was
rated high enough to perform the task. The electrician that came out to
replace the breaker indicated that the typical modern breaker is
designed to blow up at up to 20% below the rating. BS or not, this is
not the first time I have heard this.


IIRC, the code requires that a circuit be loaded to no more than 80%
ampacity, derated by temperature and raceway loading.


Well that would support the design of modern breakers to enforce that
code. ;~)


As for the OP, if the 50 is upstream of the 20, and the 50 blows
first on a dead short, the 20 should be replaced ASAP.


Now that is a logical safe first step to diagnosis.

  #13   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,377
Default electrical question (wood shop)

dpb writes:
On 8/31/2012 1:16 PM, Scott Lurndal wrote:
...

As for the OP, if the 50 is upstream of the 20, and the 50 blows
first on a dead short, the 20 should be replaced ASAP.

...

Excepting (unless he mistyped) the 20A is supposedly a brand new breaker
while the 50A is used. I'm suspecting the 50A (or something else isn't
kosher that's totally impossible to diagnose from here).


Assuming everything was wired correctly, and the 20 isn't a delayed trip device,
perhaps the 50 trips more quickly. But I agree with the "totally impossible to diagnose from here".

scott
  #15   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,559
Default electrical question (wood shop)

Bill wrote in
:



Although I don't have Doug's electrical expertise, I was thinking that
the surge was just that, a surge. It's wasn't like the turning the
flow
from a water faucet from low to high. It was more like turning the
flow from low to "Niagara Falls"!

CB'ers supposedly handle motor start-up better than fuses(don't
they?), clearly due to a delay. I think it's built into the mechanics
of the CB'er. Maybe this delay is a measurable feature of the 2
CB'ers involved?


It's possible that the current drawn would exceed the current ratings of
both circuit breakers, and in that case there would be a race condition
to see which one trips first. The used 50A breaker might move easier, so
it would tend to win that race.

Replacing the 50A breaker might let the 20A breaker "win the race" more
often. This doesn't eliminate the race condition, so the main might go
first on a dead short every now and again.

Puckdropper
--
Make it to fit, don't make it fit.


  #16   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 576
Default electrical question (wood shop)

On Thu, 30 Aug 2012 21:04:39 -0700 (PDT), Ivan Vegvary
wrote:

Finished wiring the wood-shop area. All in conduit, 12 quadplex wall outlets, and four fluorescent lights on three way switches. Also a 220V feed to the air compressor. New sub-panel in wood shop is fed by an other sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp breaker feeding the wood shop sub panel. All wiring within conduit is #12 except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would go to the breaker, turn it on and check the outlet with a clamp lamp and then turn off the breaker for further work. When I was installing the outlet group # 11, the wires shifted withing the conduit and the hot wire in # 12 touched the metal box. (Yes, I didn't cap the wires while I was working, I simply bent them out of each other's way. Stupid) Anyway, the question is "why did the 50 amp breaker feeding my sup panel break instead of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same thing happened. I dislodged the safety shield on the belt, the fan blade could not turn and ergo the motor drew too many amps on start-up. Again, instead of the 30 amp circuit feeding the compressor breaking, it's the 50 amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose everything and am left in the dark. Have to get a flashlight, go outside one building and into another to access the other side of the wall.

All comments and advise appreciated.

You don't say whether all the breakers are the same manufacturer.
Actually had that happen in a computer center where a 125 amp breaker
would trip before the 30 amp parking area breaker. Of course it
always led to a 2AM call out so we found that problem quickly. Anyway
you have two variables which is the short circuit trip time and the
overload trip time. Possible this was the result of the dead short so
you might not have to do anything. Possible a defective breaker, most
likely the one tripping to fast. A possible problem of a poor ground
path to the first breaker.

Mike M
  #17   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,710
Default electrical question (wood shop)

Puckdropper wrote:

It's possible that the current drawn would exceed the current ratings
of both circuit breakers, and in that case there would be a race
condition to see which one trips first. The used 50A breaker might
move easier, so it would tend to win that race.


No race condition at all if both breakers are working at rated capacities.
At rated capacities, a 20A breaker will trip before a 50A breaker. By your
own statement above... " It's possible that the current drawn would exceed
the current ratings of both circuit breakers", which should result in the
20A op3ning first. Obviously, there is a problem, because this is not
happening. But - to throw black magic at it is no solution to the problem.
"Maybe, kinda sorta" stuff has no place in this kind of conversation.


Replacing the 50A breaker might let the 20A breaker "win the race"
more often. This doesn't eliminate the race condition, so the main
might go first on a dead short every now and again.


Do you understand electricity at all?


--

-Mike-



  #18   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 3,350
Default electrical question (wood shop)

Somebody wrote:

The used 50A breaker might move easier, so
it would tend to win that race.

-----------------------------------
All bets are off.

A thermal-magnetic, molded case, plug-in cbk'r is a single use device.

They are a single use device that provides inrush (magnetic) or
inverse time delay (thermal) protection.

These cbk'rs only have to clear a fault ONCE to meet design spec.

There is no such thing as a USED cbk'r that you can trust.

Lew




  #19   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 170
Default electrical question (wood shop)

It happens that Mike M formulated :
On Thu, 30 Aug 2012 21:04:39 -0700 (PDT), Ivan Vegvary
wrote:

Finished wiring the wood-shop area. All in conduit, 12 quadplex wall
outlets, and four fluorescent lights on three way switches. Also a 220V
feed to the air compressor. New sub-panel in wood shop is fed by an other
sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp
breaker feeding the wood shop sub panel. All wiring within conduit is #12
except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would
go to the breaker, turn it on and check the outlet with a clamp lamp and
then turn off the breaker for further work. When I was installing the
outlet group # 11, the wires shifted withing the conduit and the hot wire in
# 12 touched the metal box. (Yes, I didn't cap the wires while I was
working, I simply bent them out of each other's way. Stupid) Anyway, the
question is "why did the 50 amp breaker feeding my sup panel break instead
of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same
thing happened. I dislodged the safety shield on the belt, the fan blade
could not turn and ergo the motor drew too many amps on start-up. Again,
instead of the 30 amp circuit feeding the compressor breaking, it's the 50
amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is
new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose
everything and am left in the dark. Have to get a flashlight, go outside
one building and into another to access the other side of the wall.

All comments and advise appreciated.

You don't say whether all the breakers are the same manufacturer.
Actually had that happen in a computer center where a 125 amp breaker
would trip before the 30 amp parking area breaker. Of course it
always led to a 2AM call out so we found that problem quickly. Anyway
you have two variables which is the short circuit trip time and the
overload trip time. Possible this was the result of the dead short so
you might not have to do anything. Possible a defective breaker, most
likely the one tripping to fast. A possible problem of a poor ground
path to the first breaker.

Mike M


Can you explain what part a ground plays in a simple 2 terminal
breaker?

--
John G


  #20   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 408
Default electrical question (wood shop)

Problem solved! Thanks for all the help.
Scrounged around for another breaker and found a 40 amp double (240 volt). Replaced the suspect 50 with the 40 and all is O.K. If I force a short in the 20 amp circuit the 20 amp now breaks and the upstream 40 amp holds. Obviously the 50 amp breaker was bad. (proved it by putting it back in and forcing a short)
BTW, I force a short by plugging in a shorted power cord. (Doesn't everybody in this group cut off the power cord on a tool prior to throwing it away?)

Thanks again, you guys are wonderful!

Ivan Vegvary



  #21   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 9,025
Default electrical question (wood shop)

On Fri, 31 Aug 2012 23:21:50 -0700 (PDT), Ivan Vegvary
wrote:

Problem solved! Thanks for all the help.
Scrounged around for another breaker and found a 40 amp double (240 volt). Replaced the suspect 50 with the 40 and all is O.K. If I force a short in the 20 amp circuit the 20 amp now breaks and the upstream 40 amp holds. Obviously the 50 amp breaker was bad. (proved it by putting it back in and forcing a short)
BTW, I force a short by plugging in a shorted power cord. (Doesn't everybody in this group cut off the power cord on a tool prior to throwing it away?)

Thanks again, you guys are wonderful!

Ivan Vegvary


Jeeze, Ivan. We usually remove the plug from the outlet before cutting
the cord. "Forcing a short" indeed!

--
I have the consolation of having added nothing to my private fortune during
my public service, and of retiring with hands clean as they are empty.
-- Thomas Jefferson, letter to Count Diodati, 1807

Too bad -none- of the current CONgresscritters are willing to do that. -LJ
  #22   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,648
Default electrical question (wood shop)

"Mike Marlow" wrote in news:45b12$504180ab
:

Puckdropper wrote:

It's possible that the current drawn would exceed the current ratings
of both circuit breakers, and in that case there would be a race
condition to see which one trips first. The used 50A breaker might
move easier, so it would tend to win that race.


No race condition at all if both breakers are working at rated capacities.
At rated capacities, a 20A breaker will trip before a 50A breaker.


Not necessarily, Mike -- it depends on the speed with which the breaker reacts to the
overcurrent. If the overcurrent is, say, 40A, of course the 20A breaker should trip first,
because the 50A breaker should not trip at all. But a dead short may result in a brief current
of well over 50A, in which case the breaker that trips will be the one that reacts fastest.

In this case, with a used 50A breaker and a new 20A breaker, one would expect the 50A
breaker to trip a little faster when subjected to a current of, say, 100A.

Even if they're both brand-new, and even if both have the same *design* trip speed, they
still won't respond at *exactly* the same speed, simply due to normal statistical variability in
the manufacturing process. Suppose the breakers are designed to trip within 10ms +/- 0.5%
when an overcurrent occurs -- if the actual trip delay is 9.95ms for the 50A breaker, and
10.05ms for the 20A, they're both within design specifications, but on a 100A overcurrent the
50A breaker will go first every time.

By your
own statement above... " It's possible that the current drawn would exceed
the current ratings of both circuit breakers", which should result in the
20A op3ning first.


No, it should not. It should result in the fastest-reacting breaker opening first. The reaction
speed of a breaker is *not* dependent on its amperage rating.

Obviously, there is a problem, because this is not
happening. But - to throw black magic at it is no solution to the problem.
"Maybe, kinda sorta" stuff has no place in this kind of conversation.


Replacing the 50A breaker might let the 20A breaker "win the race"
more often. This doesn't eliminate the race condition, so the main
might go first on a dead short every now and again.


Do you understand electricity at all?

I think you owe Puckdropper an apology for that. He's more nearly right than you are.

  #23   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,171
Default electrical question (wood shop)

On 8/31/2012 10:21 AM, Doug Miller wrote:
Ivan Vegvary wrote in
:

[...]
Anyway, the question is "why did the 50 amp breaker feeding my
sup panel break instead of the 20 amp breaker withing the sub
panel"?

[...]
Is the 50 amp breaker simply too sensitive?


Well, it's *more* sensitive, anyway. That doesn't mean, necessarily, that it's *too* sensitive (i.e.
more sensitive than it's supposed to be). It could be that way by design.


Any consideration given to the 20AMP being defective?




  #24   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 5,710
Default electrical question (wood shop)

Doug Miller wrote:


I think you owe Puckdropper an apology for that. He's more nearly
right than you are.


Point taken on the speed of each breaker affecting which will open first. I
will offer that apology to Puckdropper, however I wouldn't go so far as to
say more nearly right. You are - as is he, correct that the speed of each
breaker is the factor, but there is a 50/50 chance on either one of them
being faster just based on manufacturing limitations. Well taken point
Doug.

--

-Mike-



  #25   Report Post  
Posted to rec.woodworking
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical question (wood shop)

On 9/1/2012 7:47 PM, Mike Marlow wrote:
....


... but there is a 50/50 chance on either one of them
being faster just based on manufacturing limitations ...


Well, only if the two responses are nominally identical...which wouldn't
be necessarily so at all.

--


  #26   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,648
Default electrical question (wood shop)

Unquestionably Confused wrote in news:50428439$0$15608
:

On 8/31/2012 10:21 AM, Doug Miller wrote:
Ivan Vegvary wrote in
:

[...]
Anyway, the question is "why did the 50 amp breaker feeding my
sup panel break instead of the 20 amp breaker withing the sub
panel"?

[...]
Is the 50 amp breaker simply too sensitive?


Well, it's *more* sensitive, anyway. That doesn't mean, necessarily, that it's *too*

sensitive (i.e.
more sensitive than it's supposed to be). It could be that way by design.


Any consideration given to the 20AMP being defective?


While certainly possible, I'd consider it to be pretty unlikely -- the OP stated that the 20A
breaker is new, and the 50A is used.
  #27   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,171
Default electrical question (wood shop)

On 9/2/2012 6:34 PM, Doug Miller wrote:

Well, it's *more* sensitive, anyway. That doesn't mean, necessarily, that it's *too*

sensitive (i.e.
more sensitive than it's supposed to be). It could be that way by design.


Any consideration given to the 20AMP being defective?


While certainly possible, I'd consider it to be pretty unlikely -- the OP stated that the 20A
breaker is new, and the 50A is used.


I agree that it is unlikely, but we BOTH agree that it is possible.
Quality Control isn't always controllingg

Logically, it's worth looking at and swapping out the breaker to make
certain that is NOT the case, especially when a dead short on that
circuit won't trip the 20A breaker but will flip the 50A.




  #30   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 576
Default electrical question (wood shop)

On Sat, 01 Sep 2012 15:55:42 +1000, John G
wrote:

It happens that Mike M formulated :
On Thu, 30 Aug 2012 21:04:39 -0700 (PDT), Ivan Vegvary
wrote:

Finished wiring the wood-shop area. All in conduit, 12 quadplex wall
outlets, and four fluorescent lights on three way switches. Also a 220V
feed to the air compressor. New sub-panel in wood shop is fed by an other
sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp
breaker feeding the wood shop sub panel. All wiring within conduit is #12
except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would
go to the breaker, turn it on and check the outlet with a clamp lamp and
then turn off the breaker for further work. When I was installing the
outlet group # 11, the wires shifted withing the conduit and the hot wire in
# 12 touched the metal box. (Yes, I didn't cap the wires while I was
working, I simply bent them out of each other's way. Stupid) Anyway, the
question is "why did the 50 amp breaker feeding my sup panel break instead
of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same
thing happened. I dislodged the safety shield on the belt, the fan blade
could not turn and ergo the motor drew too many amps on start-up. Again,
instead of the 30 amp circuit feeding the compressor breaking, it's the 50
amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is
new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose
everything and am left in the dark. Have to get a flashlight, go outside
one building and into another to access the other side of the wall.

All comments and advise appreciated.

You don't say whether all the breakers are the same manufacturer.
Actually had that happen in a computer center where a 125 amp breaker
would trip before the 30 amp parking area breaker. Of course it
always led to a 2AM call out so we found that problem quickly. Anyway
you have two variables which is the short circuit trip time and the
overload trip time. Possible this was the result of the dead short so
you might not have to do anything. Possible a defective breaker, most
likely the one tripping to fast. A possible problem of a poor ground
path to the first breaker.

Mike M


Can you explain what part a ground plays in a simple 2 terminal
breaker?


Simple you can have a line to line short, or a short to ground. If it
is a short to ground and you have a poor ground path the breaker may
sense it more as an overload then a short and not trip or take longer
to trip.


  #31   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 9,025
Default electrical question (wood shop)

On Mon, 03 Sep 2012 08:49:35 -0700, Mike M
wrote:

On Sat, 01 Sep 2012 15:55:42 +1000, John G
wrote:

It happens that Mike M formulated :
On Thu, 30 Aug 2012 21:04:39 -0700 (PDT), Ivan Vegvary
wrote:

Finished wiring the wood-shop area. All in conduit, 12 quadplex wall
outlets, and four fluorescent lights on three way switches. Also a 220V
feed to the air compressor. New sub-panel in wood shop is fed by an other
sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp
breaker feeding the wood shop sub panel. All wiring within conduit is #12
except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would
go to the breaker, turn it on and check the outlet with a clamp lamp and
then turn off the breaker for further work. When I was installing the
outlet group # 11, the wires shifted withing the conduit and the hot wire in
# 12 touched the metal box. (Yes, I didn't cap the wires while I was
working, I simply bent them out of each other's way. Stupid) Anyway, the
question is "why did the 50 amp breaker feeding my sup panel break instead
of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same
thing happened. I dislodged the safety shield on the belt, the fan blade
could not turn and ergo the motor drew too many amps on start-up. Again,
instead of the 30 amp circuit feeding the compressor breaking, it's the 50
amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is
new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose
everything and am left in the dark. Have to get a flashlight, go outside
one building and into another to access the other side of the wall.

All comments and advise appreciated.

You don't say whether all the breakers are the same manufacturer.
Actually had that happen in a computer center where a 125 amp breaker
would trip before the 30 amp parking area breaker. Of course it
always led to a 2AM call out so we found that problem quickly. Anyway
you have two variables which is the short circuit trip time and the
overload trip time. Possible this was the result of the dead short so
you might not have to do anything. Possible a defective breaker, most
likely the one tripping to fast. A possible problem of a poor ground
path to the first breaker.

Mike M


Can you explain what part a ground plays in a simple 2 terminal
breaker?


Simple you can have a line to line short, or a short to ground. If it
is a short to ground and you have a poor ground path the breaker may
sense it more as an overload then a short and not trip or take longer
to trip.


This may be true in a GFI (ground fault interrupter) circuit breaker,
but in 120/240v standard breakers, there IS no ground lead.

--
The most powerful factors in the world are clear
ideas in the minds of energetic men of good will.
-- J. Arthur Thomson
  #32   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,278
Default electrical question (wood shop)

On 9/1/2012 2:21 AM, Ivan Vegvary wrote:
Problem solved! Thanks for all the help.
Scrounged around for another breaker and found a 40 amp double (240 volt). Replaced the suspect 50

with the 40 and all is O.K. If I force a short in the 20 amp circuit
the 20 amp now breaks and the
upstream 40 amp holds. Obviously the 50 amp breaker was bad. (proved
it by putting it back in and
forcing a short)

Good job. Before the woodworkers are done here, they will be plotting
things out on a Cray supercomputer, and fighting for government approval
of some sort of new electrical code.

BTW, I force a short by plugging in a shorted power cord.

Works, but I'm sure it violates a gov't code somewhere, and if you kill
yourself, neighbors, family pets, your insurance company will certainly
deny all claims.

(Doesn't everybody in this group cut off the power cord on a tool prior
to throwing it away?)

I thought I was the only one, I have a giant box of them. I tend to
save all sorts of stuff on the way to the trash. ****es the wife off
when she catches me, until she needs me to fix something she broke.

--
Jack
Add Life to your Days not Days to your Life.
http://jbstein.com
  #33   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 576
Default electrical question (wood shop)

On Mon, 03 Sep 2012 09:27:50 -0700, Larry Jaques
wrote:

On Mon, 03 Sep 2012 08:49:35 -0700, Mike M
wrote:

On Sat, 01 Sep 2012 15:55:42 +1000, John G
wrote:

It happens that Mike M formulated :
On Thu, 30 Aug 2012 21:04:39 -0700 (PDT), Ivan Vegvary
wrote:

Finished wiring the wood-shop area. All in conduit, 12 quadplex wall
outlets, and four fluorescent lights on three way switches. Also a 220V
feed to the air compressor. New sub-panel in wood shop is fed by an other
sub-panel 3 feet away on the other side of a wall. Feeder panel has a 50amp
breaker feeding the wood shop sub panel. All wiring within conduit is #12
except the 220 which is #10.

Question: As I installed each of the quad (gang of four) outlets, I would
go to the breaker, turn it on and check the outlet with a clamp lamp and
then turn off the breaker for further work. When I was installing the
outlet group # 11, the wires shifted withing the conduit and the hot wire in
# 12 touched the metal box. (Yes, I didn't cap the wires while I was
working, I simply bent them out of each other's way. Stupid) Anyway, the
question is "why did the 50 amp breaker feeding my sup panel break instead
of the 20 amp breaker withing the sub panel"?

Later, after wrestling my large air compressor into it's closet the same
thing happened. I dislodged the safety shield on the belt, the fan blade
could not turn and ergo the motor drew too many amps on start-up. Again,
instead of the 30 amp circuit feeding the compressor breaking, it's the 50
amp feeding the panel that broke.

Note: 50 amp breaker is used. 30 amp breaker is used. 20 amp breaker is
new.

Is the 50 amp breaker simply too sensitive?

I could live with the above, except when the 50 amp breaker trips I lose
everything and am left in the dark. Have to get a flashlight, go outside
one building and into another to access the other side of the wall.

All comments and advise appreciated.

You don't say whether all the breakers are the same manufacturer.
Actually had that happen in a computer center where a 125 amp breaker
would trip before the 30 amp parking area breaker. Of course it
always led to a 2AM call out so we found that problem quickly. Anyway
you have two variables which is the short circuit trip time and the
overload trip time. Possible this was the result of the dead short so
you might not have to do anything. Possible a defective breaker, most
likely the one tripping to fast. A possible problem of a poor ground
path to the first breaker.

Mike M

Can you explain what part a ground plays in a simple 2 terminal
breaker?


Simple you can have a line to line short, or a short to ground. If it
is a short to ground and you have a poor ground path the breaker may
sense it more as an overload then a short and not trip or take longer
to trip.


This may be true in a GFI (ground fault interrupter) circuit breaker,
but in 120/240v standard breakers, there IS no ground lead.


I don't know what code book your using but you'll never pass a NEC
inspection if the entire system isn't grounded. Your thinking of the
nuetral or identified conducter.

Mike M
  #34   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 583
Default electrical question (wood shop)



"Jack" wrote

BTW, I force a short by plugging in a shorted power cord.


Only thing with that is that it melts the plug contacts a bit. Plug the
cord in then short the ends together, or my favorite is a u shaped piece of
wire against the sides of the plug's hookup screws. Even better, they make
plug testers that you plug in and push a button. Not too expensive, and
tells you if you have all of the wires hooked up correctly all the way back
to the breaker box.

Jim in NC

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New shop, electrical question SonomaProducts.com Woodworking 106 September 25th 11 02:37 AM
Wood Shop Redux (the old shop *is* the new shop) Part 2-Cheapplywood & recycled drawers Swingman Woodworking 7 June 1st 11 12:00 AM
Electrical wiring question - shop related [email protected] Metalworking 22 December 8th 10 11:50 PM
shop electrical question Weyland Metalworking 12 December 1st 05 11:44 PM
Question fow wood shop teachers Silvan Woodworking 31 December 16th 04 11:51 AM


All times are GMT +1. The time now is 12:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"