Hi,
I need a little bit of info about the wire sizing for upgrading a
10 hp motor to a 15 hp motor. The present system uses a 30 amp
protective circuit. The 15 hp motor is rated @ 23.7 max amp. The wiring
is 8 gauge. Please tell if a direct swap in motors is likely. nb the
voltage is 3 phase 460 volts.

Hope for a speedy response........... Musty

  #2   Report Post  
Posted to rec.woodworking
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default tech info


musty wrote:
Hi,
I need a little bit of info about the wire sizing for upgrading a
10 hp motor to a 15 hp motor. The present system uses a 30 amp
protective circuit. The 15 hp motor is rated @ 23.7 max amp. The wiring
is 8 gauge. Please tell if a direct swap in motors is likely. nb the
voltage is 3 phase 460 volts.


Unless very high startup current, sounds fine for the wiring itself.
Will need to get starter "heaters" sized for the new motor, probably,
though.

Is wiring copper or aluminum? How long a run?

  #3   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 379
Default tech info

In article . com,
musty wrote:
Hi,
I need a little bit of info about the wire sizing for upgrading a
10 hp motor to a 15 hp motor. The present system uses a 30 amp
protective circuit. The 15 hp motor is rated @ 23.7 max amp. The wiring
is 8 gauge. Please tell if a direct swap in motors is likely. nb the
voltage is 3 phase 460 volts.

Hope for a speedy response........... Musty


Insufficient data. grin

Starting with your locale. (I'll assume U.S.A.)

Then, if there are _any_ related loads on the same circuit -- e.g. control
logic for the piece of equipment involved.

Then, there is a matter of the length of the run from the panel to the motor.
'Long' runs require increasing the wire size.


Now, making a _lot_ of assumptions --

If the equipment is permanently wired (as distinct from plugged in),
you are limited, by NEC, to 80% of the rated capacity of the circuit
protector.

That's maximum 24A load on a 30A protector. If there's mor-or-less
_anything else_ on the circuit -- including control logic -- you're
likely to be over the limit.

There's also an open question of the _starting_ draw by the motor.
Start-up current draw can be *much* higher than running load. Protective
devices need to accomodate _that_ load for the (relatiely short) start-up
intervval.

Now, on reasonably short runs, _10_ga_ is sufficent for 30A; with 8 ga.
you _could_ -- *UNLESS* the run-length necessitates 'up-sizing' the
wire -- go to a (say) 35A (or 40A) protector, which would give some
headroom.





  #4   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 2,047
Default tech info

musty wrote:
Hi,
I need a little bit of info about the wire sizing for upgrading a
10 hp motor to a 15 hp motor. The present system uses a 30 amp
protective circuit. The 15 hp motor is rated @ 23.7 max amp. The wiring
is 8 gauge. Please tell if a direct swap in motors is likely. nb the
voltage is 3 phase 460 volts.


The #8 wire is OK, the 30A protective device is not.

You need a 40A protective device.

If the protective device is a fuse, then you will have to change to a
60A fuse block to accept the 40A fuse.

If the protective device is a c'bkr, then you will have to change the
c'bkr.

You will also have to change the motor starter from a NEMA size 1 to a
NEMA size 2 complete with the proper overload heaters.

Lew



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ariston AF200 Dishwasher fault - tech info? PJ UK diy 0 October 12th 05 05:28 PM
ASK A TECH Electronics Repair 2 July 9th 05 07:42 PM
WTD Info on Tapmatic 700X and info on Tapmatics Marty Escarcega Metalworking 3 June 8th 04 04:00 AM
TECH: White flickering lines with HD Sony TV Pioneer receiver More info Electronics Repair 0 October 25th 03 05:52 PM


All times are GMT +1. The time now is 09:02 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"