Home |
Search |
Today's Posts |
![]() |
|
Woodworking (rec.woodworking) Discussion forum covering all aspects of working with wood. All levels of expertise are encouraged to particiapte. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
|
#1
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
I can't figure out what I'm doing wrong. I'm currently trying to add
an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, and installed a 6-30 plug by connecting the black and red wires to the blades on the plug, and the bare wire ground to the box 1st and then to the ground on the outlet. The white wire is capped off and not being used. When I plug in the heater it will not turn on. Breaker does not trip. I get 120v on each side of the plug with my voltmeter. I even was able to test the voltage in the heater and there is 120v going to each input inside the heater. I replaced the heater with a brand new one, and also replace the outlet and get the same results. Any ideas what I am doing wrong? Thanks in advance. |
#2
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#3
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
uh? just the red & black? Where's the nuetral connected? You gotta
have a return circuit. if you've got 10/3 then you've to red, black, white, ground right? Am I missing something here or just don't know what I'm talking about. Troy Chris Friesen wrote: wrote: I can't figure out what I'm doing wrong. I'm currently trying to add an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, and installed a 6-30 plug by connecting the black and red wires to the blades on the plug... I get 120v on each side of the plug with my voltmeter. Do you get 240V between the hots on the plug? Chris |
#4
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Troy" wrote in message ... uh? just the red & black? Where's the nuetral connected? You gotta have a return circuit. if you've got 10/3 then you've to red, black, white, ground right? Am I missing something here or just don't know what I'm talking about. The latter in this case Troy. 220v does not use a neutral. -- -Mike- |
#5
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , Troy wrote:
uh? just the red & black? Where's the nuetral connected? You gotta have a return circuit. No, he doesn't. 240V circuits don't use a neutral. if you've got 10/3 then you've to red, black, white, ground right? True. Doesn't mean you have to connect them all, though. Am I missing something here or just don't know what I'm talking about. One or the other... maybe both. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#6
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Troy wrote in :
uh? just the red & black? Where's the nuetral connected? You gotta have a return circuit. if you've got 10/3 then you've to red, black, white, ground right? Am I missing something here or just don't know what I'm talking about. Troy Troy, There are two 110 volt circuits in most CB boxes. Each is independent. They also happen to be 180 degrees out of phase with one another. The upshot is that while each is 120 volt with respect to ground, they are 220 volts with respect to each other. The neutral is there for a variety of reasons but not necessary for operation at 220vac. Ever wonder how your electric clothes dryer works? The main coils are wired for 220 but the light bulb and other parts like the timer use one side and the neutral. |
#7
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Thanks!
With the groups help I was able to figure out what I was doing wrong. As suggested I tested the main lugs in the subpanel I got 220v, but did not get 220v when I tested the outlet accross both hots. Turns out the the sub-panel installed only has two positions that will give you 220v. I didn't connect the breaker to either one of these. I removed the breaker, and re-connected it to the correct lugs and got 220v accross both hots. The heater now works! The inside of the panel door has a diagram that shows which lugs are 120v and which are 220v. Thanks for all your help! |
#8
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
SNIP
The main coils are wired for 220 but the light bulb and other parts like the timer use one side and the neutral. Wait, I thought we just got through learning there IS no neutral in a 240 circuit?? I didn't realize that they were out of phase with each other. Troy |
#9
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Troy" wrote in message ... SNIP The main coils are wired for 220 but the light bulb and other parts like the timer use one side and the neutral. Wait, I thought we just got through learning there IS no neutral in a 240 circuit?? I didn't realize that they were out of phase with each other. No - the discussion was that for a 220V circuit, no neutral is needed. However - when looking to also utilized 120V within a device that is hooked up to a 220v circuit, then a neutral must be provided. The example given was a clothes dryer. The dryer coils run on 220 and your clothes would dry just fine with no neutral. However, the timer, any lights that may come on when you open the door, etc. run on 110V. Therefore, you have to supply a neutral so that those 110V devices can operate off of one leg of the 220V, and neutral. -- -Mike- |
#10
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Troy" wrote in message ... SNIP The main coils are wired for 220 but the light bulb and other parts like the timer use one side and the neutral. Wait, I thought we just got through learning there IS no neutral in a 240 circuit?? I didn't realize that they were out of phase with each other. There is no neutral in a 240 volt circuit. Going from either leg of a 240 volt circuit to neutral gives you a 120 volt circuit. Some appliances require both 120 and 240--they need a three-wire circuit (two hots and a neutral) plus ground. |
#11
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
"R. Pierce Butler" writes:
Troy wrote in : uh? just the red & black? Where's the nuetral connected? You gotta have a return circuit. if you've got 10/3 then you've to red, black, white, ground right? Am I missing something here or just don't know what I'm talking about. Troy Troy, There are two 110 volt circuits in most CB boxes. Each is independent. They also happen to be 180 degrees out of phase with one another. Actually, the 240 in 99% of US residential settings is single-phase, using a center-tap to derive 120v. HV Distribution circuits are three phase, with the phases 120 degrees apart. One of those phases feeds the distribution transformer serving your residence, wherein there is a center-tap which provides the neutral to the service entrance. scott |
#13
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , Steve wrote:
Check for continuity of the ground wire from the plug all the way back to the panel ground. That's not the problem. If it's wired correctly (and as he describes it, it is) the unit will work without the ground at all. Won't be safe, but it will work. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#14
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() wrote in message oups.com... I can't figure out what I'm doing wrong. I'm currently trying to add an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, and installed a 6-30 plug by connecting the black and red wires to the blades on the plug, and the bare wire ground to the box 1st and then to the ground on the outlet. The white wire is capped off and not being used. When I plug in the heater it will not turn on. Breaker does not trip. I get 120v on each side of the plug with my voltmeter. I even was able to test the voltage in the heater and there is 120v going to each input inside the heater. I replaced the heater with a brand new one, and also replace the outlet and get the same results. Any ideas what I am doing wrong? Did you install a thermostat? -- -Mike- |
#15
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#16
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() wrote in message oups.com... I can't figure out what I'm doing wrong. I'm currently trying to add an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, Some panels will only accept 2 pole breakers in certain slots. I haven't looked into why that is, but maybe because of this. Look to see if your box has such a condition, and if you are doing it properly. |
#17
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Tim" wrote in message ... wrote in message oups.com... I can't figure out what I'm doing wrong. I'm currently trying to add an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, Some panels will only accept 2 pole breakers in certain slots. I haven't looked into why that is, but maybe because of this. Look to see if your box has such a condition, and if you are doing it properly. I've encountered this as well. Look closely at the buss bar in the center of the box and make sure that your 220v breaker is really connecting to alternating buss lugs. Some boxes only have 220v capability on the first few lugs of the buss bar and then everything below that point is 110v. -- -Mike- |
#18
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() On Oct 17, 9:32 am, "Mike Marlow" wrote: Some boxes only have 220v capability on the first few lugs of the buss bar and then everything below that point is 110v. Yup, a substation of mine is like that. You get 110v on each leg, and 0v across both *S*... a WTF moment. r |
#19
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() On Oct 17, 12:58 am, wrote: I can't figure out what I'm doing wrong. The crew has given you good suggestions. Please keep us informed when you discover what the problem was. It helps us with other questions. thanks, r |
#20
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
wrote in message
oups.com... I can't figure out what I'm doing wrong. I'm currently trying to add an oulet for 4800 watt construction heater in my shop. I've run 10/3 wire to the outlet, added a 2-pole 30amp breaker to the sub-panel, and installed a 6-30 plug by connecting the black and red wires to the blades on the plug, and the bare wire ground to the box 1st and then to the ground on the outlet. The white wire is capped off and not being used. When I plug in the heater it will not turn on. Breaker does not trip. I get 120v on each side of the plug with my voltmeter. I even was able to test the voltage in the heater and there is 120v going to each input inside the heater. I replaced the heater with a brand new one, and also replace the outlet and get the same results. Any ideas what I am doing wrong? Thanks in advance. Sounds like you are measuring from each leg to ground. Measure the voltage across the red and black wire. It should be 240 volts. If it is 0 or 120, check back at the breaker panel. Something is miswired. -S |
#21
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Thanks for all your help!
When I get home tonight I'll check the voltage accross for 240v. I didn't do that. At the main panel I connected the black and red to the 2 pole breaker, ground to ground bus, and white to the neutral bus (not used). I'm thinking I'll find that I don't have 220v. The sub-panel is not bonded. Could that have anything to do with it? How will I know where in the panel I can add 220v breakers and where I can't? I used the 10/3 so that I can change the configuration should my needs change in the future. |
#22
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Actually the sub-panel is a Stab-Lock.
Thanks |
#23
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#24
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
ok, I know electronics, but am NOT an electrician. But I don't quite
get why we don't need a nuetral? Where's the return path? 240v comes in and in the main service panel I know the nuetral and ground are bonded.... never have understood that one. then each leg of the 240v is one side of the bus bar array in the service panel. So what am I missing? I'm asking in all seriousness. I "added" a 220 outlet for my wife one day so she could have an electric stove and I popped the breaker immeaditly when I fired it up because of the nuetral being tied to ground. So I shrugged said I don't get why its doing that, read the directions with the receptacle and removed the nuetral. All was well. I look at my dryer cord and its got 3 wires. I know the top angled two are "hot" 120vac each and the other is the ground. I realize that we can take a +12vdc and a -12vdc circuit and using only 2 wires get +24vdc across them and then have to have a chassis ground. Man its been a long time since I studied electronics! Troy Doug Miller wrote: In article . com, wrote: By which you mean, I hope, that the ground and neutral busses in the subpanel are not bonded to each other. It's *supposed* to be that way. The *only* place where they are ever bonded together is in the service entrance panel. No. The neutral isn't used at all in a pure 240V circuit (and can be omitted altogether), and the ground isn't used except in the case of a ground fault in the equipment (i.e. in normal operation, the ground isn't used either). So nothing involving either the ground or the neutral would have any effect on the problem you're seeing. In *most* panels, any place that you can put a double-pole breaker will give you 240V. Your panel may be an exception, as at least a couple of us have noted, and the easiest way to tell where you can and can't is to look at the label on the inside of the panel cover -- that will show the possible configurations. Another way to tell is to probe between the lug screws on adjacent breakers (with the breakers on) to see where you measure 240V and where you get only 120V. Yet another way is to pull the breakers, and look at the configuration of the bus bars. But before you do any of that, the *first* thing you should do, in my opinion, is to measure the voltage between the two main breakers (or lugs) in the subpanel, and see whether you get 240V or 0V. I think you'll see 0V, because - assuming that you've described everything accurately - the simplest explanation for the problem you're seeing is that the subpanel is not wired correctly at the main. Specifically, I think that if you look in the main panel at the wires feeding the subpanel, you'll find that when the subpanel was installed, the black and red wires feeding it were connected to two separate single-pole breakers (instead of to one double-pole breaker), and those two breakers are on the same leg of the service. That's fine -- just wasn't necessary for *this* application. But planning for the future is always good. :-) |
#25
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Troy said:
ok, I know electronics, but am NOT an electrician. But I don't quite get why we don't need a nuetral? Where's the return path? You don't need a neutral to utilize the 220, in fact doing so negates it from _being_ 220v. This is 180 degree out of phase AC, not DC. All you need is a voltage potential and somewhere for it to travel, for current to flow. This is provided by the two 120v out-of-phase legs of your typical residential service. Hopefully you do not become part of the conduction path, and is the primary reason that most woodworking equipment requires a ground. It is not designed to be a current carrying conductor. Great confusion exists among novices as concerns Grounds and Neutrals, especially when it involves outbuildings. Protection against electrocution and lightning are two of the main reasons that the current grounding guidelines/codes exist. The ground on most 220vac equipment is for safety grounding only. It is a ground, not a neutral, although they do eventually connect together in your main panel, but never in an in-house subpanel. Older stoves and cloths dryers sometimes used a common ground/neutral to provide 120v for lamps and timer motors, but the new code and all new appliances require a 4 conductor plug and wiring. Two hots, a neutral, and a ground. It's a safety thing... Get a copy of the NEC if you want to read up on how to wire things safely, and to code. Otherwise, please, call an electrician. Mistakes can be deadly and cause great property loss. FWIW |
#26
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Troy writes:
ok, I know electronics, but am NOT an electrician. But I don't quite get why we don't need a nuetral? Where's the return path? Voltage is a potential difference. The difference between the two current carrying conductors measures 240v. The difference between a current carrying conductor and the grounded (aka neutral) conductor is 120v. This being AC, rather than DC, the concept of a "return path" doesn't really apply, per se. Note that the grounded conductor is derived from a center-tap on the distribution transformer. scott |
#27
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , Troy wrote:
ok, I know electronics, but am NOT an electrician. But I don't quite get why we don't need a nuetral? Where's the return path? There isn't a "return path" per se in a 240V circuit. In a 120V circuit, the hot is at a potential of 120V with respect to ground and neutral. In a 240V circuit, the potential between the two hots is 240V; each is at a potential of 120V with respect to ground and neutral. 240v comes in and in the main service panel I know the nuetral and ground are bonded.... never have understood that one. That's to ensure that the neutral is at true earth ground potential. then each leg of the 240v is one side of the bus bar array in the service panel. So what am I missing? I'm asking in all seriousness. I "added" a 220 outlet for my wife one day so she could have an electric stove and I popped the breaker immeaditly when I fired it up because of the nuetral being tied to ground. That's not why you popped the breaker. Not having seen what you did, I can't say why you *did* pop the breaker, but I can say with certainty that tying neutral to ground didn't trip the breaker, in and of itself. Unless it was a GFCI breaker. So I shrugged said I don't get why its doing that, read the directions with the receptacle and removed the nuetral. All was well. Means you had it connected to a hot lead somewhere... I look at my dryer cord and its got 3 wires. I know the top angled two are "hot" 120vac each and the other is the ground. I realize that we can take a +12vdc and a -12vdc circuit and using only 2 wires get +24vdc across them and then have to have a chassis ground. Yep, it's basically the same concept. Man its been a long time since I studied electronics! Residential electrical supply isn't quite the same animal. There are a number of books available at any decent library or bookstore, or at most home centers, if you want to learn more. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#28
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
It's AC, think about it. If you "know electronics" it should become obvious.
"Troy" wrote in message ... ok, I know electronics, but am NOT an electrician. But I don't quite get why we don't need a nuetral? Where's the return path? |
#29
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Forgot to mention. The main panel is a Siemens EQ Load center and the
sub is also a Siemens. Thanks |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Construction Heater | Home Repair | |||
New home construction: Wiring question | Home Ownership | |||
Power cost of idle electric water heater | Home Ownership | |||
Exposed Wiring problem in log wall construction | Home Repair | |||
Electric Water Heater Problem, Repair or Buy new, please help | Home Ownership |