Wiring a new shop
In article , dpb wrote:
Doug Miller wrote: In article , "Stephen M" wrote: 220 - 10/3...just in case you need it some day. We've had that discussion here before. :-) There's *no* reason to use 3-conductor cable for 240V power tools. It's just unnecessary expense. Three-conductor cable is needed for combined 240/120 loads such as a range or a dryer, that have 240V heating elements and 120V motors and/or control circuits. A power tool with a 240V motor needs only two-conductor cable; there isn't even anything to attach the third conductor to, if it's present. I have seen (but _very_ few (well, actually, precisely two ) --don't know of any current-day that do) a couple of planers that used that as well -- the main feed/cutterhead motor was 220V while the table lift and an auxiliary sharpening attachment were 110V. Fella' in a shop in VA had them. But certainly I'm unaware of anything currently on the market set up that way. Well, yes, as always, the requirements of any specific tool or appliance trump "general rules". Interesting, though -- I didn't know anything of the sort had ever been produced. Wonder if some of that might have been aftermarket mods? If you want to plan for "in case you need it some day" it's better to not run cables at all, but instead pull individual conductors through conduit: pull what you need now, now; pull what you need later, later. That's not bad advice, either... -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#42
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Chris Friesen wrote:
Lew Hodgett wrote: Chris Friesen wrote: What's the point of an insulated ground? It allows the entire distribution system to be grounded at the service entrance point. Single point grounding eliminates "Ground Loops" which can be quite nasty. I'm aware of ground loops. What does this have to do with an insulated ground bus in a subpanel? In my panel for instance, the ground bus is bonded to the panel, which is in turn grounded via a conductor going back to the main panel. As you mentioned, the entire system is grounded at the service entrance. Chris The resulting ground loop (parallel neutral current paths) will allow dangerous objectionable current to flow onto metal parts of the electrical installation (and onto metal piping and structural steel). Source: http://ecmweb.com/mag/electric_groun...g_5/index.html -- Jack Novak Buffalo, NY - USA |
#43
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Doug Miller wrote:
In article , dpb wrote: Doug Miller wrote: In article , "Stephen M" wrote: 220 - 10/3...just in case you need it some day. We've had that discussion here before. :-) There's *no* reason to use 3-conductor cable for 240V power tools. It's just unnecessary expense. Three-conductor cable is needed for combined 240/120 loads such as a range or a dryer, that have 240V heating elements and 120V motors and/or control circuits. A power tool with a 240V motor needs only two-conductor cable; there isn't even anything to attach the third conductor to, if it's present. I have seen (but _very_ few (well, actually, precisely two ) --don't know of any current-day that do) a couple of planers that used that as well -- the main feed/cutterhead motor was 220V while the table lift and an auxiliary sharpening attachment were 110V. Fella' in a shop in VA had them. But certainly I'm unaware of anything currently on the market set up that way. .... I believe these were factory jobs -- I've wished more than once I had "bought'en" one of them from Eddie when he was selling them as he was enlarging his shop, but $500 was a _lot_ of money back then and I was just out of school so the $150 for the small shaper and 6" Rockwell jointer was all I could manage at the time. As I recall, everything looked to match and the controls were all integral to the machine so I don't think it was an add-on. But I was young and pretty new to stuff at the time so didn't stick w/ me what they really were. Somebody long gone from the business now, I'm sure. They were a nondescript gray, darker than Rockwell so no real clue to try to match up like a recognizable PM green or some such. He said he had bought'en them from a factory auction somewhere in PA -- they had had a production line of 25 of them -- 5 rows of 5 in line. Started at one end w/ rough stock, came out at the other with their surfaced/thicknessed stock for the sawyers on the other. They had replaced the 25 machines/50 employees with 2 large planers and a wide belt sander and five guys. About 1969/1970 when I met Eddie by answering his classified ad. He had had the machines 2-3 years at that point. I'd guess they were at least 20 years old if a day, probably closer to 30 then... -- |
#44
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
In article 0s9ni.4506$4J4.3563@trndny05, Nova wrote:
Chris Friesen wrote: Lew Hodgett wrote: Chris Friesen wrote: What's the point of an insulated ground? It allows the entire distribution system to be grounded at the service entrance point. Single point grounding eliminates "Ground Loops" which can be quite nasty. I'm aware of ground loops. What does this have to do with an insulated ground bus in a subpanel? In my panel for instance, the ground bus is bonded to the panel, which is in turn grounded via a conductor going back to the main panel. As you mentioned, the entire system is grounded at the service entrance. The resulting ground loop (parallel neutral current paths) will allow dangerous objectionable current to flow onto metal parts of the electrical installation (and onto metal piping and structural steel). *What* "resulting ground loop"? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#46
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
In article , Frank Boettcher wrote:
On Tue, 17 Jul 2007 20:10:02 GMT, (Doug Miller) wrote: snipped a bunch Thanks, I think I understand both the theory and the mechanics. Didn't mean to suggest that you didn't, Frank - sorry if I gave that impression. I just wanted to correct the misstatements flying around, and affirm that your understanding is the correct one. If I want to have a 60 AMP subpanel, one method would be: Buy a low cost package service entrance panel making sure what joins the nuetral and ground buses is removable, remove the tie between the nuetral and ground buses, make sure the ground bus is bonded to the panel, replace the existing main breaker (which will probably be 100 amp or greater depending on the panel capacity) with a 60Amp main breaker, and I'm there? Bingo! -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#47
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Frank Boettcher wrote:
Again, goes against everything I've read and instinctively know to be true. Without the bond, the subpanel panel itself is not grounded and it has to be. Mea Culpa, Mea Culpa, Thank you for being my editor. That's what happens when you engage fingers before brain. My previous post is in error as noted by Frank. The sub panel gets a ground bar with the panel tub (enclosure) bonded to it with the bonding strap and an insulated neutral bus that then gets carried back to the service entrance panel. Sorry for the confusion. Lew |
#48
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Frank Boettcher wrote:
If I want to have a 60 AMP subpanel, one method would be: ...replace the existing main breaker (which will probably be 100 amp or greater depending on the panel capacity) with a 60Amp main breaker, and I'm there? If you're feeding the sub via a breaker on the main panel, you don't need to replace the main breaker in the subpanel. Chris |
#49
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Chris Friesen wrote:
I'm aware of ground loops. What does this have to do with an insulated ground bus in a subpanel? Absolutely nothing. (See my Mea Culpa on my response to Frank.) It should have read "Insulated neutral bus". The ground bus with the sub panel bonded to it's ground bus and then carried back to service entrance will give single point grounding. Lew |
#50
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Frank Boettcher wrote:
If I want to have a 60 AMP subpanel, one method would be: Buy a low cost package service entrance panel making sure what joins the nuetral and ground buses is removable, remove the tie between the nuetral and ground buses, make sure the ground bus is bonded to the panel, replace the existing main breaker (which will probably be 100 amp or greater depending on the panel capacity) with a 60Amp main breaker, and I'm there? The (M)ain (L)ug (O)nly panel with an assortment of main c'bkr kits was developed to provide the electrical distributor the maximum flexibility of his inventory with the minimum investment. For years, the standard was the 125A, MLO panel with various branch arrangements.(Usually 60A and 100A) As shipped from the manufacturer, they were ready to install as sub panels, if if you added an insulated neutral, and used the existing bus bar as a ground bus. To convert to a service entrance panel, all you had to do was add a main c'bkr kit since the neutral and ground connections shared the same bus. Today's higher electrical usage often dictates a 200A panel, which is a whole new family of larger c'bkrs for main c'bkrs. Lew |
#51
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
It's very common with metalworking machines. Coolant pumps and
DRO's operate on 117 v while the big motor operates on 220. It seems silly to me to go to the trouble of wiring new circuits without installing the third wire. It's a lot more trouble to add later. Doug Miller wrote: In article , "Stephen M" wrote: 220 - 10/3...just in case you need it some day. We've had that discussion here before. :-) There's *no* reason to use 3-conductor cable for 240V power tools. It's just unnecessary expense. Three-conductor cable is needed for combined 240/120 loads such as a range or a dryer, that have 240V heating elements and 120V motors and/or control circuits. A power tool with a 240V motor needs only two-conductor cable; there isn't even anything to attach the third conductor to, if it's present. |
#52
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
Mike Berger wrote:
It's very common with metalworking machines. snip You must be new. Trying to talk to Miller is like ****ing up wind. After a while, you know better. Lew |
#53
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
In article . net, Lew Hodgett wrote:
Mike Berger wrote: It's very common with metalworking machines. snip You must be new. Trying to talk to Miller is like ****ing up wind. After a while, you know better. ****ed off because I pointed out your electrical errors *again*, I see... -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#54
Posted to rec.woodworking
|
|||
|
|||
Wiring a new shop
In article , Mike Berger wrote:
It's very common with metalworking machines. Coolant pumps and DRO's operate on 117 v while the big motor operates on 220. Well, of course we were talking about woodworking machinery here... :-) It seems silly to me to go to the trouble of wiring new circuits without installing the third wire. It's a lot more trouble to add later. Which is why I said this, in the part that you snipped: If you want to plan for "in case you need it some day" it's better to not run cables at all, but instead pull individual conductors through conduit: pull what you need now, now; pull what you need later, later. Doug Miller wrote: In article , "Stephen M" wrote: 220 - 10/3...just in case you need it some day. We've had that discussion here before. :-) There's *no* reason to use 3-conductor cable for 240V power tools. It's just unnecessary expense. Three-conductor cable is needed for combined 240/120 loads such as a range or a dryer, that have 240V heating elements and 120V motors and/or control circuits. A power tool with a 240V motor needs only two-conductor cable; there isn't even anything to attach the third conductor to, if it's present. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Shop Wiring Suggestions | Woodworking | |||
New Shop Wiring? | Woodworking | |||
garage/shop wiring question | Woodworking | |||
garage/shop wiring question | Woodworking | |||
garage/shop GFI wiring? | Woodworking |